Outdoor Fan Motor -- The outdoor fan, also called the condenser fan, is exposed to external conditions. As such it is most prone to dust and debris and the extreme weather. In desert climates, the outdoor fan motor is subject to heat not only from normal operation but from the outside temperature as well. As it starts to fail, the fan may work fine in the cooler morning hours but stop by afternoon. This can shut down the entire system for hours. When they stop running completely, your air conditioner will no longer work. Running a faulty fan will lead to compressor failure, which is a very costly repair.
I’m a heating and air conditioning contractor. I’ve been in the trade for over 15 years. I’ve witnessed numerous duct cleaning projects and talked with many duct cleaners. Duct cleaning as it’s usually promoted is a fraud. Most duct cleaners claim to deliver cleaner air. They deliver exactly the opposite. The studies on duct cleaning prove it, including a May 1998 study sponsored by NADCA and the EPA! The stories are compelling, but they can come up with stories that “prove” anything they want. Internet searches are dominated by results from those who are paid to tell you that duct cleaning is worthwhile. Search a little more and you’ll find the truth.
My Carrier furnace occasionally (one-two times a day) does not start. It shows error code 15 ("BLOWER MOTOR LOCKOUT -This status code indicates the blower failed to reach 250 RPM or the blower failed to communicate to the variable speed furnace control within 30 seconds after being turned ON in two successive heating cycles."). However, when I turn off and on the furnace power switch it starts and runs fine for a while. Sometimes it runs fine all day, but does not start only once in the evening or in the night. It is 13 years old I was thinking to replace whole thing if repair cost is too high. But I am not ready to pay $10,000. 
On average, we (Indians in Ontario) receive 3-5 calls per day for duct cleaning services from India. I did get ducts cleaned twice in 25 years. For a newly built house, it should be done as material goes into the ducts. Every year, before turning the heat on, I clean the ducts, using the vacuum pipe or with wet towel. Most of the dust, pet hair, small items get to the ducts from the top floors, not where system is installed. Even in winter months, I open 2-3 windows for air circulation for 15 minutes, specially right after cooking, almost daily. We breath in the same stale air, develop health issues. Also, I have an added air cleaning and fileration system installed. At a low rate, this system constantly cleans the inside air and also that it pulls from the outside. Duct cleaning is a scam, there are other efficient and cost effective methods we can use to purify the inside air.
Contact/Relay -- Relays are electronically controlled switches that activate the various components of your HVAC system. They manage everything from the power going to the motor to automatic dampers, humidifiers, etc. Most of them are controlled by the thermostat. The most common failure for a relay is being stuck in the "open" position. Separated from its assigned contact point, it fails to complete the connection and send the message to whatever it was supposed to operate. This failure usually occurs from use over time. Each time a relay connects and sends its signal, the electrical arcing from point to point eventually causes wear and tear.

Simply living in your home creates dust and dirt. Have you ever seen dust floating in the air in your home when the sun shines in?  Dust, dirt, pet dander, mold spores, and allergens get pulled into the air handling system in your home. They build up in the ductwork; some of it gets recirculated back into your home, and some of it can be captured by a good quality air filter. Eventually, enough debris builds up to the point where most of it blows back into your home. Your furnace or air conditioner must run longer to cool or heat your home, which costs you more in utility bills. With a service call from Sears Air Duct Cleaning, you can feel comfortable knowing that the accumulation of dust, dirt, dander, mold, and allergens has been cleaned from your HVAC duct system.

In variable climates, the system may include a reversing valve that switches from heating in winter to cooling in summer. By reversing the flow of refrigerant, the heat pump refrigeration cycle is changed from cooling to heating or vice versa. This allows a facility to be heated and cooled by a single piece of equipment by the same means, and with the same hardware.


CIBSE publishes several guides to HVAC design relevant to the UK market, and also the Republic of Ireland, Australia, New Zealand and Hong Kong. These guides include various recommended design criteria and standards, some of which are cited within the UK building regulations, and therefore form a legislative requirement for major building services works. The main guides are:

I hope that those customers you have with breathing problems don't follow your advice too closely. You are doing them a disservice. Dirt in your ducts does not always stay there, depending on what the contaminants are. I bet you tell your customers not to worry about mold either- just to kill it with bleach. Educate yourself before opening your mouth- You may kill someone someday with your opinion.
You may be familiar with air ducts that are constructed of sheet metal. However, many modern residential air duct systems are constructed of fiber glass duct board or sheet metal ducts that are lined on the inside with fiber glass duct liner. Since the early 1970's, a significant increase in the use of flexible duct, which generally is internally lined with plastic or some other type of material, has occurred.
 The A/C System Cleaning and restoration industry has become a very lucrative bait and switch industry that many Carpet cleaning companies, Maid services, as well as plumbing or handyman service companies are adding on to there services. These add-ons are not fully certified, trained or even have any experience in the HVAC industry. These companies are the reason prices and quality of work are all over the place. If you are looking to make a smart decision for your home a professional Duct Cleaning service will protect you for 5-7 years. This info comes from NADCA (National Air Duct Cleaning Association) which is the closest thing to a license we have for duct cleaning. They have a great site that explains this process and pricing much more in depth and factual than what has been written here. This organization is working very hard to get these bad companies exposed and out of this industry. So in saying that do your research! Green Duct Decontamination is a certified company with certified technicians that take this work very seriously. We can not have these low rated unprofessional companies paste a bad name for an entire industry. Stay away from anything under 250$ for a full duct clean this is not feasible, go look at NADCA.com and you will understand why and what these companies are doing to rob you of your dollar.
Quality and price should come hand in hand, a too-good-to-be-true price for an efficient air duct cleaning will not give you the quality that you wanted. To make sure you are getting your money’s worth, check reviews of air duct cleaning companies, certifications from industry since this work requires continuous learning due to new techniques and research breakthrough from time to time. Make sure to shop around and get written estimates first.
I purchased one of those Amazon air duct cleaning coupons for 49.99. When the company showed up, they removed the vent closest to the air intake and immediately told me I needed $1800.00 for all new duct work. They said they could not clean the system until new duct work was installed. I thanked them and said I would give them a call. The only call I made was to Amazon to get a refund. I know I didn’t need new duct work. Be careful to not fall for unscrupulous salesmen and their pitches and scare tactics.

In addition, the service provider may propose applying chemical biocides, designed to kill microbiological contaminants, to the inside of the duct work and to other system components. Some service providers may also suggest applying chemical treatments (sealants or other encapsulants) to encapsulate or cover the inside surfaces of the air ducts and equipment housings because they believe it will control mold growth or prevent the release of dirt particles or fibers from ducts. These practices have yet to be fully researched and you should be fully informed before deciding to permit the use of biocides or chemical treatments in your air ducts. They should only be applied, if at all, after the system has been properly cleaned of all visible dust or debris.

HVAC professionals in the US can receive training through formal training institutions, where most earn associate degrees. Training for HVAC technicians includes classroom lectures and hands-on tasks, and can be followed by an apprenticeship wherein the recent graduate works alongside a professional HVAC technician for a temporary period.[33] HVAC techs who have been trained can also be certified in areas such as air conditioning, heat pumps, gas heating, and commercial refrigeration.[34]
I have lived in Calgary for quite some time now. When I first moved here I couldn’t stand the humidity levels. Its like a desert come winter. When I first moved into my new home, the house inspector insisted I have my furnace and ducts cleaned. I was very sceptical about duct cleaning to begin with. The company I hired came on time and were very respectable from the start. Before mentioning anything they asked me what my concerns were and what issues I was having. They were more concerned about addressing my issues then bringing anything non related up. I ended up going with this company and getting a humidifier installed a couple days later after the cleaning. Its been almost 4 years now that I have been here. The humidifier is working great and the difference is incredible. They took me around explained step by step what they were doing and the reasons they were doing it. With all those other companies out there, I am glad I found them at this site.

An EER certifies the cooling efficiency of HVAC units. It's calculated by the rate of the cooling in British thermal units (Btus) per hour and divided by the rate of energy input in watts at a specific temperature. The calculation goes as BtuH/WATT at dry bulb (db) versus wet bulb (wb) temperatures. The optimal rating for a cooling unit is about 80db/67wb inside and 95db/75wb outside.
If your non metal ductwork is that dirty you should just have it replaced AND sealed. Also most duct systems are not very well designed. Look for proper sizing and do not go cheap with one or two intakes (return grills) You need them through-out the house. Here in Austin the duct cleaners are carpet cleaners and chimney swifts. (this is who the duct cleaning equipment mfgs call on when the hvac people do not get on board. They DO clean other types of ductwork and we (the hvac guys) have to fix them. I am not aware of any of these non hvac guys cleaning and servicing the actual equipment. Here in Texas it is against the law for them to do so. Treat the entire house as a system, not just the ductwork and /or hvac equipment. Home performance really does work to increase comfort and air quality while reducing operating costs.

You and your family spend hours sitting on your favorite chairs, couches and sectionals. Over time, dander and body oil become trapped in the upholstery, but with regular cleanings you can keep these delicate fabrics looking, feeling and smelling great. We examine your furniture and select the best process to safely clean and protect any kind of upholstery, including leather. 
I am 79 years old, bought a condo & spent a lot of money on it. this winter my first bill was 450.00. had my furnace checked out, which is on the roof. it was old rusted out & leeking oil. i talked to owner & had new unit installed. they came out to clean ducks & they were split & worn out. there is no crawl space because theres a unit above me. my real estate lady or this company will not help me fix this problem.

Deciding if central air is worth the cost depends on your needs and local housing market. If you live in a hotter climate, it can definitely be worth the price. Not only can it keep your home at a comfortable temperature, but air conditioning can even save lives during extreme heat waves. But in a milder zone without severe temperatures, window units, fans or the breeze from an open window could be adequate.
Installing a split system may involve making modifications to the house itself for the necessary lines to be run. The heat exchangers are also more prone to picking up debris and must be cleaned on a regular basis. While they come with protective screens over the fan, care must still be taken to ensure that nothing gets in, especially in a home with children.
Venice warns homeowners to beware of air duct cleaning scams, especially the sort where unscrupulous cleaners offer a $49 special deal but start piling on extra fees. “It’s a bait and switch scam where they say they’ll offer unlimited cleaning, but then they throw around terms you might not understand, such as extra fees for a ‘main duct line,’” he says. “And many times, these cleaners end up walking out the door with twice the amount of money a reputable duct cleaner would charge. They’ve gotten very sophisticated at upselling.”

I can't believe the number of people saying a good properly installed central heating system never needs to be cleaned. Maybe they live in hermetically sealed cells? One look into a cold air return and you can see that it definitely needs periodic cleaning. The air in the house "always" has some dust in it and that's where it ends up. We just had ours cleaned and I saw what came out of it, disgusting. But always ask if they use the "air whip" to sweep/beat the inside of the metal duct. If not, don't bother. These folks used a little whip on the end of a pressure hose and swept the entire length of all the ducts. I have lighted bore scope that allowed me to see into the duct after he was done and it was spic and span. But do change your filters often, 2 or 3 times a year.
The cooling coils the air comes into contact with appear to need UV-C lights on them in humid climates. That's the biggest thing. If the ducts have never been cleaned, then getting that done goes without saying. But those coils need to be cleaned, disinfected, and then UV-C light(s) installed to prevent mold & bacteria build-up in the future on them. That appears to be chiefly responsible for the dirty laundry and/or sour milk smell coming from forced-air AC systems in humid regions.
Asking how much an HVAC installation costs is kind of like asking, “how much does a new car cost?”  Well, are you buying a Porsche or a Honda? Is it a 911 or just a Boxster, and are you going to get the leather seats? Likewise, are you going to get a Carrier or a Goodman air conditioner? Does the ductwork need to be replaced? These are all questions that will affect your HVAC installation cost, so let’s take a closer look.
Dehumidification (air drying) in an air conditioning system is provided by the evaporator. Since the evaporator operates at a temperature below the dew point, moisture in the air condenses on the evaporator coil tubes. This moisture is collected at the bottom of the evaporator in a pan and removed by piping to a central drain or onto the ground outside.
Alberto said they were busy but could either install on the upcoming Saturday.  We were going to be out of town and said unfortunately that day did not work.  He then proposed the upcoming Tuesday as a possible solution, but just had to confirm with another appointment.  I said great.  I will review the estimate and call your office to confirm I want to move forward with the install.
An energy recovery ventilator: This component helps improve the air inside your home by swapping it out with fresh air from the outside. During the winter months when houses are closed up to keep out the cold, the air inside becomes a handy way for colds and flu to infect an entire family. By circulating outside air inside, the health of your family will have a better chance.
But Tim, doesn’t this mean that a less-than-honest air conditioning company can just charge what he wants and say that it’s a difficult job? No. You see, dishonest contractors, typically, aren’t the brightest people (I figure if you’re still reading this, you’re warming up to me so I’m taking off the training-wheels). They aren’t smart enough to take difficulty into account, and will probably get confused if you ask them about it. They will tell you things like, “that’s how much the unit costs,” or “California has a new law that magically adds $5,000 to the price.”  Trust me, follow your gut, and you’ll be able to tell who the honest contractors are...or just use one of our ASM-approved contractors.

There are multiple reasons to replace your HVAC system. If you have built additions onto your house, you may find your old system no longer meets the requirements for the new dimensions. Perhaps a new technological breakthrough has provided features that will improve your comfort and air quality. Most often, however, you need to replace your system because it no longer works properly.
To qualify for a tax credit from the federal government, you must save the manufacturer's certificate from your system. The IRS won't require the certificate at the time you file your federal tax forms, but they recommend keeping it with your records in case of an audit. It proves that you purchased a qualifying product. The government offers tax credits for:

Tip – Be careful with change-outs. Ductwork deteriorates and sometimes has to be replaced.  It is only if the ductwork is in fantastic condition that you should get a change-out without ductwork (Remember – the ductwork has already been there for 15-20 years, and now it will be there another 15-20…it has to be in good shape). However, many HVAC installation companies like to push change-outs because the ductwork is the most time consuming part of the job, and a change-out is quick, easy money. Realize that it’s only about 15-20% of the jobs that qualify for a change-out, so be careful.


Many central air conditioning systems use the furnace blower to distribute cool air through the home. If you do not have a central heating system installed, it is cost-effective to install a heating and air conditioning system at the same time. If you already have central heat, you can use the existing fans and duct system for the central air system.
I even asked if this is something they don't do, as in services on a Saturday night.  I was told by the receptionist that they do and I would just be ok calling another company if they is not  part of their services. They again assured me someone WILL call me in 10 mins.  Well, unless their definition of 10 mins is never, then they got it wrong as I am still waiting to be called 5 days later.

First of all, I think it is great that there are many companies out there who look out for the customer and protect their interest. Secondly, I think it is also important that customers consider having their HVAC systems checked thoroughly before moving into a new home. I have heard a couple of horror stories where previous owners have not had the best housekeeping skills. Even when the appearance of the home seems it has been well kept, keep in mind that surface clean only goes so far. You can never tell what lies underneath.
The Antimicrobials Information Hotline provides answers to questions concerning current antimicrobial issues (disinfectants, fungicides, others) regulated by the pesticide law, rules and regulations. These cover interpretation laws, rules and regulations, and registration and re-registration of antimicrobial chemicals and products. The Hotline also provide information health & safety issues on registered antimicrobial products, product label and the proper and safe use of these antimicrobial products.
The AC contactor (relay) and start/run capacitor(s) (see illustration below) fail most often and are inexpensive. So it's a safe bet to buy and install those parts right away, especially if your air conditioning service unit is older than five years. The condenser fan motor can also fail, but it runs about $150 — hold off buying that unless you're sure that's the culprit.
×