The Chartered Institution of Building Services Engineers is a body that covers the essential Service (systems architecture) that allow buildings to operate. It includes the electrotechnical, heating, ventilating, air conditioning, refrigeration and plumbing industries. To train as a building services engineer, the academic requirements are GCSEs (A-C) / Standard Grades (1-3) in Maths and Science, which are important in measurements, planning and theory. Employers will often want a degree in a branch of engineering, such as building environment engineering, electrical engineering or mechanical engineering. To become a full member of CIBSE, and so also to be registered by the Engineering Council UK as a chartered engineer, engineers must also attain an Honours Degree and a master's degree in a relevant engineering subject.


WELL, this summer when I opened them up we had black dust spewing from one of the upstairs vents. It resembled the fuzz that comes off new towels. This prompted us to look into duct cleaning. We heard from someone who had it done several times, said it was worthwhile, and knew of a firm that did a good job. Clean Air America sent a single technician for the appointment and after counting registers and ducts gave me a price of $360.00 which included “sanitizing” the system (a $99 additional fee per can used). The small size of the plenum forced him to connect the 8” round vacuum hose from the truck to the 10” square opening from our humidifier unit. In hindsight, a mistake since it reduced the “negative” pressure in the system.
Since most states and municipalities don’t license air duct cleaners, you need to check their professional credentials instead, such as NADCA membership. EPA recommends all duct cleaners follow NADCA standards. Member companies must keep at least one technician on staff who has passed a NADCA test. “They have to pass rigorous testing to earn the certificate, and our code of ethics is very important,” Vinick says.
Cost Factors: The size of the unit, its efficiency and it’s single-stage, two-stage or variable-capacity are the top cost factors. Features like communicating technology and improved dehumidification performance also affect the price. Learn more about communicating technology here including the pros and cons, before being agreeing to a communicating system.
The number of years an HVAC system lasts depend on the type and brand of components that make up your system. The lifespan of an air conditioner averages between 15 and 20 years. The life expectancy of a tankless water heater is approximately 20 years, while a storage water heater is closer to 10-15 years. Ducts may need replacing within 10-15 years. Your equipment will have a longer life if you have regular tuneups and maintenance to keep everything in good working order. If you’re having repair problems and your HVAC system is over 10 years old, it’s a good time to consider the costs and benefits of repairing vs. replacing. Energystar.gov provides the following tips to help you decide whether to repair or replace:
Two weeks go by and no phone call from HVAC Service regarding install date, or any update at all.  I call them to check in to see if they have put me on the schedule and when I can expect to have the AC installed.    You can tell by the discussion I had with the lady on the phone that they completely forgot about me and have not scheduled anything.  She says she needs to get in contact with the owner because she has no idea on the availability of the crane.  I was told that she would call me back by the end of the day with an update.  Surprise, surprise, no phone call.  

The next step was cleaning the cold air returns. He found a good spot to drill an 8” hole for his vacuum hose. The procedure matched the other air ducts except that when he finished at the two cold return registers he drilled several holes in the cold ducts in the basement and blasted air into them. Because of our houses age and the upgraded return system, I noticed that the main sheet metal return duct had no top but was just butted up against the ceiling in the basement. When he blasted air in, dust and crap shot out the edges along the ceiling. Once he finished that he removed the filter and “swept” out anything at the bottom of the return with his hand into the 8” hose.

The cooling coils the air comes into contact with appear to need UV-C lights on them in humid climates. That's the biggest thing. If the ducts have never been cleaned, then getting that done goes without saying. But those coils need to be cleaned, disinfected, and then UV-C light(s) installed to prevent mold & bacteria build-up in the future on them. That appears to be chiefly responsible for the dirty laundry and/or sour milk smell coming from forced-air AC systems in humid regions.
On the other hand, if a service provider fails to follow proper duct cleaning procedures, duct cleaning can cause indoor air problems. For example, an inadequate vacuum collection system can release more dust, dirt and other contaminants than if you had left the ducts alone. A careless or inadequately trained service provider can damage your ducts or heating and cooling system, possibly increasing your heating and air conditioning costs or forcing you to undertake difficult and costly repairs or replacements.
i got angies list deal for 109 air duct clenaing, dryer vent cleaning, and furnace inspection, {healthy duct cleaning} i call the company, they arrive on time. did excellent service what ever i purches i got. they give me furnace inspection and the told me that my furnace is very dirty and they offer me to clean that for 250 extra. i paid and i am very happy from this service. i try before 2 diffrent company that i got deal from them as well the just give me estimate and don’t even do the job. so guys don’t spend time if you need deep cleaning just cal this guy the offer free estimate as well.

Duct system installation and repairs affect HVAC installation cost. If you’re installing a new forced air heating or cooling system, your home must have ductwork – if you don’t have ducts installed, a new duct system will need to be designed and installed. Your existing duct system may require air sealing to eliminate air loss, helping your new heating and cooling system operate efficiently.


Two weeks go by and no phone call from HVAC Service regarding install date, or any update at all.  I call them to check in to see if they have put me on the schedule and when I can expect to have the AC installed.    You can tell by the discussion I had with the lady on the phone that they completely forgot about me and have not scheduled anything.  She says she needs to get in contact with the owner because she has no idea on the availability of the crane.  I was told that she would call me back by the end of the day with an update.  Surprise, surprise, no phone call.  
yes get a good company and pay the price, I found so much dust and dirt and wood and paint chips and bugs and even bottle caps in my ductwork. I hired a major plumbing company who cleaned ductwork and i will say they did an excellent job cleaning my vent. they did miss one point in my ductwork because i still started to see dust all over my furniture and i realized that my retunduct work that was connected with a piece of sheet metal beam which was 16" across , the contractor that built my condo used a 16" wide sheet of sheet metal to connect the vent system to my return for the air to return back into my condo. The contractor should have built a 8" x16" square duct by 6 feet long to connect my intake to my return instead of using a sheet of sheet metal 16" wide by using two 3' sections by 16 inches wide. That was a shor cut which caused a major problem fir me.
Air conditioning units are prone to the pitfalls of wear and tear. You can prolong this, however, with proper maintenance procedures. Without regular maintenance even an immaculate AC installation in Fort Smith, Arkansas cannot guarantee performance. Our maintenance service is thorough, leaving no area unattended. If there’s a problem, we’ll catch it early and prevent avoidable breakdowns and costly repairs.
The number of years an HVAC system lasts depend on the type and brand of components that make up your system. The lifespan of an air conditioner averages between 15 and 20 years. The life expectancy of a tankless water heater is approximately 20 years, while a storage water heater is closer to 10-15 years. Ducts may need replacing within 10-15 years. Your equipment will have a longer life if you have regular tuneups and maintenance to keep everything in good working order. If you’re having repair problems and your HVAC system is over 10 years old, it’s a good time to consider the costs and benefits of repairing vs. replacing. Energystar.gov provides the following tips to help you decide whether to repair or replace:
I agree that good filtration and a sealed system will prevent the need for duct cleaning. However, when we do get called it is because the duct work has reached a noticeable state of restriction or dust or the homeowner is hyper-sensitive to these pollutants in their home. Most of the time we find that no filter or a cheap (99 cent) filter is being used or they have serious duct leaks in the system. If you are hiring a cleaner make sure they are using professional cleaning equipment which will consist of a rotating brush system and a vacuum source. Be highly skeptical of the contractor with no branded system or the guy who shows up with just chimney brushes and a shop vac. He will not be able to reach around all the corners or all the runs in your system and he will be taking your money for a superficial cleaning at best. Only trust a company that offers VIDEO inspection and more importantly.... a contractor who repairs, installs and seals ducts if a problem is discovered or heaven forbid, created. Good luck and get your ducts sealed if you do have a leak! It is one of the greatest energy losses to a home other than being poorly insulated.
Many homes have a forced-air HVAC system. Both the heating and the central air conditioning units share a ductwork system where they either push in or pull out warm or cooled air. There are also heating and cooling systems that don’t require ductwork — such as ductless mini-splits — but work on the same principles of heat exchange. The national average to hire an HVAC specialist is $2,920-$3,670, with costs varying depending on the work you need done and the equipment you are installing.

While a lot of people understand the consequences of AC problems throughout the summer, the summer comes with its own set of unique issues that require a call to the plumber, too. Whether it’s a malfunctioning sprinkler system or a sewer line backup, Service Experts can help. We’ve encountered it all, and you won’t have to worry about any of it with our 24/7/365 Emergency Plumbing Service. When you need a plumber, we are here for you. And, just like all of our other services and products, any plumbing repair or work completed by Service Experts is backed by the same 100% Satisfaction Guarantee*.
Demand controlled kitchen ventilation (DCKV) is a building controls approach of controlling the volume of kitchen exhaust and supply air in response to the actual cooking loads in a commercial kitchen. Traditional commercial kitchen ventilation systems operate at 100% fan speed independent of the volume of cooking activity and DCKV technology changes that to provide significant fan energy and conditioned air savings. By deploying smart sensing technology, both the exhaust and supply fans can be controlled to capitalize on the affinity laws for motor energy savings, reduce makeup air heating and cooling energy, increasing safety and reducing ambient kitchen noise levels.[29]
I always get a laugh at anyone claiming to be in the business for any length of time that doesnt understand the importance of cleaning out a ventilation system. Not only for better indoor air quality but for maintaining your heating equipment. I guess it makes more sense to some people that the furnace will just run better with a ton of dust and debris and maybe this wont be a big cause of sytem breakdown and malfunction. I mean really? Maybe this guy got a bad company and or cleaning and is a little jaded but to advise cleaning your grills , which does nothing, and replacing a filter....come on guy.
How exactly do you expect to kill or remove mold without it ? You can’t even clean your hvac systems coils without moisture of some type ,if you use a steam cleaner you can literally clean the whole system minus the electronics . You should do more research and possibly talk to people who do the work before posting , but don’t listen to me i only have a class A contractor license ,epa license , install /repair hvacs , rent and flip houses for a living .
It’s 11 years plus in the industry I have only had to sanitize two systems both were slab systems that were in concrete and could be cleaned with a different method than normal duct cleaning. We were able to use water to rinse out the disinfectant. Would you use a chemical on anything else you use to eat or drink with and not rinse it off? The ducts in your home should be thought of as your homes heart and lungs and breathe the same air that you do. And just like us we wouldn’t use bad chemicals in our lungs and heart.
An important component of natural ventilation is air change rate or air changes per hour: the hourly rate of ventilation divided by the volume of the space. For example, six air changes per hour means an amount of new air, equal to the volume of the space, is added every ten minutes. For human comfort, a minimum of four air changes per hour is typical, though warehouses might have only two. Too high of an air change rate may be uncomfortable, akin to a wind tunnel which have thousands of changes per hour. The highest air change rates are for crowded spaces, bars, night clubs, commercial kitchens at around 30 to 50 air changes per hour.[17]
I guess I should present my credentials first, I am a 30 year veteran of the heating and cooling industry. I started at the bottom and have participated in every area of the trade. Installer, service, maint. Ownership, rep, territory manager and so on. A forced air duct system is a large vacume. Like your vacume it has an air intake (return air) and an exhaust (supply registers). A filter just like a vacume (located next to furnace or air handler). Now I want you to visualize something. Put your head inside your vacume cleaner and breath. Get the picture? This is what your duct work looks like. Do you clean your vacume when it’s dirty? If it’s full and the filter is dirty you lose performance and it starts poluting the air you breathe. It’s common sense. I recommend hiring a duct cleaning outfit that you have researched to be honest, background checked, drug tested, insured, and highly recommended by your piers in the area. The service is a necessity, but like everything, it should be done by a qualified company.
If you don't agree with duct cleaning, fine. If there are some things that HVAC people can do to make the system need cleaning less often fine, but to suggest that I need to GO TO JAIL????? If you need to knock others to make yourself look better....... If duct cleaning is such a scam, why are their governing bodies like NADCA (which I do NOT belong to),several manufacturers of equipment, and national restoration franchises (I'm not a franchise either) who provide this service? I guess the whole world is stupid and only HVAC people are smart. I suppose I am scamming them when I clean puff backs, water damage, fire damage, and clean their carpets too? Or did I wake up one morning and say "ya know, it is great to be a hard working, honest owner operator, but I would love to provide a service that unlike everything else I do is a con and rips off the 90% referral business I busted my butt to earn"
So, naturally I respond with, “you don’t tell your doctor which medication to prescribe you, do you?” The point is, on the residential level, who you get to install your HVAC unit is far more important than which unit you choose.  Keep your options open and let your HVAC contractor make a few recommendations – that’s why you spent time finding a reputable contractor!

First of all, I think it is great that there are many companies out there who look out for the customer and protect their interest. Secondly, I think it is also important that customers consider having their HVAC systems checked thoroughly before moving into a new home. I have heard a couple of horror stories where previous owners have not had the best housekeeping skills. Even when the appearance of the home seems it has been well kept, keep in mind that surface clean only goes so far. You can never tell what lies underneath.
An air conditioning system, or a standalone air conditioner, provides cooling and humidity control for all or part of a building. Air conditioned buildings often have sealed windows, because open windows would work against the system intended to maintain constant indoor air conditions. Outside, fresh air is generally drawn into the system by a vent into the indoor heat exchanger section, creating positive air pressure. The percentage of return air made up of fresh air can usually be manipulated by adjusting the opening of this vent. Typical fresh air intake is about 10%.
 The A/C System Cleaning and restoration industry has become a very lucrative bait and switch industry that many Carpet cleaning companies, Maid services, as well as plumbing or handyman service companies are adding on to there services. These add-ons are not fully certified, trained or even have any experience in the HVAC industry. These companies are the reason prices and quality of work are all over the place. If you are looking to make a smart decision for your home a professional Duct Cleaning service will protect you for 5-7 years. This info comes from NADCA (National Air Duct Cleaning Association) which is the closest thing to a license we have for duct cleaning. They have a great site that explains this process and pricing much more in depth and factual than what has been written here. This organization is working very hard to get these bad companies exposed and out of this industry. So in saying that do your research! Green Duct Decontamination is a certified company with certified technicians that take this work very seriously. We can not have these low rated unprofessional companies paste a bad name for an entire industry. Stay away from anything under 250$ for a full duct clean this is not feasible, go look at NADCA.com and you will understand why and what these companies are doing to rob you of your dollar.
Ok what you said is true but in most cases ducts are in a duct flex format, and knowing that the dust in people's flex duct is just surface dust, any real debris that are in the duct itself will result in very little to no air flow which will keep your unit from performing properly, but if it is true allergy reasons then replacing your duct system is better for overall better air quality, plus if you do pay attention to the warranty on flexible duct is that it only has a 10 year warranty and typically only lasts for 20 years so do your research before having a duct cleaning, and to add one more thing if your duct work is completely metal and you can't see visible insulation then your duct on the inside has insulation inside of it, if you replace that with duct work that is clean metal on the inside and wrapped with insulation on the outside then it will further reduce the air bourne fiberglass and dust.
I am NADCA Certified Air Systems Cleaning Specialist. Over the years I have learned on simple answer to this questions: there air duct cleaners and there are pretenders. There will be no benefit at all if you use on the very cheap pretender because they will not really clean anything. On the other hand if you call a qualified air duct cleaner with a NADCA Certification you will, like 99% of my customers, report improvement with your respiratory problems, you will see less dust and the job will pay for itself with energy savings and repair prevention.

McMahon's Cleaning & Restoration, LLC provides healthy improvements for your home or business. Our certified professionals specialize in air duct cleanings to increase air flow and improve the quality of the air your family breathes. We provide clean air certification for homes with past or current mold/fungi issues (including black mold). We restore smoke, fire, and flood damaged homes. We also offer chimney sweep services and inspections to ensure safe usage of your fireplace, wood stove or insert. Since 1999, we've been working with the community to better homes, industrial sites and commercial environments.
Your contractor will do a load calculation to determine the proper central air conditioning unit for your home. This calculation accounts for the climate, size, shape and orientation of your home, as well as its square footage. A professional will also look at the insulation, windows, walls, floors and other materials that compose your home. He/she will then examine any leaks, seals and existing ducts or vents.
My father started in the business of home comfort back in 1968, an I around 1986. We still don't have a duct cleaning machine. I am sure there are always applications for all tools in this industry. However I missed where anyone talked about where dust even comes from..........We do not have these little dust machines sitting in a corner puffing out little clouds of dust....soooo where does it come from?
Capacitors -- Capacitors help your HVAC motor start from a standstill. Over time they can weaken. As they weaken, they cause the motor to run hotter. This can shorten the life expectancy of your motor. Once a capacitor fails, the whole motor will stop working. You usually won't notice that a capacitor has weakened until your motor stops turning on.
I have a white gritty dust throughout my whole house. Dust and it comes right back. We have central air. In 2013 had all the air conditioning tubing in the attic replaced. Old ones were completely clean. Why?? Thought dust would be in there. Put everything in plastic containers. Furniture everything is always covered with this. Problem is always there year round. Furnace people said it is not coming from furnace. We built house in 1971. Only started with this @ 19 years ago. Thinking when air conditioning went in. We cough all the time and sneeze. I do not have friends come here because I hate how dirty my house looks.
Air duct cleaning service providers may tell you that they need to apply a chemical biocide to the inside of your ducts to kill bacteria (germs) and fungi (mold), and prevent future biological growth. Some duct cleaning service providers may propose to introduce ozone to kill biological contaminants. Ozone is a highly reactive gas that is regulated in the outside air as a lung irritant. However, there remains considerable controversy over the necessity and wisdom of introducing chemical biocides or ozone into the duct work.

You and your family spend hours sitting on your favorite chairs, couches and sectionals. Over time, dander and body oil become trapped in the upholstery, but with regular cleanings you can keep these delicate fabrics looking, feeling and smelling great. We examine your furniture and select the best process to safely clean and protect any kind of upholstery, including leather. 


While you consider having your air ducts cleaned, it is a good idea to take a look at your dryer vent. If your dryer vent is clogged, you could be losing energy efficiency. Worse yet, you could be increasing the risk of a house fire. Having your dryer vent professionally cared for costs about $130 on average, and could save you a bit of money and a lot of headaches in the future. For more information on the benefits and cost of having your dryer vent cleaned, take a look at our comprehensive cost guide.

Central home air conditioner service systems consist of two major components: a condensing unit that sits outside your house, and the evaporator coil (often referred to as an A-coil) that sits in the plenum of your furnace or air handler. The refrigerant in the A-coil picks up the heat from your home and moves it to the outdoor condensing unit. The condensing unit fan blows outside air through the condensing coil to remove the heat. The condensing unit houses the three parts replaceable by a DIYer: the AC contactor, the start/run capacitor(s) and the condenser fan motor. The condensing unit also houses the compressor, but only a pro can replace that. The A-coil has no parts that can be serviced by a DIYer.
×