If you believe that the AC's not working or you're getting little or no cold air, check these three things first. Make sure all the registers in the house are wide open. Then be sure the furnace filter is clean. Then go outside and clean off the condenser coils (Photo 2). If several registers were closed or the filter was clogged, the reduced airflow could have caused the evaporator coil to ice up and stop cooling your home. If you've changed the filter and opened all the registers and you're still not getting airflow at the registers, deice the A-coil. Move the thermostat mode switch from “Cooling” to “Off” and move the fan switch from “Auto” to “On.” Let the blower run for at least 30 minutes or until there's good airflow at the registers. Then turn the AC back on to test it. If it works for the next 12 hours, you've solved the problem.

I spent a lot of time reading all these posts and frankly I can’t believe the way some people think. 1. If there is dust and dirt of any kind in my HVAC system I want it out, the mentality that it can stay there and it’s fine is fulish as the system turns on and off microscopic particulates will move in and out of your living space and you will definitely breath them in. The air quality of your home or office will only be as clean as the system that produces it. We don’t not clean things simply because we can’t see them, it’s what we can’t see that can do the most harm. Dust will build up in a system fairly quickly and will get damp at times allowing mold to grow and mold releases spores without any movement as part of its defense meconisam so don’t tell me that when your system turns on it won’t blow the spores out into the living spaces of your home. A build up of dust will cause failures to your system over time, equipment that works harder to do its job will run hotter with more strain and this will lead to brake downs and until then the system will run less efficient then it should. The system was engineered to move a certain volume of air through a specific duct size, when that duct size starts to become narowed down with dust build up your system has to work harder to move that air this is why you will end up with a loss of efficiency and eventually breakdowns or failures. I have seen systems develop a significant amount of dust build up in as little as two years, just look at how fast the filter gets clogged up and it isn’t all that hard to believe. As for all the scams that are out there they hurt the industry because people can’t decipher between them and the legitimate companies, BBB is helpful. Recommendations from HVAC contractors will be a good resource and a good company will provide a written estimate with a complete brake down of what they are going to do and why, most of which is comen sence once they explain it to you, then if you spend about 5 minutes watching them once they are set up you can see they are doing what they said they would do and let’s get real would you do a job that should take approx 3 hours per system for $29/$39/59 or something close to that, if you think you are going to get a good job from a comp that has to make money at that price you shouldn’t be mad at anyone but your self for trying to get quality work at a scam price. If it’s done right it will be very beneficial and depending on the size of your system and where you are in the world it’s going to cost you approx $300 to $600 per system large and or older systems may cost even more. Remember a quality job isn’t wasting money but a lousy job is, even if it’s only $29. I’d rather spend $600 on a quality job then $29 on a lousy job!! Good luck..
The most effective way to clean air ducts and ventilation systems is to employ Source Removal methods of cleaning. This requires a contractor to place the system under negative pressure, through the use of a specialized, powerful vacuum. While the vacuum draws air through the system, devices are inserted into the ducts to dislodge any debris that might be stuck to interior surfaces. The debris can then travel down the ducts to the vacuum, which removes it from the system and the home.
Some of these components can be repaired or replaced by the homeowner, such as filters, fuses, and clogged up drain lines. Coils, compressors and the other components are best left to a professional. In some cases, you may have a system that is so old that parts are no longer available or else they aren't up to code. In this case you will have to consider replacing the entire system.
We hope you found this article on a fair HVAC installation cost helpful. In the end, you’ll be alright so don’t worry too much. Do your research on reputable air conditioning contractors in your area, and spend time making sure that you have a company that you can trust – it will cost you less in the long-run, trust me. Take your time, follow the tips above, and you will end up with an HVAC installation cost that is more than reasonable, keeping your family comfortable for years to come. For more on topics like this, see: ASM’s Air Conditioning Blog.
I guess I should present my credentials first, I am a 30 year veteran of the heating and cooling industry. I started at the bottom and have participated in every area of the trade. Installer, service, maint. Ownership, rep, territory manager and so on. A forced air duct system is a large vacume. Like your vacume it has an air intake (return air) and an exhaust (supply registers). A filter just like a vacume (located next to furnace or air handler). Now I want you to visualize something. Put your head inside your vacume cleaner and breath. Get the picture? This is what your duct work looks like. Do you clean your vacume when it’s dirty? If it’s full and the filter is dirty you lose performance and it starts poluting the air you breathe. It’s common sense. I recommend hiring a duct cleaning outfit that you have researched to be honest, background checked, drug tested, insured, and highly recommended by your piers in the area. The service is a necessity, but like everything, it should be done by a qualified company.
Asbestos removal tip.  Don’t trust any HVAC installation company that says that they will remove asbestos for you. They will do either one of two things: remove it and do a horrible job because they don’t know how (an illegal act in California, finable by up to $250,000), or they will say they did and never actually do it, which is dangerous to your health. Any HVAC contractor worth their weight will know not to touch it. Call an asbestos abatement company – it should cost around $500-$1,000, and your HVAC installation company will come in right after them and do the installation to decrease cost and inconvenience.
Rheem's RRNL features a scroll compressor with fewer moving parts and less noise than traditional reciprocating compressors. A louvered compressor compartment protects the compressor from the elements and from debris that can shorten the life of the compressor. The Classic series continues to be one of their best sellers, with the addition of the Comfort Alert diagnostics module integrated to assist technicians in the event your system needs repair. 2-5 tons, 13 SEER, 80% AFUE.

Prices for central-air HVAC systems will vary. The national average to hire an HVAC specialist is $2,920-$3,670 but can run as high as $5,000 or even $12,000 depending on the capacity you need and other factors. Installing central air conditioning requires an entire system that works together to draw hot air out of your home. The system includes an outdoor unit, which houses the condenser and compressor, and the evaporator coils. If you don’t have an existing duct system, ductwork will need to be installed, which will affect labor and material costs. Leaking or damaged ducts will also need to be replaced.

What about ringworm? If the fungus is as contagious as doctors warn, and the spores can live several months, doesn’t it make sense to spray some sort of fungus killer into the HVAC system to kill the spores that it has sucked in from the air? Duct cleaning would not be helpful at all here; these spores are microscopic and it could actually spread them further. But given how severely contagious ringworm is, body and especially scalp, does anyone make an aerosol product that will clean the system and kill the fungus? One the resident can use, not call an HVAC company; you can’t do that when you are in an apartment. I hear it’s not the same as mold, it is much more difficult. Truth?
Humidifiers/Dehumidifiers: Humidifiers add needed moisture to the air in winter and very dry climates. Dehumidifiers remove dampness any time of the year. Central air conditioners dehumidify too, but in very humid climates, you might want to remove humidity without also cooling the air. You have a good range of options for both of these HVAC accessories. Whole-house humidifiers cost $350 to $800 installed, while dehumidifiers are $1,250 to $2,000 or slightly more.
You may consider having your air ducts cleaned simply because it seems logical that air ducts will get dirty over time and should be occasionally cleaned. Provided that the cleaning is done properly, no evidence suggests that such cleaning would be detrimental. EPA does not recommend that the air ducts be cleaned routinely, but only as needed. EPA does, however, recommend that if you have a fuel burning furnace, stove or fireplace, they be inspected for proper functioning and serviced before each heating season to protect against carbon monoxide poisoning.
An air conditioning system's SEER is especially important if you live in a climate that changes temperature dramatically. The SEER is determined by the cooling output during the winter divided by its electric input during the winter. The higher the rating, the more efficient it will be. In January of 2006, the U.S. put standards in place for cooling units which are still in effect today. They must have a minimum SEER of 13. So, if you live in a home with a system installed before the new standards went into effect, consider having it replaced. SEER 13 units increase home efficiency by 30 percent.
One of the best ways to know if your ducts or vents need to be cleaned is to just check them. Your eyes will be able to check for indications of mold, dust or pollen buildup. You might also be able to smell the presence of mold, which would be a clear indicator. Ductwork will have some buildup of dust, since the return registrars pull air back in. However, this doesn't mean your ducts have too much debris, and you can easily clean them with a duster or vacuum.
Many homes have a forced-air HVAC system. Both the heating and the central air conditioning units share a ductwork system where they either push in or pull out warm or cooled air. There are also heating and cooling systems that don’t require ductwork — such as ductless mini-splits — but work on the same principles of heat exchange. The national average to hire an HVAC specialist is $2,920-$3,670, with costs varying depending on the work you need done and the equipment you are installing.

Fast forward 1 year and 1 week and the circuit board that HVAC Service had installed has failed again. They came out and said that it failed from water condensation dripping onto it, so we needed to replace it and reroute the pipes to prevent future water damage.  That would cost double what I paid last year.  Why didn't they fix the problem last year at the initial repair instead of putting in a circuit board that was bound to fail again?!? They were strongly recommending that the furnace be completely replace for a huge fee to avoid the same thing happening again.  I paid $59 for them to tell me they didn't fix it right last year. This didn't feel right, so I sought a second opinion.

My best advice has always been that a proper duct cleaning is a valuable investment when moving into a home (new or old), after major renovations and if the ducts have never been cleaned before. It is unlikely that there will be increased air flow, as finding major blockage is unusual, but this will eliminate this as a possible concern if there are air flow concerns. It is also true that the "dust" that is cleared out will most likely never have been distributed through the house unless there has been some work done on the ducts. What is cleared out will be pet hair, toys, clothes, construction material, and biological material (small carcasses and/or feces). Once a proper cleaning is done a follow-up is rarely necessary, but up to the home owners discression.


Air duct cleaning service providers may tell you that they need to apply a chemical biocide to the inside of your ducts to kill bacteria (germs) and fungi (mold), and prevent future biological growth. Some duct cleaning service providers may propose to introduce ozone to kill biological contaminants. Ozone is a highly reactive gas that is regulated in the outside air as a lung irritant. However, there remains considerable controversy over the necessity and wisdom of introducing chemical biocides or ozone into the duct work.
All of you have dentists, you have doctors, you have preachers, you have mechanics. You don’t have to know everything about everything but you have to have people in your life that you can trust. Don’t just open up the phone book and pick a mechanical (HVAC) contractor. Call your friends and family and ask for referrals. There are no black and white (scam or not a scam) answers here.
The most effective way to clean air ducts and ventilation systems is to employ Source Removal methods of cleaning. This requires a contractor to place the system under negative pressure, through the use of a specialized, powerful vacuum. While the vacuum draws air through the system, devices are inserted into the ducts to dislodge any debris that might be stuck to interior surfaces. The debris can then travel down the ducts to the vacuum, which removes it from the system and the home.
Important Tip: Don’t just pay attention to the high-end of the price range! – which is what I know you are all looking at, but also look at the low range. If a contractor is cheaper than this, ask “why?” Usually it is because they don’t have liability insurance, workman’s compensation insurance, are unlicensed, all of the above, or worst yet, they don’t use HVAC technicians. You are spending a lot of money.  Make sure that they are licensed (In California, check here at CSLB License Checker) and insured.
To qualify for a tax credit from the federal government, you must save the manufacturer's certificate from your system. The IRS won't require the certificate at the time you file your federal tax forms, but they recommend keeping it with your records in case of an audit. It proves that you purchased a qualifying product. The government offers tax credits for:
As a person with severe mold allergies, I live in a the South where the climate naturally breeds molds.We noticed a difference when we had our ducts cleaned.The company used a vacumn type system and covered all of our vents with plastic that was held up by the suction. We had no damage, no leaking dust/dirt back into the house and it took several hours. I think if you use a reputable company it makes the world of difference. Now we use better air filters and also have a UV light to prevent mold growth on ours system.We 'd do it again when the time comes. From your car's air filter to your dryer...anything works more efficiently when it is not filthy dirty.That's just common sense.
NADCA and EPA both have good points. Although, organizations are made to make money. Common sense and looking at NADCA and EPA pre-checklist. If you don't see it in the check list, you don't have to do it! But, if you do, look up Diamond certified co.s and the BBB. Beware of bait and switch scams, $60 vents and the like coupons which claim to help all for the measley sum of $79.00 bucks.
The average cost of keeping your residential ductwork orderly is going to vary greatly from that of a commercial building. This is because commercial air ducts are often larger and more extensive. Residential cleanings can cost an average of about $20-$30 per vent. For commercial buildings, service providers must do an estimate of your space before they can provide an accurate quote. Before factoring in the materials and the number A/C and furnace units, you can expect a commercial project to cost at least $35-$50 per hour.
I turned on the AC when he was finished and immediately saw black fuzz balls the size of marbles come out of several of the registers. He said that was expected since everything was shaken up. So much for describing the service as cleaning. I paid him and sent him on his way. I cannot imagine that this type of service is worthwhile in anything but a new house. Apparently in old houses such as mine I can expect that using a whole house humidifier in the winter followed by a great AC can loosen the soot. Maybe this is to be expected for the first few weeks of summer each year. I now have lined the inside of the registers with cheesecloth to catch the fuzz. I’ll see if it stops after a couple of weeks.

A BTU is the amount of energy required to heat or cool one pound of water by one degree Fahrenheit. So a 1-ton air conditioner can cool 12,000 pounds of water by one degree every hour. That’s all it means, so don’t let yourself be lost in jargon! How this affects your HVAC installation cost is that the larger your house is, the more tons will be required to heat and cool it.
As a homeowner and an owner of rental property I can tell you that the air ducts sometimes need to be cleaned. If you have had pets or anyone smoking in your home (even a visitor) for any length of time, having the ducts cleaned is really good idea. I had a tenant who did not smoke, but got married to a smoker more than year after moving in. When I realized someone was smoking I had them move out, but the smell was awful. I had the ducts cleaned and sanitized (it was a bit extra). The ducts were shiny like new afterwards. I left the windows open for a few days and we cleaned the place super clean and then replaced the carpets. The duct cleaning was worth every penny because the house looked, smelled, and felt new afterward. I plan to have my own house ducts cleaned again this year as we have two cats. We had them cleaned about 12 years ago and they found building materials in the ducts! If you move into a house that has never had them cleaned, it is good to do it. If you have allergies, clean the ducts to see if it helps. You never know what is in your ducts if you have never had them cleaned.
Maybe I took him to literally but I am pretty sure cops wont show up to ensure that my duct gets replaced. He said it would be over 1000 dollars to replace the ductwork if that is the case. Now, I spoke to a friend who did 2 ductwork lines on his own in his attic and he said it was like 15 dollars for the plastic wirewound tubing to create new ducts. Should I cancel that appointment and just do the work on my own? I feel like I’m a chump or lazy for considering paying someone to do this work.
Clean the condenser fan blades before the start of the cooling season. Brush any dust or debris off gently and then uncover the condenser coils, gently cleaning the dirty side. Then wrap the motor and other electrical components in plastic bags and gently spray from the inside with a hose. Now check the base pan under the unit and clear it out of any debris that has gathered.
You may consider having your air ducts cleaned simply because it seems logical that air ducts will get dirty over time and should be occasionally cleaned. Provided that the cleaning is done properly, no evidence suggests that such cleaning would be detrimental. EPA does not recommend that the air ducts be cleaned routinely, but only as needed. EPA does, however, recommend that if you have a fuel burning furnace, stove or fireplace, they be inspected for proper functioning and serviced before each heating season to protect against carbon monoxide poisoning.
×