Because an air conditioner moves heat between the indoor coil and the outdoor coil, both must be kept clean. This means that, in addition to replacing the air filter at the evaporator coil, it is also necessary to regularly clean the condenser coil. Failure to keep the condenser clean will eventually result in harm to the compressor, because the condenser coil is responsible for discharging both the indoor heat (as picked up by the evaporator) and the heat generated by the electric motor driving the compressor.

Pro Tips: Before you buy one of the learning thermostats available, you should beware of their shortcomings. First, many require a c-wire to work properly. A common problem is that the old thermostat might not use a c-wire, and this makes it confusing when swapping wires to the new thermostat. Secondly, if you change your thermostat setting often, you might become frustrated with a nest thermostat or other learning thermostat. It will be constantly trying to learn patterns in your random setting changes, and will therefore change your home’s temperature when you don’t want it to. If you have a fairly consistent schedule or don’t mind overriding the unit either manually or via the app on your way home or when leaving, then you won’t experience this issue.
DIY: Most DIY installations go smoothly. The major brands have compatibility checkers to see which of their models will work with the wiring your old thermostat is using. Potential problems involve the need for a C-wire, or common wire, when the existing bundle doesn’t include one. There are solutions discussed in our Thermostat Buying Guide, linked to below.
You can adjust for seasons: During the summer, you can have the air conditioner stay off during the cooler morning hours and start cooling the house as everyone gets up and starts moving around. During the winter, you can have your heater stay off while you are away at work and turn on about a half hour or so before you get home so that you are coming home to a nice, warm house.
A Full Installation is the most common type of HVAC installation for a reputable contractor. The ductwork adds two days of labor and about $2,000 to $3,000 to the price, but realize that this is a very important part of your HVAC system. Although it might sound like a good idea to reduce HVAC installation cost and get a quick change-out, realize that there is dirt and debris collecting in your ducts, and the ducts themselves develop holes and full breaks over the lifetime of your unit, all of which may be hidden from sight by insulation. Remember, many contractors will push a quick change-out on you because it is easy and good money for them – you need to be involved and ask questions.
PickHVAC Tips: First, see the PickHVAC tip above about sizing a central air conditioner. It applies to heat pumps just as much. Secondly, Even if the line set for the new heat pump is the correct size, we recommend replacing the set or at least the fittings. Old lines and fittings are a major source of leaks. When refrigerant leaks out, the heat pump efficiency suffers. Eventually, the unit stops providing heating and air conditioning, and it might break down.
I have been a plumbing/gas/hvac tech for 19 years, before that I installed ductwork in commercial buildings and office towers. As the article states, unless you have undergone some type of extensive reno, or ducts have become contaminated, paying for cleaning is pointless. Its one thing if you have a 30 year old home that has never had a duct cleaning and you can actually see mounds of dust built up , especially in the return side, then go for it. Keep in mind that most duct cleaning companies will only get 80% of the dust , or less at best. Keep in mind that most of the dust in your home is lint from clothes and linens, and skin cells from you and your pets and is constantly being generated. Dust that builds up in ductwork , generally stays in the ductwork. The power of suggestion, scare tactics, up sell!!!
If the one noticeable spot is where the wall [or ceiling or floor] is white.......first.....take a pair of needle nose pliers and bend each louver of the register to a straight outward position [as they all come brand new with a slant to each side]....so the register is shooting all supply air straight outward. If its a round register [in ceiling].....no help there. You also should always burn soy or beeswax candles.
PickHVAC Tips: Oil burns dirty, so it is important to have your plenum and ducts checked to see if they should be cleaned when replacing an oil furnace. If you don’t clean the plenum and ducts when replacing the furnace, the new furnace might not run as efficiently and comfortably as possible due to restricted airflow. This can also reduce the oily smell sometimes associated with oil furnaces.
Without proper ventilation, carbon monoxide can be lethal at concentrations of 1000 ppm (0.1%). However, at several hundred ppm, carbon monoxide exposure induces headaches, fatigue, nausea, and vomiting. Carbon monoxide binds with hemoglobin in the blood, forming carboxyhemoglobin, reducing the blood's ability to transport oxygen. The primary health concerns associated with carbon monoxide exposure are its cardiovascular and neurobehavioral effects. Carbon monoxide can cause atherosclerosis (the hardening of arteries) and can also trigger heart attacks. Neurologically, carbon monoxide exposure reduces hand to eye coordination, vigilance, and continuous performance. It can also affect time discrimination.[15]
Although HVAC is executed in individual buildings or other enclosed spaces (like NORAD's underground headquarters), the equipment involved is in some cases an extension of a larger district heating (DH) or district cooling (DC) network, or a combined DHC network. In such cases, the operating and maintenance aspects are simplified and metering becomes necessary to bill for the energy that is consumed, and in some cases energy that is returned to the larger system. For example, at a given time one building may be utilizing chilled water for air conditioning and the warm water it returns may be used in another building for heating, or for the overall heating-portion of the DHC network (likely with energy added to boost the temperature).[4][5][6]
Despite such anecdotal experiences, there's no scientific evidence that regular residential air duct cleaning improves air quality, according to a 1997 brochure published by the Environmental Protection Agency. Laureen Burton, senior scientist in the EPA Indoor Environments Division, says that while the document is nearly two decades old, the science hasn't changed and the agency stands by its recommendations.
Manufacturers of products marketed to coat and encapsulate duct surfaces claim that these sealants prevent dust and dirt particles inside air ducts from being released into the air. As with biocides, a sealant is often applied by spraying it into the operating duct system. Laboratory tests indicate that materials introduced in this manner tend not to completely coat the duct surface. Application of sealants may also affect the acoustical (noise) and fire retarding characteristics of fiber glass lined or constructed ducts and may invalidate the manufacturer's warranty.
An example of a geothermal heat pump that uses a body of water as the heat sink, is the system used by the Trump International Hotel and Tower in Chicago, Illinois. This building is situated on the Chicago River, and uses cold river water by pumping it into a recirculating cooling system, where heat exchangers transfer heat from the building into the water, and then the now-warmed water is pumped back into the Chicago River.[24]
Hi John, Thanks for reaching out, we would be happy to help you connect with a pro for your project. You can submit a request to our pros here: www.homeadvisor.com, browse a list of pros that serve your area here: http://www.homeadvisor.com/c.html, or send your info to emailus@homeadvisor.com and a project advisor will reach out to assist you. –HASupport
I am a service technician [since '92].....and as to double filtering.....I have never recommended it. Granted.....it would be noticeably helpful if the fiberglass filters are the main ones used [which I also never recommend.....as long as system can deliver appropriate air flow with a pleated cotton filter...and any decent service tech can check the air flow for proper cfm]. Any particles small enough to pass through a pleated cotton filter are going to pass through a second filter as well....unless the second filters are so tight that the system is starving for air flow. Has anybody ever accidentally put two filters in their automatic drip coffee maker? What if cars used two fuel filters or air filters? I have told some homeowners to try using second filters at each register [the black thin filter material cut-to-fit....same type used in many window air conditioners].....but I only suggest this when I know they will still get at least 400 cfm per ton of air flow [350 absolute minimum]......as some homeowners know others who say it has helped and it gives them a peace of mind knowing they are doing something to help contribute to a solution, so it HAS to help [even though I think it falls in the "one-born-every-minute" category.....similar to duct cleaning].

After one company just took a cursory glance at our A/C and found nothing wrong, I called HVAC. I called them mostly based on Michael W's post on 8/10/14 where he told us the owner, Alberto, took his feedback and took it SERIOUSLY. That speaks VOLUMES to anyone who has been around long enough to know the characteristics of the serious players are and those who are the wannabes.
fact is most homes have bad filter racks. when you insert the filter it doesn’t seal well to the sides so some of the air and dust bypass it and end up in the supply ductwork and into the house. Most of the dust in the supply ductwork settles down and doesn’t get blown in the house but some of it does when the blower starts up or when you put a new filter. If you have allergies or other health problems put in an electronic air cleaner, get your ducts cleaned and run the fan as much as you can afford. you can also get an ECM motor installed which is going to be worth it if you want to run the fan 24/7. If you have uninsulated metal ducts take down the ones you can and wash them. Then put them back and seal the joints. Cleaning the ductwork also improves airflow which is important to AC and Heat pump systems for efficiency. An electronic air cleaner will also improve airflow and static pressure because they usually have a much larger filter surface area. An electronic air cleaner also keeps the ac coil clean like new which means better efficiency and no cleaning needed. AC furnaces sometimes grow mold around the coil because of the condensation. Electronic air cleaners should be able to filter mold spores but the best remedy is installing a UV light next to the coil which will kill the mold.

HVAC professionals in the US can receive training through formal training institutions, where most earn associate degrees. Training for HVAC technicians includes classroom lectures and hands-on tasks, and can be followed by an apprenticeship wherein the recent graduate works alongside a professional HVAC technician for a temporary period.[33] HVAC techs who have been trained can also be certified in areas such as air conditioning, heat pumps, gas heating, and commercial refrigeration.[34]
I’m really not convinced that duct cleaning is of any value. My roommate wanted the ducts cleaned so he called some company. My scam senses is already tingling. They came in with a big negative pressure fan. Did some blowing and sucking in different vents. Then they tried to upsell a full system cleaning. They wanted to pull the blower and clean the heat transfer box at $700 per heater unit. I have a big house so we have two units. They also tried to sell us some “custom” $250.00 Air Lifetime air filters. At that point I pulled the BS get the hell out bell. After paying $520.00 for just the cleaning, I paid the bill and sent them on their way. I replaced the existing filter with the good old and cheap paper filters at $10.00 each. Duct cleaning… I’m not Impressed.
Unfortunately, manufacturers and contractors don’t publish this information…it’s a secret. Why? Who knows…but we have access to a full contractor pricing database of 1,000’s of different units in our online HVAC installation cost calculator, so let’s choose one for our example calculation. We’ll go with Carrier equipment, since our readers always bother us about them (despite us telling them that they are overpriced):

Quality and price should come hand in hand, a too-good-to-be-true price for an efficient air duct cleaning will not give you the quality that you wanted. To make sure you are getting your money’s worth, check reviews of air duct cleaning companies, certifications from industry since this work requires continuous learning due to new techniques and research breakthrough from time to time. My mom is located in Arizona and they trust J&M Restoration air duct cleaning company, they have an A+ BBB rating, they used EPA approved sanitizing agents, their technicians are NADCA certified, and the company is certified by the Institute of Inspection, cleaning and Restoration. Make sure to shop around and get written estimates first.
Most organizations concerned with duct cleaning, including EPA, NADCA, NAIMA and the Sheet Metal and Air Conditioning Contractors' National Association (SMACNA) do not currently recommend the routine use of sealants to encapsulate contaminants in any type of duct. Instances when the use of sealants to encapsulate the duct surfaces may be appropriate include the repair of damaged fiber glass insulation or when combating fire damage within ducts. Sealants should never be used on wet duct liner, to cover actively growing mold, or to cover debris in the ducts, and should only be applied after cleaning according to NADCA or other appropriate guidelines or standards.
As I type this, I am having my ducts cleaned. About 30 including returns and the furnace. $543.00. I am watching the team do it and can see the clear vacuuming tubing and how dirty it has become. I like the gentleman’s comment on “stick your head in your vacuum and breath”….I get it. The team showed me the machine and it’s filtration system…and they will show me it again after the cleaning. However, like I said before, I am actively seeing the tubing that is clear before they start and how dirty it is once they begin and continue cleaning. Reputable company and not a “fly by night” coupon service. People don’t be so cheap, that is your problem.
Having the most energy-efficient system ever built won't matter much if it's not maintained. Lack of maintenance is the number one killer of HVAC systems. Before each cooling season, it's recommended that your system get a professional tune-up. However, there are things you can do in the meantime to make sure your system runs efficiently throughout the year.
Fast forward 1 year and 1 week and the circuit board that HVAC Service had installed has failed again. They came out and said that it failed from water condensation dripping onto it, so we needed to replace it and reroute the pipes to prevent future water damage.  That would cost double what I paid last year.  Why didn't they fix the problem last year at the initial repair instead of putting in a circuit board that was bound to fail again?!? They were strongly recommending that the furnace be completely replace for a huge fee to avoid the same thing happening again.  I paid $59 for them to tell me they didn't fix it right last year. This didn't feel right, so I sought a second opinion.
Refrigerant Metering Device -- Every HVAC system has one of these, and heat pumps have two. They regulate the amount of refrigerant going through your air-conditioner. If it fails, either too much or too little refrigerant will course along the lines and either not perform well or will overwhelm the compressor and cause it to fail. A total failure of this component will result in a complete loss of operation.

Heating, ventilation, and air conditioning (HVAC) systems have been shown to act as a collection source for a variety of contaminants that have the potential to affect health, such as mold, fungi, bacteria, and very small particles of dust. The removal of such contaminants from the HVAC system and home should be considered as one component in an overall plan to improve indoor air quality.

"OTHER THAN A SMALL SCHEDULING HICK-UP THEIR SERVICE WAS EXCELLENT. JOSH THE TECHNICIAN THAT PREFORMED THE DIAGNOSTICS AND REPAIR WAS EXTREMLEY PROFESIONAL AND FRIENDLY â ¦ HE WAS ABLE TO FIND THE PROBLEM WHICH WAS VERY DIFFICULT TO FIND AND FIX THE PROBLEM. I WISH THAT ALL HOME SERVICE PEOPLE WERE AS GOOD AS HE WAS. I WOULD HIRE AGAIN...JOB WELL DONE !!!"
×