I can't believe the number of people saying a good properly installed central heating system never needs to be cleaned. Maybe they live in hermetically sealed cells? One look into a cold air return and you can see that it definitely needs periodic cleaning. The air in the house "always" has some dust in it and that's where it ends up. We just had ours cleaned and I saw what came out of it, disgusting. But always ask if they use the "air whip" to sweep/beat the inside of the metal duct. If not, don't bother. These folks used a little whip on the end of a pressure hose and swept the entire length of all the ducts. I have lighted bore scope that allowed me to see into the duct after he was done and it was spic and span. But do change your filters often, 2 or 3 times a year.
My father started in the business of home comfort back in 1968, an I around 1986. We still don't have a duct cleaning machine. I am sure there are always applications for all tools in this industry. However I missed where anyone talked about where dust even comes from..........We do not have these little dust machines sitting in a corner puffing out little clouds of dust....soooo where does it come from?

Compressor -- Compressors are outdoor components in your system. The compressor is the pump that circulates the refrigerants through the air-conditioner. You can hear it when it's running so you'll know if it's working just by listening. If it starts getting louder, your compressor is about to fail. If it makes no sound when it should be on, it has already failed. Compressors fail for a number of reasons. Most often they fail due to strain from another failed part such as the fan motor. Electrical storms can also damage compressors. If the sound from the compressor gets louder or if you see a decrease in performance, you should have your compressor checked. A failed compressor will not heat or cool your house.
Furnace cleaners are mostly young men, I know this, I have been one for 15 years or so……so heres the truth, if there are any allergies, children, older people with health issues, we are GOING to make money. do not tell the company you have hired about any health complication. they are salesmen. and they don’t care about you. or your money. make sure they do a good job, then kick them out. you don’t need all the bells and whistles they wanna sell you. any idiot can clean duct work, like I said, I am one of them. I am very good at it, but I don’t have the back bone to sell a widowed old lady a humidifier that she doesn’t need for 500 bucks, overall, if you think you need this service done, which you probably don’t, get it done, do not spend anything over 300$ and do not do it again for at least ten years.
The Chartered Institution of Building Services Engineers is a body that covers the essential Service (systems architecture) that allow buildings to operate. It includes the electrotechnical, heating, ventilating, air conditioning, refrigeration and plumbing industries. To train as a building services engineer, the academic requirements are GCSEs (A-C) / Standard Grades (1-3) in Maths and Science, which are important in measurements, planning and theory. Employers will often want a degree in a branch of engineering, such as building environment engineering, electrical engineering or mechanical engineering. To become a full member of CIBSE, and so also to be registered by the Engineering Council UK as a chartered engineer, engineers must also attain an Honours Degree and a master's degree in a relevant engineering subject.
We moved to a house built in 1965 from a 1915 house with a dirt basement. Against what I anticipated, the 1965 house was much dustier. It was like felt on top of everything. I cleaned and cleaned and it did become less dusty over time. We then found out a cat lady with over 2 dozen cats lived in the house in the past. We then had to get our furnace replaced and I was able to look down some of the duct work, the dirt and debris was 3-5 inches deep. Additionally, the basement ducts were entirely plugged with debris including dirt, seeds, ants, toys, etc. I had already removed what I could from those. We had our ducts cleaned last year, and the dust in the house is greatly reduced. Also have lost the runny nose I got after moving here. There are duct cleaning con artists out there, but ours did a good job.
I know it has to have a new concentric venting system installed, I believe it needs new plenums ( mine are rusty but both of these require extra work , so someHVAC persons are saying I do not need either!! RED FLAG THERE. Also, it will need a new drain using PVCP ?? Piping run maybe two, depending on where my evep coil drain is conected (here in TN they use to run them in with the septic lines, now they cannot be run through that way), Lastly I am not where or what these things do beides hold water but I was told It needs a filter rack and new filter base safety pan. THATSSS it that is all I know about this stuff aside from the fact that nothing up there is to code thus far LOL. !!
We hope you found this article on a fair HVAC installation cost helpful. In the end, you’ll be alright so don’t worry too much. Do your research on reputable air conditioning contractors in your area, and spend time making sure that you have a company that you can trust – it will cost you less in the long-run, trust me. Take your time, follow the tips above, and you will end up with an HVAC installation cost that is more than reasonable, keeping your family comfortable for years to come. For more on topics like this, see: ASM’s Air Conditioning Blog.
Whether you’re starting your air conditioner for the first time this year, or a unit isn’t running properly and you need to service an air conditioner, following a few simple steps can save you time and money. While some service jobs should be left to a professional, there are several do-it-yourself fixes you can do to keep your air conditioner cooling all summer long.
I even asked if this is something they don't do, as in services on a Saturday night.  I was told by the receptionist that they do and I would just be ok calling another company if they is not  part of their services. They again assured me someone WILL call me in 10 mins.  Well, unless their definition of 10 mins is never, then they got it wrong as I am still waiting to be called 5 days later.
My best advice has always been that a proper duct cleaning is a valuable investment when moving into a home (new or old), after major renovations and if the ducts have never been cleaned before. It is unlikely that there will be increased air flow, as finding major blockage is unusual, but this will eliminate this as a possible concern if there are air flow concerns. It is also true that the "dust" that is cleared out will most likely never have been distributed through the house unless there has been some work done on the ducts. What is cleared out will be pet hair, toys, clothes, construction material, and biological material (small carcasses and/or feces). Once a proper cleaning is done a follow-up is rarely necessary, but up to the home owners discression.
Although i love to burn candles, depending on the type your asking for problems big ones! At work one day i had been talking with co workers about these black shadows that were appearing on my ceilings and higher wall areas. They seemed to in the corners and along the stud supports , i could even see what i thought to be where all had been nailed. There would be dark shadows perfectly straight across my ceiling and then real dark circels every few inches within the lines. I thought it was the propane heat but learned quickly that oil heat will do that but not normally propane. A co worker brought me a magazine with a huge article about candles and what actually burns off them when lit, an ashy soot that is attracted to the areas on walls and ceilings that omit the most heat or warmth, of course where the drywall and studs meet and corners of the room. Its been about 8 years since i painted the entire house. I started bending to my love for candles again in the last 3 years, surprise i will be spending part of my summer re painting again!! No more candles ,well maybe at the holidays LOL
If you’re purchasing from a big-box store, you can expect to pay approximately $120-$1,000 for a window unit. Window units are appealing for their quick setup and relatively low cost, but they can use more energy over time than central air and only cool the room in which they’re installed. The price will vary depending on the type of air conditioner you buy and its cooling capacity. Window units, which require minimal installation, are one of the most affordable options on the market. Portable air conditioners don’t have the cooling power of a window unit, but they do have the perk of being transportable from room to room. Expect to pay between $225 and $800 for a portable air conditioner, on average. The cost of an air conditioning system with coils, condenser and line (not including installation or ductwork) can range from approximately $2,000 to $4,000 or more. If you don’t have (and don’t want to put in) ducts, a ductless mini-split air conditioner is a good option, although pricey up front. Pricing can range from $650 to $4,250 per unit on average; you’ll need one unit for each room in which you want temperature control.

Whether or not central air adds value to your home depends on your location. You probably won't recoup the entire cost for the installation, as it is an expensive project that isn't as flashy as something like a new deck. But this invisible upgrade can help you sell your home if you live in a hot climate. And many buyers are willing to pay a bit more for a working AC.

My Carrier furnace occasionally (one-two times a day) does not start. It shows error code 15 ("BLOWER MOTOR LOCKOUT -This status code indicates the blower failed to reach 250 RPM or the blower failed to communicate to the variable speed furnace control within 30 seconds after being turned ON in two successive heating cycles."). However, when I turn off and on the furnace power switch it starts and runs fine for a while. Sometimes it runs fine all day, but does not start only once in the evening or in the night. It is 13 years old I was thinking to replace whole thing if repair cost is too high. But I am not ready to pay $10,000. 
An alternative to packaged systems is the use of separate indoor and outdoor coils in split systems. Split systems are preferred and widely used worldwide except in North America. In North America, split systems are most often seen in residential applications, but they are gaining popularity in small commercial buildings. The split systems are a great choice for small buildings where ductwork is not feasible or where the space conditioning efficiency is of prime concern [20]. The benefits of ductless air conditioning systems include easy installation, no ductwork, greater zonal control, flexibility of control and quiet operation [21]. In space conditioning, the duct losses can account for 30% of energy consumption [22]. The use of minisplit can result in energy savings in space conditioning as there are no losses associated with ducting.
Ground source, or geothermal, heat pumps are similar to ordinary heat pumps, but instead of transferring heat to or from outside air, they rely on the stable, even temperature of the earth to provide heating and air conditioning. Many regions experience seasonal temperature extremes, which would require large-capacity heating and cooling equipment to heat or cool buildings. For example, a conventional heat pump system used to heat a building in Montana's −70 °F (−57 °C) low temperature or cool a building in the highest temperature ever recorded in the US—134 °F (57 °C) in Death Valley, California, in 1913 would require a large amount of energy due to the extreme difference between inside and outside air temperatures. A few feet below the earth's surface, however, the ground remains at a relatively constant temperature. Utilizing this large source of relatively moderate temperature earth, a heating or cooling system's capacity can often be significantly reduced. Although ground temperatures vary according to latitude, at 6 feet (1.8 m) underground, temperatures generally only range from 45 to 75 °F (7 to 24 °C).
I guess I should present my credentials first, I am a 30 year veteran of the heating and cooling industry. I started at the bottom and have participated in every area of the trade. Installer, service, maint. Ownership, rep, territory manager and so on. A forced air duct system is a large vacume. Like your vacume it has an air intake (return air) and an exhaust (supply registers). A filter just like a vacume (located next to furnace or air handler). Now I want you to visualize something. Put your head inside your vacume cleaner and breath. Get the picture? This is what your duct work looks like. Do you clean your vacume when it’s dirty? If it’s full and the filter is dirty you lose performance and it starts poluting the air you breathe. It’s common sense. I recommend hiring a duct cleaning outfit that you have researched to be honest, background checked, drug tested, insured, and highly recommended by your piers in the area. The service is a necessity, but like everything, it should be done by a qualified company.

fact is most homes have bad filter racks. when you insert the filter it doesn’t seal well to the sides so some of the air and dust bypass it and end up in the supply ductwork and into the house. Most of the dust in the supply ductwork settles down and doesn’t get blown in the house but some of it does when the blower starts up or when you put a new filter. If you have allergies or other health problems put in an electronic air cleaner, get your ducts cleaned and run the fan as much as you can afford. you can also get an ECM motor installed which is going to be worth it if you want to run the fan 24/7. If you have uninsulated metal ducts take down the ones you can and wash them. Then put them back and seal the joints. Cleaning the ductwork also improves airflow which is important to AC and Heat pump systems for efficiency. An electronic air cleaner will also improve airflow and static pressure because they usually have a much larger filter surface area. An electronic air cleaner also keeps the ac coil clean like new which means better efficiency and no cleaning needed. AC furnaces sometimes grow mold around the coil because of the condensation. Electronic air cleaners should be able to filter mold spores but the best remedy is installing a UV light next to the coil which will kill the mold.

Those of you who read our posts regularly know that we built our reputation as a U.S. Veteran-Owned business that prides ourselves on giving people straight, honest answers to their questions...and there’s no question that makes people cringe more than asking, what does a new HVAC installation cost? Oddly enough, most contractors keep their air conditioning installation cost a closely guarded secret, as if the knowledge of how much it should cost will somehow change your decision when you have to buy a new AC. What I will tell you, is that the fair price of an HVAC installation will vary greatly based on the type of heating and air conditioning system installed, as well as the options needed or desired (Ductwork included? Zoning system?). In this article, we’ll discuss the five system features that affect HVAC installation cost, fair price ranges you can expect to pay for your new system, we will then perform an example calculation of how you can calculate a fair price, and finally, what you can do to keep from getting ripped off on your new HVAC installation price.
I had someone out to clean my ducts last weekend. He took a blue bag up in my attic. He came back down in just a few minutes and said I had mold and he even showed me a picture of something saying it was mold but I couldn’t really tell. I refused his service to take care of the mold. He went back up in the attic for a little while and then came down. I never heard any sounds that he was actually up there doing anything. How do I know if he actually cleaned the air ducts?
Ventilation is the process of changing or replacing air in any space to control temperature or remove any combination of moisture, odors, smoke, heat, dust, airborne bacteria, or carbon dioxide, and to replenish oxygen. Ventilation includes both the exchange of air with the outside as well as circulation of air within the building. It is one of the most important factors for maintaining acceptable indoor air quality in buildings. Methods for ventilating a building may be divided into mechanical/forced and natural types.[16]
On average, we (Indians in Ontario) receive 3-5 calls per day for duct cleaning services from India. I did get ducts cleaned twice in 25 years. For a newly built house, it should be done as material goes into the ducts. Every year, before turning the heat on, I clean the ducts, using the vacuum pipe or with wet towel. Most of the dust, pet hair, small items get to the ducts from the top floors, not where system is installed. Even in winter months, I open 2-3 windows for air circulation for 15 minutes, specially right after cooking, almost daily. We breath in the same stale air, develop health issues. Also, I have an added air cleaning and fileration system installed. At a low rate, this system constantly cleans the inside air and also that it pulls from the outside. Duct cleaning is a scam, there are other efficient and cost effective methods we can use to purify the inside air.
My heat pump/hvac system is not blowing cold air anymore, got checked out was told compressor broken. was told it cost  almost the same to repair/replace they recommend whole system. It's the same company that installed it 18 years ago, telling me that system is old and it will cost $9-10k for new system, because furnace has to be replaced with new hvac. what to do, need answers thanks????
Free cooling systems can have very high efficiencies, and are sometimes combined with seasonal thermal energy storage so that the cold of winter can be used for summer air conditioning. Common storage mediums are deep aquifers or a natural underground rock mass accessed via a cluster of small-diameter, heat-exchanger-equipped boreholes. Some systems with small storages are hybrids, using free cooling early in the cooling season, and later employing a heat pump to chill the circulation coming from the storage. The heat pump is added-in because the storage acts as a heat sink when the system is in cooling (as opposed to charging) mode, causing the temperature to gradually increase during the cooling season.
Compressor -- Compressors are outdoor components in your system. The compressor is the pump that circulates the refrigerants through the air-conditioner. You can hear it when it's running so you'll know if it's working just by listening. If it starts getting louder, your compressor is about to fail. If it makes no sound when it should be on, it has already failed. Compressors fail for a number of reasons. Most often they fail due to strain from another failed part such as the fan motor. Electrical storms can also damage compressors. If the sound from the compressor gets louder or if you see a decrease in performance, you should have your compressor checked. A failed compressor will not heat or cool your house.

WELL, this summer when I opened them up we had black dust spewing from one of the upstairs vents. It resembled the fuzz that comes off new towels. This prompted us to look into duct cleaning. We heard from someone who had it done several times, said it was worthwhile, and knew of a firm that did a good job. Clean Air America sent a single technician for the appointment and after counting registers and ducts gave me a price of $360.00 which included “sanitizing” the system (a $99 additional fee per can used). The small size of the plenum forced him to connect the 8” round vacuum hose from the truck to the 10” square opening from our humidifier unit. In hindsight, a mistake since it reduced the “negative” pressure in the system.
Heaters are appliances whose purpose is to generate heat (i.e. warmth) for the building. This can be done via central heating. Such a system contains a boiler, furnace, or heat pump to heat water, steam, or air in a central location such as a furnace room in a home, or a mechanical room in a large building. The heat can be transferred by convection, conduction, or radiation.

You should be aware that although a substance may look like mold, a positive determination of whether it is mold or not can be made only by an expert and may require laboratory analysis for final confirmation. For about $50, some microbiology laboratories can tell you whether a sample sent to them on a clear strip of sticky household tape is mold or simply a substance that resembles it.
×