NADCA and EPA both have good points. Although, organizations are made to make money. Common sense and looking at NADCA and EPA pre-checklist. If you don't see it in the check list, you don't have to do it! But, if you do, look up Diamond certified co.s and the BBB. Beware of bait and switch scams, $60 vents and the like coupons which claim to help all for the measley sum of $79.00 bucks.


Indoor Coil -- The indoor coil is a heat transfer device. It absorbs the heat from the inside of the house and passes it on to the refrigerant and is pumped outside. Dust that builds up on the coil can hamper its ability to absorb heat. High heat transference coils use very thin metal. Airborne chemicals can cause corrosion which leads to leaks. The constant vibration of the compressor can also cause solder joints to weaken and leak. An indoor coil may operate for weeks with a tiny leak, and you may not notice the loss in performance right away. As soon as a leak is made known, it should be replaced or repaired immediately.
Good article, but it fails to point out that leaky return-side ducts could be drawing dust and allergens into the duct system from the enclosed spaces in which they run, e.g. between walls, below floors, attic. So duct cleaning may only be a temporary solution. The homeowner can get a home energy audit -- free in many states -- to determine if they have significant duct leakage. An Aeroseal dealer may be able to effectively seal up the duct system without needing to tear into walls etc to get to the ducts.

Knowing what you should be paying for your HVAC equipment and installation is essential to getting a fair deal. Most HVAC prices aren’t advertised. Contractor strategy is to get a salesperson into your home to sell you on a package of equipment, accessories and installation. This makes comparing systems difficult, and some sales pressure might be applied.


Most people are now aware that indoor air pollution is an issue of growing concern and increased visibility. Many companies are marketing products and services intended to improve the quality of your indoor air. You have probably seen an advertisement, received a coupon in the mail, or been approached directly by a company offering to clean your air ducts as a means of improving your home's indoor air quality. These services typically — but not always — range in cost from $450 to $1,000 per heating and cooling system, depending on:

Prices, promotions, styles, and availability may vary. Our local stores do not honor online pricing. Prices and availability of products and services are subject to change without notice. Errors will be corrected where discovered, and Lowe's reserves the right to revoke any stated offer and to correct any errors, inaccuracies or omissions including after an order has been submitted.
You may consider having your air ducts cleaned simply because it seems logical that air ducts will get dirty over time and should be occasionally cleaned. Provided that the cleaning is done properly, no evidence suggests that such cleaning would be detrimental. EPA does not recommend that the air ducts be cleaned routinely, but only as needed. EPA does, however, recommend that if you have a fuel burning furnace, stove or fireplace, they be inspected for proper functioning and serviced before each heating season to protect against carbon monoxide poisoning.

From Day 1, Alberto walked us through the process, and present us with a variety of options based our budget for the project. His customer service is the best as he did not oversell any services and did not nudge us towards buying a unit that would stretch our budget. On installation day, HVAC Services sent out a crew of 6-7 guys, all of whom were very polite and kept their work areas clean, and installed the whole system the same day.
In variable climates, the system may include a reversing valve that switches from heating in winter to cooling in summer. By reversing the flow of refrigerant, the heat pump refrigeration cycle is changed from cooling to heating or vice versa. This allows a facility to be heated and cooled by a single piece of equipment by the same means, and with the same hardware.
I'd have to disagree with all of your statements. Not only are they derived from no experience in the field, you are missing keys facts. Ducts even if air tight will get dirty. If they are not getting dirty, it means they are not working. Your returns side of the duct work is always under negative pressure when the system is operational.Therefore it is always drawing air in. Seeing how dust is made up mostly from dead skin humans shed daily. Around 1.6 Pounds of skin a year per human. Living in your home anything that is air born will be drawn back towards the cold air returns. That is what they are designed for, to draw stale air back to the system to be filtered and sent back through the house.Homes with carpet will actually have cleaner duct work than home with all tile or hardwood. This is because carpets hold onto dust particles and you vacuum them up. Whereas on hardwood or tile, dust can run freely back to the returns. Even if a duct system was sealed 100%, which is next to impossible to achieve 100% would still need to be cleaned. The cleaning may only have to be every 7-10 years for example. Most homes require every 5-7 years. And that's if it was done properly the first time. If you constantly hire people that have no or minimal knowledge of duct cleaning, You home would require cleaning more often. Every 2 years. That's a trade secret, The longer they recommend before the next cleaning, the odds are they did it right. That's not to say there aren't people that lie, because there are. Just have your duct cleaner take pictures before and after cleaning. Not just an outside view. Get in there, picture entire joist liners, Whole main runs and even long round pipes. Also it helps to have a company that guarantees their work. If it's not done right, they will come back and do it until it is. Most companies that do this make sure it is right the first time. Your not getting paid to do the job twice.
After major damage to a small addition on our home was damaged in the windstorm in May, the insurer’s preferred vendor sanded drywall without taping off the area. They relied on heat from the furnace to dry the mudding compound. They claimed they shut the furnace off while sanding and regardless of whether they did or not, they never cleaned up the drywall dust before turning the furnace back on. I now have drywall dust everywhere and my husband took photos to verify our concerns. They even sanded right above a cold air return. Vents were never covered either. The same company that created this mess is cleaning my ducts today. They have refused to clean the furnace. Their are health concerns for my almost 85 yr old mother who resides with us. I’ve tried 3 times in the last 7 days to escalate to a manager and they will not return my call. They just keep sending it back down to my adjuster. There are many other issues we’ve encountered since May as well. This is a major insurance company who has the resources to fix this mess but refuse. Please help!
CIBSE publishes several guides to HVAC design relevant to the UK market, and also the Republic of Ireland, Australia, New Zealand and Hong Kong. These guides include various recommended design criteria and standards, some of which are cited within the UK building regulations, and therefore form a legislative requirement for major building services works. The main guides are:
If there is stuff in the ducts, the fact that it’s laying there and not being blown into the rooms is proof positive that it is hurting no-one. The 5-6 exceptions you cite in this article I’ll buy, but only with the caveat that at least some of those could have been avoided by proper protection (during remodeling for example) – and if asbestos/lead/whatever winds up in your ducts- the remodeling contractor should be the one paying to remove it.
Air conditioning units are prone to the pitfalls of wear and tear. You can prolong this, however, with proper maintenance procedures. Without regular maintenance even an immaculate AC installation in Fort Smith, Arkansas cannot guarantee performance. Our maintenance service is thorough, leaving no area unattended. If there’s a problem, we’ll catch it early and prevent avoidable breakdowns and costly repairs.
All modern air conditioning systems, even small window package units, are equipped with internal air filters. These are generally of a lightweight gauze-like material, and must be replaced or washed as conditions warrant. For example, a building in a high dust environment, or a home with furry pets, will need to have the filters changed more often than buildings without these dirt loads. Failure to replace these filters as needed will contribute to a lower heat exchange rate, resulting in wasted energy, shortened equipment life, and higher energy bills; low air flow can result in iced-over evaporator coils, which can completely stop air flow. Additionally, very dirty or plugged filters can cause overheating during a heating cycle, and can result in damage to the system or even fire.
Had duct cleaned (apartment) however, dust is still settling throughout the apartment. Contractor said no other cleaning necessary until two (2) years. Is there a time period before dust no longer settles prior to that time? Should the vendor had worn a mask? He did not cover his face the vents and dust was blown throughout the apartment (had family help with the cleanup). I had to leave when they left because I have asthma and I couldn’t breathe without coughing. Please help!
Just had my air ducts cleaned. They used a high pressure air hose in all the heat ducts and cold air returns. He showed me the stuff that came out, the reason for the duct cleaning was the fact that I had a problem. With rodents. There was quite a few mummified rats and mice, and he said I wouldn’t have to have them done again unless I incur another problem or have renovations done. Cost me 345.00 for a 2 storey large old home. Not a bad price as I had them done when I moved in 28 years ago and it cost me 500.00. Lots of dog hair, toys, balls and assorted goodies came out as well. Took them 2 hours. I did have sanitizer put in the ducts because of the dead rodents.

Sounds like your first hvac company was ripping you off. Ask your new company to go to your coil and see if there is a leak. If there isn't the last company was just lining their pockets. If you have had ducts unhooked for a long time I would recommend duct cleaning, trust me I'm not a fan of duct cleaning myself. I have done hvac for 20 yrs. in GA. When I just bought a home built in 1996, we had all the ducts replaced immediately.
You can adjust for seasons: During the summer, you can have the air conditioner stay off during the cooler morning hours and start cooling the house as everyone gets up and starts moving around. During the winter, you can have your heater stay off while you are away at work and turn on about a half hour or so before you get home so that you are coming home to a nice, warm house.
Refrigerant Metering Device -- Every HVAC system has one of these, and heat pumps have two. They regulate the amount of refrigerant going through your air-conditioner. If it fails, either too much or too little refrigerant will course along the lines and either not perform well or will overwhelm the compressor and cause it to fail. A total failure of this component will result in a complete loss of operation.
I was told that 15 out vents would be cleaned and one main vent. the guy came over and gave me an estimate of $500. I had acquired a groupon for $49. the guy said just doing the out vents and one main vent would accomplish nothing. Now I am in dispute with the groupon people for a refund which they won’t give and have to go ahead and waste the money and let them do it. Is their doing the 15 outvents and one main one going to accomplish anything?
I took off stars for two reasons. Minus one star for issues trying to use the $50 for $25 voucher I purchased through Yelp. Although there was no minimum stipulated, the office wouldn't take it for the initial $59 diagnostic fee. If I used the 10% off First service that they offer, then they won't let me use the voucher on the actual repair bill.  I was stuck with paying the full $59 diagnostic fee.
Be careful with HVAC change-outs.  Change-outs are only about 15-20% of the HVAC installation industry. Decrease HVAC installation cost by investing in new ductwork now if needed. Your ducts wear out too, and make sure that your ducts are in fantastic shape if you do this. Many contractors push this because it’s easy and cheap for them, with good pay-off. Do your research and replace them if you need to in order to avoid doing it later, as well as avoid potential health hazards from using old, broken ductwork.
In addition, the service provider may propose applying chemical biocides, designed to kill microbiological contaminants, to the inside of the duct work and to other system components. Some service providers may also suggest applying chemical treatments (sealants or other encapsulants) to encapsulate or cover the inside surfaces of the air ducts and equipment housings because they believe it will control mold growth or prevent the release of dirt particles or fibers from ducts. These practices have yet to be fully researched and you should be fully informed before deciding to permit the use of biocides or chemical treatments in your air ducts. They should only be applied, if at all, after the system has been properly cleaned of all visible dust or debris.
Some of these components can be repaired or replaced by the homeowner, such as filters, fuses, and clogged up drain lines. Coils, compressors and the other components are best left to a professional. In some cases, you may have a system that is so old that parts are no longer available or else they aren't up to code. In this case you will have to consider replacing the entire system.
In the case of heated water or steam, piping is used to transport the heat to the rooms. Most modern hot water boiler heating systems have a circulator, which is a pump, to move hot water through the distribution system (as opposed to older gravity-fed systems). The heat can be transferred to the surrounding air using radiators, hot water coils (hydro-air), or other heat exchangers. The radiators may be mounted on walls or installed within the floor to produce floor heat.
Just had my HVAC System restored and working again on a Sunday and before the 104 weather tomorrow!!!! Called Big Mountain Heating and Air and spoke to very helpful woman named Martina. She connected me to a Technician named Josh. He was at my home within a few minutes and tackled my Honey Well system's issues. He is both skilled, personable and better yet, he got my system up and going and safe. He installed a surge suppressor on the system to prevent power surges that can kick off any system, when the electric company has to reduce power, etc.  I will be using Big Mountain in the future. Truly grateful for such good service and people. Thank you!  I recommend this firm to everyone!
What if you move into a 20 year old house and find that the people who owned it previously NEVER replaced the filter? It was so dirty that the HVAC system did not work at all. For most people - duct cleaning is NOT a waste of time or money. You must not have allergies. I have very bad ones plus asthma. It makes it very hard for me if I don't get it done every few years. By the way - the ducts get dusty just sitting there - especially without air going through them. Dust settles on them just like it does the furniture.
I forgot about a pot of sweet water I had on the stove to boil. When I finally smelled it the kitchen and dining room I=was smoke filled. I mean thick smoke. I opened doors and windows for a few hours to remove the smoke but the smell is still here and terrible. I had to use the AC and that smell started coming out of the vents. Now what do I do? I have COPD emphysema so I have to be very careful about what I inhale. I already have inhaled too much smoke from all of this which has hurt my lungs even more. I can’t afford for them to get worse over this. How can I get the right person to come out and clean the ducts and furnace or is that the only way to remove that burnt smokey smell. The pot never caught on fire but it sure did produce a lot of smoke. I already have replaced the filter on the furnace. It needed it even though it had just been replaced just last week. I need help or really my lungs need help. Who do I call here in Indpls IN.
We have provided Arkansas families and businesses with quality HVAC products and services for 42 years. Offering reasonable rates and personalized service, we are a dedicated team of experts equipped to handle any service requirement. Your source for modern heating, cooling, and ventilation equipment and servicing, Wilson's Heating & Air Conditioning is the HVAC specialist in Van Buren.

Typically speaking, the lower SEER, more basic models are also more reliable.  Reliability is big with us, so we steer clear of features with reliability issues, and it’s as simple as that. When you factor in the price of repairs and the extra expense of the 21-SEER, you may actually lose money! 16 SEER is the sweet-spot, and it is key to reducing your HVAC installation cost.
The cooling coils the air comes into contact with appear to need UV-C lights on them in humid climates. That's the biggest thing. If the ducts have never been cleaned, then getting that done goes without saying. But those coils need to be cleaned, disinfected, and then UV-C light(s) installed to prevent mold & bacteria build-up in the future on them. That appears to be chiefly responsible for the dirty laundry and/or sour milk smell coming from forced-air AC systems in humid regions.
Most people are now aware that indoor air pollution is an issue of growing concern and increased visibility. Many companies are marketing products and services intended to improve the quality of your indoor air. You have probably seen an advertisement, received a coupon in the mail, or been approached directly by a company offering to clean your air ducts as a means of improving your home's indoor air quality. These services typically — but not always — range in cost from $450 to $1,000 per heating and cooling system, depending on:
×