2. If air quality is so important and duct cleaniliness is so uncertain, why not adopt doubling filtering; that is, in addition to the existing main furnace filter, add a filter at each air outlet. I understand replacing so many filters would be a burden, but air outlets can be designed for easy filter replacement. The builders and home design engineers should bear responsibility to provide good and low maintenance homes, rather than prioritizing on fancy or costly featuers for homes.
A little simple math can help determine the size system you need. A rule of thumb is 20 BTUs per square foot. So, a 500 square foot room would need 10,000 BTUs to cool or warm it efficiently. This assumes that you live in a temperate region and have adequate insulation with no energy loss. In the real world, all units have some degree of energy loss. This is reflected in an HVAC system's SEER rating for cooling and AFUE rating for heating.
The cooling coils the air comes into contact with appear to need UV-C lights on them in humid climates. That's the biggest thing. If the ducts have never been cleaned, then getting that done goes without saying. But those coils need to be cleaned, disinfected, and then UV-C light(s) installed to prevent mold & bacteria build-up in the future on them. That appears to be chiefly responsible for the dirty laundry and/or sour milk smell coming from forced-air AC systems in humid regions.
Sounds like your first hvac company was ripping you off. Ask your new company to go to your coil and see if there is a leak. If there isn't the last company was just lining their pockets. If you have had ducts unhooked for a long time I would recommend duct cleaning, trust me I'm not a fan of duct cleaning myself. I have done hvac for 20 yrs. in GA. When I just bought a home built in 1996, we had all the ducts replaced immediately.
Many central air conditioning systems use the furnace blower to distribute cool air through the home. If you do not have a central heating system installed, it is cost-effective to install a heating and air conditioning system at the same time. If you already have central heat, you can use the existing fans and duct system for the central air system.
Good article, but it fails to point out that leaky return-side ducts could be drawing dust and allergens into the duct system from the enclosed spaces in which they run, e.g. between walls, below floors, attic. So duct cleaning may only be a temporary solution. The homeowner can get a home energy audit -- free in many states -- to determine if they have significant duct leakage. An Aeroseal dealer may be able to effectively seal up the duct system without needing to tear into walls etc to get to the ducts.
I had someone out to clean my ducts last weekend. He took a blue bag up in my attic. He came back down in just a few minutes and said I had mold and he even showed me a picture of something saying it was mold but I couldn’t really tell. I refused his service to take care of the mold. He went back up in the attic for a little while and then came down. I never heard any sounds that he was actually up there doing anything. How do I know if he actually cleaned the air ducts?
You've probably noticed many appliances boasting an Energy Star Certification. What this means is that manufacturer voluntarily built the product to help reduce greenhouse gases and meet non-regulatory guidelines offered by the Environmental Protection Agency. To earn an Energy Star rating, a product or system must be tested by a third party that has been recognized by the EPA for meeting their testing qualifications.
All of the products discussed above are registered solely for the purpose of sanitizing the smooth surfaces of unlined (bare) sheet metal ducts. No products are currently registered as biocides for use on fiber glass duct board or fiber glass lined ducts, so it is important to determine if sections of your system contain these materials before permitting the application of any biocide.

Whether you’re looking for air conditioning maintenance, air conditioner repair, or a new air conditioning system, Sears Home Services can help. We’re your best, most-trusted option for fast, quick, and easy local service, repair, and maintenance of your home air conditioning system. If your air conditioner isn’t cooling or your central air conditioner is leaking water, we’ll connect you to the best local AC repair service technicians in the business.We have local technicians in your neighborhood that are highly trained, licensed, vetted, and guaranteed to help fix all of your air conditioning needs.
Did not realize cost had gone up so much for this service. Two years ago I had furnace and ducts cleaned at my old house and it was under $400. Now the cost is $700 for this house. I will keep looking for someone to offer a lower price, check them out, and have it done. Or will find the paperwork to see who did it before. I liked this article and did learn some things. Thanks.
They work less jobs, thus increasing profits – think about it…if they got only half of the jobs, then they only pay half of the money required to pay employees, expenses, etc., but still have the same amount of net profit. In fact, if you do the math, they actually make more profit that their competitors do…twice as much, once you factor in their savings form only doing half of the jobs at the same amount of profit (Total Revenue – (half the normal expenses) = twice the profit). In other words, they save money by doing half of the jobs as others, for the same profit, thus increasing their overall profits.
I purchased a Groupon for cleaning of unlimited air ducts and one return vent for $39. I should have checked into their hours first because they only offer services during normal business hours. So, with no evenings or weekends available you have to take time off work. I asked Groupon for a refund when I realized this and they refused because it wasn’t within the three day window. Then they didn’t even show up or call for the appointment. I called them after they were an hour late and they were going to call the local dispatch office and have them call me back within 15 minutes. I did not receive that call. I called again and was told I would get a call back from a manager. That didn’t happen either. So I asked Groupon for a refund again and they gave me Groupon bucks. When the survey came asking if I was satisfied with the Groupon customer service I said no, I want real money. I got my real refund the next day. Seems to me Groupon should stop dealing with these companies.
Consider what kind of heating and cooling system you want installed for the square footage of your home. Do you want a full system with a thermostat or a specific machine for the summer like a swamp cooler? Do you need a new furnace just for the winter? For any of these projects, the cost will vary depending on the quality, style and machine size you choose. If you have a tight budget, think of going smaller and upgrading over time. For example, if you can't afford to convert your entire home to solar power, you may want to consider only utilizing it to heat your water. Some other types of heating systems are:

You may consider having your air ducts cleaned simply because it seems logical that air ducts will get dirty over time and should be occasionally cleaned. Provided that the cleaning is done properly, no evidence suggests that such cleaning would be detrimental. EPA does not recommend that the air ducts be cleaned routinely, but only as needed. EPA does, however, recommend that if you have a fuel burning furnace, stove or fireplace, they be inspected for proper functioning and serviced before each heating season to protect against carbon monoxide poisoning.
Those of you who read our posts regularly know that we built our reputation as a U.S. Veteran-Owned business that prides ourselves on giving people straight, honest answers to their questions...and there’s no question that makes people cringe more than asking, what does a new HVAC installation cost? Oddly enough, most contractors keep their air conditioning installation cost a closely guarded secret, as if the knowledge of how much it should cost will somehow change your decision when you have to buy a new AC. What I will tell you, is that the fair price of an HVAC installation will vary greatly based on the type of heating and air conditioning system installed, as well as the options needed or desired (Ductwork included? Zoning system?). In this article, we’ll discuss the five system features that affect HVAC installation cost, fair price ranges you can expect to pay for your new system, we will then perform an example calculation of how you can calculate a fair price, and finally, what you can do to keep from getting ripped off on your new HVAC installation price.
2. If air quality is so important and duct cleaniliness is so uncertain, why not adopt doubling filtering; that is, in addition to the existing main furnace filter, add a filter at each air outlet. I understand replacing so many filters would be a burden, but air outlets can be designed for easy filter replacement. The builders and home design engineers should bear responsibility to provide good and low maintenance homes, rather than prioritizing on fancy or costly featuers for homes.

Duct cleaning is a complete scam, I was a “duct cleaning technician” for a whole week before I was fired for not upselling elderly widowed women $2000 extra for “toxic mold remediation” when their ducts were spotless to begin with. The last two days I was employed there I worked as a “helper” alongside a technician thats been with the company 7 years. He scammed every customer on mold and would at times get as much as $2500 extra for treating “toxic mold” in a typical 3 bedroom house in the suburbs. Wait…it gets even better, the “Biocide” the company used was simply a cheap $4.99 per gallon bought at Home Depot air freshener with no anti-microbial properties that was fogged into the HVAC system for 5 minutes, maybe using 1/2 cup of the stuff. In order to provide the customer with evidence of “mold infestation” the technician would be given bogus mold tests that always resulted in “toxic spores present” regardless if you swabbed the actual duct or nothing at all. Not to mention the actual duct cleaning job (typically $400) did basically nothing and the homeowner could’ve done a better job with a shopvac
Very interesting article. I searched articles about services for cleaning ventilation systems. But I have some questions. For cleaning ventilation system used special products for cleaning. Can I know in company manager about, which type of cleaning products they use? Your family members may be allergic in some components. It’s very big problem. And one more problem it’s how to choose the right company in Internet. Sometimes I don’t have much time to find a company in my town and I use the Internet. But I find a lot of company. It is very popular services, for example, Stanley Steemer – https://www.stanleysteemer.com/ or my local not very popular service, for example, AllstatesAirDuctPro – http://allstatesairductpro.us/. Can I understand the company is professional or not, only looking through the website? What must I check on the website? Who has helpful information? I will very grateful for your help. Links I add for understanding my problem. They are random and not for advertising.
Outdoor Fan Motor -- The outdoor fan, also called the condenser fan, is exposed to external conditions. As such it is most prone to dust and debris and the extreme weather. In desert climates, the outdoor fan motor is subject to heat not only from normal operation but from the outside temperature as well. As it starts to fail, the fan may work fine in the cooler morning hours but stop by afternoon. This can shut down the entire system for hours. When they stop running completely, your air conditioner will no longer work. Running a faulty fan will lead to compressor failure, which is a very costly repair.
An energy recovery ventilator: This component helps improve the air inside your home by swapping it out with fresh air from the outside. During the winter months when houses are closed up to keep out the cold, the air inside becomes a handy way for colds and flu to infect an entire family. By circulating outside air inside, the health of your family will have a better chance.
in response to this reply " should your ducts be cleaned", i have to politely correct the person who answered this. you are not using common sense. first, most of the country uses metal duct work, so for you to say what you did, is wrong. second, the duct system in a house is a circulatory system. that means it draws air into the furnace, it gets filtered, and then it is blown out into the house to heat or cool. So, obviously that air is being brought into the house from somewhere right? Yes, its coming from the outside where there are many allergens and dust particles . For you to says that about whether a duct system is sealed or not, makes no difference. The air is coming from somewhere right? It has to originate from somewhere right? Just look on top of your cieling fan. If there is a bunch of dust up there, then there is obviously a bunch in your ducts. And the duct air is being circulated every day, and every hour through your house. Its simple, dust collects everywhere in your house. Imagine if you never dusted your shelves, or tv? There would be a ton of dust after a while. Well, now think about the air in the duct system. Of course theres gonna be a ton of dust in there. For you to say that it is not benififcial to clean the ducts, is plain ignorant. 90% of the air we breathe is in our household. Wouldnt you want that air to be as dust and allergen free? I could go on for hours about the benifits of duct cleaning, but i just wanted to make a quick point that the person whose says it is not benificial to clean them, is not using common sense. Not to mention, giving the people who clean ducts for a living, a bad name. Use your head .
Humidifiers/Dehumidifiers: Humidifiers add needed moisture to the air in winter and very dry climates. Dehumidifiers remove dampness any time of the year. Central air conditioners dehumidify too, but in very humid climates, you might want to remove humidity without also cooling the air. You have a good range of options for both of these HVAC accessories. Whole-house humidifiers cost $350 to $800 installed, while dehumidifiers are $1,250 to $2,000 or slightly more.
When these aren't properly maintained and sanitized, they can build up dust, pollen, and even mold. This means when the air conditioner or heater turns on, the spores are released into the air for you to inhale. While some are less harmful, people who have allergies or sensitivity to certain spores will react negatively. Plus, mold is dangerous for anyone to ingest and should be avoided by regular maintenance.
I’m having my duct work cleaned this Saturday. Have a coupon for $49 through Amazon. Job normally $249. Had my basement remodeled about 18 months ago. The contractors were very thorough at blocking the vents, as far as I can tell. The offer is for HVAC and dryer vent cleaning. My house is 11 years old. I figured, $49 is not much. I appreciate your tips on not getting talked into any additional service, not to use solvents to clean, the certification information and before and after pictures. Very useful and I’ll be sure that all I spend is the $49 for the voucher.
Energy efficiency can be improved even more in central heating systems by introducing zoned heating. This allows a more granular application of heat, similar to non-central heating systems. Zones are controlled by multiple thermostats. In water heating systems the thermostats control zone valves, and in forced air systems they control zone dampers inside the vents which selectively block the flow of air. In this case, the control system is very critical to maintaining a proper temperature.
You can install the greatest HVAC system ever built, but if your house is not insulated well, it's only going to end up costing you more money. Older homes may have fiberglass insulation that has broken down due to pests, moisture, or improper installation. Spray foam insulation can be damaged by careless repair or modification work or can be improperly installed. If your insulation in compromised, your attempts to save money and be comfortable will be in vain.
Very interesting article. I searched articles about services for cleaning ventilation systems. But I have some questions. For cleaning ventilation system used special products for cleaning. Can I know in company manager about, which type of cleaning products they use? Your family members may be allergic in some components. It’s very big problem. And one more problem it’s how to choose the right company in Internet. Sometimes I don’t have much time to find a company in my town and I use the Internet. But I find a lot of company. It is very popular services, for example, Stanley Steemer – https://www.stanleysteemer.com/ or my local not very popular service, for example, AllstatesAirDuctPro – http://allstatesairductpro.us/. Can I understand the company is professional or not, only looking through the website? What must I check on the website? Who has helpful information? I will very grateful for your help. Links I add for understanding my problem. They are random and not for advertising.
HVAC professionals in the US can receive training through formal training institutions, where most earn associate degrees. Training for HVAC technicians includes classroom lectures and hands-on tasks, and can be followed by an apprenticeship wherein the recent graduate works alongside a professional HVAC technician for a temporary period.[33] HVAC techs who have been trained can also be certified in areas such as air conditioning, heat pumps, gas heating, and commercial refrigeration.[34]

Outdoor Fan Motor -- The outdoor fan, also called the condenser fan, is exposed to external conditions. As such it is most prone to dust and debris and the extreme weather. In desert climates, the outdoor fan motor is subject to heat not only from normal operation but from the outside temperature as well. As it starts to fail, the fan may work fine in the cooler morning hours but stop by afternoon. This can shut down the entire system for hours. When they stop running completely, your air conditioner will no longer work. Running a faulty fan will lead to compressor failure, which is a very costly repair.


Monday the following week, no phone calls, or follow up.  I call to get an update and am told that they cannot install my system because they don't have time.  I ask what does that mean, one year? One week? Until the end of summer they say.  What does that mean I ask?  They say at the end of September.  I say thank you for wasting 1 month of my time.
We use third party data sources to conduct a criminal search, in the state in which the owner/principal of the company is located, for any relevant criminal activity associated with the owner/principal of the business, within the three years prior to such service professional's application for membership in the HomeAdvisor network. HomeAdvisor's third-party vendor uses a national criminal database ("NCD") to screen our service professionals. The comprehensiveness of the NCD varies by state. Please be aware that the reporting in the NCD is particularly limited in the following states: AL, CO, DE, GA, ID, KS, KY, LA, ME, MA, MI, MS, MT, NE, NV, NH, NM, SD, UT, VA, VT, and WY.
×