Pay particular attention to cooling coils, which are designed to remove water from the air and can be a major source of moisture contamination of the system that can lead to mold growth. Make sure the condensate pan drains properly. The presence of substantial standing water and/or debris indicates a problem requiring immediate attention. Check any insulation near cooling coils for wet spots.


I have been a plumbing/gas/hvac tech for 19 years, before that I installed ductwork in commercial buildings and office towers. As the article states, unless you have undergone some type of extensive reno, or ducts have become contaminated, paying for cleaning is pointless. Its one thing if you have a 30 year old home that has never had a duct cleaning and you can actually see mounds of dust built up , especially in the return side, then go for it. Keep in mind that most duct cleaning companies will only get 80% of the dust , or less at best. Keep in mind that most of the dust in your home is lint from clothes and linens, and skin cells from you and your pets and is constantly being generated. Dust that builds up in ductwork , generally stays in the ductwork. The power of suggestion, scare tactics, up sell!!!
There are many interesting comments from several informed individuals. The question that has not been answered is how do duct systems get dusty and dirty? As a RESNET Home Energy Rater, I perform pressure tests on homes and duct systems, and the one common thread is . . . most air delivery sytems have large amounts of air leakage. The solution is to seal the duct system, and pay particular attention to the return duct system and ductwork near the air handler (the 'blower'). As others have said, a captive (sealed) duct system with proper filter maintenance should be more then adequate for most occupants. For those who have allergy, asthma, or other breathing problems, a filter with a higher MERV rating (number should be listed on the package) or a HEPA filter are good choices. These filters will capture smaller particulates and should improve the indoor air quality. Again, make certain that the entire duct system is sealed, preferably with mastic, second choice UL-181 foil tape - never use cloth duct (also known as duck) tape.
DIY: We don’t recommend a DIY approach. Depending on the system, working with gas, electricity and refrigerant create dangers. Beyond that, it is essential that split system components be selected for compatibility. DIY installation of an HVAC system will void the warranty of most brands. The manufacturers won’t stand behind the warranty when anyone other than a certified installer does the work. This is true since improper installation is the main cause of poor system performance and mechanical breakdowns.
Our Fort Smith, Arkansas area restoration services are available at your convenience. We provide emergency services after devastating property damage and work hard to restore and clean as much of the contents and structure as possible. We'll Work With You and Your Insurance Company to cover costs and expedite the process. If you need cleaning and restoration services or are looking for ways to create a healthier, more efficient environment, contact McMahon's Cleaning & Restoration, LLC to get started.
Demand controlled kitchen ventilation (DCKV) is a building controls approach of controlling the volume of kitchen exhaust and supply air in response to the actual cooking loads in a commercial kitchen. Traditional commercial kitchen ventilation systems operate at 100% fan speed independent of the volume of cooking activity and DCKV technology changes that to provide significant fan energy and conditioned air savings. By deploying smart sensing technology, both the exhaust and supply fans can be controlled to capitalize on the affinity laws for motor energy savings, reduce makeup air heating and cooling energy, increasing safety and reducing ambient kitchen noise levels.[29]
Installation: The old furnace is disconnected from the ductwork plenum, exhaust flue, gas and electrical hookups. In most cases, a new plenum must be made onsite or ordered from a local sheet metal fabricator. A new vent might be required too. The furnace is set and reconnected. Adjustments to the blower fan speed and burner are made to optimize furnace performance for your home and climate.
Air conditioner size is measured in “tons.” However, the tonnage of an HVAC unit is not actually based on its weight. A “ton” is simply a measure of an air conditioner’s ability to cool your home. One ton is the ability of your air conditioning system to cool 12,000 BTUs (BTU stands for British Thermal Unit) in an hour. Likewise, a “2-ton” central air conditioner is able to cool 24,000 BTUs per hour.
Indoor Fan Motor -- Indoor fans circulate the air from your house and through the system. Age and dust buildup are the two biggest contributing factors to their failure. When they are starting to fail they will often make noise. Failure of the fan will result in no heating or cooling, and if it is not repaired soon, it can cause other components to fail.
A dehumidifier is an air-conditioner-like device that controls the humidity of a room or building. It is often employed in basements which have a higher relative humidity because of their lower temperature (and propensity for damp floors and walls). In food retailing establishments, large open chiller cabinets are highly effective at dehumidifying the internal air. Conversely, a humidifier increases the humidity of a building.
I just had my blower module replaced because my AC coil was frozen over. The underside of my coils had a thick mat of dust because I had never had it cleaned. I cleaned it myself by using a soft brush attachement on a shop vac. The inside of the blower appears to have a white/green growth, and I am sure the ductwork of my 30 year old house can’t be in good condition.

In reading through all this about duct cleaning, THE ONE preventative measure people need to realize is that a poorly installed HVAC system that is not sealed and air tight to ensure that ALL indoor air passes through a GOOD air filtration system IS THE best means of ensuring your ducts remain clean. Duct cleaning does not now and will NEVER improve an HVAC systems efficiency. Proper maintenance and installation are the key just as improper installation practices allow for dust infiltration into the duct system. I am a state licensed contractor in Texas, and unless people have their hvac system sealed and/or properly installed, duct cleaning is an absolute waste of money. My duct system is 12 years old as is as clean today as the day I installed the system with ductwork. SO before ANYONE jumps on the bandwagon of duct cleaning, get with your hvac professional FIRST.
A house breathes just like you an I.For example every time your clothes dryer comes on it automatically creates a negative pressure inside the home.So if air goes out of the living area it has to be replaced.....now look above the ceiling fan ....you see the cover...underneath that is a hole straight to your attic....Now the stuff on your ceiling fan you call dust...call it insulation,rat fecies or anything else that is in your attic that could be pulled in your due to a negative pressure.
I am NADCA Certified Air Systems Cleaning Specialist. Over the year I have learned on simple answer to this questions: there air duct cleaners and there are pretenders. There will be no benefit at all if you use on the very cheap pretender because they will not really clean anything. On the other hand if you call a qualified air duct cleaner with a NADCA Certification you will, like 99% of my customers, report improvement with your respiratory problems, you will see less dust and the job will pay for itself with energy savings and repair prevention.
What if you move into a 20 year old house and find that the people who owned it previously NEVER replaced the filter? It was so dirty that the HVAC system did not work at all. For most people - duct cleaning is NOT a waste of time or money. You must not have allergies. I have very bad ones plus asthma. It makes it very hard for me if I don't get it done every few years. By the way - the ducts get dusty just sitting there - especially without air going through them. Dust settles on them just like it does the furniture.
Knowing what you should be paying for your HVAC equipment and installation is essential to getting a fair deal. Most HVAC prices aren’t advertised. Contractor strategy is to get a salesperson into your home to sell you on a package of equipment, accessories and installation. This makes comparing systems difficult, and some sales pressure might be applied.

An EER certifies the cooling efficiency of HVAC units. It's calculated by the rate of the cooling in British thermal units (Btus) per hour and divided by the rate of energy input in watts at a specific temperature. The calculation goes as BtuH/WATT at dry bulb (db) versus wet bulb (wb) temperatures. The optimal rating for a cooling unit is about 80db/67wb inside and 95db/75wb outside.
As I type this, I am having my ducts cleaned. About 30 including returns and the furnace. $543.00. I am watching the team do it and can see the clear vacuuming tubing and how dirty it has become. I like the gentleman’s comment on “stick your head in your vacuum and breath”….I get it. The team showed me the machine and it’s filtration system…and they will show me it again after the cleaning. However, like I said before, I am actively seeing the tubing that is clear before they start and how dirty it is once they begin and continue cleaning. Reputable company and not a “fly by night” coupon service. People don’t be so cheap, that is your problem.
Just had my air ducts cleaned. They used a high pressure air hose in all the heat ducts and cold air returns. He showed me the stuff that came out, the reason for the duct cleaning was the fact that I had a problem. With rodents. There was quite a few mummified rats and mice, and he said I wouldn’t have to have them done again unless I incur another problem or have renovations done. Cost me 345.00 for a 2 storey large old home. Not a bad price as I had them done when I moved in 28 years ago and it cost me 500.00. Lots of dog hair, toys, balls and assorted goodies came out as well. Took them 2 hours. I did have sanitizer put in the ducts because of the dead rodents.

Ground source, or geothermal, heat pumps are similar to ordinary heat pumps, but instead of transferring heat to or from outside air, they rely on the stable, even temperature of the earth to provide heating and air conditioning. Many regions experience seasonal temperature extremes, which would require large-capacity heating and cooling equipment to heat or cool buildings. For example, a conventional heat pump system used to heat a building in Montana's −70 °F (−57 °C) low temperature or cool a building in the highest temperature ever recorded in the US—134 °F (57 °C) in Death Valley, California, in 1913 would require a large amount of energy due to the extreme difference between inside and outside air temperatures. A few feet below the earth's surface, however, the ground remains at a relatively constant temperature. Utilizing this large source of relatively moderate temperature earth, a heating or cooling system's capacity can often be significantly reduced. Although ground temperatures vary according to latitude, at 6 feet (1.8 m) underground, temperatures generally only range from 45 to 75 °F (7 to 24 °C).
Ventilation is the process of changing or replacing air in any space to control temperature or remove any combination of moisture, odors, smoke, heat, dust, airborne bacteria, or carbon dioxide, and to replenish oxygen. Ventilation includes both the exchange of air with the outside as well as circulation of air within the building. It is one of the most important factors for maintaining acceptable indoor air quality in buildings. Methods for ventilating a building may be divided into mechanical/forced and natural types.[16]

Mitsubishi Electric is a world leader in air conditioning systems for residential, commercial and industrial use. Challenged to create air conditioning systems that provide exemplary performance in the wide-ranging climatic conditions found throughout Japan, our engineers develop amazingly sophisticated yet durable units and systems capable of constant use under virtually any natural climatic condition on earth.
The next step was cleaning the cold air returns. He found a good spot to drill an 8” hole for his vacuum hose. The procedure matched the other air ducts except that when he finished at the two cold return registers he drilled several holes in the cold ducts in the basement and blasted air into them. Because of our houses age and the upgraded return system, I noticed that the main sheet metal return duct had no top but was just butted up against the ceiling in the basement. When he blasted air in, dust and crap shot out the edges along the ceiling. Once he finished that he removed the filter and “swept” out anything at the bottom of the return with his hand into the 8” hose.
How exactly do you expect to kill or remove mold without it ? You can’t even clean your hvac systems coils without moisture of some type ,if you use a steam cleaner you can literally clean the whole system minus the electronics . You should do more research and possibly talk to people who do the work before posting , but don’t listen to me i only have a class A contractor license ,epa license , install /repair hvacs , rent and flip houses for a living .
An EER certifies the cooling efficiency of HVAC units. It's calculated by the rate of the cooling in British thermal units (Btus) per hour and divided by the rate of energy input in watts at a specific temperature. The calculation goes as BtuH/WATT at dry bulb (db) versus wet bulb (wb) temperatures. The optimal rating for a cooling unit is about 80db/67wb inside and 95db/75wb outside.
Although most new homes have ducts and vents already in place, many older homes have old convection heating systems or baseboard heaters without ductwork. In such cases, you will need to install ducts and vents to provide the air conditioning with a flow system. This would be the time to explore upgrading the existing heating system as well, as it will be much cheaper to do together.
Heaters exist for various types of fuel, including solid fuels, liquids, and gases. Another type of heat source is electricity, normally heating ribbons composed of high resistance wire (see Nichrome). This principle is also used for baseboard heaters and portable heaters. Electrical heaters are often used as backup or supplemental heat for heat pump systems.

Did you know that cleaning your ducts and vents can help airflow and increase energy efficiency? According to the Environmental Protection Agency (EPA), keeping your air ducts and vents clear can increase energy efficiency and indoor air quality. While the cost to clean ducts and vents might sound high, the benefits to homeowners–especially those sensitive to allergens–is worth considering.
The HVAC industry is a worldwide enterprise, with roles including operation and maintenance, system design and construction, equipment manufacturing and sales, and in education and research. The HVAC industry was historically regulated by the manufacturers of HVAC equipment, but regulating and standards organizations such as HARDI, ASHRAE, SMACNA, ACCA, Uniform Mechanical Code, International Mechanical Code, and AMCA have been established to support the industry and encourage high standards and achievement.
DIY: We don’t recommend a DIY approach. Depending on the system, working with gas, electricity and refrigerant create dangers. Beyond that, it is essential that split system components be selected for compatibility. DIY installation of an HVAC system will void the warranty of most brands. The manufacturers won’t stand behind the warranty when anyone other than a certified installer does the work. This is true since improper installation is the main cause of poor system performance and mechanical breakdowns.

The answer to your question is most likely "Yes," but not defiitely. It depends on where the dust is coming from. Now, if your house is more than say, 12 years old then you likely do have leaks in your ducts that can let in insulation particles and dust from your attic. If this is the case then cleaning of the ducts-PROPER CLEANING, which like the article sas doess include EVERYTHING that the conditioned air passes through, such as your indoor evaporator coil and blower housing assembly-is definitely a good first step to getting that dust under control! Of course I highly recommend that you also have your ducts SEALED as well, or else you will have to repeat the cleaning some time down the line. As a 3rd step, consider an electronic air filter. I always thought they were a scam, personally, so I never bothered selling them to my clients. Then one day my manager sent me to install one for a senior couple in a mobile home. The wife had bad allergies, and her eyes were constantly watering and puffy and red. Well, I did a quality check 60 days later and she could not stop praising that air filter! Keep in mind that in a mobile home, duct seals are not as complete as those in other homes due to access issues.

Do you live in a historic home and want to tie your new system in to work with existing features? The price will go up to do the job right. All of these things add up to slow down the HVAC company, which takes more time, which costs more money for labor and parts. This is especially true if they are a legitimate company which is licensed, bonded and insured. Simply put, this is the “X-Factor” in your HVAC installation cost. Again, you could get people to do it for cheaper…but you won’t be happy with the results, I promise.

I'd have to disagree with all of your statements. Not only are they derived from no experience in the field, you are missing keys facts. Ducts even if air tight will get dirty. If they are not getting dirty, it means they are not working. Your returns side of the duct work is always under negative pressure when the system is operational.Therefore it is always drawing air in. Seeing how dust is made up mostly from dead skin humans shed daily. Around 1.6 Pounds of skin a year per human. Living in your home anything that is air born will be drawn back towards the cold air returns. That is what they are designed for, to draw stale air back to the system to be filtered and sent back through the house.Homes with carpet will actually have cleaner duct work than home with all tile or hardwood. This is because carpets hold onto dust particles and you vacuum them up. Whereas on hardwood or tile, dust can run freely back to the returns. Even if a duct system was sealed 100%, which is next to impossible to achieve 100% would still need to be cleaned. The cleaning may only have to be every 7-10 years for example. Most homes require every 5-7 years. And that's if it was done properly the first time. If you constantly hire people that have no or minimal knowledge of duct cleaning, You home would require cleaning more often. Every 2 years. That's a trade secret, The longer they recommend before the next cleaning, the odds are they did it right. That's not to say there aren't people that lie, because there are. Just have your duct cleaner take pictures before and after cleaning. Not just an outside view. Get in there, picture entire joist liners, Whole main runs and even long round pipes. Also it helps to have a company that guarantees their work. If it's not done right, they will come back and do it until it is. Most companies that do this make sure it is right the first time. Your not getting paid to do the job twice.
Moisture can enter the duct system through leaks or if the system has been improperly installed or serviced. Research suggests that condensation (which occurs when a surface temperature is lower than the dew point temperature of the surrounding air) on or near cooling coils of air conditioning units is a major factor in moisture contamination of the system. The presence of condensation or high relative humidity is an important indicator of the potential for mold growth on any type of duct. Controlling moisture can often be difficult, but here are some steps you can take:
HVAC System Quality Installation Contractor Checklist -- This checklist identifies all of the steps the contractor has taken for the Energy Star Certification and identifies what work the contractor has done. If the system is later modified, this checklist can help identify what was done to proper Energy Star specifications and what was added later that may not meet the requirements.

Maybe I took him to literally but I am pretty sure cops wont show up to ensure that my duct gets replaced. He said it would be over 1000 dollars to replace the ductwork if that is the case. Now, I spoke to a friend who did 2 ductwork lines on his own in his attic and he said it was like 15 dollars for the plastic wirewound tubing to create new ducts. Should I cancel that appointment and just do the work on my own? I feel like I’m a chump or lazy for considering paying someone to do this work.

American design standards are legislated in the Uniform Mechanical Code or International Mechanical Code. In certain states, counties, or cities, either of these codes may be adopted and amended via various legislative processes. These codes are updated and published by the International Association of Plumbing and Mechanical Officials (IAPMO) or the International Code Council (ICC) respectively, on a 3-year code development cycle. Typically, local building permit departments are charged with enforcement of these standards on private and certain public properties.


The average cost of keeping your residential ductwork orderly is going to vary greatly from that of a commercial building. This is because commercial air ducts are often larger and more extensive. Residential cleanings can cost an average of about $20-$30 per vent. For commercial buildings, service providers must do an estimate of your space before they can provide an accurate quote. Before factoring in the materials and the number A/C and furnace units, you can expect a commercial project to cost at least $35-$50 per hour.
If your non metal ductwork is that dirty you should just have it replaced AND sealed. Also most duct systems are not very well designed. Look for proper sizing and do not go cheap with one or two intakes (return grills) You need them through-out the house. Here in Austin the duct cleaners are carpet cleaners and chimney swifts. (this is who the duct cleaning equipment mfgs call on when the hvac people do not get on board. They DO clean other types of ductwork and we (the hvac guys) have to fix them. I am not aware of any of these non hvac guys cleaning and servicing the actual equipment. Here in Texas it is against the law for them to do so. Treat the entire house as a system, not just the ductwork and /or hvac equipment. Home performance really does work to increase comfort and air quality while reducing operating costs.

American design standards are legislated in the Uniform Mechanical Code or International Mechanical Code. In certain states, counties, or cities, either of these codes may be adopted and amended via various legislative processes. These codes are updated and published by the International Association of Plumbing and Mechanical Officials (IAPMO) or the International Code Council (ICC) respectively, on a 3-year code development cycle. Typically, local building permit departments are charged with enforcement of these standards on private and certain public properties.


A BTU is the amount of energy required to heat or cool one pound of water by one degree Fahrenheit. So a 1-ton air conditioner can cool 12,000 pounds of water by one degree every hour. That’s all it means, so don’t let yourself be lost in jargon! How this affects your HVAC installation cost is that the larger your house is, the more tons will be required to heat and cool it.
Excalibur Water Systems helps solve the water challenges around the globe with water solutions for any possible water concerns in: water hardness, filtration of any contaminant, bacteria removal and high purity water needs and also comes with a warranty of up to 20 years at no extra cost. The best warranty for the water treatment equipment industry.
These factors are included in a "Manual J" calculation. Contractors who make these calculations before recommending a size can take a couple of hours collecting the information and making the calculation. If your contractor doesn't do it, there are services that will do it for around $99. If you're feeling particularly on the ball, there are also free online calculators.
DIY: We don’t recommend a DIY approach. Depending on the system, working with gas, electricity and refrigerant create dangers. Beyond that, it is essential that split system components be selected for compatibility. DIY installation of an HVAC system will void the warranty of most brands. The manufacturers won’t stand behind the warranty when anyone other than a certified installer does the work. This is true since improper installation is the main cause of poor system performance and mechanical breakdowns.

HVAC is an important part of residential structures such as single family homes, apartment buildings, hotels and senior living facilities, medium to large industrial and office buildings such as skyscrapers and hospitals, vehicles such as cars, trains, airplanes, ships and submarines, and in marine environments, where safe and healthy building conditions are regulated with respect to temperature and humidity, using fresh air from outdoors.
This is to Blueberry who.wrote.about home rental dust problems on 12/ 06/2016. If you’ve been there 13 years.your landlord has made enough money to have those problems repaired.I would call your city property standards dept. And let them know what.conditions you are having to live.There is no excuse for living in those conditions when most problems like that are easy fixes.Especially if your kids are getting sick. Tell your landlord your.calling City Health Inspector if he doesn’t fix.the problems.
An AC contactor is a $25 mechanical relay that uses low-voltage power from the thermostat to switch 220-volt high-amperage current to the compressor and condenser fan. AC contactors can wear out and are at the top of the list of common air conditioning service failures. Even if your AC contactor is working, it pays to replace it every five years or so. Unscrew the old AC contactor before removing the wires. Then move the wires to the new unit (Photo 6).
×