NADCA and EPA both have good points. Although, organizations are made to make money. Common sense and looking at NADCA and EPA pre-checklist. If you don't see it in the check list, you don't have to do it! But, if you do, look up Diamond certified co.s and the BBB. Beware of bait and switch scams, $60 vents and the like coupons which claim to help all for the measley sum of $79.00 bucks.
My Carrier furnace occasionally (one-two times a day) does not start. It shows error code 15 ("BLOWER MOTOR LOCKOUT -This status code indicates the blower failed to reach 250 RPM or the blower failed to communicate to the variable speed furnace control within 30 seconds after being turned ON in two successive heating cycles."). However, when I turn off and on the furnace power switch it starts and runs fine for a while. Sometimes it runs fine all day, but does not start only once in the evening or in the night. It is 13 years old I was thinking to replace whole thing if repair cost is too high. But I am not ready to pay $10,000. 

I’m really not convinced that duct cleaning is of any value. My roommate wanted the ducts cleaned so he called some company. My scam senses is already tingling. They came in with a big negative pressure fan. Did some blowing and sucking in different vents. Then they tried to upsell a full system cleaning. They wanted to pull the blower and clean the heat transfer box at $700 per heater unit. I have a big house so we have two units. They also tried to sell us some “custom” $250.00 Air Lifetime air filters. At that point I pulled the BS get the hell out bell. After paying $520.00 for just the cleaning, I paid the bill and sent them on their way. I replaced the existing filter with the good old and cheap paper filters at $10.00 each. Duct cleaning… I’m not Impressed.
Quality and price should come hand in hand, a too-good-to-be-true price for an efficient air duct cleaning will not give you the quality that you wanted. To make sure you are getting your money’s worth, check reviews of air duct cleaning companies, certifications from industry since this work requires continuous learning due to new techniques and research breakthrough from time to time. Make sure to shop around and get written estimates first.

The Environmental Protection Agency says that “duct cleaning services typically – but not always – range in cost from $450 to $1000 per heating and cooling system, depending on the services offered, the size of the system to be cleaned, system accessibility, climactic region, and level of contamination” and type of duct material. Consumers should beware of air duct cleaning companies that making sweeping claims about the health benefits of duct cleaning – such claims are unsubstantiated. Consumers should also beware of “blow-and-go” air duct cleaning companies. These companies often charge a nominal fee and do a poor job of cleaning the heating and cooling system. These companies may also persuade the consumer into unneeded services with and/or without their permission. (If you have knowledge of a practicing “blow-and-go” air duct cleaner, contact your local Better Business Bureau to report the company, and your local, federal, and state elected officials to demand legislation.)
If there is stuff in the ducts, the fact that it’s laying there and not being blown into the rooms is proof positive that it is hurting no-one. The 5-6 exceptions you cite in this article I’ll buy, but only with the caveat that at least some of those could have been avoided by proper protection (during remodeling for example) – and if asbestos/lead/whatever winds up in your ducts- the remodeling contractor should be the one paying to remove it.

Stick with a maximum of 16 SEER units in most cases.  Like I said above, contractors push higher SEER units because they make more money, but these units can be expensive at this stage of development, and can drive up your HVAC installation cost.  21 SEER units run about twice the price of a 14 SEER unit, so unless you live in a desert and plan on being there for 30 more years... Likewise, a 16 SEER unit typically costs only about $600-$1,000 more than a 14 SEER, and will usually pay for itself over the lifetime of the unit.

I know it has to have a new concentric venting system installed, I believe it needs new plenums ( mine are rusty but both of these require extra work , so someHVAC persons are saying I do not need either!! RED FLAG THERE. Also, it will need a new drain using PVCP ?? Piping run maybe two, depending on where my evep coil drain is conected (here in TN they use to run them in with the septic lines, now they cannot be run through that way), Lastly I am not where or what these things do beides hold water but I was told It needs a filter rack and new filter base safety pan. THATSSS it that is all I know about this stuff aside from the fact that nothing up there is to code thus far LOL. !!


Some of these components can be repaired or replaced by the homeowner, such as filters, fuses, and clogged up drain lines. Coils, compressors and the other components are best left to a professional. In some cases, you may have a system that is so old that parts are no longer available or else they aren't up to code. In this case you will have to consider replacing the entire system.
Internal insulation provides better acoustical (noise) control. Flexible duct is very low cost. These products are engineered specifically for use in ducts or as ducts themselves, and are tested in accordance with standards established by Underwriters Laboratories (UL), the American Society for Testing and Materials (ASTM), and the National Fire Protection Association (NFPA). Many insulated duct systems have operated for years without supporting significant mold growth. Keeping them reasonably clean and dry is generally adequate. However, there is substantial debate about whether porous insulation materials (e.g., fiber glass) are more prone to microbial contamination than bare sheet metal ducts. If enough dirt and moisture are permitted to enter the duct system, there may be no significant difference in the rate or extent of microbial growth in internally lined or bare sheet metal ducts. However, treatment of mold contamination on bare sheet metal is much easier. Cleaning and treatment with an EPA-registered biocide are possible. Once fiberglass duct liner is contaminated with mold, cleaning is not sufficient to prevent re-growth and there are no EPA-registered biocides for the treatment of porous duct materials. EPA, NADCA and NAIMA all recommend the replacement of wet or moldy fiber glass duct material.
All of you have dentists, you have doctors, you have preachers, you have mechanics. You don’t have to know everything about everything but you have to have people in your life that you can trust. Don’t just open up the phone book and pick a mechanical (HVAC) contractor. Call your friends and family and ask for referrals. There are no black and white (scam or not a scam) answers here.
 The A/C System Cleaning and restoration industry has become a very lucrative bait and switch industry that many Carpet cleaning companies, Maid services, as well as plumbing or handyman service companies are adding on to there services. These add-ons are not fully certified, trained or even have any experience in the HVAC industry. These companies are the reason prices and quality of work are all over the place. If you are looking to make a smart decision for your home a professional Duct Cleaning service will protect you for 5-7 years. This info comes from NADCA (National Air Duct Cleaning Association) which is the closest thing to a license we have for duct cleaning. They have a great site that explains this process and pricing much more in depth and factual than what has been written here. This organization is working very hard to get these bad companies exposed and out of this industry. So in saying that do your research! Green Duct Decontamination is a certified company with certified technicians that take this work very seriously. We can not have these low rated unprofessional companies paste a bad name for an entire industry. Stay away from anything under 250$ for a full duct clean this is not feasible, go look at NADCA.com and you will understand why and what these companies are doing to rob you of your dollar.
I had someone out to clean my ducts last weekend. He took a blue bag up in my attic. He came back down in just a few minutes and said I had mold and he even showed me a picture of something saying it was mold but I couldn’t really tell. I refused his service to take care of the mold. He went back up in the attic for a little while and then came down. I never heard any sounds that he was actually up there doing anything. How do I know if he actually cleaned the air ducts?
HVAC services is our go to contractor when it comes to our HVAC needs. Back in 2013, we were dealt some unforeseeable home projects, as our  HVAC was failing and needed to replace the whole system, e.g. Furnace, Blower, A/C, Condenser, Vents, etc... We reached out to a few HVAC companies (Contra Costa Heating and Air, EP builders, High Performance Heating and Air) so we could compare the bids for the job. We have had some issues with past contractors and after thoroughly screening a few of the above mentioned HVAC contractors, we awarded the bid to HVAC services because of their superior customer service and very reasonable pricing.
Preventing against air leakage is great, but the only way to keep dust and debris out of a duct system would be to completely seal off the return-air side of the system, which would render the system useless. Cold-air returns will always pull dust and other particles into the system. A high-MERV rated filter is definitely a good idea, but it does nothing to keep the return side of the system clean. Definitely agree though to use foil tape to seal seams, etc. Duct tape dries out over time and as it does can actually add more particles to the air.

I was with you until you said avoid steaming cleaning or moisture, there is no way you can remove mold or any other type of biological without moisture. The best way to do this is in fact with a steamer using a commercial disinfectant and a non reactive odor remover so your home smells refreshed and not like a hospital . This is directly contradictory to your article.
Installation: Replacement is quite easy, especially when an old refrigerant line set can be used. If the set is worn, it’s much better to pay the extra $400-$600 to replace it rather than risking it leaking later. When your AC loses refrigerant, you lose your cool air and the compressor is at risk of failing. A new installation means installing a coil in your furnace or air handler, running the line set between it and the coil in the condensing unit and adding refrigerant, if needed. Most ACs come pre-charged for 20-30 feet of line. If the line set is longer, a small amount of refrigerant is added.
Having the most energy-efficient system ever built won't matter much if it's not maintained. Lack of maintenance is the number one killer of HVAC systems. Before each cooling season, it's recommended that your system get a professional tune-up. However, there are things you can do in the meantime to make sure your system runs efficiently throughout the year.
Simply living in your home creates dust and dirt. Have you ever seen dust floating in the air in your home when the sun shines in?  Dust, dirt, pet dander, mold spores, and allergens get pulled into the air handling system in your home. They build up in the ductwork; some of it gets recirculated back into your home, and some of it can be captured by a good quality air filter. Eventually, enough debris builds up to the point where most of it blows back into your home. Your furnace or air conditioner must run longer to cool or heat your home, which costs you more in utility bills. With a service call from Sears Air Duct Cleaning, you can feel comfortable knowing that the accumulation of dust, dirt, dander, mold, and allergens has been cleaned from your HVAC duct system.
The Chartered Institution of Building Services Engineers is a body that covers the essential Service (systems architecture) that allow buildings to operate. It includes the electrotechnical, heating, ventilating, air conditioning, refrigeration and plumbing industries. To train as a building services engineer, the academic requirements are GCSEs (A-C) / Standard Grades (1-3) in Maths and Science, which are important in measurements, planning and theory. Employers will often want a degree in a branch of engineering, such as building environment engineering, electrical engineering or mechanical engineering. To become a full member of CIBSE, and so also to be registered by the Engineering Council UK as a chartered engineer, engineers must also attain an Honours Degree and a master's degree in a relevant engineering subject.
Wiring up the thermostat is usually pretty straightforward if an old one is being replaced. If a thermostat is being put in where one had never been before, that could involve running new wiring. The placement of the thermostat is also important so that its sensors can get an accurate reading of the temperature. A thermostat that is blocked by a bookcase or other large furniture will not get a good reading and will not perform efficiently.
AC installation in Fort Smith, AR is vital to comfort, safety, and quality of life. The region is infamous for the unbearable heat that can often become debilitating. This is why investing into an AC to improve the overall lifestyle of your family is well worth the cost. Avoid the constant frustration by seeking the assistance of a professional team.
Here in Atlanta we get 6 to 10 $49 coupons in the mail weekly…I have always consider them a complete scam….just had my master bathroom& bedroom and guest bath completely remodeled down to the studs…Had my 3 returns nearest the area sealed to prevent sheet rock dust to spread…it worked and I personally cleaned all 7 returns when a 5 HP , new Rigid shop Vac($99 from HD)…took one hour and I found little evidence that “I need my ducts cleaned” Had quotes from $400 to $600…I use the best air filters for my air handler and change it every 2 to 3 months…..any dust is trapped in it and I believe the Air Duct folks are all cons….
Had duct cleaned (apartment) however, dust is still settling throughout the apartment. Contractor said no other cleaning necessary until two (2) years. Is there a time period before dust no longer settles prior to that time? Should the vendor had worn a mask? He did not cover his face the vents and dust was blown throughout the apartment (had family help with the cleanup). I had to leave when they left because I have asthma and I couldn’t breathe without coughing. Please help!
While a lot of people understand the consequences of AC problems throughout the summer, the summer comes with its own set of unique issues that require a call to the plumber, too. Whether it’s a malfunctioning sprinkler system or a sewer line backup, Service Experts can help. We’ve encountered it all, and you won’t have to worry about any of it with our 24/7/365 Emergency Plumbing Service. When you need a plumber, we are here for you. And, just like all of our other services and products, any plumbing repair or work completed by Service Experts is backed by the same 100% Satisfaction Guarantee*.
1/27/2015Jim, we are committed to 100% satisfaction so every customer is very important to us.  Unfortunately, with all companies, there will be times when a customer may feel they have been let down.  If that happens with us, we certainly want to hear from you.  To better address your concerns, please contact Steve, our Customer Relations Specialist, directly by email at steve@hvacserviceinc.net... or give him a call at 925-318-4795. Hopefully we will hear from you soon so that we can promptly understand your issue and address the issue! Thanks Jim
Air duct cleaning service providers may tell you that they need to apply a chemical biocide to the inside of your ducts to kill bacteria (germs) and fungi (mold), and prevent future biological growth. Some duct cleaning service providers may propose to introduce ozone to kill biological contaminants. Ozone is a highly reactive gas that is regulated in the outside air as a lung irritant. However, there remains considerable controversy over the necessity and wisdom of introducing chemical biocides or ozone into the duct work.

While you consider having your air ducts cleaned, it is a good idea to take a look at your dryer vent. If your dryer vent is clogged, you could be losing energy efficiency. Worse yet, you could be increasing the risk of a house fire. Having your dryer vent professionally cared for costs about $130 on average, and could save you a bit of money and a lot of headaches in the future. For more information on the benefits and cost of having your dryer vent cleaned, take a look at our comprehensive cost guide.
Reinstall the access panel and disconnect block. Turn on the circuit breaker and furnace switch. Then set the thermostat to a lower temperature and wait for the AC to start (see “Be Patient at Startup,” below). The compressor should run and the condenser fan should spin. If the compressor starts but the fan doesn't, the fan motor is most likely shot. Shut off the power and remove the screws around the condenser cover. Lift the cover and remove the fan blade and motor (Photo 7). Reinstall the blade and secure the cover. Then repower the unit and see if the fan starts. If it doesn't, you've given it your best shot—it's time to call a pro.
×