Contact/Relay -- Relays are electronically controlled switches that activate the various components of your HVAC system. They manage everything from the power going to the motor to automatic dampers, humidifiers, etc. Most of them are controlled by the thermostat. The most common failure for a relay is being stuck in the "open" position. Separated from its assigned contact point, it fails to complete the connection and send the message to whatever it was supposed to operate. This failure usually occurs from use over time. Each time a relay connects and sends its signal, the electrical arcing from point to point eventually causes wear and tear.
You can install the greatest HVAC system ever built, but if your house is not insulated well, it's only going to end up costing you more money. Older homes may have fiberglass insulation that has broken down due to pests, moisture, or improper installation. Spray foam insulation can be damaged by careless repair or modification work or can be improperly installed. If your insulation in compromised, your attempts to save money and be comfortable will be in vain.
Many disconnect blocks contain two cartridge fuses. Check them before you proceed with repairs (Photo 3). A blown fuse is a sign of a failing part inside the condensing unit. So don't just replace it and think you've solved the problem. Instead, replace the parts we show here. Then install new fuses and fire up the unit. If it blows again, call a pro—you've got more serious issues.
I have been a plumbing/gas/hvac tech for 19 years, before that I installed ductwork in commercial buildings and office towers. As the article states, unless you have undergone some type of extensive reno, or ducts have become contaminated, paying for cleaning is pointless. Its one thing if you have a 30 year old home that has never had a duct cleaning and you can actually see mounds of dust built up , especially in the return side, then go for it. Keep in mind that most duct cleaning companies will only get 80% of the dust , or less at best. Keep in mind that most of the dust in your home is lint from clothes and linens, and skin cells from you and your pets and is constantly being generated. Dust that builds up in ductwork , generally stays in the ductwork. The power of suggestion, scare tactics, up sell!!!

Within the construction sector, it is the job of the building services engineer to design and oversee the installation and maintenance of the essential services such as gas, electricity, water, heating and lighting, as well as many others. These all help to make buildings comfortable and healthy places to live and work in. Building Services is part of a sector that has over 51,000 businesses and employs represents 2%-3% of the GDP.


Ok what you said is true but in most cases ducts are in a duct flex format, and knowing that the dust in people's flex duct is just surface dust, any real debris that are in the duct itself will result in very little to no air flow which will keep your unit from performing properly, but if it is true allergy reasons then replacing your duct system is better for overall better air quality, plus if you do pay attention to the warranty on flexible duct is that it only has a 10 year warranty and typically only lasts for 20 years so do your research before having a duct cleaning, and to add one more thing if your duct work is completely metal and you can't see visible insulation then your duct on the inside has insulation inside of it, if you replace that with duct work that is clean metal on the inside and wrapped with insulation on the outside then it will further reduce the air bourne fiberglass and dust.
The key to the continued and efficient operation of your heating and cooling system is periodic maintenance. Cleaning the air duct vent system, and servicing you heating and cooling equipment will keep the system operating at its peak performance. Air ducts are cleaned for two reasons. One: to prevent debris from entering furnace and air conditioning components. Two: to prevent debris from cycling through the home. The air duct cleaning contractor needs to employ cleaning methods which successfully removes debris, and ensures that debris does not enter the occupied space. Most contractors can verify the results of the cleaning through video or pictures.

My point is that the brand of equipment you choose is going to affect your HVAC installation cost greatly. People often call us for an air conditioning installation job and say, “I would like to install Carrier equipment.” Now, if you are a future client of ours, I’ll have to warn you – I can be a bit of a smart-ass. Why can’t work be fun? Besides…I was in the Navy for 11 years, what do you expect. 
The sky is the limit. I am a big fan of adding zoning systems, but realize that this will typically add $2,300 to $3,500 (or more) to the price. “Why a price range, isn’t it just a part?” No, the part then has to be installed, and the customized ductwork required will vary based on the difficulty of the job and layout of your attic. It is very labor intensive, and most people don’t do it right. It should also include a bypass damper and ductwork! Simply put, the more you add, the more it will affect your HVAC installation cost.
We hope you found this article on a fair HVAC installation cost helpful. In the end, you’ll be alright so don’t worry too much. Do your research on reputable air conditioning contractors in your area, and spend time making sure that you have a company that you can trust – it will cost you less in the long-run, trust me. Take your time, follow the tips above, and you will end up with an HVAC installation cost that is more than reasonable, keeping your family comfortable for years to come. For more on topics like this, see: ASM’s Air Conditioning Blog.
Pro Tips: Before you buy one of the learning thermostats available, you should beware of their shortcomings. First, many require a c-wire to work properly. A common problem is that the old thermostat might not use a c-wire, and this makes it confusing when swapping wires to the new thermostat. Secondly, if you change your thermostat setting often, you might become frustrated with a nest thermostat or other learning thermostat. It will be constantly trying to learn patterns in your random setting changes, and will therefore change your home’s temperature when you don’t want it to. If you have a fairly consistent schedule or don’t mind overriding the unit either manually or via the app on your way home or when leaving, then you won’t experience this issue.

I originally took off one star because of the SNAFU with getting the part ordered.  When Alberto called me on the phone he admitted the person had "gotten busy with other things" and apologized.  THAT was taking the high road and I was impressed by that.  Sadly, for reasons I won't guess at, Alberto has decided to take the low road in his comments and imply that they got the part as quickly as possible.  Well, we called at 2:30 so did someone spend six and a half hours finding the part??  That seems very doubtful.
An air conditioner's compressor contains a refrigerant. As it works, it sends this refrigerant through the system. As warm air blows across the coil that carries this refrigerant, the heat transfers to the refrigerant (cool always absorbs warm). A fan moves the cooled air through the ducting and out of vents that lead into the rooms of your house. The refrigerant returns to the compressor where the absorbed heat is moved outside. The refrigerant is then sent through the coil once again to continue the cycle.
Duct cleaning has never been shown to actually prevent health problems. Neither do studies conclusively demonstrate that particle (e.g., dust) levels in homes increase because of dirty air ducts. This is because much of the dirt in air ducts adheres to duct surfaces and does not necessarily enter the living space. It is important to keep in mind that dirty air ducts are only one of many possible sources of particles that are present in homes. Pollutants that enter the home both from outdoors and indoor activities such as cooking, cleaning, smoking, or just moving around can cause greater exposure to contaminants than dirty air ducts. Moreover, there is no evidence that a light amount of household dust or other particulate matter in air ducts poses any risk to your health.
Quality and price should come hand in hand, a too-good-to-be-true price for an efficient air duct cleaning will not give you the quality that you wanted. To make sure you are getting your money’s worth, check reviews of air duct cleaning companies, certifications from industry since this work requires continuous learning due to new techniques and research breakthrough from time to time. My mom is located in Arizona and they trust J&M Restoration air duct cleaning company, they have an A+ BBB rating, they used EPA approved sanitizing agents, their technicians are NADCA certified, and the company is certified by the Institute of Inspection, cleaning and Restoration. Make sure to shop around and get written estimates first.
And if you have flex duct and/or fiberglass ductboard in your home- the last thing you want is a big brush or anything abrasive running through it. Even high-pressure air can erode ductboard so I wouldn’t clean it with anything. If it becomes contaminated, get rid of it and install real ductwork. If your ductwork is accessible in the basement – the best thing to do is take it down and manually clean it if it’s full of junk. It’s not going to cost a nickel more to do that than to pay $500-1000 for a ‘duct cleaning machine” AKA big blower and vacuum – to do the job.
This article was very good. It should be noted that the EPA building in Washington, DC, was cited years ago as one of the worst "sick building syndrome" buildings. Wish you had mentioned about having people's dryer vents cleaned since they can cause so many fires in homes. Most homeowners forget to check the air flow on the dryer vent. Our company, which cleans by NADCA standards, does both air ducts and dryer vents. Thanks again for keeping the public informed, especially regarding the cost of air duct cleaning...you get what you pay for...don't be fooled by the lowest cost out there. Frequently these are bait and switch companies or will keep adding on features they say a customer needs until the price is so high it's ridiculous.
Feel perfectly comfortable at home with our innovative Lennox Residential heating, cooling and air quality systems. Lennox manufactures high-efficiency HVAC systems including furnaces and air conditioners designed to conserve energy and save money. Our complementing air filtration systems, humidifiers and dehumidifiers help keep indoor air quality healthy and clean.
I'm very glad that I found another guy to come replace the circuit board and put it away from the water, fix the water leak, and also find and fix another impending failure.  All of that was for much less than HVAC Service wanted to charge for repair or replacement. The other guy did a great repair, so I'm confident it will not break down again, but if it does, I will not call HVAC Service. Don't get suckered by their Yelp Deal.
Hi guys if your not convinced yet that duct cleaning is a waste of time. I’m a HVAC business owner install heaters and air conditioners. Simple facts if you have an old system get a new return air fitted with a filter it will catch all the dirt and dust. If you still have as many do black flecks and stuff coming through it is the lining inside your ducting that has perished. So somewhere you have a hole or very old ducting. If you had rats etc its a hole somewhere. To clean, stick your vacuum in the outlet and push the hose as far as it will go this gets 99% of toys and coins fur and alike. Think about it if the object is not heavy it will come out the duct when unit is on. Service the heaters or air con units but not the ducting. I would go further to say that duct cleaning actually damages the ducting in my opinion.
If you believe that the AC's not working or you're getting little or no cold air, check these three things first. Make sure all the registers in the house are wide open. Then be sure the furnace filter is clean. Then go outside and clean off the condenser coils (Photo 2). If several registers were closed or the filter was clogged, the reduced airflow could have caused the evaporator coil to ice up and stop cooling your home. If you've changed the filter and opened all the registers and you're still not getting airflow at the registers, deice the A-coil. Move the thermostat mode switch from “Cooling” to “Off” and move the fan switch from “Auto” to “On.” Let the blower run for at least 30 minutes or until there's good airflow at the registers. Then turn the AC back on to test it. If it works for the next 12 hours, you've solved the problem.
×