The most recognized standards for HVAC design are based on ASHRAE data. The most general of four volumes of the ASHRAE Handbook is Fundamentals; it includes heating and cooling calculations. Each volume of the ASHRAE Handbook is updated every four years. The design professional must consult ASHRAE data for the standards of design and care as the typical building codes provide little to no information on HVAC design practices; codes such as the UMC and IMC do include much detail on installation requirements, however. Other useful reference materials include items from SMACNA, ACGIH, and technical trade journals.
While you consider having your air ducts cleaned, it is a good idea to take a look at your dryer vent. If your dryer vent is clogged, you could be losing energy efficiency. Worse yet, you could be increasing the risk of a house fire. Having your dryer vent professionally cared for costs about $130 on average, and could save you a bit of money and a lot of headaches in the future. For more information on the benefits and cost of having your dryer vent cleaned, take a look at our comprehensive cost guide.
There are many interesting comments from several informed individuals. The question that has not been answered is how do duct systems get dusty and dirty? As a RESNET Home Energy Rater, I perform pressure tests on homes and duct systems, and the one common thread is . . . most air delivery sytems have large amounts of air leakage. The solution is to seal the duct system, and pay particular attention to the return duct system and ductwork near the air handler (the 'blower'). As others have said, a captive (sealed) duct system with proper filter maintenance should be more then adequate for most occupants. For those who have allergy, asthma, or other breathing problems, a filter with a higher MERV rating (number should be listed on the package) or a HEPA filter are good choices. These filters will capture smaller particulates and should improve the indoor air quality. Again, make certain that the entire duct system is sealed, preferably with mastic, second choice UL-181 foil tape - never use cloth duct (also known as duck) tape.

Maybe I took him to literally but I am pretty sure cops wont show up to ensure that my duct gets replaced. He said it would be over 1000 dollars to replace the ductwork if that is the case. Now, I spoke to a friend who did 2 ductwork lines on his own in his attic and he said it was like 15 dollars for the plastic wirewound tubing to create new ducts. Should I cancel that appointment and just do the work on my own? I feel like I’m a chump or lazy for considering paying someone to do this work.
Here in Frisco, TX…just had a tech come out to clean vents. I used a 30 bucks groupon for “complete vent cleaning”. He told me I have 3 AC units and groupon covers only 1. I told him to do the unit upstairs where the kids sleep. He decided on his own to do the downstairs unit. I yelled at him why he is not doing the unit I told him to do! He said they are all connected. I will clean two for you for the price of one… Oh really?
Some of the research I have done suggests to have your ducts cleaned when you first purchase a new home to remove drywall dust. Maintain your system well and you shouldn't have to do it again until you want to sell. Those are the two times cleaning was suggested. So for peace of mind maybe it is a good idea to do it even if you buy a used home and then maybe every 5-10 years.
The short answer is yes, duct cleaning, done right by a reputable company will help with the smell. It is likely though the smell is coming from another source, ie the crawl space. It could also be that another rodent is dead in the duct work. A visual inspection would be in order to check for any breach in the duct system. A duct pressure test would be able to tell you how much air is leaking from the system over all. A hole large enough for an animal to enter would loses a great deal of air, over 300 CFM. It would be worth looking into having this test done and it should cost around $200. Cleaning the air handler and evaporator coil will greatly improve the performance of the air conditioner. Dirt and dust on the evaporator acts as insulation and reduces the amount of cooling done be the coil. Any quality duct cleaning should include cleaning the air handler and coil, and the tech should allow you to watch him perform the work as it is done.
Air conditioning and refrigeration are provided through the removal of heat. Heat can be removed through radiation, convection, or conduction. Refrigeration conduction media such as water, air, ice, and chemicals are referred to as refrigerants. A refrigerant is employed either in a heat pump system in which a compressor is used to drive thermodynamic refrigeration cycle, or in a free cooling system which uses pumps to circulate a cool refrigerant (typically water or a glycol mix).
Yes everyone should get all their ductwork cleaned, because it does help, incame down with major allergies and had serval operations on my sinues because of this problem of air quality and dust, plus i almost died from one of the operations, i was suffering so much. Yes you can seal your duct system by buyind duct seal t instead of tape to tape all the corners of the vent system, tape wears out and gets brittle, the sealant you can buy at home depot, and you just brush it all over the connections of your ductwork, it comes in a container and it is like a thick paste and dries making a good seal for your ductwork.

I to had an odd layer of white'ish dust building up especially during seasonal periods when the HVAC ran a a lot. I carefully swept up the fine dust into a small pile and had it analyzed. Turns out it was very fine fiberglass powder dust. It turns out it is the insulation form the attic! (My attic has blown in insulation). Turns out if you (I) had small gaps around my HVAC registers in the ceiling whee the airs blows into the room. What occurred in my case was that the exiting air at that seam creates a vacuum effect at the grate vent cover and draws and then blows fine insulation dust from the attic into the house. Removing each register grate and sealing each tin outlet gap with calking between the dry wall ceiling and tin fixed the issue. A couple were so bad with bowed gaps I had to screw down the bowed tin to the attaching stud better. Checking the very same glass top desk that catches and shows any dust accumulation now shows only very small amounts of normal house dust build up over several weeks. A big, big improvement. You might have a look by simply removing a couple vent covers yourself.


Many central air conditioning systems use the furnace blower to distribute cool air through the home. If you do not have a central heating system installed, it is cost-effective to install a heating and air conditioning system at the same time. If you already have central heat, you can use the existing fans and duct system for the central air system.
They work less jobs, thus increasing profits – think about it…if they got only half of the jobs, then they only pay half of the money required to pay employees, expenses, etc., but still have the same amount of net profit. In fact, if you do the math, they actually make more profit that their competitors do…twice as much, once you factor in their savings form only doing half of the jobs at the same amount of profit (Total Revenue – (half the normal expenses) = twice the profit). In other words, they save money by doing half of the jobs as others, for the same profit, thus increasing their overall profits.

Mitsubishi Electric is a world leader in air conditioning systems for residential, commercial and industrial use. Challenged to create air conditioning systems that provide exemplary performance in the wide-ranging climatic conditions found throughout Japan, our engineers develop amazingly sophisticated yet durable units and systems capable of constant use under virtually any natural climatic condition on earth.
On the other hand, if family members are experiencing unusual or unexplained symptoms or illnesses that you think might be related to your home environment, you should discuss the situation with your doctor. EPA has published the following publications for guidance on identifying possible indoor air quality problems and ways to prevent or fix them.
1). Busy companies: The company is so busy, it doesn’t need the work. It will add 70% to 100% profit, and if the customer accepts the estimate, it will move that high-margin customer to the front of the line. This often happens in the worst heat of summer when overburdened ACs and heat pumps quit and the dead of winter when furnaces give up. This is a good reason to consider pre-emptively replacing your system once it’s about 15 years old and/or has had major repairs.

Within the construction sector, it is the job of the building services engineer to design and oversee the installation and maintenance of the essential services such as gas, electricity, water, heating and lighting, as well as many others. These all help to make buildings comfortable and healthy places to live and work in. Building Services is part of a sector that has over 51,000 businesses and employs represents 2%-3% of the GDP.
If you’re purchasing from a big-box store, you can expect to pay approximately $120-$1,000 for a window unit. Window units are appealing for their quick setup and relatively low cost, but they can use more energy over time than central air and only cool the room in which they’re installed. The price will vary depending on the type of air conditioner you buy and its cooling capacity. Window units, which require minimal installation, are one of the most affordable options on the market. Portable air conditioners don’t have the cooling power of a window unit, but they do have the perk of being transportable from room to room. Expect to pay between $225 and $800 for a portable air conditioner, on average. The cost of an air conditioning system with coils, condenser and line (not including installation or ductwork) can range from approximately $2,000 to $4,000 or more. If you don’t have (and don’t want to put in) ducts, a ductless mini-split air conditioner is a good option, although pricey up front. Pricing can range from $650 to $4,250 per unit on average; you’ll need one unit for each room in which you want temperature control.
The original furnace was a coal fired “octopus” design which had no blower to circulate the air but relied upon warm air rising to distribute the heat. That also means that the system breathed air in from the basement and most of this type did not have a cold air return system. At some point (probably in the 1940’s) the system was upgraded to a forced air gas furnace. The upgrade included replacing the 12″ diameter air ducts exposed in the basement with 6″ ducts and a cold air return system of ducts from the two (only two) air returns on the first floor.
I had my ducts somewhat cleaned December 22, 2014. The hose of the machine the technitian used did not fit in some of my vents, therefore, he did not clean them. But I still paid $428.00 for the service. I will be calling the company on Monday, and kindly ask them to come back and clean the ducts they did not as they did not fullfill their part of the service.
Although HVAC is executed in individual buildings or other enclosed spaces (like NORAD's underground headquarters), the equipment involved is in some cases an extension of a larger district heating (DH) or district cooling (DC) network, or a combined DHC network. In such cases, the operating and maintenance aspects are simplified and metering becomes necessary to bill for the energy that is consumed, and in some cases energy that is returned to the larger system. For example, at a given time one building may be utilizing chilled water for air conditioning and the warm water it returns may be used in another building for heating, or for the overall heating-portion of the DHC network (likely with energy added to boost the temperature).[4][5][6]
Our HVAC Ductwork Installation Cost Guide is the most comprehensive guide of its type. It fully explains the purpose of ductwork and all your options. Pricing is included for all duct types and plenums/drops too. Material and installation costs are listed. Ductwork cost varies greatly by the size and type of duct plus the complexity of the installation, but you can expect to pay $10.20 to $17.25 per linear foot installed.

I called a company name “GREEN RHVAC” with their $29.00 one system air duck cleaning. When the guy came with a truck I asked him to tell me how much he will charge and he said that if he gave me price and I didn’t want the service then he would charge me $89 or he would tell me how much he charge me after he finished the work. I immoderately sense that I made mistake to call him to my house. To cut my lost I asked him to give me the price and it was $1600 for two systems house. I paid $100 to him for my lesson to learn and search online to find this site is very helpfully and I should do it before to call anyone for air duck cleaning.
Window air conditioners cost less than central units, averaging $300. These systems generally suffice to keep a room cool on warm spring and summer days. They can bring added comfort for a reasonable price but are less powerful than a central air conditioner. If you have a bigger home with multiple rooms, you will probably need to have a larger system installed. Central air can cool several rooms at once, while window AC units usually only cover one or two rooms at a time.
Our Fort Smith, Arkansas area restoration services are available at your convenience. We provide emergency services after devastating property damage and work hard to restore and clean as much of the contents and structure as possible. We'll Work With You and Your Insurance Company to cover costs and expedite the process. If you need cleaning and restoration services or are looking for ways to create a healthier, more efficient environment, contact McMahon's Cleaning & Restoration, LLC to get started.
It's always changing: Some newer thermostats take advantage of wireless technology. You can adjust your thermostat remotely so that if you leave and forget to adjust it, or if you are going to be home later than you thought, you can adjust it via your smartphone. Some can even give you reports on how efficient your system is performing based on usage. These are very efficient models, but they are also very expensive with some costing over $250.00.

The most recognized standards for HVAC design are based on ASHRAE data. The most general of four volumes of the ASHRAE Handbook is Fundamentals; it includes heating and cooling calculations. Each volume of the ASHRAE Handbook is updated every four years. The design professional must consult ASHRAE data for the standards of design and care as the typical building codes provide little to no information on HVAC design practices; codes such as the UMC and IMC do include much detail on installation requirements, however. Other useful reference materials include items from SMACNA, ACGIH, and technical trade journals.
I replaced all the ducts but the trunks in my 1969 home when I replaced the horizontal furnace under the house with a gas pack. I got advice from a friend who was an HVAC contractor. I was surprised to find the trunks and other ducts very clean. I replaced the individual runs with flex primarily for the insulation. I wrapped the trunks with insulation also.
One of the best ways to know if your ducts or vents need to be cleaned is to just check them. Your eyes will be able to check for indications of mold, dust or pollen buildup. You might also be able to smell the presence of mold, which would be a clear indicator. Ductwork will have some buildup of dust, since the return registrars pull air back in. However, this doesn't mean your ducts have too much debris, and you can easily clean them with a duster or vacuum.
Our heater went out last Saturday, which was a cold day.  Called a few different places and they were the only ones that called back.  The technician Tony came out and after a little testing said the main control board needed to be replaced.  He quoted us a total of $489 which seemed on the high side but it was cold and we were somewhat desperate, so we agreed and paid a parts deposit.
Clean air delivery rate is the amount of clean air an air cleaner provides to a room or space. When determining CADR, the amount of airflow in a space is taken into account. For example, an air cleaner with a flow rate of 100 cfm (cubic feet per minute) and an efficiency of 50% has a CADR of 50 cfm. Along with CADR, filtration performance is very important when it comes to the air in our indoor environment. Filter performance depends on the size of the particle or fiber, the filter packing density and depth and also the air flow rate.[30]
Yes, ducts can look terribly dusty. However, that dust will not become aerosolized during the normal operation of your furnace. There is an easy way to test this. Rent a particle counter and test the air flowing out of your registers before and after cleaning. You will not see any improvement in the air quality or any reduction in the airborne dust level. Think of it this way. Duct cleaning companies tell you that you need to clean your ducts when you can see a layer of dust in your ducts. Yet that very layer of dust is proof that duct cleaning is unnecessary, because that dust proves that the air movement in your furnace is not fast enough to re-aerosolize the dust.
I agree, if you replace (or wash depending on type) your air filters regularly AND vaccum, then you probably don't need the ducts or air coils cleaned. However, if you purchase a pre-owned home, and the previous owners did not regularly change the air filter or vaccum the home, then duct cleaning is worth the expense especially if you are sensitive to allergens. Especially if the previous owners had pets.
I purchased one of those Amazon air duct cleaning coupons for 49.99. When the company showed up, they removed the vent closest to the air intake and immediately told me I needed $1800.00 for all new duct work. They said they could not clean the system until new duct work was installed. I thanked them and said I would give them a call. The only call I made was to Amazon to get a refund. I know I didn’t need new duct work. Be careful to not fall for unscrupulous salesmen and their pitches and scare tactics.
Interesting. Giuliano Cuete and Carlo Olcese have the exact same post about pretenders and being NADCA certified, word for word. So how do you become NADCA certified? And does that mean you are not a scam artist or a "blow and do" ripoff? hmmm, interesting. The EPA says that under normal conditions, a properly maintained system should NEVER need it's ducts cleaned.
Two weeks go by and no phone call from HVAC Service regarding install date, or any update at all.  I call them to check in to see if they have put me on the schedule and when I can expect to have the AC installed.    You can tell by the discussion I had with the lady on the phone that they completely forgot about me and have not scheduled anything.  She says she needs to get in contact with the owner because she has no idea on the availability of the crane.  I was told that she would call me back by the end of the day with an update.  Surprise, surprise, no phone call.  
The heat pump gained popularity in the 1950s in Japan and the United States.[13] Heat pumps can extract heat from various sources, such as environmental air, exhaust air from a building, or from the ground. Heat pumps transfer heat from outside the structure into the air inside. Initially, heat pump HVAC systems were only used in moderate climates, but with improvements in low temperature operation and reduced loads due to more efficient homes, they are increasing in popularity in cooler climates.
DIY: Most DIY installations go smoothly. The major brands have compatibility checkers to see which of their models will work with the wiring your old thermostat is using. Potential problems involve the need for a C-wire, or common wire, when the existing bundle doesn’t include one. There are solutions discussed in our Thermostat Buying Guide, linked to below.
You've probably noticed many appliances boasting an Energy Star Certification. What this means is that manufacturer voluntarily built the product to help reduce greenhouse gases and meet non-regulatory guidelines offered by the Environmental Protection Agency. To earn an Energy Star rating, a product or system must be tested by a third party that has been recognized by the EPA for meeting their testing qualifications.
fact is most homes have bad filter racks. when you insert the filter it doesn’t seal well to the sides so some of the air and dust bypass it and end up in the supply ductwork and into the house. Most of the dust in the supply ductwork settles down and doesn’t get blown in the house but some of it does when the blower starts up or when you put a new filter. If you have allergies or other health problems put in an electronic air cleaner, get your ducts cleaned and run the fan as much as you can afford. you can also get an ECM motor installed which is going to be worth it if you want to run the fan 24/7. If you have uninsulated metal ducts take down the ones you can and wash them. Then put them back and seal the joints. Cleaning the ductwork also improves airflow which is important to AC and Heat pump systems for efficiency. An electronic air cleaner will also improve airflow and static pressure because they usually have a much larger filter surface area. An electronic air cleaner also keeps the ac coil clean like new which means better efficiency and no cleaning needed. AC furnaces sometimes grow mold around the coil because of the condensation. Electronic air cleaners should be able to filter mold spores but the best remedy is installing a UV light next to the coil which will kill the mold.
The most effective way to clean air ducts and ventilation systems is to employ Source Removal methods of cleaning. This requires a contractor to place the system under negative pressure, through the use of a specialized, powerful vacuum. While the vacuum draws air through the system, devices are inserted into the ducts to dislodge any debris that might be stuck to interior surfaces. The debris can then travel down the ducts to the vacuum, which removes it from the system and the home.
Deciding if central air is worth the cost depends on your needs and local housing market. If you live in a hotter climate, it can definitely be worth the price. Not only can it keep your home at a comfortable temperature, but air conditioning can even save lives during extreme heat waves. But in a milder zone without severe temperatures, window units, fans or the breeze from an open window could be adequate.
We are all getting migraines several times a month. I have asthma but not ever as bad as it has been and my 2 year olds dr just informed me she potentially has asthma too. We all get sinus infections regularly and eczema and contact dermatitis. None of us have been this way until recently in our apartment. A roof leak with mold was repaired recently mold was sealed off not removed. We also had lead paint removed from a few window trims this year. I wasn’t here to see if they covered the vents. We had mice too. I vacuum everyday we have hardwood floors no one wears shoes past the font door and I’m getting over a cup full of dirt every time I vacuum. Dust on everything daily. White dust. It’s a 4 room apartment with 1 intake. They are filthy from what I can see when I change the filters. The filters are black after a few months. I feel bad to ask the homeowner to get the system cleaned, can’t afford to move (we live in the city & it’s expensive). I am going to try the shop vac to remove what I can. Any experienced hvac people please give your opinion. Should I just get it done and pay for it myself? We have lived here for 13 years. It’s never been cleaned since ive been here. Is it something I can do with a shop vac? Can i use a wet rag to get the powder dust on the inside of the vents off. One vent has what looks like chunks of dry wall or thick paint sitting in the vent and none of the vents screw into the wall, the screws just fall out. No one ever reinforced the area so the wall just basically crumbles. Kind of useless to spend the money on filters since the air and dust just blows out around the sides of the vents and one of the vents just falls right out of the wall when the heat is turned on. I don’t know why the owner doesn’t fix it. He’s been here to replace filters and saw the condition.
As for the price I think my review was fair in stating what value we got for what I deemed to be a slightly higher price than others might charge.  I did not take any stars off for the price, and still am not, but I am taking another star off because of Alberto's comments, which are deceptive and not the same thing he told me in person.  Alberto, I suggest you stick with the high road in the future.

As a person with severe mold allergies, I live in a the South where the climate naturally breeds molds.We noticed a difference when we had our ducts cleaned.The company used a vacumn type system and covered all of our vents with plastic that was held up by the suction. We had no damage, no leaking dust/dirt back into the house and it took several hours. I think if you use a reputable company it makes the world of difference. Now we use better air filters and also have a UV light to prevent mold growth on ours system.We 'd do it again when the time comes. From your car's air filter to your dryer...anything works more efficiently when it is not filthy dirty.That's just common sense.
From Day 1, Alberto walked us through the process, and present us with a variety of options based our budget for the project. His customer service is the best as he did not oversell any services and did not nudge us towards buying a unit that would stretch our budget. On installation day, HVAC Services sent out a crew of 6-7 guys, all of whom were very polite and kept their work areas clean, and installed the whole system the same day.
There is a lot of good, general information in the article. As with anything, the homeowner should do their due diligence in getting enough information to make an educated decision. Should duct-work be cleaned? YES! Does it need to be cleaned annually or even every second or third year? Not necessarily. It all depends on a bunch of variables. You're right that a well designed and balanced system will deliver the right amount of air flow, but sometimes conditions outside the home/business, make it a necessity to get the ducts cleaned. As for mold? NO filter is going to address a mold issue. If you have mold, you have a moisture issue that needs to be addressed. Also, in my 38 years of experience in the HVAC and sheet metal industries, washable filters are one of the reasons ducts need to be cleaned. They are no where near efficient in cleaning/filtering the air to the level that they should.
If the system is sealed air-tight and a really good filtering system is in place then you should NEVER have to clean your ductwork. Most dust people see in their homes (on beds furniture etc....) is broken down insulation that is being blown into the home from the attic (venturi effect) where the duct bucket (box etc...) is not sealed at the sheetrock ceiling. On the return side, ANY leaks in the ductwork will pull hot attic air and dust into the system, clogging up everything.
I agree that good filtration and a sealed system will prevent the need for duct cleaning. However, when we do get called it is because the duct work has reached a noticeable state of restriction or dust or the homeowner is hyper-sensitive to these pollutants in their home. Most of the time we find that no filter or a cheap (99 cent) filter is being used or they have serious duct leaks in the system. If you are hiring a cleaner make sure they are using professional cleaning equipment which will consist of a rotating brush system and a vacuum source. Be highly skeptical of the contractor with no branded system or the guy who shows up with just chimney brushes and a shop vac. He will not be able to reach around all the corners or all the runs in your system and he will be taking your money for a superficial cleaning at best. Only trust a company that offers VIDEO inspection and more importantly.... a contractor who repairs, installs and seals ducts if a problem is discovered or heaven forbid, created. Good luck and get your ducts sealed if you do have a leak! It is one of the greatest energy losses to a home other than being poorly insulated.

Hi guys if your not convinced yet that duct cleaning is a waste of time. I’m a HVAC business owner install heaters and air conditioners. Simple facts if you have an old system get a new return air fitted with a filter it will catch all the dirt and dust. If you still have as many do black flecks and stuff coming through it is the lining inside your ducting that has perished. So somewhere you have a hole or very old ducting. If you had rats etc its a hole somewhere. To clean, stick your vacuum in the outlet and push the hose as far as it will go this gets 99% of toys and coins fur and alike. Think about it if the object is not heavy it will come out the duct when unit is on. Service the heaters or air con units but not the ducting. I would go further to say that duct cleaning actually damages the ducting in my opinion.


We are a hvac company that provide air duct cleaning service are minimum charge $400 to do a proper air duct cleaning with 2 techs avg 3-6 hours that includes sanitizing. I get phone calls all day about the $99 your not going to get much of a cleaning for that price it for them to get there foot in the door and up sell that the only way for them to stay in business. Just from my 15 years of duct cleaning experience.
I own and live in a mobile home and was told to install a mobile home air condition well I did not want one because the ones for moblie homes are to small,so I install a home air-condidtion and its good for heating and cooling the only thing I do is change is the filter every month or two,What I want to know is how does dirt and dust comes from????
Clean the condenser fan blades before the start of the cooling season. Brush any dust or debris off gently and then uncover the condenser coils, gently cleaning the dirty side. Then wrap the motor and other electrical components in plastic bags and gently spray from the inside with a hose. Now check the base pan under the unit and clear it out of any debris that has gathered.
i got angies list deal for 109 air duct clenaing, dryer vent cleaning, and furnace inspection, {healthy duct cleaning} i call the company, they arrive on time. did excellent service what ever i purches i got. they give me furnace inspection and the told me that my furnace is very dirty and they offer me to clean that for 250 extra. i paid and i am very happy from this service. i try before 2 diffrent company that i got deal from them as well the just give me estimate and don’t even do the job. so guys don’t spend time if you need deep cleaning just cal this guy the offer free estimate as well.
Do you live in a historic home and want to tie your new system in to work with existing features? The price will go up to do the job right. All of these things add up to slow down the HVAC company, which takes more time, which costs more money for labor and parts. This is especially true if they are a legitimate company which is licensed, bonded and insured. Simply put, this is the “X-Factor” in your HVAC installation cost. Again, you could get people to do it for cheaper…but you won’t be happy with the results, I promise.
yes get a good company and pay the price, I found so much dust and dirt and wood and paint chips and bugs and even bottle caps in my ductwork. I hired a major plumbing company who cleaned ductwork and i will say they did an excellent job cleaning my vent. they did miss one point in my ductwork because i still started to see dust all over my furniture and i realized that my retunduct work that was connected with a piece of sheet metal beam which was 16" across , the contractor that built my condo used a 16" wide sheet of sheet metal to connect the vent system to my return for the air to return back into my condo. The contractor should have built a 8" x16" square duct by 6 feet long to connect my intake to my return instead of using a sheet of sheet metal 16" wide by using two 3' sections by 16 inches wide. That was a shor cut which caused a major problem fir me.
My best advice has always been that a proper duct cleaning is a valuable investment when moving into a home (new or old), after major renovations and if the ducts have never been cleaned before. It is unlikely that there will be increased air flow, as finding major blockage is unusual, but this will eliminate this as a possible concern if there are air flow concerns. It is also true that the "dust" that is cleared out will most likely never have been distributed through the house unless there has been some work done on the ducts. What is cleared out will be pet hair, toys, clothes, construction material, and biological material (small carcasses and/or feces). Once a proper cleaning is done a follow-up is rarely necessary, but up to the home owners discression.
I recently did some remodeling and figured I’d get the air ducts cleaned in our 12 year old home. After obtaining 4 estimates between $572 and a whopping $3,075 for 25 vents and 2 air handlers, I knew I was in for a ride. I read through this blog and decided to use a $79 inspection camera I just found online (Home Depot) to take a look at all my ducts by removing the ceiling grilles first and then try to get into the ducts from the other end. From what I have just learned here, I believe that will take care of my “concerns”.
Manufacturers of products marketed to coat and encapsulate duct surfaces claim that these sealants prevent dust and dirt particles inside air ducts from being released into the air. As with biocides, a sealant is often applied by spraying it into the operating duct system. Laboratory tests indicate that materials introduced in this manner tend not to completely coat the duct surface. Application of sealants may also affect the acoustical (noise) and fire retarding characteristics of fiber glass lined or constructed ducts and may invalidate the manufacturer's warranty.
×