Hi John, Thanks for reaching out, we would be happy to help you connect with a pro for your project. You can submit a request to our pros here: www.homeadvisor.com, browse a list of pros that serve your area here: http://www.homeadvisor.com/c.html, or send your info to emailus@homeadvisor.com and a project advisor will reach out to assist you. –HASupport
Furnace cleaners are mostly young men, I know this, I have been one for 15 years or so……so heres the truth, if there are any allergies, children, older people with health issues, we are GOING to make money. do not tell the company you have hired about any health complication. they are salesmen. and they don’t care about you. or your money. make sure they do a good job, then kick them out. you don’t need all the bells and whistles they wanna sell you. any idiot can clean duct work, like I said, I am one of them. I am very good at it, but I don’t have the back bone to sell a widowed old lady a humidifier that she doesn’t need for 500 bucks, overall, if you think you need this service done, which you probably don’t, get it done, do not spend anything over 300$ and do not do it again for at least ten years.
If there is stuff in the ducts, the fact that it’s laying there and not being blown into the rooms is proof positive that it is hurting no-one. The 5-6 exceptions you cite in this article I’ll buy, but only with the caveat that at least some of those could have been avoided by proper protection (during remodeling for example) – and if asbestos/lead/whatever winds up in your ducts- the remodeling contractor should be the one paying to remove it.
The cooling coils the air comes into contact with appear to need UV-C lights on them in humid climates. That's the biggest thing. If the ducts have never been cleaned, then getting that done goes without saying. But those coils need to be cleaned, disinfected, and then UV-C light(s) installed to prevent mold & bacteria build-up in the future on them. That appears to be chiefly responsible for the dirty laundry and/or sour milk smell coming from forced-air AC systems in humid regions.
1). Busy companies: The company is so busy, it doesn’t need the work. It will add 70% to 100% profit, and if the customer accepts the estimate, it will move that high-margin customer to the front of the line. This often happens in the worst heat of summer when overburdened ACs and heat pumps quit and the dead of winter when furnaces give up. This is a good reason to consider pre-emptively replacing your system once it’s about 15 years old and/or has had major repairs.
Replacing a capacitor is easy. Just take a photo of the wires before disconnecting anything (you may need a reference later on). Then discharge the stored energy in the old capacitor (Photo 4). Use needle-nose pliers to pluck one wire at a time from the old capacitor and snap it onto the corresponding tab of the new capacitor. The female crimp connectors should snap tightly onto the capacitor tabs. Wiggle each connector to see if it's tight. If it's not, remove the connector and bend the rounded edges of it so it makes a tighter fit on the tab. When you've swapped all the wires, secure the new capacitor (Photo 5).
Pro HVAC company Southern Comfort Mechanical says on its blog, “If there’s mold growth inside the handler due to excess moisture, algae in the condenser drain line or a dirty evaporator coil, it can negatively impact your AC unit’s efficiency. The filters inside may also build up excess dirt and become clogged, which will also make your AC [or heat pump] waste energy trying to sustain the cool climate inside your home.” These issues are easy to solve. They don’t require replacing the air handler.
Wiring up the thermostat is usually pretty straightforward if an old one is being replaced. If a thermostat is being put in where one had never been before, that could involve running new wiring. The placement of the thermostat is also important so that its sensors can get an accurate reading of the temperature. A thermostat that is blocked by a bookcase or other large furniture will not get a good reading and will not perform efficiently.
We are a hvac company that provide air duct cleaning service are minimum charge $400 to do a proper air duct cleaning with 2 techs avg 3-6 hours that includes sanitizing. I get phone calls all day about the $99 your not going to get much of a cleaning for that price it for them to get there foot in the door and up sell that the only way for them to stay in business. Just from my 15 years of duct cleaning experience.
Consider what kind of heating and cooling system you want installed for the square footage of your home. Do you want a full system with a thermostat or a specific machine for the summer like a swamp cooler? Do you need a new furnace just for the winter? For any of these projects, the cost will vary depending on the quality, style and machine size you choose. If you have a tight budget, think of going smaller and upgrading over time. For example, if you can't afford to convert your entire home to solar power, you may want to consider only utilizing it to heat your water. Some other types of heating systems are:
Pro HVAC company Southern Comfort Mechanical says on its blog, “If there’s mold growth inside the handler due to excess moisture, algae in the condenser drain line or a dirty evaporator coil, it can negatively impact your AC unit’s efficiency. The filters inside may also build up excess dirt and become clogged, which will also make your AC [or heat pump] waste energy trying to sustain the cool climate inside your home.” These issues are easy to solve. They don’t require replacing the air handler.
Hi John, Thanks for reaching out, we would be happy to help you connect with a pro for your project. You can submit a request to our pros here: www.homeadvisor.com, browse a list of pros that serve your area here: http://www.homeadvisor.com/c.html, or send your info to emailus@homeadvisor.com and a project advisor will reach out to assist you. –HASupport

An important component of natural ventilation is air change rate or air changes per hour: the hourly rate of ventilation divided by the volume of the space. For example, six air changes per hour means an amount of new air, equal to the volume of the space, is added every ten minutes. For human comfort, a minimum of four air changes per hour is typical, though warehouses might have only two. Too high of an air change rate may be uncomfortable, akin to a wind tunnel which have thousands of changes per hour. The highest air change rates are for crowded spaces, bars, night clubs, commercial kitchens at around 30 to 50 air changes per hour.[17]

We were following up on this review and the service call we did for you. We could not find you in our system of ever having gone out to your home. If you could please provide us with the date we were out and the name under which the call was placed that would be great as we would like to see if there is any way we can rectify the situation. We do offer a 100% Satisfaction Guarantee, we have tried to private message you to no avail. Can you please call us at 925-318-4795?  


HRV/ERV Ventilators: These whole-house ventilators exchange air. They are ideal for homes with what is called a “tight envelope,” homes where house wrap has been applied and airgaps in the attic, around windows, doors and outlets have been sealed. Air in these homes becomes stale and polluted, so exchanging the air is important to IAQ. Heat recovery ventilators (HRV) are designed for cold climates. Energy recovery ventilators (ERV) are best for warm climates.  Your cost for an installed HRV or ERV will range from about $2,000 to more than $5,000 based on its capacity and features.
So, whether you need an AC repair or you’re in search of a new heating and air conditioning system—or you need a new water heater now–you can count on our team in North America. We’re experts in AC and plumbing repair, and offering top-notch AC and plumbing service is what we do best. Call Service Experts 24/7/365 at 866-397-3787 or request an appointment online today, and don’t forget to check out our coupons page for savings on your AC or plumbing repair service.
#3 The ONLY time Duct cleaning is needed is when the home had a fire, Bad roof leak on to FIBERGLASS ductwork or house sat vacant for many years with out the air running. And its better to replace than to do “abrasive” duct cleaning. If the duct cleaning has a rotating brush it will remove part of the glue that is holding the Fiberglass in the ducts together, PERIOD no matter how much the say it don’t because the brush is soft.
I have a white gritty dust throughout my whole house. Dust and it comes right back. We have central air. In 2013 had all the air conditioning tubing in the attic replaced. Old ones were completely clean. Why?? Thought dust would be in there. Put everything in plastic containers. Furniture everything is always covered with this. Problem is always there year round. Furnace people said it is not coming from furnace. We built house in 1971. Only started with this @ 19 years ago. Thinking when air conditioning went in. We cough all the time and sneeze. I do not have friends come here because I hate how dirty my house looks.
The cooling coils the air comes into contact with appear to need UV-C lights on them in humid climates. That's the biggest thing. If the ducts have never been cleaned, then getting that done goes without saying. But those coils need to be cleaned, disinfected, and then UV-C light(s) installed to prevent mold & bacteria build-up in the future on them. That appears to be chiefly responsible for the dirty laundry and/or sour milk smell coming from forced-air AC systems in humid regions.
Well, I had the cleaning done. The handler is definitely much quieter. It was explained to me that with the coils clean, the condensation will be able to sweat off instead of sticking to the dust and dirt, therefore the humidity (lots of humidity in florida) will be removed better. I feel as if it was worth it, but, I will definitely change that filter every 3 weeks or so from now on. I don’t want to pay that cost again.
Hi guys if your not convinced yet that duct cleaning is a waste of time. I’m a HVAC business owner install heaters and air conditioners. Simple facts if you have an old system get a new return air fitted with a filter it will catch all the dirt and dust. If you still have as many do black flecks and stuff coming through it is the lining inside your ducting that has perished. So somewhere you have a hole or very old ducting. If you had rats etc its a hole somewhere. To clean, stick your vacuum in the outlet and push the hose as far as it will go this gets 99% of toys and coins fur and alike. Think about it if the object is not heavy it will come out the duct when unit is on. Service the heaters or air con units but not the ducting. I would go further to say that duct cleaning actually damages the ducting in my opinion.
Capacitors -- Capacitors help your HVAC motor start from a standstill. Over time they can weaken. As they weaken, they cause the motor to run hotter. This can shorten the life expectancy of your motor. Once a capacitor fails, the whole motor will stop working. You usually won't notice that a capacitor has weakened until your motor stops turning on.
As you can see, if we know what the contractor is actually paying for specific equipment, we know what their labor rates are, and we know what they bid the project for, then we can also use some basic algebra (or just let the program do it for us because we’re lazy) to figure out how much of a profit they are making off of us (you) at different bid prices:

Ground source, or geothermal, heat pumps are similar to ordinary heat pumps, but instead of transferring heat to or from outside air, they rely on the stable, even temperature of the earth to provide heating and air conditioning. Many regions experience seasonal temperature extremes, which would require large-capacity heating and cooling equipment to heat or cool buildings. For example, a conventional heat pump system used to heat a building in Montana's −70 °F (−57 °C) low temperature or cool a building in the highest temperature ever recorded in the US—134 °F (57 °C) in Death Valley, California, in 1913 would require a large amount of energy due to the extreme difference between inside and outside air temperatures. A few feet below the earth's surface, however, the ground remains at a relatively constant temperature. Utilizing this large source of relatively moderate temperature earth, a heating or cooling system's capacity can often be significantly reduced. Although ground temperatures vary according to latitude, at 6 feet (1.8 m) underground, temperatures generally only range from 45 to 75 °F (7 to 24 °C).
In some older homes, there was a grey Mylar flexible duct. After years of use, it started to decompose. A duct cleaning company can come out and find why your air is so dirty and why your building doesn’t heat or cool like it used to. This is a savings on your part. You could also be sucking in Hot, dirty attic air. However, sometimes when a duct cleaning company comes out to clean it, the old duct can be destroyed and have to be replaced. Someone with little experience can replace this ductwork but if it isn’t done right it can ruin a lot of things and cost a lot in repairs.
All of you have dentists, you have doctors, you have preachers, you have mechanics. You don’t have to know everything about everything but you have to have people in your life that you can trust. Don’t just open up the phone book and pick a mechanical (HVAC) contractor. Call your friends and family and ask for referrals. There are no black and white (scam or not a scam) answers here.
Before you choose any duct cleaning service provider, interview as many service providers as you can. Ensure that the service provider is certified by the National Air Duct Cleaners Association or NADCA. Make sure that they hold a good standing in the Better Business Bureau and have all the necessary certifications and license. Be clear about their terms of service. Make sure they have the right equipment to do the job. It is best to go for a company that has been tried and tested successfully by any of your acquaintances or opt for a service provider that has been in the business for quite some time.
All of the products discussed above are registered solely for the purpose of sanitizing the smooth surfaces of unlined (bare) sheet metal ducts. No products are currently registered as biocides for use on fiber glass duct board or fiber glass lined ducts, so it is important to determine if sections of your system contain these materials before permitting the application of any biocide.
Good article, but it fails to point out that leaky return-side ducts could be drawing dust and allergens into the duct system from the enclosed spaces in which they run, e.g. between walls, below floors, attic. So duct cleaning may only be a temporary solution. The homeowner can get a home energy audit -- free in many states -- to determine if they have significant duct leakage. An Aeroseal dealer may be able to effectively seal up the duct system without needing to tear into walls etc to get to the ducts.

As a person with severe mold allergies, I live in a the South where the climate naturally breeds molds.We noticed a difference when we had our ducts cleaned.The company used a vacumn type system and covered all of our vents with plastic that was held up by the suction. We had no damage, no leaking dust/dirt back into the house and it took several hours. I think if you use a reputable company it makes the world of difference. Now we use better air filters and also have a UV light to prevent mold growth on ours system.We 'd do it again when the time comes. From your car's air filter to your dryer...anything works more efficiently when it is not filthy dirty.That's just common sense.

What you might not know is that the brand you choose is one of the most important factors in determining a fair HVAC installation cost. So, before delving in-depth, let’s take a quick look at the average prices of a new air conditioner and matching coil by brand…keep in mind, these are the average prices (by brand) that contractors pay for your AC equipment, and it is meant to give you a rough guideline until you are closer to buying:
Yes everyone should get all their ductwork cleaned, because it does help, incame down with major allergies and had serval operations on my sinues because of this problem of air quality and dust, plus i almost died from one of the operations, i was suffering so much. Yes you can seal your duct system by buyind duct seal t instead of tape to tape all the corners of the vent system, tape wears out and gets brittle, the sealant you can buy at home depot, and you just brush it all over the connections of your ductwork, it comes in a container and it is like a thick paste and dries making a good seal for your ductwork.
The short answer is yes, duct cleaning, done right by a reputable company will help with the smell. It is likely though the smell is coming from another source, ie the crawl space. It could also be that another rodent is dead in the duct work. A visual inspection would be in order to check for any breach in the duct system. A duct pressure test would be able to tell you how much air is leaking from the system over all. A hole large enough for an animal to enter would loses a great deal of air, over 300 CFM. It would be worth looking into having this test done and it should cost around $200. Cleaning the air handler and evaporator coil will greatly improve the performance of the air conditioner. Dirt and dust on the evaporator acts as insulation and reduces the amount of cooling done be the coil. Any quality duct cleaning should include cleaning the air handler and coil, and the tech should allow you to watch him perform the work as it is done.
I’m having my duct work cleaned this Saturday. Have a coupon for $49 through Amazon. Job normally $249. Had my basement remodeled about 18 months ago. The contractors were very thorough at blocking the vents, as far as I can tell. The offer is for HVAC and dryer vent cleaning. My house is 11 years old. I figured, $49 is not much. I appreciate your tips on not getting talked into any additional service, not to use solvents to clean, the certification information and before and after pictures. Very useful and I’ll be sure that all I spend is the $49 for the voucher.
Greetings from Mama Duck from Ductz of Greater Atlanta. These are some awesome comments and a few are from high quality duct cleaners that I personally know. After 19 years in this industry I agree that a government agency is not always up to date with their knowledge but won't admit it. If they were out in the field with our technicians every day they would upgrade their info. I get calls all the time where customers have been taken advantage of by "go and blow" companies. The customers don't know what they don't know but many are too lazy to do the research and are just looking for cheap. The industry has gotten a bad rap due to these con artists but the customer has to take some responsibility. I ask them why they would want to do business with a company who lies to them in print? Are they stupid or just cheap? Thankfully there are those of us in the industry who are working diligently to raise the bar on quality, protect the consumer and perform high quality work. At Ductz all our technicians are NADCA certified, trained by the best in the industry and know how to clean the entire system.

Without proper ventilation, carbon monoxide can be lethal at concentrations of 1000 ppm (0.1%). However, at several hundred ppm, carbon monoxide exposure induces headaches, fatigue, nausea, and vomiting. Carbon monoxide binds with hemoglobin in the blood, forming carboxyhemoglobin, reducing the blood's ability to transport oxygen. The primary health concerns associated with carbon monoxide exposure are its cardiovascular and neurobehavioral effects. Carbon monoxide can cause atherosclerosis (the hardening of arteries) and can also trigger heart attacks. Neurologically, carbon monoxide exposure reduces hand to eye coordination, vigilance, and continuous performance. It can also affect time discrimination.[15]
It seems all the average costs for a complete heating and cooling system replacement I've found on websites are usually at least 1/4 less, mostly half lower, then quotes I've gotten from companies. The worst quote I got was from One Hour Heating & Air Conditioning (the company with the Mike Rowe commercials), for over $15,000! I finally settled on a Carrier dealer, for $10,700 & I'll get $950 of that back in energy co rebates eventually. The company I went with's basic system would have been around $8800 (the only one that sorta matched up with web avg cost). They did all the correct planning as far as I could see, not like One Hour, who just showed me a price guide for the same size units already in place. And they do all the rebate paperwork and submit it to the energy co, One Hour never even mentioned possible rebates! Plus Carrier gets above avg reviews. I would have greatly liked a price under 9 grand, but this company got me 0% APR financing, so at least nothing out of pocket. My advice is stay away from national chains, and shop around with local area companies. Of course, One Hour says local companies will fold before you need warranty service lol. For their cost, there should be a technician living in his work van outside my house hahaha.
You've probably noticed many appliances boasting an Energy Star Certification. What this means is that manufacturer voluntarily built the product to help reduce greenhouse gases and meet non-regulatory guidelines offered by the Environmental Protection Agency. To earn an Energy Star rating, a product or system must be tested by a third party that has been recognized by the EPA for meeting their testing qualifications.
Heaters exist for various types of fuel, including solid fuels, liquids, and gases. Another type of heat source is electricity, normally heating ribbons composed of high resistance wire (see Nichrome). This principle is also used for baseboard heaters and portable heaters. Electrical heaters are often used as backup or supplemental heat for heat pump systems.
Duct cleaning generally refers to the cleaning of various heating and cooling system components of forced air systems, including the supply and return air ducts and registers, grilles and diffusers, heat exchangers heating and cooling coils, condensate drain pans (drip pans), fan motor and fan housing, and the air handling unit housing (See diagram).
×