Tip – Be careful with change-outs. Ductwork deteriorates and sometimes has to be replaced.  It is only if the ductwork is in fantastic condition that you should get a change-out without ductwork (Remember – the ductwork has already been there for 15-20 years, and now it will be there another 15-20…it has to be in good shape). However, many HVAC installation companies like to push change-outs because the ductwork is the most time consuming part of the job, and a change-out is quick, easy money. Realize that it’s only about 15-20% of the jobs that qualify for a change-out, so be careful.
Most organizations concerned with duct cleaning, including EPA, NADCA, NAIMA and the Sheet Metal and Air Conditioning Contractors' National Association (SMACNA) do not currently recommend the routine use of sealants to encapsulate contaminants in any type of duct. Instances when the use of sealants to encapsulate the duct surfaces may be appropriate include the repair of damaged fiber glass insulation or when combating fire damage within ducts. Sealants should never be used on wet duct liner, to cover actively growing mold, or to cover debris in the ducts, and should only be applied after cleaning according to NADCA or other appropriate guidelines or standards.
I was able to get a next day appointment with them last week after multiple other providers did not have availability. The tech was on time and did a good job to diagnose and eventually replace the circuit board and get it up running again. The service itself would be 5 stars, although it did take a week to complete the job due to ordering the part.

An air conditioner's compressor contains a refrigerant. As it works, it sends this refrigerant through the system. As warm air blows across the coil that carries this refrigerant, the heat transfers to the refrigerant (cool always absorbs warm). A fan moves the cooled air through the ducting and out of vents that lead into the rooms of your house. The refrigerant returns to the compressor where the absorbed heat is moved outside. The refrigerant is then sent through the coil once again to continue the cycle.


Just had my air ducts cleaned. They used a high pressure air hose in all the heat ducts and cold air returns. He showed me the stuff that came out, the reason for the duct cleaning was the fact that I had a problem. With rodents. There was quite a few mummified rats and mice, and he said I wouldn’t have to have them done again unless I incur another problem or have renovations done. Cost me 345.00 for a 2 storey large old home. Not a bad price as I had them done when I moved in 28 years ago and it cost me 500.00. Lots of dog hair, toys, balls and assorted goodies came out as well. Took them 2 hours. I did have sanitizer put in the ducts because of the dead rodents.

I originally took off one star because of the SNAFU with getting the part ordered.  When Alberto called me on the phone he admitted the person had "gotten busy with other things" and apologized.  THAT was taking the high road and I was impressed by that.  Sadly, for reasons I won't guess at, Alberto has decided to take the low road in his comments and imply that they got the part as quickly as possible.  Well, we called at 2:30 so did someone spend six and a half hours finding the part??  That seems very doubtful.
Multiple inventions within this time frame preceded the beginnings of first comfort air conditioning system, which was designed in 1902 by Alfred Wolff (Cooper, 2003) for the New York Stock Exchange, while Willis Carrier equipped the Sacketts-Wilhems Printing Company with the process AC unit the same year. Coyne College was the first school to offer HVAC training in 1899.[12]
As you can see, if we know what the contractor is actually paying for specific equipment, we know what their labor rates are, and we know what they bid the project for, then we can also use some basic algebra (or just let the program do it for us because we’re lazy) to figure out how much of a profit they are making off of us (you) at different bid prices:
Air conditioning and refrigeration are provided through the removal of heat. Heat can be removed through radiation, convection, or conduction. Refrigeration conduction media such as water, air, ice, and chemicals are referred to as refrigerants. A refrigerant is employed either in a heat pump system in which a compressor is used to drive thermodynamic refrigeration cycle, or in a free cooling system which uses pumps to circulate a cool refrigerant (typically water or a glycol mix).
Once on the scene, trained Sears professionals utilize powerful, truck-mounted equipment to clear your air ducts of dust, debris, pet dander, allergens, and grime. Our powerful air duct cleaning suction equipment vacuums out years of accumulated dust from your air ducts, leaving them clean and clear. Once finished, our technicians remove all equipment and make sure that your ducts and HVAC unit are restored to their best condition. For continued protection against dirty air ducts, your service technician may suggest a variety of air purification products.
Do you live in a historic home and want to tie your new system in to work with existing features? The price will go up to do the job right. All of these things add up to slow down the HVAC company, which takes more time, which costs more money for labor and parts. This is especially true if they are a legitimate company which is licensed, bonded and insured. Simply put, this is the “X-Factor” in your HVAC installation cost. Again, you could get people to do it for cheaper…but you won’t be happy with the results, I promise.

Refrigerant Metering Device -- Every HVAC system has one of these, and heat pumps have two. They regulate the amount of refrigerant going through your air-conditioner. If it fails, either too much or too little refrigerant will course along the lines and either not perform well or will overwhelm the compressor and cause it to fail. A total failure of this component will result in a complete loss of operation.
What if you move into a 20 year old house and find that the people who owned it previously NEVER replaced the filter? It was so dirty that the HVAC system did not work at all. For most people - duct cleaning is NOT a waste of time or money. You must not have allergies. I have very bad ones plus asthma. It makes it very hard for me if I don't get it done every few years. By the way - the ducts get dusty just sitting there - especially without air going through them. Dust settles on them just like it does the furniture.
On average, we (Indians in Ontario) receive 3-5 calls per day for duct cleaning services from India. I did get ducts cleaned twice in 25 years. For a newly built house, it should be done as material goes into the ducts. Every year, before turning the heat on, I clean the ducts, using the vacuum pipe or with wet towel. Most of the dust, pet hair, small items get to the ducts from the top floors, not where system is installed. Even in winter months, I open 2-3 windows for air circulation for 15 minutes, specially right after cooking, almost daily. We breath in the same stale air, develop health issues. Also, I have an added air cleaning and fileration system installed. At a low rate, this system constantly cleans the inside air and also that it pulls from the outside. Duct cleaning is a scam, there are other efficient and cost effective methods we can use to purify the inside air.

DIY: We don’t recommend a DIY approach. Depending on the system, working with gas, electricity and refrigerant create dangers. Beyond that, it is essential that split system components be selected for compatibility. DIY installation of an HVAC system will void the warranty of most brands. The manufacturers won’t stand behind the warranty when anyone other than a certified installer does the work. This is true since improper installation is the main cause of poor system performance and mechanical breakdowns.


They were quick to come out and diagnose the problem with my furnace, but I thought the estimate of $549 a bit high to replace the circuit board.  So called around and found Leo's Appliance in Concord that sells appliance parts and the circuit board was only $90.49 - that is the retail cost to me, so I imagine the wholesale cost is a lot less.  So BEWARE of this company since they wanted $500!!! to replace the circuit board which is located right in the front of the furnace - extremely easy to access.  I hate it that you cannot trust repair companies.
So HVAC sent Tony Diaz to my house. I was at work so he was subjected to the most excruciatingly exacting woman on the planet (my wife). Tony impressed her with his friendliness, professionalism and the obvious jouneyman-level knowledge of his craft. He found literally --burnt-out-- parts in our system and replaced them. It cost us a bit but I know enough about the parts to see there was no gouging on the parts and a fair rate for the labor. It wasn't cheap but it was fair and worth every dime.

One of the best ways to know if your ducts or vents need to be cleaned is to just check them. Your eyes will be able to check for indications of mold, dust or pollen buildup. You might also be able to smell the presence of mold, which would be a clear indicator. Ductwork will have some buildup of dust, since the return registrars pull air back in. However, this doesn't mean your ducts have too much debris, and you can easily clean them with a duster or vacuum.
The three major functions of heating, ventilation, and air conditioning are interrelated, especially with the need to provide thermal comfort and acceptable indoor air quality within reasonable installation, operation, and maintenance costs. HVAC systems can be used in both domestic and commercial environments. HVAC systems can provide ventilation, and maintain pressure relationships between spaces. The means of air delivery and removal from spaces is known as room air distribution.[3]
There is much more to air conditioning than AC installation in Fort Smith, AR then just maintenance and repairs. A variety of other services is required throughout the lifespan of your cooling unit. We are the professional team capable of completing them all. Replacements, troubleshooting, indoor air management, these are all part of our repertoire.
Window air conditioners cost less than central units, averaging $300. These systems generally suffice to keep a room cool on warm spring and summer days. They can bring added comfort for a reasonable price but are less powerful than a central air conditioner. If you have a bigger home with multiple rooms, you will probably need to have a larger system installed. Central air can cool several rooms at once, while window AC units usually only cover one or two rooms at a time.

1. Ducts need cleaning mostly because they were not installed properly. There should be regulatory inpection and approval of clean and proper duct works on new houses. I was extremely unpset when I looked and found significant amounts of construction dust in parts of the ducts in my new house. There is apparently no way to hold the bullder to be responsible for clean ducts.

All these pro duct cleaners answer with "it's common sense, everything operates better when cleaner" etc. But your explanation is correct. Especially so with flex tube ducting where dust gets "stuck" between the lowest valleys (between wire coil supports) where air flow is drastically reduced -- which is more than 50 pct of the entire interior surface area of the flex ducting. That sounds like a bad thing but also has a good effect of trapping dust from escaping.


I had someone out to clean my ducts last weekend. He took a blue bag up in my attic. He came back down in just a few minutes and said I had mold and he even showed me a picture of something saying it was mold but I couldn’t really tell. I refused his service to take care of the mold. He went back up in the attic for a little while and then came down. I never heard any sounds that he was actually up there doing anything. How do I know if he actually cleaned the air ducts?
In reading through all this about duct cleaning, THE ONE preventative measure people need to realize is that a poorly installed HVAC system that is not sealed and air tight to ensure that ALL indoor air passes through a GOOD air filtration system IS THE best means of ensuring your ducts remain clean. Duct cleaning does not now and will NEVER improve an HVAC systems efficiency. Proper maintenance and installation are the key just as improper installation practices allow for dust infiltration into the duct system. I am a state licensed contractor in Texas, and unless people have their hvac system sealed and/or properly installed, duct cleaning is an absolute waste of money. My duct system is 12 years old as is as clean today as the day I installed the system with ductwork. SO before ANYONE jumps on the bandwagon of duct cleaning, get with your hvac professional FIRST.

One of the difficulties encountered by many air duct cleaning service companies is that their attention is not really on air duct cleaning. For example, many heating and cooling companies offer duct cleaning as a supplemental service, but of course their primary business is installing and servicing heating and cooling equipment. For these companies, air duct cleaning is not always given the attention it deserves and is often done by less experienced employees whose interest is not in duct cleaning but in repairs and installs. And it is almost always done with inferior air duct cleaning equipment. Still other firms (like carpet cleaners) offer a large variety of services and claim to “do everything.” Because of their lack of focus they may not actually be very good at many, if any, of the services they offer. They cannot simply buy an attachment for their carpet cleaning machine and magically become a great duct cleaner.


I know it has to have a new concentric venting system installed, I believe it needs new plenums ( mine are rusty but both of these require extra work , so someHVAC persons are saying I do not need either!! RED FLAG THERE. Also, it will need a new drain using PVCP ?? Piping run maybe two, depending on where my evep coil drain is conected (here in TN they use to run them in with the septic lines, now they cannot be run through that way), Lastly I am not where or what these things do beides hold water but I was told It needs a filter rack and new filter base safety pan. THATSSS it that is all I know about this stuff aside from the fact that nothing up there is to code thus far LOL. !!

I am very interested by your post. We recently had a lead inspection on our property and one thing the lead inspector suggested was to get the air ducts cleaned out. We had our ducts cleaned last year after we under went a large renovation project (since we have a toddler in the house). This year we decided to go for lead compliance and had all our lead removed (we moved out for the work). Recently, my son had a false positive lead test, which prompted us to get a lead dust inspection around the house (including having the vents dust-wiped on the inside). The levels inside the ducts weren't crazy high (but more than would be acceptable for a floor). As it turned out my son's lead levels are very low (but not zero). Is it possible however that lead dust from the inside of a vent can come out? Would this be a scenario where you think air duct cleaning would be beneficial?


Although HVAC is executed in individual buildings or other enclosed spaces (like NORAD's underground headquarters), the equipment involved is in some cases an extension of a larger district heating (DH) or district cooling (DC) network, or a combined DHC network. In such cases, the operating and maintenance aspects are simplified and metering becomes necessary to bill for the energy that is consumed, and in some cases energy that is returned to the larger system. For example, at a given time one building may be utilizing chilled water for air conditioning and the warm water it returns may be used in another building for heating, or for the overall heating-portion of the DHC network (likely with energy added to boost the temperature).[4][5][6]
The Antimicrobials Information Hotline provides answers to questions concerning current antimicrobial issues (disinfectants, fungicides, others) regulated by the pesticide law, rules and regulations. These cover interpretation laws, rules and regulations, and registration and re-registration of antimicrobial chemicals and products. The Hotline also provide information health & safety issues on registered antimicrobial products, product label and the proper and safe use of these antimicrobial products.
BIG THANK YOU for being honest, and advising us that for some reason the fuse/switch was in the reverse position so the AC unit would not properly turn on.   The unit turned back on immediately, and began cooling the house.   And then providing advice that the AC/Heating system needed some TLC, and giving us options to save money by purchasing a maintenance plan that included the filters plus cleaning services since we were already being charged for the service today.
Duct cleaning has never been shown to actually prevent health problems. Neither do studies conclusively demonstrate that particle (e.g., dust) levels in homes increase because of dirty air ducts or go down after cleaning. This is because much of the dirt that may accumulate inside air ducts adheres to duct surfaces and does not necessarily enter the living space. It is important to keep in mind that dirty air ducts are only one of many possible sources of particles that are present in homes. Pollutants that enter the home both from outdoors and indoor activities such as cooking, cleaning, smoking, or just moving around can cause greater exposure to contaminants than dirty air ducts. Moreover, there is no evidence that a light amount of household dust or other particulate matter in air ducts poses any risk to health.
×