I believe a $3 [sic] pleated cotton filter is all that is ever needed to keep a system running top notch. A cleaning of the blower squirrel cage and of the evaporator [indoor] coil may be needed one time if fiberglass or no filters have been previously used. The return air grille [or grilles] need vacuumed off occasionally, as they are upstream from the filter. The $3 filter should be changed every 3 months [rule of thumb]....and most of them have a little white square on the cardboard frame to write install date.....and the arrow should point into the duct [if at filter grille]....or towards the furnace [if in ductwork slot]...or towards the blower [if in blower compartment]. My two cents.....
At the state level the rebates are still substantial. For example, switching to a zoned system can get you a $100 rebate from various A/C companies, and state rebates are also included. In Pennsylvania a high-efficiency air conditioner alone can get you up to $300, and a high-efficiency complete HVAC system can see up to $1000. Maryland's incentives get up to $1,250, with a $100 rebate on a tune up of an existing system.
Once on the scene, trained Sears professionals utilize powerful, truck-mounted equipment to clear your air ducts of dust, debris, pet dander, allergens, and grime. Our powerful air duct cleaning suction equipment vacuums out years of accumulated dust from your air ducts, leaving them clean and clear. Once finished, our technicians remove all equipment and make sure that your ducts and HVAC unit are restored to their best condition. For continued protection against dirty air ducts, your service technician may suggest a variety of air purification products.
We installed a TRANE XL18 HVAC with a TRANE HV80 furnace 16 years ago and it still works great in Tucson, AZ.  We inquired into a replacement for the future since the R-22 refrigerant will be off market at the end of this year.  Our maintenance folks want to sell me a new system anyway (even though the TRANE works great).  We are considering the BOSCH Inverter heat pump as a lower cost option down the road.  Watch out for the tricky salesmen trying to sell beer at champagne prices though. Get estimates on whether you need to replace your current system and how much it could cost.  And if they are factory certified.
I purchased one of those Amazon air duct cleaning coupons for 49.99. When the company showed up, they removed the vent closest to the air intake and immediately told me I needed $1800.00 for all new duct work. They said they could not clean the system until new duct work was installed. I thanked them and said I would give them a call. The only call I made was to Amazon to get a refund. I know I didn’t need new duct work. Be careful to not fall for unscrupulous salesmen and their pitches and scare tactics.
Air conditioning and refrigeration are provided through the removal of heat. Heat can be removed through radiation, convection, or conduction. Refrigeration conduction media such as water, air, ice, and chemicals are referred to as refrigerants. A refrigerant is employed either in a heat pump system in which a compressor is used to drive thermodynamic refrigeration cycle, or in a free cooling system which uses pumps to circulate a cool refrigerant (typically water or a glycol mix).
The HVAC installation costs below are based on residential installations only, and are priced for a single unit. Two units should be about twice the price. “Tim, shouldn’t there be a discount?” If people start giving you discounts, they are probably charging you too much to begin with.  That’s our philosophy anyway. Twice the parts and time should be twice the price from a fair contractor. The prices listed include component parts (with warranty), labor, and all materials for a complete HVAC installation.
After one company just took a cursory glance at our A/C and found nothing wrong, I called HVAC. I called them mostly based on Michael W's post on 8/10/14 where he told us the owner, Alberto, took his feedback and took it SERIOUSLY. That speaks VOLUMES to anyone who has been around long enough to know the characteristics of the serious players are and those who are the wannabes.
Indoor Fan Motor -- Indoor fans circulate the air from your house and through the system. Age and dust buildup are the two biggest contributing factors to their failure. When they are starting to fail they will often make noise. Failure of the fan will result in no heating or cooling, and if it is not repaired soon, it can cause other components to fail.

Knowing what you should be paying for your HVAC equipment and installation is essential to getting a fair deal. Most HVAC prices aren’t advertised. Contractor strategy is to get a salesperson into your home to sell you on a package of equipment, accessories and installation. This makes comparing systems difficult, and some sales pressure might be applied.


Energy efficiency can be improved even more in central heating systems by introducing zoned heating. This allows a more granular application of heat, similar to non-central heating systems. Zones are controlled by multiple thermostats. In water heating systems the thermostats control zone valves, and in forced air systems they control zone dampers inside the vents which selectively block the flow of air. In this case, the control system is very critical to maintaining a proper temperature.


Excalibur Water Systems helps solve the water challenges around the globe with water solutions for any possible water concerns in: water hardness, filtration of any contaminant, bacteria removal and high purity water needs and also comes with a warranty of up to 20 years at no extra cost. The best warranty for the water treatment equipment industry.

SEER is useful for comparing one model to another much in the same way that a car's calculate MPG is useful. It's not an accurate prediction of exactly how efficient the system is, but it can tell you which one is more efficient. Also, since SEER is based on a "cooling season", what region you live in will determine how long or short your cooling season is.
In most modern homes with up-to-date heating and air conditioning systems, filters are changed regularly through the year, so you may not even need to hire a professional. However, keep your eyes open for the accumulation of dust, dirt, dander and mold. If you see it despite regularly changing your filters it could be an indication you need a high-pressure cleaning.
The cooling coils the air comes into contact with appear to need UV-C lights on them in humid climates. That's the biggest thing. If the ducts have never been cleaned, then getting that done goes without saying. But those coils need to be cleaned, disinfected, and then UV-C light(s) installed to prevent mold & bacteria build-up in the future on them. That appears to be chiefly responsible for the dirty laundry and/or sour milk smell coming from forced-air AC systems in humid regions.
Natural ventilation is a key factor in reducing the spread of airborne illnesses such as tuberculosis, the common cold, influenza and meningitis. Opening doors, windows, and using ceiling fans are all ways to maximize natural ventilation and reduce the risk of airborne contagion. Natural ventilation requires little maintenance and is inexpensive.[19]
This is to Blueberry who.wrote.about home rental dust problems on 12/ 06/2016. If you’ve been there 13 years.your landlord has made enough money to have those problems repaired.I would call your city property standards dept. And let them know what.conditions you are having to live.There is no excuse for living in those conditions when most problems like that are easy fixes.Especially if your kids are getting sick. Tell your landlord your.calling City Health Inspector if he doesn’t fix.the problems.

I’m a heating and air conditioning contractor. I’ve been in the trade for over 15 years. I’ve witnessed numerous duct cleaning projects and talked with many duct cleaners. Duct cleaning as it’s usually promoted is a fraud. Most duct cleaners claim to deliver cleaner air. They deliver exactly the opposite. The studies on duct cleaning prove it, including a May 1998 study sponsored by NADCA and the EPA! The stories are compelling, but they can come up with stories that “prove” anything they want. Internet searches are dominated by results from those who are paid to tell you that duct cleaning is worthwhile. Search a little more and you’ll find the truth.
Having evaporator and condenser coils cleaned could cost between $100 and $400. If your coils can be accessed in-place, you'll be looking at a lower service cost. If your technician needs to remove the them first, the cost should be around $400. Having the evaporator and condenser coils cleaned can have a significant impact on the efficiency of your system. If your coils are excessively dirty, they won't be able to do their job and your system will have to work harder. Keeping up with the hygiene of these components can save you money in both the short and long-term. For example, replacing evaporator coils can cost anywhere from $650 to $1200.
An air conditioner's compressor contains a refrigerant. As it works, it sends this refrigerant through the system. As warm air blows across the coil that carries this refrigerant, the heat transfers to the refrigerant (cool always absorbs warm). A fan moves the cooled air through the ducting and out of vents that lead into the rooms of your house. The refrigerant returns to the compressor where the absorbed heat is moved outside. The refrigerant is then sent through the coil once again to continue the cycle.
Monday the following week, no phone calls, or follow up.  I call to get an update and am told that they cannot install my system because they don't have time.  I ask what does that mean, one year? One week? Until the end of summer they say.  What does that mean I ask?  They say at the end of September.  I say thank you for wasting 1 month of my time.
Pay particular attention to cooling coils, which are designed to remove water from the air and can be a major source of moisture contamination of the system that can lead to mold growth. Make sure the condensate pan drains properly. The presence of substantial standing water and/or debris indicates a problem requiring immediate attention. Check any insulation near cooling coils for wet spots.
Concealed behind your walls and mostly ignored, your air ducts serve as vital pathways that deliver warm and cool air throughout your home. While they may be unseen, your air ducts are working whenever you have your air conditioner or furnace running–nearly year round. Attached to your HVAC, air ducts transfer the air from these systems throughout your home. What many homeowners don't realize is that your air ducts, in nearly constant use, continually accumulate dust, grime, debris, pet dander, and allergens throughout the year. A professional air duct cleaning is necessary for better indoor air quality and the health of your family.
I have lived in Calgary for quite some time now. When I first moved here I couldn’t stand the humidity levels. Its like a desert come winter. When I first moved into my new home, the house inspector insisted I have my furnace and ducts cleaned. I was very sceptical about duct cleaning to begin with. The company I hired came on time and were very respectable from the start. Before mentioning anything they asked me what my concerns were and what issues I was having. They were more concerned about addressing my issues then bringing anything non related up. I ended up going with this company and getting a humidifier installed a couple days later after the cleaning. Its been almost 4 years now that I have been here. The humidifier is working great and the difference is incredible. They took me around explained step by step what they were doing and the reasons they were doing it. With all those other companies out there, I am glad I found them at this site.

Duct cleaning is a complete scam, I was a “duct cleaning technician” for a whole week before I was fired for not upselling elderly widowed women $2000 extra for “toxic mold remediation” when their ducts were spotless to begin with. The last two days I was employed there I worked as a “helper” alongside a technician thats been with the company 7 years. He scammed every customer on mold and would at times get as much as $2500 extra for treating “toxic mold” in a typical 3 bedroom house in the suburbs. Wait…it gets even better, the “Biocide” the company used was simply a cheap $4.99 per gallon bought at Home Depot air freshener with no anti-microbial properties that was fogged into the HVAC system for 5 minutes, maybe using 1/2 cup of the stuff. In order to provide the customer with evidence of “mold infestation” the technician would be given bogus mold tests that always resulted in “toxic spores present” regardless if you swabbed the actual duct or nothing at all. Not to mention the actual duct cleaning job (typically $400) did basically nothing and the homeowner could’ve done a better job with a shopvac
I'm very glad that I found another guy to come replace the circuit board and put it away from the water, fix the water leak, and also find and fix another impending failure.  All of that was for much less than HVAC Service wanted to charge for repair or replacement. The other guy did a great repair, so I'm confident it will not break down again, but if it does, I will not call HVAC Service. Don't get suckered by their Yelp Deal.
The Chartered Institution of Building Services Engineers is a body that covers the essential Service (systems architecture) that allow buildings to operate. It includes the electrotechnical, heating, ventilating, air conditioning, refrigeration and plumbing industries. To train as a building services engineer, the academic requirements are GCSEs (A-C) / Standard Grades (1-3) in Maths and Science, which are important in measurements, planning and theory. Employers will often want a degree in a branch of engineering, such as building environment engineering, electrical engineering or mechanical engineering. To become a full member of CIBSE, and so also to be registered by the Engineering Council UK as a chartered engineer, engineers must also attain an Honours Degree and a master's degree in a relevant engineering subject.
At the state level the rebates are still substantial. For example, switching to a zoned system can get you a $100 rebate from various A/C companies, and state rebates are also included. In Pennsylvania a high-efficiency air conditioner alone can get you up to $300, and a high-efficiency complete HVAC system can see up to $1000. Maryland's incentives get up to $1,250, with a $100 rebate on a tune up of an existing system.

I agree, if you replace (or wash depending on type) your air filters regularly AND vaccum, then you probably don't need the ducts or air coils cleaned. However, if you purchase a pre-owned home, and the previous owners did not regularly change the air filter or vaccum the home, then duct cleaning is worth the expense especially if you are sensitive to allergens. Especially if the previous owners had pets.


Your cleaning service should involve all aspects of your duct work to maximize energy efficiency and air quality. This includes attending to the heat exchanger, blower, drain pan, plenum and coils as well. In the process, your service provider may find that you're facing larger issues than debris and build-up. The professional may recommend having your furnace repaired if they notice, for example, damage to your heat exchanger or blower motor. Generally, a furnace repair costs between $130 and $500. They may also find that an A/C coil needs to be replaced rather than cleaned and would then recommend A/C repair.
Undertaking an AC installation in Fort Smith, AR? The first thing to remember is that your air conditioning unit will need repairs now and then to remain efficient. Granted, many repair emergencies can be avoided through proper maintenance procedures. When your AC fails we provide reliable, affordable repairs of the highest standards. Enhanced efficiency and longevity is the name of our game.
Duct cleaning has never been shown to actually prevent health problems. Neither do studies conclusively demonstrate that particle (e.g., dust) levels in homes increase because of dirty air ducts or go down after cleaning. This is because much of the dirt that may accumulate inside air ducts adheres to duct surfaces and does not necessarily enter the living space. It is important to keep in mind that dirty air ducts are only one of many possible sources of particles that are present in homes. Pollutants that enter the home both from outdoors and indoor activities such as cooking, cleaning, smoking, or just moving around can cause greater exposure to contaminants than dirty air ducts. Moreover, there is no evidence that a light amount of household dust or other particulate matter in air ducts poses any risk to health.
×