I own an HVAC company. Dirt in your ducts stays there and hurts no one. It is like dirt on the ground outside. This industry was infiltrated by a bunch of money grubbing low lifes years ago. As a credible company, we do not clean air ducts. Some who were credible probably signed on not knowing what else to do or to try to make a buck another way. These companies, because they also do HVAC work not only rip off private homeowners, they are ripping off legitimate HVAC company's customers and the integrity of what can and should as a rule be a great service industry. Some probably have gotten into this to simply offer what competitors who were ripping off their customers were offering. Anyone cleaning ducts is in my opinion raising a big red flag that they cannot and should not be trusted. Political pressure from NADCA, advertising dollars, manufacturers and marketers of duct cleaning equipment, and intense competition for the customers is the only reason the government and adverstising companies have not run them out of business and that this cancer perpetuates itself.
The sky is the limit. I am a big fan of adding zoning systems, but realize that this will typically add $2,300 to $3,500 (or more) to the price. “Why a price range, isn’t it just a part?” No, the part then has to be installed, and the customized ductwork required will vary based on the difficulty of the job and layout of your attic. It is very labor intensive, and most people don’t do it right. It should also include a bypass damper and ductwork! Simply put, the more you add, the more it will affect your HVAC installation cost.

Internal insulation provides better acoustical (noise) control. Flexible duct is very low cost. These products are engineered specifically for use in ducts or as ducts themselves, and are tested in accordance with standards established by Underwriters Laboratories (UL), the American Society for Testing and Materials (ASTM), and the National Fire Protection Association (NFPA). Many insulated duct systems have operated for years without supporting significant mold growth. Keeping them reasonably clean and dry is generally adequate. However, there is substantial debate about whether porous insulation materials (e.g., fiber glass) are more prone to microbial contamination than bare sheet metal ducts. If enough dirt and moisture are permitted to enter the duct system, there may be no significant difference in the rate or extent of microbial growth in internally lined or bare sheet metal ducts. However, treatment of mold contamination on bare sheet metal is much easier. Cleaning and treatment with an EPA-registered biocide are possible. Once fiberglass duct liner is contaminated with mold, cleaning is not sufficient to prevent re-growth and there are no EPA-registered biocides for the treatment of porous duct materials. EPA, NADCA and NAIMA all recommend the replacement of wet or moldy fiber glass duct material.

The Chartered Institution of Building Services Engineers is a body that covers the essential Service (systems architecture) that allow buildings to operate. It includes the electrotechnical, heating, ventilating, air conditioning, refrigeration and plumbing industries. To train as a building services engineer, the academic requirements are GCSEs (A-C) / Standard Grades (1-3) in Maths and Science, which are important in measurements, planning and theory. Employers will often want a degree in a branch of engineering, such as building environment engineering, electrical engineering or mechanical engineering. To become a full member of CIBSE, and so also to be registered by the Engineering Council UK as a chartered engineer, engineers must also attain an Honours Degree and a master's degree in a relevant engineering subject.
You can install the greatest HVAC system ever built, but if your house is not insulated well, it's only going to end up costing you more money. Older homes may have fiberglass insulation that has broken down due to pests, moisture, or improper installation. Spray foam insulation can be damaged by careless repair or modification work or can be improperly installed. If your insulation in compromised, your attempts to save money and be comfortable will be in vain.
Whether you’re starting your air conditioner for the first time this year, or a unit isn’t running properly and you need to service an air conditioner, following a few simple steps can save you time and money. While some service jobs should be left to a professional, there are several do-it-yourself fixes you can do to keep your air conditioner cooling all summer long.
Once on the scene, trained Sears professionals utilize powerful, truck-mounted equipment to clear your air ducts of dust, debris, pet dander, allergens, and grime. Our powerful air duct cleaning suction equipment vacuums out years of accumulated dust from your air ducts, leaving them clean and clear. Once finished, our technicians remove all equipment and make sure that your ducts and HVAC unit are restored to their best condition. For continued protection against dirty air ducts, your service technician may suggest a variety of air purification products.

I own and live in a mobile home and was told to install a mobile home air condition well I did not want one because the ones for moblie homes are to small,so I install a home air-condidtion and its good for heating and cooling the only thing I do is change is the filter every month or two,What I want to know is how does dirt and dust comes from????
I am in need of HVAC ADVICE!! I need a new furnace badly, mine is cracked. I have bought both a 95 % AFUE furnace and a 5 Ton evap coil, I figured it should all be replaced at once for both cost and efficency. My question is with all the negaitive things I have heard about companies ripping you off, what type of price should I pay someone for putting in those two items and bringing everything in my attic up to code? I have been quoted $550 - $ 3300. Wide margin here!! Then of course comes the licencing part!! I know in my heart that I should use a licenced contractor but I have had such bad luck and prices from them that honestly one that was licened in Ga. and just not here in TN and is a tech. which charges 1100 - 2200 less sounds good as so long as I pay some type of Profenial HVAC person say $100 to inspect the work after its done and before I pay them.
The performance of vapor compression refrigeration cycles[26] is limited by thermodynamics. These air conditioning and heat pump devices move heat rather than convert it from one form to another, so thermal efficiencies do not appropriately describe the performance of these devices. The Coefficient-of-Performance (COP) measures performance, but this dimensionless measure has not been adopted. Instead, the Energy Efficiency Ratio (EER) has traditionally been used to characterize the performance of many HVAC systems. EER is the Energy Efficiency Ratio based on a 35 °C (95 °F) outdoor temperature. To more accurately describe the performance of air conditioning equipment over a typical cooling season a modified version of the EER, the Seasonal Energy Efficiency Ratio (SEER), or in Europe the ESEER, is used. SEER ratings are based on seasonal temperature averages instead of a constant 35 °C (95 °F) outdoor temperature. The current industry minimum SEER rating is 14 SEER.[27][dead link]

I’m really not convinced that duct cleaning is of any value. My roommate wanted the ducts cleaned so he called some company. My scam senses is already tingling. They came in with a big negative pressure fan. Did some blowing and sucking in different vents. Then they tried to upsell a full system cleaning. They wanted to pull the blower and clean the heat transfer box at $700 per heater unit. I have a big house so we have two units. They also tried to sell us some “custom” $250.00 Air Lifetime air filters. At that point I pulled the BS get the hell out bell. After paying $520.00 for just the cleaning, I paid the bill and sent them on their way. I replaced the existing filter with the good old and cheap paper filters at $10.00 each. Duct cleaning… I’m not Impressed.


Moisture can enter the duct system through leaks or if the system has been improperly installed or serviced. Research suggests that condensation (which occurs when a surface temperature is lower than the dew point temperature of the surrounding air) on or near cooling coils of air conditioning units is a major factor in moisture contamination of the system. The presence of condensation or high relative humidity is an important indicator of the potential for mold growth on any type of duct. Controlling moisture can often be difficult, but here are some steps you can take:
I hired duct cleaning company out of "Service Magic" website. I did not realize the name of his company was Duck cleaning of Central Florida...that should have given me a hint.. The guy did a very poor, incomplete job, and ruined a closet full of clothes when he sprayed up to clean a vent instead of taking it down and cleaning it outside. He left me with more than 1/2 dirty vents and ducts, did not do the air handler in the garage and failed to fog the system. He spent 6 useless hours at my residence and now his insurance is denying coverage..very disappointed in Service Magic....
For more than 60 years Stanley Steemer has been perfecting our hot water extraction method to clean carpet with unparalleled results. Take control of the environment in your home and enjoy a cleaner, healthier living space for your family. Every carpet cleaning is Certified to remove an average of 94% of common household allergens. We remove the dirt you can see and the allergens you can't. 

Hi John, Thanks for reaching out, we would be happy to help you connect with a pro for your project. You can submit a request to our pros here: www.homeadvisor.com, browse a list of pros that serve your area here: http://www.homeadvisor.com/c.html, or send your info to emailus@homeadvisor.com and a project advisor will reach out to assist you. –HASupport
I have been a plumbing/gas/hvac tech for 19 years, before that I installed ductwork in commercial buildings and office towers. As the article states, unless you have undergone some type of extensive reno, or ducts have become contaminated, paying for cleaning is pointless. Its one thing if you have a 30 year old home that has never had a duct cleaning and you can actually see mounds of dust built up , especially in the return side, then go for it. Keep in mind that most duct cleaning companies will only get 80% of the dust , or less at best. Keep in mind that most of the dust in your home is lint from clothes and linens, and skin cells from you and your pets and is constantly being generated. Dust that builds up in ductwork , generally stays in the ductwork. The power of suggestion, scare tactics, up sell!!!
Venice warns homeowners to beware of air duct cleaning scams, especially the sort where unscrupulous cleaners offer a $49 special deal but start piling on extra fees. “It’s a bait and switch scam where they say they’ll offer unlimited cleaning, but then they throw around terms you might not understand, such as extra fees for a ‘main duct line,’” he says. “And many times, these cleaners end up walking out the door with twice the amount of money a reputable duct cleaner would charge. They’ve gotten very sophisticated at upselling.”
All information provided is provided for information purposes only and does not constitute a legal contract between Wilson's Heating & Air Conditioning and any person or entity unless otherwise specified. Information is subject to change without prior notice. Although every reasonable effort is made to present current and accurate information, LinkNow™ Media makes no guarantees of any kind.
Refrigerant Metering Device -- Every HVAC system has one of these, and heat pumps have two. They regulate the amount of refrigerant going through your air-conditioner. If it fails, either too much or too little refrigerant will course along the lines and either not perform well or will overwhelm the compressor and cause it to fail. A total failure of this component will result in a complete loss of operation.

CIBSE publishes several guides to HVAC design relevant to the UK market, and also the Republic of Ireland, Australia, New Zealand and Hong Kong. These guides include various recommended design criteria and standards, some of which are cited within the UK building regulations, and therefore form a legislative requirement for major building services works. The main guides are:
SEER is useful for comparing one model to another much in the same way that a car's calculate MPG is useful. It's not an accurate prediction of exactly how efficient the system is, but it can tell you which one is more efficient. Also, since SEER is based on a "cooling season", what region you live in will determine how long or short your cooling season is.
"Customer service was great, and the price was in-line with other places, and fast service. We had a whole replacement of the outside and inside. I would have liked to see a better install for the furnace and new thermostat - the new thermostat should have gone where the old one was, and even tho the new furnace was a tight fit, they didn't offer to come back and repair the case molding, or give me a discount on the damage done, and I believe they should have put a disconnect box on the outside of the home, to make it easier for any future repairs needed. Other than that, am very happy with the cooling and heating!"
×