Ventilating or ventilation (the V in HVAC) is the process of exchanging or replacing air in any space to provide high indoor air quality which involves temperature control, oxygen replenishment, and removal of moisture, odors, smoke, heat, dust, airborne bacteria, carbon dioxide, and other gases. Ventilation removes unpleasant smells and excessive moisture, introduces outside air, keeps interior building air circulating, and prevents stagnation of the interior air.
Maybe I took him to literally but I am pretty sure cops wont show up to ensure that my duct gets replaced. He said it would be over 1000 dollars to replace the ductwork if that is the case. Now, I spoke to a friend who did 2 ductwork lines on his own in his attic and he said it was like 15 dollars for the plastic wirewound tubing to create new ducts. Should I cancel that appointment and just do the work on my own? I feel like I’m a chump or lazy for considering paying someone to do this work.
Ok what you said is true but in most cases ducts are in a duct flex format, and knowing that the dust in people's flex duct is just surface dust, any real debris that are in the duct itself will result in very little to no air flow which will keep your unit from performing properly, but if it is true allergy reasons then replacing your duct system is better for overall better air quality, plus if you do pay attention to the warranty on flexible duct is that it only has a 10 year warranty and typically only lasts for 20 years so do your research before having a duct cleaning, and to add one more thing if your duct work is completely metal and you can't see visible insulation then your duct on the inside has insulation inside of it, if you replace that with duct work that is clean metal on the inside and wrapped with insulation on the outside then it will further reduce the air bourne fiberglass and dust.
My heat pump/hvac system is not blowing cold air anymore, got checked out was told compressor broken. was told it cost  almost the same to repair/replace they recommend whole system. It's the same company that installed it 18 years ago, telling me that system is old and it will cost $9-10k for new system, because furnace has to be replaced with new hvac. what to do, need answers thanks????
Capacitors -- Capacitors help your HVAC motor start from a standstill. Over time they can weaken. As they weaken, they cause the motor to run hotter. This can shorten the life expectancy of your motor. Once a capacitor fails, the whole motor will stop working. You usually won't notice that a capacitor has weakened until your motor stops turning on.
Duct cleaning has never been shown to actually prevent health problems. Neither do studies conclusively demonstrate that particle (e.g., dust) levels in homes increase because of dirty air ducts or go down after cleaning. This is because much of the dirt that may accumulate inside air ducts adheres to duct surfaces and does not necessarily enter the living space. It is important to keep in mind that dirty air ducts are only one of many possible sources of particles that are present in homes. Pollutants that enter the home both from outdoors and indoor activities such as cooking, cleaning, smoking, or just moving around can cause greater exposure to contaminants than dirty air ducts. Moreover, there is no evidence that a light amount of household dust or other particulate matter in air ducts poses any risk to health.
In reading through all this about duct cleaning, THE ONE preventative measure people need to realize is that a poorly installed HVAC system that is not sealed and air tight to ensure that ALL indoor air passes through a GOOD air filtration system IS THE best means of ensuring your ducts remain clean. Duct cleaning does not now and will NEVER improve an HVAC systems efficiency. Proper maintenance and installation are the key just as improper installation practices allow for dust infiltration into the duct system. I am a state licensed contractor in Texas, and unless people have their hvac system sealed and/or properly installed, duct cleaning is an absolute waste of money. My duct system is 12 years old as is as clean today as the day I installed the system with ductwork. SO before ANYONE jumps on the bandwagon of duct cleaning, get with your hvac professional FIRST.
On the other hand, if a service provider fails to follow proper duct cleaning procedures, duct cleaning can cause indoor air problems. For example, an inadequate vacuum collection system can release more dust, dirt and other contaminants than if you had left the ducts alone. A careless or inadequately trained service provider can damage your ducts or heating and cooling system, possibly increasing your heating and air conditioning costs or forcing you to undertake difficult and costly repairs or replacements.
Some of the research I have done suggests to have your ducts cleaned when you first purchase a new home to remove drywall dust. Maintain your system well and you shouldn't have to do it again until you want to sell. Those are the two times cleaning was suggested. So for peace of mind maybe it is a good idea to do it even if you buy a used home and then maybe every 5-10 years.
An air conditioning system, or a standalone air conditioner, provides cooling and humidity control for all or part of a building. Air conditioned buildings often have sealed windows, because open windows would work against the system intended to maintain constant indoor air conditions. Outside, fresh air is generally drawn into the system by a vent into the indoor heat exchanger section, creating positive air pressure. The percentage of return air made up of fresh air can usually be manipulated by adjusting the opening of this vent. Typical fresh air intake is about 10%.
Yes, ducts can look terribly dusty. However, that dust will not become aerosolized during the normal operation of your furnace. There is an easy way to test this. Rent a particle counter and test the air flowing out of your registers before and after cleaning. You will not see any improvement in the air quality or any reduction in the airborne dust level. Think of it this way. Duct cleaning companies tell you that you need to clean your ducts when you can see a layer of dust in your ducts. Yet that very layer of dust is proof that duct cleaning is unnecessary, because that dust proves that the air movement in your furnace is not fast enough to re-aerosolize the dust.
If you don't agree with duct cleaning, fine. If there are some things that HVAC people can do to make the system need cleaning less often fine, but to suggest that I need to GO TO JAIL????? If you need to knock others to make yourself look better....... If duct cleaning is such a scam, why are their governing bodies like NADCA (which I do NOT belong to),several manufacturers of equipment, and national restoration franchises (I'm not a franchise either) who provide this service? I guess the whole world is stupid and only HVAC people are smart. I suppose I am scamming them when I clean puff backs, water damage, fire damage, and clean their carpets too? Or did I wake up one morning and say "ya know, it is great to be a hard working, honest owner operator, but I would love to provide a service that unlike everything else I do is a con and rips off the 90% referral business I busted my butt to earn"
Chemical biocides are regulated by EPA under Federal pesticide law. A product must be registered by EPA for a specific use before it can be legally used for that purpose. The specific use(s) must appear on the pesticide (e.g., biocide) label, along with other important information. It is a violation of federal law to use a pesticide product in any manner inconsistent with the label directions.
Air conditioning units are prone to the pitfalls of wear and tear. You can prolong this, however, with proper maintenance procedures. Without regular maintenance even an immaculate AC installation in Fort Smith, Arkansas cannot guarantee performance. Our maintenance service is thorough, leaving no area unattended. If there’s a problem, we’ll catch it early and prevent avoidable breakdowns and costly repairs.
There is much more to air conditioning than AC installation in Fort Smith, AR then just maintenance and repairs. A variety of other services is required throughout the lifespan of your cooling unit. We are the professional team capable of completing them all. Replacements, troubleshooting, indoor air management, these are all part of our repertoire.
I'd have to disagree with all of your statements. Not only are they derived from no experience in the field, you are missing keys facts. Ducts even if air tight will get dirty. If they are not getting dirty, it means they are not working. Your returns side of the duct work is always under negative pressure when the system is operational.Therefore it is always drawing air in. Seeing how dust is made up mostly from dead skin humans shed daily. Around 1.6 Pounds of skin a year per human. Living in your home anything that is air born will be drawn back towards the cold air returns. That is what they are designed for, to draw stale air back to the system to be filtered and sent back through the house.Homes with carpet will actually have cleaner duct work than home with all tile or hardwood. This is because carpets hold onto dust particles and you vacuum them up. Whereas on hardwood or tile, dust can run freely back to the returns. Even if a duct system was sealed 100%, which is next to impossible to achieve 100% would still need to be cleaned. The cleaning may only have to be every 7-10 years for example. Most homes require every 5-7 years. And that's if it was done properly the first time. If you constantly hire people that have no or minimal knowledge of duct cleaning, You home would require cleaning more often. Every 2 years. That's a trade secret, The longer they recommend before the next cleaning, the odds are they did it right. That's not to say there aren't people that lie, because there are. Just have your duct cleaner take pictures before and after cleaning. Not just an outside view. Get in there, picture entire joist liners, Whole main runs and even long round pipes. Also it helps to have a company that guarantees their work. If it's not done right, they will come back and do it until it is. Most companies that do this make sure it is right the first time. Your not getting paid to do the job twice.

There are many interesting comments from several informed individuals. The question that has not been answered is how do duct systems get dusty and dirty? As a RESNET Home Energy Rater, I perform pressure tests on homes and duct systems, and the one common thread is . . . most air delivery sytems have large amounts of air leakage. The solution is to seal the duct system, and pay particular attention to the return duct system and ductwork near the air handler (the 'blower'). As others have said, a captive (sealed) duct system with proper filter maintenance should be more then adequate for most occupants. For those who have allergy, asthma, or other breathing problems, a filter with a higher MERV rating (number should be listed on the package) or a HEPA filter are good choices. These filters will capture smaller particulates and should improve the indoor air quality. Again, make certain that the entire duct system is sealed, preferably with mastic, second choice UL-181 foil tape - never use cloth duct (also known as duck) tape.
Demonstrate visible evidence of microbial growth in your duct work. Some service providers may attempt to convince you that your air ducts are contaminated by demonstrating that the microorganisms found in your home grow on a settling plate (i.e., petri dish). This is inappropriate. Some microorganisms are always present in the air, and some growth on a settling plate is normal. As noted earlier, only an expert can positively identify a substance as biological growth and lab analysis may be required for final confirmation. Other testing methods are not reliable.

Humidifiers/Dehumidifiers: Humidifiers add needed moisture to the air in winter and very dry climates. Dehumidifiers remove dampness any time of the year. Central air conditioners dehumidify too, but in very humid climates, you might want to remove humidity without also cooling the air. You have a good range of options for both of these HVAC accessories. Whole-house humidifiers cost $350 to $800 installed, while dehumidifiers are $1,250 to $2,000 or slightly more.
All these pro duct cleaners answer with "it's common sense, everything operates better when cleaner" etc. But your explanation is correct. Especially so with flex tube ducting where dust gets "stuck" between the lowest valleys (between wire coil supports) where air flow is drastically reduced -- which is more than 50 pct of the entire interior surface area of the flex ducting. That sounds like a bad thing but also has a good effect of trapping dust from escaping.
I had my ducts somewhat cleaned December 22, 2014. The hose of the machine the technitian used did not fit in some of my vents, therefore, he did not clean them. But I still paid $428.00 for the service. I will be calling the company on Monday, and kindly ask them to come back and clean the ducts they did not as they did not fullfill their part of the service.

Quality and price should come hand in hand, a too-good-to-be-true price for an efficient air duct cleaning will not give you the quality that you wanted. To make sure you are getting your money’s worth, check reviews of air duct cleaning companies, certifications from industry since this work requires continuous learning due to new techniques and research breakthrough from time to time. Make sure to shop around and get written estimates first.
Appliance Maintenance Book Snow Blower Maintenance Appointment Schedule Appointment for HVAC Maintenance Carpet Cleaning Services Air Duct Cleaning Services Handyman Service Riding Mower Maintenance Sears Warranty and Satisfaction Guarantee Heating and Cooling Home Renovation Tulsa Window Replacement Home Kitchen Design Roof Installation & Replacement Service Home Improvement Cabinet Refacing & Replacement Home Improvement
Whether you’re looking for air conditioning maintenance, air conditioner repair, or a new air conditioning system, Sears Home Services can help. We’re your best, most-trusted option for fast, quick, and easy local service, repair, and maintenance of your home air conditioning system. If your air conditioner isn’t cooling or your central air conditioner is leaking water, we’ll connect you to the best local AC repair service technicians in the business.We have local technicians in your neighborhood that are highly trained, licensed, vetted, and guaranteed to help fix all of your air conditioning needs.
Air conditioning and refrigeration are provided through the removal of heat. Heat can be removed through radiation, convection, or conduction. Refrigeration conduction media such as water, air, ice, and chemicals are referred to as refrigerants. A refrigerant is employed either in a heat pump system in which a compressor is used to drive thermodynamic refrigeration cycle, or in a free cooling system which uses pumps to circulate a cool refrigerant (typically water or a glycol mix).
The original furnace was a coal fired “octopus” design which had no blower to circulate the air but relied upon warm air rising to distribute the heat. That also means that the system breathed air in from the basement and most of this type did not have a cold air return system. At some point (probably in the 1940’s) the system was upgraded to a forced air gas furnace. The upgrade included replacing the 12″ diameter air ducts exposed in the basement with 6″ ducts and a cold air return system of ducts from the two (only two) air returns on the first floor.
Despite such anecdotal experiences, there's no scientific evidence that regular residential air duct cleaning improves air quality, according to a 1997 brochure published by the Environmental Protection Agency. Laureen Burton, senior scientist in the EPA Indoor Environments Division, says that while the document is nearly two decades old, the science hasn't changed and the agency stands by its recommendations.
Concealed behind your walls and mostly ignored, your air ducts serve as vital pathways that deliver warm and cool air throughout your home. While they may be unseen, your air ducts are working whenever you have your air conditioner or furnace running–nearly year round. Attached to your HVAC, air ducts transfer the air from these systems throughout your home. What many homeowners don't realize is that your air ducts, in nearly constant use, continually accumulate dust, grime, debris, pet dander, and allergens throughout the year. A professional air duct cleaning is necessary for better indoor air quality and the health of your family.
If you want to get some of the dust and debris out of your ventilation system, you can mix household cleaners like bleach with water, dip a cloth in the mix and then the wipe out the system. This will remove a layer of the spores, which could increase the quality of air a bit and help with the flow of air throughout the house until a pro can come out.
Having evaporator and condenser coils cleaned could cost between $100 and $400. If your coils can be accessed in-place, you'll be looking at a lower service cost. If your technician needs to remove the them first, the cost should be around $400. Having the evaporator and condenser coils cleaned can have a significant impact on the efficiency of your system. If your coils are excessively dirty, they won't be able to do their job and your system will have to work harder. Keeping up with the hygiene of these components can save you money in both the short and long-term. For example, replacing evaporator coils can cost anywhere from $650 to $1200.
Is there a such thing as a PQ-15 valve? No…but how do we know? And oh, by the way, there are only two types of line-sets: 3/4 inch, and 7/8 inch. All modern equipment runs on a 7/8 inch line-set, so the only time they’ll have to change something is if you have antiquated 3/4 inch line-set from the 60’s or 70’s. I’m digressing though…the point is that they can easily prey on uninformed consumers…like you, baby bird! Don’t worry though…you’ll be flying by the end of this article.
Some research suggests that cleaning heating and cooling system components (e.g., cooling coils, fans and heat exchangers) may improve the efficiency of your system, resulting in a longer operating life, as well as some energy and maintenance cost savings. However, little evidence exists that cleaning only the ducts will improve the efficiency of the system.
×