Had our ducts cleaned late April, 2016. Sodium Chlorite was sprayed into ducts after cleaning. Ever since, we have been bothered with eye and nasal passage irritation because of a “chemical” and “musty” odor. This odor is present whether or not a/c is on.) We are told the sodium chlorite (“EnviroCon, manufactured by Bio-Cide International) is used in hospital and nursing home settings and is not hazardous to health. The air duct company’s suggestion is that they come out and spray even more sodium chlorite…we absolutely don’t want this done! Have had various other recommendations about what we need to have done to remedy our problem. We will be unable to stay in our home if a resolution cannot be found. We’d be willing to replace the ductwork if necessary. (One professional suggested that the cleaning may have “knocked something loose” inside the ductwork and that is the source of the irritant.) This home was built in 1920…no idea when the present ductwork was installed. Any suggestions would be appreciated.

The liquid refrigerant is returned to another heat exchanger where it is allowed to evaporate, hence the heat exchanger is often called an evaporating coil or evaporator. As the liquid refrigerant evaporates it absorbs energy (heat) from the inside air, returns to the compressor, and repeats the cycle. In the process, heat is absorbed from indoors and transferred outdoors, resulting in cooling of the building.
Metal is way better than flex duct or ductboard. It gets better airflow, holds up to critters and duct cleaners. I know of no hvac company here that cleans ductwork. (there probably is one somewhere) The mfg's of duct cleaning equipment keep trying to sell us hvac people on their benefits and profit potential but most all hvac people know that unless you have metal ductwork you are NOT doing the customer any favors.
Air conditioning and refrigeration are provided through the removal of heat. Heat can be removed through radiation, convection, or conduction. Refrigeration conduction media such as water, air, ice, and chemicals are referred to as refrigerants. A refrigerant is employed either in a heat pump system in which a compressor is used to drive thermodynamic refrigeration cycle, or in a free cooling system which uses pumps to circulate a cool refrigerant (typically water or a glycol mix).

Window air conditioners cost less than central units, averaging $300. These systems generally suffice to keep a room cool on warm spring and summer days. They can bring added comfort for a reasonable price but are less powerful than a central air conditioner. If you have a bigger home with multiple rooms, you will probably need to have a larger system installed. Central air can cool several rooms at once, while window AC units usually only cover one or two rooms at a time.


The cooling coils the air comes into contact with appear to need UV-C lights on them in humid climates. That's the biggest thing. If the ducts have never been cleaned, then getting that done goes without saying. But those coils need to be cleaned, disinfected, and then UV-C light(s) installed to prevent mold & bacteria build-up in the future on them. That appears to be chiefly responsible for the dirty laundry and/or sour milk smell coming from forced-air AC systems in humid regions.
Stick with a maximum of 16 SEER units in most cases.  Like I said above, contractors push higher SEER units because they make more money, but these units can be expensive at this stage of development, and can drive up your HVAC installation cost.  21 SEER units run about twice the price of a 14 SEER unit, so unless you live in a desert and plan on being there for 30 more years... Likewise, a 16 SEER unit typically costs only about $600-$1,000 more than a 14 SEER, and will usually pay for itself over the lifetime of the unit.
Feel perfectly comfortable at home with our innovative Lennox Residential heating, cooling and air quality systems. Lennox manufactures high-efficiency HVAC systems including furnaces and air conditioners designed to conserve energy and save money. Our complementing air filtration systems, humidifiers and dehumidifiers help keep indoor air quality healthy and clean.
Once i received a call from a Person he Named Steve and He told me that he is from some like GTA Home services and providing Air duct Cleaning in around 105$ and i booked an appointment because he convince me in very will mannered so i agree the services i placed an order and i don't think that they guyz do a great job as he describe but they do same as he told me on phone i'm just surprised that they do a great job and they provide me free inspections of furnace and A/C as well and they really do a great job and they don't waist my money and time. thanks Adam Stevenson and GTA home service Team.
NADCA and EPA both have good points. Although, organizations are made to make money. Common sense and looking at NADCA and EPA pre-checklist. If you don't see it in the check list, you don't have to do it! But, if you do, look up Diamond certified co.s and the BBB. Beware of bait and switch scams, $60 vents and the like coupons which claim to help all for the measley sum of $79.00 bucks.
Despite Bergendahl's experience, Vinick says NADCA's certification standards have improved the situation. "A lot of [service companies] weren't going about it the correct way," he says. “We have an anti-fraud task force, and we’ve gone after some fraudulent duct cleaners with the help of state attorneys general.” He suggests that in addition to NADCA membership, homeowners make sure their cleaners are an established business, have appropriate insurance and are registered to do business in their state and locality.
In the case of heated water or steam, piping is used to transport the heat to the rooms. Most modern hot water boiler heating systems have a circulator, which is a pump, to move hot water through the distribution system (as opposed to older gravity-fed systems). The heat can be transferred to the surrounding air using radiators, hot water coils (hydro-air), or other heat exchangers. The radiators may be mounted on walls or installed within the floor to produce floor heat.
I always get a laugh at anyone claiming to be in the business for any length of time that doesnt understand the importance of cleaning out a ventilation system. Not only for better indoor air quality but for maintaining your heating equipment. I guess it makes more sense to some people that the furnace will just run better with a ton of dust and debris and maybe this wont be a big cause of sytem breakdown and malfunction. I mean really? Maybe this guy got a bad company and or cleaning and is a little jaded but to advise cleaning your grills , which does nothing, and replacing a filter....come on guy.
Manufacturers of products marketed to coat and encapsulate duct surfaces claim that these sealants prevent dust and dirt particles inside air ducts from being released into the air. As with biocides, a sealant is often applied by spraying it into the operating duct system. Laboratory tests indicate that materials introduced in this manner tend not to completely coat the duct surface. Application of sealants may also affect the acoustical (noise) and fire retarding characteristics of fiber glass lined or constructed ducts and may invalidate the manufacturer's warranty.
I have worked cleaning HVAC in my area for almost 5 years. I always do a thorough inspection and cleaning, providing before and after photos. I have completed some jobs where I felt that it was not entirely necessary, but ultimately what the customer wanted. With that being said, I have endless photos of unspeakable horrors. Hotels are usually nasty, post construction mess is certain, pets and kids create lots off debris, bugs congregate and die, then spiders set up and die, I have even had one supply that was nearly plugged with sand!
In variable climates, the system may include a reversing valve that switches from heating in winter to cooling in summer. By reversing the flow of refrigerant, the heat pump refrigeration cycle is changed from cooling to heating or vice versa. This allows a facility to be heated and cooled by a single piece of equipment by the same means, and with the same hardware.
Here in Atlanta we get 6 to 10 $49 coupons in the mail weekly…I have always consider them a complete scam….just had my master bathroom& bedroom and guest bath completely remodeled down to the studs…Had my 3 returns nearest the area sealed to prevent sheet rock dust to spread…it worked and I personally cleaned all 7 returns when a 5 HP , new Rigid shop Vac($99 from HD)…took one hour and I found little evidence that “I need my ducts cleaned” Had quotes from $400 to $600…I use the best air filters for my air handler and change it every 2 to 3 months…..any dust is trapped in it and I believe the Air Duct folks are all cons….
An air conditioner's compressor contains a refrigerant. As it works, it sends this refrigerant through the system. As warm air blows across the coil that carries this refrigerant, the heat transfers to the refrigerant (cool always absorbs warm). A fan moves the cooled air through the ducting and out of vents that lead into the rooms of your house. The refrigerant returns to the compressor where the absorbed heat is moved outside. The refrigerant is then sent through the coil once again to continue the cycle.
The EPA is so far behind on useful knowledge because of the lack of funding so don't be mislead. The Hvac old timers were left at the dock so to speak and missed out on the IAQ movement. The ones that are savvy and up to date on the information do Air Duct Cleaning, even tho that will lead to a few less service calls its the right thing to do for their customer. Please take a look into a return duct that has never been cleaned, I dare anyone to say it does not need to be cleaned.
The original furnace was a coal fired “octopus” design which had no blower to circulate the air but relied upon warm air rising to distribute the heat. That also means that the system breathed air in from the basement and most of this type did not have a cold air return system. At some point (probably in the 1940’s) the system was upgraded to a forced air gas furnace. The upgrade included replacing the 12″ diameter air ducts exposed in the basement with 6″ ducts and a cold air return system of ducts from the two (only two) air returns on the first floor.
Deciding if central air is worth the cost depends on your needs and local housing market. If you live in a hotter climate, it can definitely be worth the price. Not only can it keep your home at a comfortable temperature, but air conditioning can even save lives during extreme heat waves. But in a milder zone without severe temperatures, window units, fans or the breeze from an open window could be adequate.
Pay particular attention to cooling coils, which are designed to remove water from the air and can be a major source of moisture contamination of the system that can lead to mold growth. Make sure the condensate pan drains properly. The presence of substantial standing water and/or debris indicates a problem requiring immediate attention. Check any insulation near cooling coils for wet spots.
Good article, but it fails to point out that leaky return-side ducts could be drawing dust and allergens into the duct system from the enclosed spaces in which they run, e.g. between walls, below floors, attic. So duct cleaning may only be a temporary solution. The homeowner can get a home energy audit -- free in many states -- to determine if they have significant duct leakage. An Aeroseal dealer may be able to effectively seal up the duct system without needing to tear into walls etc to get to the ducts.
I think that the coding and permit industry is a joke!! They will not allow the homeowner to apply for the permit it has to be the licenced contractor. It would make since to allow the homeowner to apply for this. But it is all about money!! They really don't care if its up to code because if they did then they wouldnt care who applied and payeed for it, but they want the contractor to do it so if they do something wrong they can fine them instead of just pointing it out and allowing them to do it right.

My heat pump/hvac system is not blowing cold air anymore, got checked out was told compressor broken. was told it cost  almost the same to repair/replace they recommend whole system. It's the same company that installed it 18 years ago, telling me that system is old and it will cost $9-10k for new system, because furnace has to be replaced with new hvac. what to do, need answers thanks????


I call to follow up at the end of the next day and she said that she has not been able to get in touch with the owner.  By this time, I am starting to get frustrated because I am starting to get the run around.  I question her if I am even on the schedule or if they attempted to schedule a crane.  She says they are extremely busy and that she does not know.  So I say, basically I have waited over 2 weeks and you have not put me on the schedule and I am at the end of the install line.  No answer.  I tell her to talk to her boss and find out what is happening, and I will think about what direction I want to move in at this point.  

Just had my air ducts cleaned. They used a high pressure air hose in all the heat ducts and cold air returns. He showed me the stuff that came out, the reason for the duct cleaning was the fact that I had a problem. With rodents. There was quite a few mummified rats and mice, and he said I wouldn’t have to have them done again unless I incur another problem or have renovations done. Cost me 345.00 for a 2 storey large old home. Not a bad price as I had them done when I moved in 28 years ago and it cost me 500.00. Lots of dog hair, toys, balls and assorted goodies came out as well. Took them 2 hours. I did have sanitizer put in the ducts because of the dead rodents.
I was with you until you said avoid steaming cleaning or moisture, there is no way you can remove mold or any other type of biological without moisture. The best way to do this is in fact with a steamer using a commercial disinfectant and a non reactive odor remover so your home smells refreshed and not like a hospital . This is directly contradictory to your article.
Engineers have pointed out some areas where efficiency of the existing hardware could be improved. For example, the fan blades used to move the air are usually stamped from sheet metal, an economical method of manufacture, but as a result they are not aerodynamically efficient. A well-designed blade could reduce electrical power required to move the air by a third.[28]
If the one noticeable spot is where the wall [or ceiling or floor] is white.......first.....take a pair of needle nose pliers and bend each louver of the register to a straight outward position [as they all come brand new with a slant to each side]....so the register is shooting all supply air straight outward. If its a round register [in ceiling].....no help there. You also should always burn soy or beeswax candles.
Air conditioner size is measured in “tons.” However, the tonnage of an HVAC unit is not actually based on its weight. A “ton” is simply a measure of an air conditioner’s ability to cool your home. One ton is the ability of your air conditioning system to cool 12,000 BTUs (BTU stands for British Thermal Unit) in an hour. Likewise, a “2-ton” central air conditioner is able to cool 24,000 BTUs per hour.
They are also often harder to install. A proper location on the roof must be selected that can support the weight of the unit. Then a platform must be built and a drain pipe for the unit must be run along the roof to avoid problems with mold and corrosion. A crane must be used to lift the unit onto the roof while a team guides it into place and hooks it up.
I own a small mechanical company. My main work is service and system replacements. I have never been a believer in duct cleaning. The company I worked for before had our duct man come out and do my house. I saw no difference. Preventive maintance is what I recomend. Remove fan and clean, seal fan compartment to prevent dust from being pulled in, filters I install media filters, they are 5″ thick and pleated. I have tested them to make sure static presure was not a issue. Heat exchangers and AC coils need to be cleaned. I will tell you this to do a good cleaning I usually spent 1-2 hrs, When I’m finished I would not have a problem eating my diner on the system. Good filters, clean system and properly tuned up are my recomdation to anyone. I’ve included my email feel free to contact me with any questions. winkcfd@yahoo.com
A house breathes just like you an I.For example every time your clothes dryer comes on it automatically creates a negative pressure inside the home.So if air goes out of the living area it has to be replaced.....now look above the ceiling fan ....you see the cover...underneath that is a hole straight to your attic....Now the stuff on your ceiling fan you call dust...call it insulation,rat fecies or anything else that is in your attic that could be pulled in your due to a negative pressure.

Heating, ventilation, and air conditioning (HVAC[1]) is the technology of indoor and vehicular environmental comfort. Its goal is to provide thermal comfort and acceptable indoor air quality. HVAC system design is a subdiscipline of mechanical engineering, based on the principles of thermodynamics, fluid mechanics and heat transfer. "Refrigeration" is sometimes added to the field's abbreviation, as HVAC&R or HVACR or "ventilation" is dropped, as in HACR (as in the designation of HACR-rated circuit breakers).
Deciding if central air is worth the cost depends on your needs and local housing market. If you live in a hotter climate, it can definitely be worth the price. Not only can it keep your home at a comfortable temperature, but air conditioning can even save lives during extreme heat waves. But in a milder zone without severe temperatures, window units, fans or the breeze from an open window could be adequate.
Concealed behind your walls and mostly ignored, your air ducts serve as vital pathways that deliver warm and cool air throughout your home. While they may be unseen, your air ducts are working whenever you have your air conditioner or furnace running–nearly year round. Attached to your HVAC, air ducts transfer the air from these systems throughout your home. What many homeowners don't realize is that your air ducts, in nearly constant use, continually accumulate dust, grime, debris, pet dander, and allergens throughout the year. A professional air duct cleaning is necessary for better indoor air quality and the health of your family.
R-22 Freon is being phased out & isn't readily available. So the service company may only purchase as needed and the lack of availability would make their cost high. But, as long as they can get it, whatever the cost, unfortunately, is less expensive than replacing the A/C. Which will be the case eventually since it's no longer manufactured or sooner as in my case with a not so old a/c that sprang a leak, that would have been just a repair, but since it uses R-22 the whole unit has to be upgraded(replaced).  
To qualify for a tax credit from the federal government, you must save the manufacturer's certificate from your system. The IRS won't require the certificate at the time you file your federal tax forms, but they recommend keeping it with your records in case of an audit. It proves that you purchased a qualifying product. The government offers tax credits for:
A house breathes just like you an I.For example every time your clothes dryer comes on it automatically creates a negative pressure inside the home.So if air goes out of the living area it has to be replaced.....now look above the ceiling fan ....you see the cover...underneath that is a hole straight to your attic....Now the stuff on your ceiling fan you call dust...call it insulation,rat fecies or anything else that is in your attic that could be pulled in your due to a negative pressure.

I paid $49 for a groupon. When the guy came today, he did an inspection first and said the ductwork first needed to be treated for mold; $348 for a spray that would last 8 months or $680 for an UV light purifier that would last 2 years. Also, the furnace needed to be cleaned for another $260. When I told him to just clean the ductwork, he said I would owe an additional $305 because the groupon was only good for 1 return and I had 2. I sent him packing with no services performed. Thankfully I am only out of $49! I will complain to groupon.
Metal is way better than flex duct or ductboard. It gets better airflow, holds up to critters and duct cleaners. I know of no hvac company here that cleans ductwork. (there probably is one somewhere) The mfg's of duct cleaning equipment keep trying to sell us hvac people on their benefits and profit potential but most all hvac people know that unless you have metal ductwork you are NOT doing the customer any favors.
Duct cleaning generally refers to the cleaning of various heating and cooling system components of forced air systems, including the supply and return air ducts and registers, grilles and diffusers, heat exchangers heating and cooling coils, condensate drain pans (drip pans), fan motor and fan housing, and the air handling unit housing (See diagram).
×