Metal is way better than flex duct or ductboard. It gets better airflow, holds up to critters and duct cleaners. I know of no hvac company here that cleans ductwork. (there probably is one somewhere) The mfg's of duct cleaning equipment keep trying to sell us hvac people on their benefits and profit potential but most all hvac people know that unless you have metal ductwork you are NOT doing the customer any favors.
20 yrs ago I bought the house I am in and a Central H/A was installed at that time. At the beginning of ea season I have the unit serviced. Every yr since I have owned the house I have had to have freon added and been told that I must have a freon leak. Fast forward to this yr when I hired a new company to do the service. They went up into the attic as part of their overall servicing. Nobody else has ever done that. He came down showing me pics on his camera phone of ducts that were not even connected to anything and in my estimation have probably been laying there for 20 yrs. Of course he fixed this. I have not needed freon this year either. I have been complaining to friends about the huge amount of dust and how I can't keep up with the cleaning away of it for a long time. Now it makes so much sense.To me it is like that duct work was just up there laying around and every time my unit was blowing, all the insulation, debris, dust and whatever else over the years was just randomly filling up those ducts. What now that they are re-connected? Will it be better? Or am I someone that needs to have my ducts cleaned? I am so confused after reading all these comments. Can one of you experts tell me what you would do before I spend a bunch of money that I don't really have? Thank you for any input you can provide. Also, feel free to respond to email address denise@digitalflak.com
The University of Virginia - 2005 / The Wharton School of Finance - 2016 / U.S. Naval Aviator 2005-2015. At All Systems Mechanical air conditioning and heating, we believe that the experience our clients have is every bit as important as the products they receive. Simply put, our results speak for themselves, and we'd be happy to help. If you're in the market for a new AC or furnace, make sure that you get a fair price! Try our online calculator; click the tab on the top of this page for more information.

The most recognized standards for HVAC design are based on ASHRAE data. The most general of four volumes of the ASHRAE Handbook is Fundamentals; it includes heating and cooling calculations. Each volume of the ASHRAE Handbook is updated every four years. The design professional must consult ASHRAE data for the standards of design and care as the typical building codes provide little to no information on HVAC design practices; codes such as the UMC and IMC do include much detail on installation requirements, however. Other useful reference materials include items from SMACNA, ACGIH, and technical trade journals.
Furnace cleaners are mostly young men, I know this, I have been one for 15 years or so……so heres the truth, if there are any allergies, children, older people with health issues, we are GOING to make money. do not tell the company you have hired about any health complication. they are salesmen. and they don’t care about you. or your money. make sure they do a good job, then kick them out. you don’t need all the bells and whistles they wanna sell you. any idiot can clean duct work, like I said, I am one of them. I am very good at it, but I don’t have the back bone to sell a widowed old lady a humidifier that she doesn’t need for 500 bucks, overall, if you think you need this service done, which you probably don’t, get it done, do not spend anything over 300$ and do not do it again for at least ten years.

Most organizations concerned with duct cleaning, including EPA, NADCA, NAIMA and the Sheet Metal and Air Conditioning Contractors' National Association (SMACNA) do not currently recommend the routine use of sealants to encapsulate contaminants in any type of duct. Instances when the use of sealants to encapsulate the duct surfaces may be appropriate include the repair of damaged fiber glass insulation or when combating fire damage within ducts. Sealants should never be used on wet duct liner, to cover actively growing mold, or to cover debris in the ducts, and should only be applied after cleaning according to NADCA or other appropriate guidelines or standards.

I spent a lot of time reading all these posts and frankly I can’t believe the way some people think. 1. If there is dust and dirt of any kind in my HVAC system I want it out, the mentality that it can stay there and it’s fine is fulish as the system turns on and off microscopic particulates will move in and out of your living space and you will definitely breath them in. The air quality of your home or office will only be as clean as the system that produces it. We don’t not clean things simply because we can’t see them, it’s what we can’t see that can do the most harm. Dust will build up in a system fairly quickly and will get damp at times allowing mold to grow and mold releases spores without any movement as part of its defense meconisam so don’t tell me that when your system turns on it won’t blow the spores out into the living spaces of your home. A build up of dust will cause failures to your system over time, equipment that works harder to do its job will run hotter with more strain and this will lead to brake downs and until then the system will run less efficient then it should. The system was engineered to move a certain volume of air through a specific duct size, when that duct size starts to become narowed down with dust build up your system has to work harder to move that air this is why you will end up with a loss of efficiency and eventually breakdowns or failures. I have seen systems develop a significant amount of dust build up in as little as two years, just look at how fast the filter gets clogged up and it isn’t all that hard to believe. As for all the scams that are out there they hurt the industry because people can’t decipher between them and the legitimate companies, BBB is helpful. Recommendations from HVAC contractors will be a good resource and a good company will provide a written estimate with a complete brake down of what they are going to do and why, most of which is comen sence once they explain it to you, then if you spend about 5 minutes watching them once they are set up you can see they are doing what they said they would do and let’s get real would you do a job that should take approx 3 hours per system for $29/$39/59 or something close to that, if you think you are going to get a good job from a comp that has to make money at that price you shouldn’t be mad at anyone but your self for trying to get quality work at a scam price. If it’s done right it will be very beneficial and depending on the size of your system and where you are in the world it’s going to cost you approx $300 to $600 per system large and or older systems may cost even more. Remember a quality job isn’t wasting money but a lousy job is, even if it’s only $29. I’d rather spend $600 on a quality job then $29 on a lousy job!! Good luck..


Two weeks go by and no phone call from HVAC Service regarding install date, or any update at all.  I call them to check in to see if they have put me on the schedule and when I can expect to have the AC installed.    You can tell by the discussion I had with the lady on the phone that they completely forgot about me and have not scheduled anything.  She says she needs to get in contact with the owner because she has no idea on the availability of the crane.  I was told that she would call me back by the end of the day with an update.  Surprise, surprise, no phone call.  

I call to follow up at the end of the next day and she said that she has not been able to get in touch with the owner.  By this time, I am starting to get frustrated because I am starting to get the run around.  I question her if I am even on the schedule or if they attempted to schedule a crane.  She says they are extremely busy and that she does not know.  So I say, basically I have waited over 2 weeks and you have not put me on the schedule and I am at the end of the install line.  No answer.  I tell her to talk to her boss and find out what is happening, and I will think about what direction I want to move in at this point.  
Be careful of dishonest HVAC contractors. There’s no magical formula to see if an HVAC contractor is scamming you, unfortunately, but remember that they typically do this in one of two ways: first, they are charging grossly low prices (far below everyone else), or second, they aren’t including what everyone else is. In the first situation, they will charge you change fees, other hidden fees, or they stole the equipment and are passing themselves off as legitimate contractors (very common in California these days). In the second situation, they are charging you a very fair price, but aren’t including what the other contractors are (i.e. charging $10,500 for the installation which is fair, but not including the ductwork which is a scam unless there is some other, complex stuff going on there).

The key to the continued and efficient operation of your heating and cooling system is periodic maintenance. Cleaning the air duct vent system, and servicing you heating and cooling equipment will keep the system operating at its peak performance. Air ducts are cleaned for two reasons. One: to prevent debris from entering furnace and air conditioning components. Two: to prevent debris from cycling through the home. The air duct cleaning contractor needs to employ cleaning methods which successfully removes debris, and ensures that debris does not enter the occupied space. Most contractors can verify the results of the cleaning through video or pictures.


You might also want to check your home for thermal insulation if you live in extreme heat or freezing temperatures. Insulation keeps the heat and cool air in your home, which can lead to a lower electric bill. If the heated or cool air leaks out, your system turns on more often. There are various types of insulation that you can install in your home and a home energy auditor can point out the best places for it in your house.
Furnace Circuit Board -- The furnace circuit board controls a variety of functions. It not only handles the regular operation of the furnace, it also monitors the furnace's various safety circuits. Over time, vibrations from the furnace can weaken solder point and cause them to separate. Dirt and debris can cause short-circuits that damage the board. Failure of the circuit board can cause a variety of effects ranging from the fan not turning on to the complete shutdown of the furnace.
I am 79 years old, bought a condo & spent a lot of money on it. this winter my first bill was 450.00. had my furnace checked out, which is on the roof. it was old rusted out & leeking oil. i talked to owner & had new unit installed. they came out to clean ducks & they were split & worn out. there is no crawl space because theres a unit above me. my real estate lady or this company will not help me fix this problem.

If you think duct cleaning might be a good idea for your home, but you are not sure, talk to a professional. The company that services your heating and cooling system may be a good source of advice. You may also want to contact professional duct cleaning service providers and ask them about the services they provide. Remember, they are trying to sell you a service, so ask questions and insist on complete and knowledgeable answers.
Dehumidification (air drying) in an air conditioning system is provided by the evaporator. Since the evaporator operates at a temperature below the dew point, moisture in the air condenses on the evaporator coil tubes. This moisture is collected at the bottom of the evaporator in a pan and removed by piping to a central drain or onto the ground outside.
Knowing what you should be paying for your HVAC equipment and installation is essential to getting a fair deal. Most HVAC prices aren’t advertised. Contractor strategy is to get a salesperson into your home to sell you on a package of equipment, accessories and installation. This makes comparing systems difficult, and some sales pressure might be applied.
Consider what kind of heating and cooling system you want installed for the square footage of your home. Do you want a full system with a thermostat or a specific machine for the summer like a swamp cooler? Do you need a new furnace just for the winter? For any of these projects, the cost will vary depending on the quality, style and machine size you choose. If you have a tight budget, think of going smaller and upgrading over time. For example, if you can't afford to convert your entire home to solar power, you may want to consider only utilizing it to heat your water. Some other types of heating systems are:

Equipment used to clean ducts varies widely. The cheaper the equipment used the more you are just wasting money. This is why it's typically not worth doing. In some situations it may be beneficial, but only after determining and investigating the duct system. This should be done by a licensed HVAC contractor and not a duct cleaner that typically do not hold and HVAC license. (Duct cleaners aren't required to be licensed in HVAC in many areas.)
Central, "all-air" air-conditioning systems (or package systems) with a combined outdoor condenser/evaporator unit are often installed in North American residences, offices, and public buildings, but are difficult to retrofit (install in a building that was not designed to receive it) because of the bulky air ducts required. (Minisplit ductless systems are used in these situations.) Outside of North America, packaged systems are only used in limited applications involving large indoor space such as stadiums, theatres or exhibition halls.

I always get a laugh at anyone claiming to be in the business for any length of time that doesnt understand the importance of cleaning out a ventilation system. Not only for better indoor air quality but for maintaining your heating equipment. I guess it makes more sense to some people that the furnace will just run better with a ton of dust and debris and maybe this wont be a big cause of sytem breakdown and malfunction. I mean really? Maybe this guy got a bad company and or cleaning and is a little jaded but to advise cleaning your grills , which does nothing, and replacing a filter....come on guy.

They were quick to come out and diagnose the problem with my furnace, but I thought the estimate of $549 a bit high to replace the circuit board.  So called around and found Leo's Appliance in Concord that sells appliance parts and the circuit board was only $90.49 - that is the retail cost to me, so I imagine the wholesale cost is a lot less.  So BEWARE of this company since they wanted $500!!! to replace the circuit board which is located right in the front of the furnace - extremely easy to access.  I hate it that you cannot trust repair companies.
Do not hire duct cleaners who make sweeping claims about the health benefits of duct cleaning — such claims are unsubstantiated. Do not hire duct cleaners who recommend duct cleaning as a routine part of your heating and cooling system maintenance. You should also be wary of duct cleaners who claim to be certified by EPA. Note: EPA neither establishes duct cleaning standards nor certifies, endorses, or approves duct cleaning companies.
Capacitors -- Capacitors help your HVAC motor start from a standstill. Over time they can weaken. As they weaken, they cause the motor to run hotter. This can shorten the life expectancy of your motor. Once a capacitor fails, the whole motor will stop working. You usually won't notice that a capacitor has weakened until your motor stops turning on.

If you want to get some of the dust and debris out of your ventilation system, you can mix household cleaners like bleach with water, dip a cloth in the mix and then the wipe out the system. This will remove a layer of the spores, which could increase the quality of air a bit and help with the flow of air throughout the house until a pro can come out.
Manufacturers of products marketed to coat and encapsulate duct surfaces claim that these sealants prevent dust and dirt particles inside air ducts from being released into the air. As with biocides, a sealant is often applied by spraying it into the operating duct system. Laboratory tests indicate that materials introduced in this manner tend not to completely coat the duct surface. Application of sealants may also affect the acoustical (noise) and fire retarding characteristics of fiber glass lined or constructed ducts and may invalidate the manufacturer's warranty.
While you consider having your air ducts cleaned, it is a good idea to take a look at your dryer vent. If your dryer vent is clogged, you could be losing energy efficiency. Worse yet, you could be increasing the risk of a house fire. Having your dryer vent professionally cared for costs about $130 on average, and could save you a bit of money and a lot of headaches in the future. For more information on the benefits and cost of having your dryer vent cleaned, take a look at our comprehensive cost guide.
In modern buildings, the design, installation, and control systems of these functions are integrated into one or more HVAC systems. For very small buildings, contractors normally estimate the capacity and type of system needed and then design the system, selecting the appropriate refrigerant and various components needed. For larger buildings, building service designers, mechanical engineers, or building services engineers analyze, design, and specify the HVAC systems. Specialty mechanical contractors then fabricate and commission the systems. Building permits and code-compliance inspections of the installations are normally required for all sizes of building.
Vinick calls air duct cleaning an essential part of home maintenance, akin to mopping and vacuuming. "It’s like changing the oil in your car,” he says. “If you don’t change the oil, you’re going to have a problem. When your components are loaded up with debris, the system has to work harder. When you remove that debris, you get energy consumption savings.”
WELL, this summer when I opened them up we had black dust spewing from one of the upstairs vents. It resembled the fuzz that comes off new towels. This prompted us to look into duct cleaning. We heard from someone who had it done several times, said it was worthwhile, and knew of a firm that did a good job. Clean Air America sent a single technician for the appointment and after counting registers and ducts gave me a price of $360.00 which included “sanitizing” the system (a $99 additional fee per can used). The small size of the plenum forced him to connect the 8” round vacuum hose from the truck to the 10” square opening from our humidifier unit. In hindsight, a mistake since it reduced the “negative” pressure in the system.
Contact/Relay -- Relays are electronically controlled switches that activate the various components of your HVAC system. They manage everything from the power going to the motor to automatic dampers, humidifiers, etc. Most of them are controlled by the thermostat. The most common failure for a relay is being stuck in the "open" position. Separated from its assigned contact point, it fails to complete the connection and send the message to whatever it was supposed to operate. This failure usually occurs from use over time. Each time a relay connects and sends its signal, the electrical arcing from point to point eventually causes wear and tear.
My heat pump/hvac system is not blowing cold air anymore, got checked out was told compressor broken. was told it cost  almost the same to repair/replace they recommend whole system. It's the same company that installed it 18 years ago, telling me that system is old and it will cost $9-10k for new system, because furnace has to be replaced with new hvac. what to do, need answers thanks????
One of the difficulties encountered by many air duct cleaning service companies is that their attention is not really on air duct cleaning. For example, many heating and cooling companies offer duct cleaning as a supplemental service, but of course their primary business is installing and servicing heating and cooling equipment. For these companies, air duct cleaning is not always given the attention it deserves and is often done by less experienced employees whose interest is not in duct cleaning but in repairs and installs. And it is almost always done with inferior air duct cleaning equipment. Still other firms (like carpet cleaners) offer a large variety of services and claim to “do everything.” Because of their lack of focus they may not actually be very good at many, if any, of the services they offer. They cannot simply buy an attachment for their carpet cleaning machine and magically become a great duct cleaner.
Knowing what you should be paying for your HVAC equipment and installation is essential to getting a fair deal. Most HVAC prices aren’t advertised. Contractor strategy is to get a salesperson into your home to sell you on a package of equipment, accessories and installation. This makes comparing systems difficult, and some sales pressure might be applied.
Because an air conditioner moves heat between the indoor coil and the outdoor coil, both must be kept clean. This means that, in addition to replacing the air filter at the evaporator coil, it is also necessary to regularly clean the condenser coil. Failure to keep the condenser clean will eventually result in harm to the compressor, because the condenser coil is responsible for discharging both the indoor heat (as picked up by the evaporator) and the heat generated by the electric motor driving the compressor.
But Tim, doesn’t this mean that a less-than-honest air conditioning company can just charge what he wants and say that it’s a difficult job? No. You see, dishonest contractors, typically, aren’t the brightest people (I figure if you’re still reading this, you’re warming up to me so I’m taking off the training-wheels). They aren’t smart enough to take difficulty into account, and will probably get confused if you ask them about it. They will tell you things like, “that’s how much the unit costs,” or “California has a new law that magically adds $5,000 to the price.”  Trust me, follow your gut, and you’ll be able to tell who the honest contractors are...or just use one of our ASM-approved contractors.
1). Busy companies: The company is so busy, it doesn’t need the work. It will add 70% to 100% profit, and if the customer accepts the estimate, it will move that high-margin customer to the front of the line. This often happens in the worst heat of summer when overburdened ACs and heat pumps quit and the dead of winter when furnaces give up. This is a good reason to consider pre-emptively replacing your system once it’s about 15 years old and/or has had major repairs.
In the United States, HVAC engineers generally are members of the American Society of Heating, Refrigerating, and Air-Conditioning Engineers (ASHRAE), EPA Universal CFC certified (for installation and service of CFC HVAC devices), or locally engineer certified such as a Special to Chief Boilers License issued by the state or, in some jurisdictions, the city. ASHRAE is an international technical society for all individuals and organizations interested in HVAC. The Society, organized into regions, chapters, and student branches, allows exchange of HVAC knowledge and experiences for the benefit of the field's practitioners and the public. ASHRAE provides many opportunities to participate in the development of new knowledge via, for example, research and its many technical committees. These committees typically meet twice per year at the ASHRAE Annual and Winter Meetings. A popular product show, the AHR Expo, is held in conjunction with each winter meeting. The Society has approximately 50,000 members and has headquarters in Atlanta, Georgia.
Your HVAC unit and air ducts deliver heated or cooled air throughout your home year-in and year-out. The air your HVAC unit produces travels through your ductwork and heats or cools your home via the air vents in each room. The dust and other particles in your home’s air are known as particulate matter, which the EPA defines as "a complex mixture of extremely small particles and liquid droplets." The EPA also notes that "particle pollution is made up of a number of components, including acids (such as nitrates and sulfates), organic chemicals, metals, and soil or dust particles." Having clean air ducts means fewer of these particles moving through your home. If you remove your furnace filter and hold it up to the light, you can probably see several hundred of these minuscule particles floating in the air. 

PickHVAC Tips: Don’t be sold on systems with features you don’t want or need. Called “upselling,” it is rampant in the HVAC industry. Some features are nice – if you want them. If your single-stage furnace was loud and pushed out cold air at the start of the cycle, then a two-stage model will improve those issues. If you didn’t notice them, the upgrade will be a waste of money. That’s just one common example.
The heat pump gained popularity in the 1950s in Japan and the United States.[13] Heat pumps can extract heat from various sources, such as environmental air, exhaust air from a building, or from the ground. Heat pumps transfer heat from outside the structure into the air inside. Initially, heat pump HVAC systems were only used in moderate climates, but with improvements in low temperature operation and reduced loads due to more efficient homes, they are increasing in popularity in cooler climates.
I have lived in Calgary for quite some time now. When I first moved here I couldn’t stand the humidity levels. Its like a desert come winter. When I first moved into my new home, the house inspector insisted I have my furnace and ducts cleaned. I was very sceptical about duct cleaning to begin with. The company I hired came on time and were very respectable from the start. Before mentioning anything they asked me what my concerns were and what issues I was having. They were more concerned about addressing my issues then bringing anything non related up. I ended up going with this company and getting a humidifier installed a couple days later after the cleaning. Its been almost 4 years now that I have been here. The humidifier is working great and the difference is incredible. They took me around explained step by step what they were doing and the reasons they were doing it. With all those other companies out there, I am glad I found them at this site.
Though this installation is not always complicated, it's best to work with an air conditioning contractor to ensure it's done correctly. Permits are usually required for this type of work and can be obtained by a state-licensed contractor. You should not attempt to install central air conditioning on your own since you need a license to handle the refrigerant chemicals (Freon) involved.
Quality and price should come hand in hand, a too-good-to-be-true price for an efficient air duct cleaning will not give you the quality that you wanted. To make sure you are getting your money’s worth, check reviews of air duct cleaning companies, certifications from industry since this work requires continuous learning due to new techniques and research breakthrough from time to time. Make sure to shop around and get written estimates first.
I purchased a Groupon for cleaning of unlimited air ducts and one return vent for $39. I should have checked into their hours first because they only offer services during normal business hours. So, with no evenings or weekends available you have to take time off work. I asked Groupon for a refund when I realized this and they refused because it wasn’t within the three day window. Then they didn’t even show up or call for the appointment. I called them after they were an hour late and they were going to call the local dispatch office and have them call me back within 15 minutes. I did not receive that call. I called again and was told I would get a call back from a manager. That didn’t happen either. So I asked Groupon for a refund again and they gave me Groupon bucks. When the survey came asking if I was satisfied with the Groupon customer service I said no, I want real money. I got my real refund the next day. Seems to me Groupon should stop dealing with these companies.

Since most states and municipalities don’t license air duct cleaners, you need to check their professional credentials instead, such as NADCA membership. EPA recommends all duct cleaners follow NADCA standards. Member companies must keep at least one technician on staff who has passed a NADCA test. “They have to pass rigorous testing to earn the certificate, and our code of ethics is very important,” Vinick says.
Some of the research I have done suggests to have your ducts cleaned when you first purchase a new home to remove drywall dust. Maintain your system well and you shouldn't have to do it again until you want to sell. Those are the two times cleaning was suggested. So for peace of mind maybe it is a good idea to do it even if you buy a used home and then maybe every 5-10 years.

The amount of time it takes to clean a residential HVAC system depends on many variables such as the size of the home, the number of systems, the extent of the contamination and the number of HVAC cleaners performing the job. Ask at least two contractors to inspect your system and give you a time estimate for your particular system. This will give you a general idea of how long the job should take as well as an idea of how thoroughly the contractor plans to do the job.

As a homeowner and an owner of rental property I can tell you that the air ducts sometimes need to be cleaned. If you have had pets or anyone smoking in your home (even a visitor) for any length of time, having the ducts cleaned is really good idea. I had a tenant who did not smoke, but got married to a smoker more than year after moving in. When I realized someone was smoking I had them move out, but the smell was awful. I had the ducts cleaned and sanitized (it was a bit extra). The ducts were shiny like new afterwards. I left the windows open for a few days and we cleaned the place super clean and then replaced the carpets. The duct cleaning was worth every penny because the house looked, smelled, and felt new afterward. I plan to have my own house ducts cleaned again this year as we have two cats. We had them cleaned about 12 years ago and they found building materials in the ducts! If you move into a house that has never had them cleaned, it is good to do it. If you have allergies, clean the ducts to see if it helps. You never know what is in your ducts if you have never had them cleaned.

Two weeks go by and no phone call from HVAC Service regarding install date, or any update at all.  I call them to check in to see if they have put me on the schedule and when I can expect to have the AC installed.    You can tell by the discussion I had with the lady on the phone that they completely forgot about me and have not scheduled anything.  She says she needs to get in contact with the owner because she has no idea on the availability of the crane.  I was told that she would call me back by the end of the day with an update.  Surprise, surprise, no phone call.  
Our HVAC Ductwork Installation Cost Guide is the most comprehensive guide of its type. It fully explains the purpose of ductwork and all your options. Pricing is included for all duct types and plenums/drops too. Material and installation costs are listed. Ductwork cost varies greatly by the size and type of duct plus the complexity of the installation, but you can expect to pay $10.20 to $17.25 per linear foot installed.
Installation: Replacement is quite easy, especially when an old refrigerant line set can be used. If the set is worn, it’s much better to pay the extra $400-$600 to replace it rather than risking it leaking later. When your AC loses refrigerant, you lose your cool air and the compressor is at risk of failing. A new installation means installing a coil in your furnace or air handler, running the line set between it and the coil in the condensing unit and adding refrigerant, if needed. Most ACs come pre-charged for 20-30 feet of line. If the line set is longer, a small amount of refrigerant is added.
Mitsubishi Electric is a world leader in air conditioning systems for residential, commercial and industrial use. Challenged to create air conditioning systems that provide exemplary performance in the wide-ranging climatic conditions found throughout Japan, our engineers develop amazingly sophisticated yet durable units and systems capable of constant use under virtually any natural climatic condition on earth.
If there is stuff in the ducts, the fact that it’s laying there and not being blown into the rooms is proof positive that it is hurting no-one. The 5-6 exceptions you cite in this article I’ll buy, but only with the caveat that at least some of those could have been avoided by proper protection (during remodeling for example) – and if asbestos/lead/whatever winds up in your ducts- the remodeling contractor should be the one paying to remove it.

No one has addressed mfg homes and doesn't seem any of the comments are from people in So CA which of course does make a difference as my dust comes from the outside not from the vents. My windows are open pretty much 365 days a year. Secondly mfg homes don't have basements or attics I keep mine clean with my vacuum as they are only about 2 ft deep. I purchased my home 10 yrs ago and it is a high end home but have never had a problem. I clean my furnace filter about twice a month as I have cats and most everything in there is cat fur. I am not saying they don't ever need to be cleaned but I am questioning mfg homes, I also clean my own filters in my AC unit outside as the HVAC guy told me too he QUATITY they would sell. I use this same company every year now for my tune up and inspection which takes them about 10 minutes. Not a bad return for them and I don't mind the $79 fee. If anyone has more info than this on mfg homes please let me know!


My father started in the business of home comfort back in 1968, an I around 1986. We still don't have a duct cleaning machine. I am sure there are always applications for all tools in this industry. However I missed where anyone talked about where dust even comes from..........We do not have these little dust machines sitting in a corner puffing out little clouds of dust....soooo where does it come from?
Ventilating or ventilation (the V in HVAC) is the process of exchanging or replacing air in any space to provide high indoor air quality which involves temperature control, oxygen replenishment, and removal of moisture, odors, smoke, heat, dust, airborne bacteria, carbon dioxide, and other gases. Ventilation removes unpleasant smells and excessive moisture, introduces outside air, keeps interior building air circulating, and prevents stagnation of the interior air.
I hope that those customers you have with breathing problems don't follow your advice too closely. You are doing them a disservice. Dirt in your ducts does not always stay there, depending on what the contaminants are. I bet you tell your customers not to worry about mold either- just to kill it with bleach. Educate yourself before opening your mouth- You may kill someone someday with your opinion.

No matter what time it is, our experts will have you lounging in the cool air of your home quickly. We stand by our workmanship so much so that we guarantee it in writing for one full year. Our 100% Satisfaction Guarantee* firmly backs our dedication to providing the highest level of air conditioning service in the industry. In fact, Service Experts repairs, sells and installs more air conditioners than any other HVAC company through North America. More people count on us for their home comfort, so you can be certain your home will be back to being cool and comfortable in no time.
Although i love to burn candles, depending on the type your asking for problems big ones! At work one day i had been talking with co workers about these black shadows that were appearing on my ceilings and higher wall areas. They seemed to in the corners and along the stud supports , i could even see what i thought to be where all had been nailed. There would be dark shadows perfectly straight across my ceiling and then real dark circels every few inches within the lines. I thought it was the propane heat but learned quickly that oil heat will do that but not normally propane. A co worker brought me a magazine with a huge article about candles and what actually burns off them when lit, an ashy soot that is attracted to the areas on walls and ceilings that omit the most heat or warmth, of course where the drywall and studs meet and corners of the room. Its been about 8 years since i painted the entire house. I started bending to my love for candles again in the last 3 years, surprise i will be spending part of my summer re painting again!! No more candles ,well maybe at the holidays LOL

Many disconnect blocks contain two cartridge fuses. Check them before you proceed with repairs (Photo 3). A blown fuse is a sign of a failing part inside the condensing unit. So don't just replace it and think you've solved the problem. Instead, replace the parts we show here. Then install new fuses and fire up the unit. If it blows again, call a pro—you've got more serious issues.
×