If you believe that the AC's not working or you're getting little or no cold air, check these three things first. Make sure all the registers in the house are wide open. Then be sure the furnace filter is clean. Then go outside and clean off the condenser coils (Photo 2). If several registers were closed or the filter was clogged, the reduced airflow could have caused the evaporator coil to ice up and stop cooling your home. If you've changed the filter and opened all the registers and you're still not getting airflow at the registers, deice the A-coil. Move the thermostat mode switch from “Cooling” to “Off” and move the fan switch from “Auto” to “On.” Let the blower run for at least 30 minutes or until there's good airflow at the registers. Then turn the AC back on to test it. If it works for the next 12 hours, you've solved the problem.
DIY: We don’t recommend a DIY approach. Depending on the system, working with gas, electricity and refrigerant create dangers. Beyond that, it is essential that split system components be selected for compatibility. DIY installation of an HVAC system will void the warranty of most brands. The manufacturers won’t stand behind the warranty when anyone other than a certified installer does the work. This is true since improper installation is the main cause of poor system performance and mechanical breakdowns.
After major damage to a small addition on our home was damaged in the windstorm in May, the insurer’s preferred vendor sanded drywall without taping off the area. They relied on heat from the furnace to dry the mudding compound. They claimed they shut the furnace off while sanding and regardless of whether they did or not, they never cleaned up the drywall dust before turning the furnace back on. I now have drywall dust everywhere and my husband took photos to verify our concerns. They even sanded right above a cold air return. Vents were never covered either. The same company that created this mess is cleaning my ducts today. They have refused to clean the furnace. Their are health concerns for my almost 85 yr old mother who resides with us. I’ve tried 3 times in the last 7 days to escalate to a manager and they will not return my call. They just keep sending it back down to my adjuster. There are many other issues we’ve encountered since May as well. This is a major insurance company who has the resources to fix this mess but refuse. Please help!
If your non metal ductwork is that dirty you should just have it replaced AND sealed. Also most duct systems are not very well designed. Look for proper sizing and do not go cheap with one or two intakes (return grills) You need them through-out the house. Here in Austin the duct cleaners are carpet cleaners and chimney swifts. (this is who the duct cleaning equipment mfgs call on when the hvac people do not get on board. They DO clean other types of ductwork and we (the hvac guys) have to fix them. I am not aware of any of these non hvac guys cleaning and servicing the actual equipment. Here in Texas it is against the law for them to do so. Treat the entire house as a system, not just the ductwork and /or hvac equipment. Home performance really does work to increase comfort and air quality while reducing operating costs.
I need a complete system replacement , before I was trying to get an evaporator coil replaced , of course the price is between $2200 an $2800 , then get told it probably will over tax my ac unit within months , so now and like everyone else what do you buy 14 ,15 16 17 seer units ,price and how do we know its reasonable  why can't there be '" a estimated price ,in the ball park, a range of prices ,so we can at least go from their .....  Now it's from 7500 to 15000. Frustrating  from the start so everybody good LUCK.   Draw a # from the hat    Unregulated  and who do you BELIEVE, just like on NCIS go with your gut feelin   
Hi John, Thanks for reaching out, we would be happy to help you connect with a pro for your project. You can submit a request to our pros here: www.homeadvisor.com, browse a list of pros that serve your area here: http://www.homeadvisor.com/c.html, or send your info to emailus@homeadvisor.com and a project advisor will reach out to assist you. –HASupport

I am in need of HVAC ADVICE!! I need a new furnace badly, mine is cracked. I have bought both a 95 % AFUE furnace and a 5 Ton evap coil, I figured it should all be replaced at once for both cost and efficency. My question is with all the negaitive things I have heard about companies ripping you off, what type of price should I pay someone for putting in those two items and bringing everything in my attic up to code? I have been quoted $550 - $ 3300. Wide margin here!! Then of course comes the licencing part!! I know in my heart that I should use a licenced contractor but I have had such bad luck and prices from them that honestly one that was licened in Ga. and just not here in TN and is a tech. which charges 1100 - 2200 less sounds good as so long as I pay some type of Profenial HVAC person say $100 to inspect the work after its done and before I pay them.
Duct cleaning generally refers to the cleaning of various heating and cooling system components of forced air systems, including the supply and return air ducts and registers, grilles and diffusers, heat exchangers heating and cooling coils, condensate drain pans (drip pans), fan motor and fan housing, and the air handling unit housing (See diagram).

Concrete Blocks -- Concrete blocks are used in foundations and are often found in full basements. Insulating the spaces in the blocks is not the way to insulate them as the heat energy will travel along the concrete itself. The best way to insulate with concrete blocks is to use insulated concrete blocks, which have polystyrene incorporated into them.
Ventilating or ventilation (the V in HVAC) is the process of exchanging or replacing air in any space to provide high indoor air quality which involves temperature control, oxygen replenishment, and removal of moisture, odors, smoke, heat, dust, airborne bacteria, carbon dioxide, and other gases. Ventilation removes unpleasant smells and excessive moisture, introduces outside air, keeps interior building air circulating, and prevents stagnation of the interior air.
It seems all the average costs for a complete heating and cooling system replacement I've found on websites are usually at least 1/4 less, mostly half lower, then quotes I've gotten from companies. The worst quote I got was from One Hour Heating & Air Conditioning (the company with the Mike Rowe commercials), for over $15,000! I finally settled on a Carrier dealer, for $10,700 & I'll get $950 of that back in energy co rebates eventually. The company I went with's basic system would have been around $8800 (the only one that sorta matched up with web avg cost). They did all the correct planning as far as I could see, not like One Hour, who just showed me a price guide for the same size units already in place. And they do all the rebate paperwork and submit it to the energy co, One Hour never even mentioned possible rebates! Plus Carrier gets above avg reviews. I would have greatly liked a price under 9 grand, but this company got me 0% APR financing, so at least nothing out of pocket. My advice is stay away from national chains, and shop around with local area companies. Of course, One Hour says local companies will fold before you need warranty service lol. For their cost, there should be a technician living in his work van outside my house hahaha. 

First of all, I think it is great that there are many companies out there who look out for the customer and protect their interest. Secondly, I think it is also important that customers consider having their HVAC systems checked thoroughly before moving into a new home. I have heard a couple of horror stories where previous owners have not had the best housekeeping skills. Even when the appearance of the home seems it has been well kept, keep in mind that surface clean only goes so far. You can never tell what lies underneath.
Equipment used to clean ducts varies widely. The cheaper the equipment used the more you are just wasting money. This is why it's typically not worth doing. In some situations it may be beneficial, but only after determining and investigating the duct system. This should be done by a licensed HVAC contractor and not a duct cleaner that typically do not hold and HVAC license. (Duct cleaners aren't required to be licensed in HVAC in many areas.)
PICKHVAC Terms of Use: Some of the products seen on our site are delivered through a relationship with outside suppliers like Networx.com, Google, and others. We may or may not be compensated for purchased you make as a result of our recommendation. This will NEVER affect our opinion of a product or service! PickHVAC is also a participant in the Amazon Services LLC Associates Program, an affiliate advertising program designed to provide a means for sites to earn advertising fees by advertising and linking to amazon.com
You might also want to check your home for thermal insulation if you live in extreme heat or freezing temperatures. Insulation keeps the heat and cool air in your home, which can lead to a lower electric bill. If the heated or cool air leaks out, your system turns on more often. There are various types of insulation that you can install in your home and a home energy auditor can point out the best places for it in your house.

I had someone out to clean my ducts last weekend. He took a blue bag up in my attic. He came back down in just a few minutes and said I had mold and he even showed me a picture of something saying it was mold but I couldn’t really tell. I refused his service to take care of the mold. He went back up in the attic for a little while and then came down. I never heard any sounds that he was actually up there doing anything. How do I know if he actually cleaned the air ducts?
Your cleaning service should involve all aspects of your duct work to maximize energy efficiency and air quality. This includes attending to the heat exchanger, blower, drain pan, plenum and coils as well. In the process, your service provider may find that you're facing larger issues than debris and build-up. The professional may recommend having your furnace repaired if they notice, for example, damage to your heat exchanger or blower motor. Generally, a furnace repair costs between $130 and $500. They may also find that an A/C coil needs to be replaced rather than cleaned and would then recommend A/C repair.
The key to the continued and efficient operation of your heating and cooling system is periodic maintenance. Cleaning the air duct vent system, and servicing you heating and cooling equipment will keep the system operating at its peak performance. Air ducts are cleaned for two reasons. One: to prevent debris from entering furnace and air conditioning components. Two: to prevent debris from cycling through the home. The air duct cleaning contractor needs to employ cleaning methods which successfully removes debris, and ensures that debris does not enter the occupied space. Most contractors can verify the results of the cleaning through video or pictures.
Ventilation is the process of changing or replacing air in any space to control temperature or remove any combination of moisture, odors, smoke, heat, dust, airborne bacteria, or carbon dioxide, and to replenish oxygen. Ventilation includes both the exchange of air with the outside as well as circulation of air within the building. It is one of the most important factors for maintaining acceptable indoor air quality in buildings. Methods for ventilating a building may be divided into mechanical/forced and natural types.[16]
Be careful of dishonest HVAC contractors. There’s no magical formula to see if an HVAC contractor is scamming you, unfortunately, but remember that they typically do this in one of two ways: first, they are charging grossly low prices (far below everyone else), or second, they aren’t including what everyone else is. In the first situation, they will charge you change fees, other hidden fees, or they stole the equipment and are passing themselves off as legitimate contractors (very common in California these days). In the second situation, they are charging you a very fair price, but aren’t including what the other contractors are (i.e. charging $10,500 for the installation which is fair, but not including the ductwork which is a scam unless there is some other, complex stuff going on there).

Wiring up the thermostat is usually pretty straightforward if an old one is being replaced. If a thermostat is being put in where one had never been before, that could involve running new wiring. The placement of the thermostat is also important so that its sensors can get an accurate reading of the temperature. A thermostat that is blocked by a bookcase or other large furniture will not get a good reading and will not perform efficiently.
We bought 2 top of the line Lennox HAC for $29,000 less about $3,500 rebates, thinking they would at least last 10 years. Well, after 6 years, the system leaked. We are paying $1,700 to fix that leak. We thought at least it is still under warranty - yes BUT - the warranty covered $15 & the rest we were up for ,even though they advertise 10 year warranty. We are trying to sell & move out of high cost southern Calif & have looked at 20+ places in Arizona. Most of the houses we looked at were built from 1998 to 2005. We asked if the HAC was original & in most case it was - even though the highs were 115 to 120 & the lows 90F - versus where we live the highs run 85 to 95 & the lows are in the 60s. I asked the repairman WHY ours went out at 6 years. He replied that they just do not build them the same anymore. In Arizona, I did not see any Lennox - mostly Trane or Carrier. We had Fujistu in Australia which were fantastic - nothing went wrong in the 9 years we had them. Also, they had full induction motors not like the energy consuming 2 stage motors in Lennox. Maybe the Japanese built Fujusita still builds quality & the warranty is meaningful?

I'd have to disagree with all of your statements. Not only are they derived from no experience in the field, you are missing keys facts. Ducts even if air tight will get dirty. If they are not getting dirty, it means they are not working. Your returns side of the duct work is always under negative pressure when the system is operational.Therefore it is always drawing air in. Seeing how dust is made up mostly from dead skin humans shed daily. Around 1.6 Pounds of skin a year per human. Living in your home anything that is air born will be drawn back towards the cold air returns. That is what they are designed for, to draw stale air back to the system to be filtered and sent back through the house.Homes with carpet will actually have cleaner duct work than home with all tile or hardwood. This is because carpets hold onto dust particles and you vacuum them up. Whereas on hardwood or tile, dust can run freely back to the returns. Even if a duct system was sealed 100%, which is next to impossible to achieve 100% would still need to be cleaned. The cleaning may only have to be every 7-10 years for example. Most homes require every 5-7 years. And that's if it was done properly the first time. If you constantly hire people that have no or minimal knowledge of duct cleaning, You home would require cleaning more often. Every 2 years. That's a trade secret, The longer they recommend before the next cleaning, the odds are they did it right. That's not to say there aren't people that lie, because there are. Just have your duct cleaner take pictures before and after cleaning. Not just an outside view. Get in there, picture entire joist liners, Whole main runs and even long round pipes. Also it helps to have a company that guarantees their work. If it's not done right, they will come back and do it until it is. Most companies that do this make sure it is right the first time. Your not getting paid to do the job twice.

You can adjust for seasons: During the summer, you can have the air conditioner stay off during the cooler morning hours and start cooling the house as everyone gets up and starts moving around. During the winter, you can have your heater stay off while you are away at work and turn on about a half hour or so before you get home so that you are coming home to a nice, warm house.


Indoor Fan Motor -- Indoor fans circulate the air from your house and through the system. Age and dust buildup are the two biggest contributing factors to their failure. When they are starting to fail they will often make noise. Failure of the fan will result in no heating or cooling, and if it is not repaired soon, it can cause other components to fail.
The use of furnaces, space heaters, and boilers as a method of indoor heating could result in incomplete combustion and the emission of carbon monoxide, nitrogen oxides, formaldehyde, volatile organic compounds, and other combustion byproducts. Incomplete combustion occurs when there is insufficient oxygen; the inputs are fuels containing various contaminants and the outputs are harmful byproducts, most dangerously carbon monoxide, which is a tasteless and odorless gas with serious adverse health effects.[14]
BIG THANK YOU for being honest, and advising us that for some reason the fuse/switch was in the reverse position so the AC unit would not properly turn on.   The unit turned back on immediately, and began cooling the house.   And then providing advice that the AC/Heating system needed some TLC, and giving us options to save money by purchasing a maintenance plan that included the filters plus cleaning services since we were already being charged for the service today.
How exactly do you expect to kill or remove mold without it ? You can’t even clean your hvac systems coils without moisture of some type ,if you use a steam cleaner you can literally clean the whole system minus the electronics . You should do more research and possibly talk to people who do the work before posting , but don’t listen to me i only have a class A contractor license ,epa license , install /repair hvacs , rent and flip houses for a living .
It’s 11 years plus in the industry I have only had to sanitize two systems both were slab systems that were in concrete and could be cleaned with a different method than normal duct cleaning. We were able to use water to rinse out the disinfectant. Would you use a chemical on anything else you use to eat or drink with and not rinse it off? The ducts in your home should be thought of as your homes heart and lungs and breathe the same air that you do. And just like us we wouldn’t use bad chemicals in our lungs and heart.
in response to this reply " should your ducts be cleaned", i have to politely correct the person who answered this. you are not using common sense. first, most of the country uses metal duct work, so for you to say what you did, is wrong. second, the duct system in a house is a circulatory system. that means it draws air into the furnace, it gets filtered, and then it is blown out into the house to heat or cool. So, obviously that air is being brought into the house from somewhere right? Yes, its coming from the outside where there are many allergens and dust particles . For you to says that about whether a duct system is sealed or not, makes no difference. The air is coming from somewhere right? It has to originate from somewhere right? Just look on top of your cieling fan. If there is a bunch of dust up there, then there is obviously a bunch in your ducts. And the duct air is being circulated every day, and every hour through your house. Its simple, dust collects everywhere in your house. Imagine if you never dusted your shelves, or tv? There would be a ton of dust after a while. Well, now think about the air in the duct system. Of course theres gonna be a ton of dust in there. For you to say that it is not benififcial to clean the ducts, is plain ignorant. 90% of the air we breathe is in our household. Wouldnt you want that air to be as dust and allergen free? I could go on for hours about the benifits of duct cleaning, but i just wanted to make a quick point that the person whose says it is not benificial to clean them, is not using common sense. Not to mention, giving the people who clean ducts for a living, a bad name. Use your head .
I need a complete system replacement , before I was trying to get an evaporator coil replaced , of course the price is between $2200 an $2800 , then get told it probably will over tax my ac unit within months , so now and like everyone else what do you buy 14 ,15 16 17 seer units ,price and how do we know its reasonable  why can't there be '" a estimated price ,in the ball park, a range of prices ,so we can at least go from their .....  Now it's from 7500 to 15000. Frustrating  from the start so everybody good LUCK.   Draw a # from the hat    Unregulated  and who do you BELIEVE, just like on NCIS go with your gut feelin   

Did you know that cleaning your ducts and vents can help airflow and increase energy efficiency? According to the Environmental Protection Agency (EPA), keeping your air ducts and vents clear can increase energy efficiency and indoor air quality. While the cost to clean ducts and vents might sound high, the benefits to homeowners–especially those sensitive to allergens–is worth considering.


The cost to replace a central air conditioner is about $5,000. However, this price varies depending on the size of your home and the difficulty of the project. It can cost as much as $12,500 to replace an AC unit. The labor required to remove and dispose of the old system adds to the price. The size of your home, brand of AC unit and ductwork complexity can all raise the cost as well.
If you don't agree with duct cleaning, fine. If there are some things that HVAC people can do to make the system need cleaning less often fine, but to suggest that I need to GO TO JAIL????? If you need to knock others to make yourself look better....... If duct cleaning is such a scam, why are their governing bodies like NADCA (which I do NOT belong to),several manufacturers of equipment, and national restoration franchises (I'm not a franchise either) who provide this service? I guess the whole world is stupid and only HVAC people are smart. I suppose I am scamming them when I clean puff backs, water damage, fire damage, and clean their carpets too? Or did I wake up one morning and say "ya know, it is great to be a hard working, honest owner operator, but I would love to provide a service that unlike everything else I do is a con and rips off the 90% referral business I busted my butt to earn"

Contact/Relay -- Relays are electronically controlled switches that activate the various components of your HVAC system. They manage everything from the power going to the motor to automatic dampers, humidifiers, etc. Most of them are controlled by the thermostat. The most common failure for a relay is being stuck in the "open" position. Separated from its assigned contact point, it fails to complete the connection and send the message to whatever it was supposed to operate. This failure usually occurs from use over time. Each time a relay connects and sends its signal, the electrical arcing from point to point eventually causes wear and tear.


I turned on the AC when he was finished and immediately saw black fuzz balls the size of marbles come out of several of the registers. He said that was expected since everything was shaken up. So much for describing the service as cleaning. I paid him and sent him on his way. I cannot imagine that this type of service is worthwhile in anything but a new house. Apparently in old houses such as mine I can expect that using a whole house humidifier in the winter followed by a great AC can loosen the soot. Maybe this is to be expected for the first few weeks of summer each year. I now have lined the inside of the registers with cheesecloth to catch the fuzz. I’ll see if it stops after a couple of weeks.

Since most states and municipalities don’t license air duct cleaners, you need to check their professional credentials instead, such as NADCA membership. EPA recommends all duct cleaners follow NADCA standards. Member companies must keep at least one technician on staff who has passed a NADCA test. “They have to pass rigorous testing to earn the certificate, and our code of ethics is very important,” Vinick says.
I replaced all the ducts but the trunks in my 1969 home when I replaced the horizontal furnace under the house with a gas pack. I got advice from a friend who was an HVAC contractor. I was surprised to find the trunks and other ducts very clean. I replaced the individual runs with flex primarily for the insulation. I wrapped the trunks with insulation also.
You can install the greatest HVAC system ever built, but if your house is not insulated well, it's only going to end up costing you more money. Older homes may have fiberglass insulation that has broken down due to pests, moisture, or improper installation. Spray foam insulation can be damaged by careless repair or modification work or can be improperly installed. If your insulation in compromised, your attempts to save money and be comfortable will be in vain.
DIY: We don’t recommend a DIY approach. Depending on the system, working with gas, electricity and refrigerant create dangers. Beyond that, it is essential that split system components be selected for compatibility. DIY installation of an HVAC system will void the warranty of most brands. The manufacturers won’t stand behind the warranty when anyone other than a certified installer does the work. This is true since improper installation is the main cause of poor system performance and mechanical breakdowns.
Having the most energy-efficient system ever built won't matter much if it's not maintained. Lack of maintenance is the number one killer of HVAC systems. Before each cooling season, it's recommended that your system get a professional tune-up. However, there are things you can do in the meantime to make sure your system runs efficiently throughout the year.
Having the most energy-efficient system ever built won't matter much if it's not maintained. Lack of maintenance is the number one killer of HVAC systems. Before each cooling season, it's recommended that your system get a professional tune-up. However, there are things you can do in the meantime to make sure your system runs efficiently throughout the year.
If you think duct cleaning might be a good idea for your home, but you are not sure, talk to a professional. The company that services your heating and cooling system may be a good source of advice. You may also want to contact professional duct cleaning service providers and ask them about the services they provide. Remember, they are trying to sell you a service, so ask questions and insist on complete and knowledgeable answers.
×