Metal is way better than flex duct or ductboard. It gets better airflow, holds up to critters and duct cleaners. I know of no hvac company here that cleans ductwork. (there probably is one somewhere) The mfg's of duct cleaning equipment keep trying to sell us hvac people on their benefits and profit potential but most all hvac people know that unless you have metal ductwork you are NOT doing the customer any favors.
I guess I should present my credentials first, I am a 30 year veteran of the heating and cooling industry. I started at the bottom and have participated in every area of the trade. Installer, service, maint. Ownership, rep, territory manager and so on. A forced air duct system is a large vacume. Like your vacume it has an air intake (return air) and an exhaust (supply registers). A filter just like a vacume (located next to furnace or air handler). Now I want you to visualize something. Put your head inside your vacume cleaner and breath. Get the picture? This is what your duct work looks like. Do you clean your vacume when it’s dirty? If it’s full and the filter is dirty you lose performance and it starts poluting the air you breathe. It’s common sense. I recommend hiring a duct cleaning outfit that you have researched to be honest, background checked, drug tested, insured, and highly recommended by your piers in the area. The service is a necessity, but like everything, it should be done by a qualified company.
1). Busy companies: The company is so busy, it doesn’t need the work. It will add 70% to 100% profit, and if the customer accepts the estimate, it will move that high-margin customer to the front of the line. This often happens in the worst heat of summer when overburdened ACs and heat pumps quit and the dead of winter when furnaces give up. This is a good reason to consider pre-emptively replacing your system once it’s about 15 years old and/or has had major repairs.

Despite Bergendahl's experience, Vinick says NADCA's certification standards have improved the situation. "A lot of [service companies] weren't going about it the correct way," he says. “We have an anti-fraud task force, and we’ve gone after some fraudulent duct cleaners with the help of state attorneys general.” He suggests that in addition to NADCA membership, homeowners make sure their cleaners are an established business, have appropriate insurance and are registered to do business in their state and locality.

Your cleaning service should involve all aspects of your duct work to maximize energy efficiency and air quality. This includes attending to the heat exchanger, blower, drain pan, plenum and coils as well. In the process, your service provider may find that you're facing larger issues than debris and build-up. The professional may recommend having your furnace repaired if they notice, for example, damage to your heat exchanger or blower motor. Generally, a furnace repair costs between $130 and $500. They may also find that an A/C coil needs to be replaced rather than cleaned and would then recommend A/C repair.
We bought 2 top of the line Lennox HAC for $29,000 less about $3,500 rebates, thinking they would at least last 10 years. Well, after 6 years, the system leaked. We are paying $1,700 to fix that leak. We thought at least it is still under warranty - yes BUT - the warranty covered $15 & the rest we were up for ,even though they advertise 10 year warranty. We are trying to sell & move out of high cost southern Calif & have looked at 20+ places in Arizona. Most of the houses we looked at were built from 1998 to 2005. We asked if the HAC was original & in most case it was - even though the highs were 115 to 120 & the lows 90F - versus where we live the highs run 85 to 95 & the lows are in the 60s. I asked the repairman WHY ours went out at 6 years. He replied that they just do not build them the same anymore. In Arizona, I did not see any Lennox - mostly Trane or Carrier. We had Fujistu in Australia which were fantastic - nothing went wrong in the 9 years we had them. Also, they had full induction motors not like the energy consuming 2 stage motors in Lennox. Maybe the Japanese built Fujusita still builds quality & the warranty is meaningful?
Metal is way better than flex duct or ductboard. It gets better airflow, holds up to critters and duct cleaners. I know of no hvac company here that cleans ductwork. (there probably is one somewhere) The mfg's of duct cleaning equipment keep trying to sell us hvac people on their benefits and profit potential but most all hvac people know that unless you have metal ductwork you are NOT doing the customer any favors.
If your non metal ductwork is that dirty you should just have it replaced AND sealed. Also most duct systems are not very well designed. Look for proper sizing and do not go cheap with one or two intakes (return grills) You need them through-out the house. Here in Austin the duct cleaners are carpet cleaners and chimney swifts. (this is who the duct cleaning equipment mfgs call on when the hvac people do not get on board. They DO clean other types of ductwork and we (the hvac guys) have to fix them. I am not aware of any of these non hvac guys cleaning and servicing the actual equipment. Here in Texas it is against the law for them to do so. Treat the entire house as a system, not just the ductwork and /or hvac equipment. Home performance really does work to increase comfort and air quality while reducing operating costs.
Air conditioning and refrigeration are provided through the removal of heat. Heat can be removed through radiation, convection, or conduction. Refrigeration conduction media such as water, air, ice, and chemicals are referred to as refrigerants. A refrigerant is employed either in a heat pump system in which a compressor is used to drive thermodynamic refrigeration cycle, or in a free cooling system which uses pumps to circulate a cool refrigerant (typically water or a glycol mix).
The bottom line is: no one knows. There are examples of ducts that have become badly contaminated with a variety of materials that may pose risks to your health. The duct system can serve as a means to distribute these contaminants throughout a home. In these cases, duct cleaning may make sense. However, a light amount of household dust in your air ducts is normal. Duct cleaning is not considered to be a necessary part of yearly maintenance of your heating and cooling system, which consists of regular cleaning of drain pans and heating and cooling coils, regular filter changes and yearly inspections of heating equipment. Research continues in an effort to evaluate the potential benefits of air duct cleaning.
Simply living in your home creates dust and dirt. Have you ever seen dust floating in the air in your home when the sun shines in?  Dust, dirt, pet dander, mold spores, and allergens get pulled into the air handling system in your home. They build up in the ductwork; some of it gets recirculated back into your home, and some of it can be captured by a good quality air filter. Eventually, enough debris builds up to the point where most of it blows back into your home. Your furnace or air conditioner must run longer to cool or heat your home, which costs you more in utility bills. With a service call from Sears Air Duct Cleaning, you can feel comfortable knowing that the accumulation of dust, dirt, dander, mold, and allergens has been cleaned from your HVAC duct system.
Important Tip: Don’t just pay attention to the high-end of the price range! – which is what I know you are all looking at, but also look at the low range. If a contractor is cheaper than this, ask “why?” Usually it is because they don’t have liability insurance, workman’s compensation insurance, are unlicensed, all of the above, or worst yet, they don’t use HVAC technicians. You are spending a lot of money.  Make sure that they are licensed (In California, check here at CSLB License Checker) and insured.
We divided new HVAC installation cost into three groups: first, the Change-Out, which is an installation of just your HVAC components without the ductwork; Full Installation, which is the installation of all HVAC equipment including ductwork; and finally, Full Installation with Features, which is a full installation with additional features such as a zoning system or media filter with a complimentary Ferrari Portofino.
Chemical biocides are regulated by EPA under Federal pesticide law. A product must be registered by EPA for a specific use before it can be legally used for that purpose. The specific use(s) must appear on the pesticide (e.g., biocide) label, along with other important information. It is a violation of federal law to use a pesticide product in any manner inconsistent with the label directions.
Despite such anecdotal experiences, there's no scientific evidence that regular residential air duct cleaning improves air quality, according to a 1997 brochure published by the Environmental Protection Agency. Laureen Burton, senior scientist in the EPA Indoor Environments Division, says that while the document is nearly two decades old, the science hasn't changed and the agency stands by its recommendations.

Roof-mounted systems have the heating and cooling systems in one cabinet. Sometimes called "gas packs" (if the heater uses natural gas), they typically cost less than a comparable split system. In dry regions, most homes originally had "swamp-coolers" installed. When replacing them with HVAC systems, it's often cheaper to use existing mounts and ducting.

The original furnace was a coal fired “octopus” design which had no blower to circulate the air but relied upon warm air rising to distribute the heat. That also means that the system breathed air in from the basement and most of this type did not have a cold air return system. At some point (probably in the 1940’s) the system was upgraded to a forced air gas furnace. The upgrade included replacing the 12″ diameter air ducts exposed in the basement with 6″ ducts and a cold air return system of ducts from the two (only two) air returns on the first floor.
Our heater went out last Saturday, which was a cold day.  Called a few different places and they were the only ones that called back.  The technician Tony came out and after a little testing said the main control board needed to be replaced.  He quoted us a total of $489 which seemed on the high side but it was cold and we were somewhat desperate, so we agreed and paid a parts deposit.
The short answer is yes, duct cleaning, done right by a reputable company will help with the smell. It is likely though the smell is coming from another source, ie the crawl space. It could also be that another rodent is dead in the duct work. A visual inspection would be in order to check for any breach in the duct system. A duct pressure test would be able to tell you how much air is leaking from the system over all. A hole large enough for an animal to enter would loses a great deal of air, over 300 CFM. It would be worth looking into having this test done and it should cost around $200. Cleaning the air handler and evaporator coil will greatly improve the performance of the air conditioner. Dirt and dust on the evaporator acts as insulation and reduces the amount of cooling done be the coil. Any quality duct cleaning should include cleaning the air handler and coil, and the tech should allow you to watch him perform the work as it is done.
Maybe I took him to literally but I am pretty sure cops wont show up to ensure that my duct gets replaced. He said it would be over 1000 dollars to replace the ductwork if that is the case. Now, I spoke to a friend who did 2 ductwork lines on his own in his attic and he said it was like 15 dollars for the plastic wirewound tubing to create new ducts. Should I cancel that appointment and just do the work on my own? I feel like I’m a chump or lazy for considering paying someone to do this work.

I'm very glad that I found another guy to come replace the circuit board and put it away from the water, fix the water leak, and also find and fix another impending failure.  All of that was for much less than HVAC Service wanted to charge for repair or replacement. The other guy did a great repair, so I'm confident it will not break down again, but if it does, I will not call HVAC Service. Don't get suckered by their Yelp Deal.
Central, "all-air" air-conditioning systems (or package systems) with a combined outdoor condenser/evaporator unit are often installed in North American residences, offices, and public buildings, but are difficult to retrofit (install in a building that was not designed to receive it) because of the bulky air ducts required. (Minisplit ductless systems are used in these situations.) Outside of North America, packaged systems are only used in limited applications involving large indoor space such as stadiums, theatres or exhibition halls.
Installing a split system may involve making modifications to the house itself for the necessary lines to be run. The heat exchangers are also more prone to picking up debris and must be cleaned on a regular basis. While they come with protective screens over the fan, care must still be taken to ensure that nothing gets in, especially in a home with children.

CIBSE publishes several guides to HVAC design relevant to the UK market, and also the Republic of Ireland, Australia, New Zealand and Hong Kong. These guides include various recommended design criteria and standards, some of which are cited within the UK building regulations, and therefore form a legislative requirement for major building services works. The main guides are:
In some older homes, there was a grey Mylar flexible duct. After years of use, it started to decompose. A duct cleaning company can come out and find why your air is so dirty and why your building doesn’t heat or cool like it used to. This is a savings on your part. You could also be sucking in Hot, dirty attic air. However, sometimes when a duct cleaning company comes out to clean it, the old duct can be destroyed and have to be replaced. Someone with little experience can replace this ductwork but if it isn’t done right it can ruin a lot of things and cost a lot in repairs.
With today’s consistently rising energy costs, improperly sealed windows, ductwork, and poor insulation can pose serious problems for many home and business owners in Arkansas. Wilson's Heating & Air Conditioning provides complete HVAC system servicing including sales, installation, maintenance and repair, and offers numerous practical solutions that will reduce your energy costs.
Some of the research I have done suggests to have your ducts cleaned when you first purchase a new home to remove drywall dust. Maintain your system well and you shouldn't have to do it again until you want to sell. Those are the two times cleaning was suggested. So for peace of mind maybe it is a good idea to do it even if you buy a used home and then maybe every 5-10 years.

No one has addressed mfg homes and doesn't seem any of the comments are from people in So CA which of course does make a difference as my dust comes from the outside not from the vents. My windows are open pretty much 365 days a year. Secondly mfg homes don't have basements or attics I keep mine clean with my vacuum as they are only about 2 ft deep. I purchased my home 10 yrs ago and it is a high end home but have never had a problem. I clean my furnace filter about twice a month as I have cats and most everything in there is cat fur. I am not saying they don't ever need to be cleaned but I am questioning mfg homes, I also clean my own filters in my AC unit outside as the HVAC guy told me too he QUATITY they would sell. I use this same company every year now for my tune up and inspection which takes them about 10 minutes. Not a bad return for them and I don't mind the $79 fee. If anyone has more info than this on mfg homes please let me know!


1. Ducts need cleaning mostly because they were not installed properly. There should be regulatory inpection and approval of clean and proper duct works on new houses. I was extremely unpset when I looked and found significant amounts of construction dust in parts of the ducts in my new house. There is apparently no way to hold the bullder to be responsible for clean ducts.

So, naturally I respond with, “you don’t tell your doctor which medication to prescribe you, do you?” The point is, on the residential level, who you get to install your HVAC unit is far more important than which unit you choose.  Keep your options open and let your HVAC contractor make a few recommendations – that’s why you spent time finding a reputable contractor!

Ground source, or geothermal, heat pumps are similar to ordinary heat pumps, but instead of transferring heat to or from outside air, they rely on the stable, even temperature of the earth to provide heating and air conditioning. Many regions experience seasonal temperature extremes, which would require large-capacity heating and cooling equipment to heat or cool buildings. For example, a conventional heat pump system used to heat a building in Montana's −70 °F (−57 °C) low temperature or cool a building in the highest temperature ever recorded in the US—134 °F (57 °C) in Death Valley, California, in 1913 would require a large amount of energy due to the extreme difference between inside and outside air temperatures. A few feet below the earth's surface, however, the ground remains at a relatively constant temperature. Utilizing this large source of relatively moderate temperature earth, a heating or cooling system's capacity can often be significantly reduced. Although ground temperatures vary according to latitude, at 6 feet (1.8 m) underground, temperatures generally only range from 45 to 75 °F (7 to 24 °C).

Is there a such thing as a PQ-15 valve? No…but how do we know? And oh, by the way, there are only two types of line-sets: 3/4 inch, and 7/8 inch. All modern equipment runs on a 7/8 inch line-set, so the only time they’ll have to change something is if you have antiquated 3/4 inch line-set from the 60’s or 70’s. I’m digressing though…the point is that they can easily prey on uninformed consumers…like you, baby bird! Don’t worry though…you’ll be flying by the end of this article.
Duct cleaning has never been shown to actually prevent health problems. Neither do studies conclusively demonstrate that particle (e.g., dust) levels in homes increase because of dirty air ducts. This is because much of the dirt in air ducts adheres to duct surfaces and does not necessarily enter the living space. It is important to keep in mind that dirty air ducts are only one of many possible sources of particles that are present in homes. Pollutants that enter the home both from outdoors and indoor activities such as cooking, cleaning, smoking, or just moving around can cause greater exposure to contaminants than dirty air ducts. Moreover, there is no evidence that a light amount of household dust or other particulate matter in air ducts poses any risk to your health.
×