WELL, this summer when I opened them up we had black dust spewing from one of the upstairs vents. It resembled the fuzz that comes off new towels. This prompted us to look into duct cleaning. We heard from someone who had it done several times, said it was worthwhile, and knew of a firm that did a good job. Clean Air America sent a single technician for the appointment and after counting registers and ducts gave me a price of $360.00 which included “sanitizing” the system (a $99 additional fee per can used). The small size of the plenum forced him to connect the 8” round vacuum hose from the truck to the 10” square opening from our humidifier unit. In hindsight, a mistake since it reduced the “negative” pressure in the system.

Good article, but it fails to point out that leaky return-side ducts could be drawing dust and allergens into the duct system from the enclosed spaces in which they run, e.g. between walls, below floors, attic. So duct cleaning may only be a temporary solution. The homeowner can get a home energy audit -- free in many states -- to determine if they have significant duct leakage. An Aeroseal dealer may be able to effectively seal up the duct system without needing to tear into walls etc to get to the ducts.
Once on the scene, trained Sears professionals utilize powerful, truck-mounted equipment to clear your air ducts of dust, debris, pet dander, allergens, and grime. Our powerful air duct cleaning suction equipment vacuums out years of accumulated dust from your air ducts, leaving them clean and clear. Once finished, our technicians remove all equipment and make sure that your ducts and HVAC unit are restored to their best condition. For continued protection against dirty air ducts, your service technician may suggest a variety of air purification products.
The most recognized standards for HVAC design are based on ASHRAE data. The most general of four volumes of the ASHRAE Handbook is Fundamentals; it includes heating and cooling calculations. Each volume of the ASHRAE Handbook is updated every four years. The design professional must consult ASHRAE data for the standards of design and care as the typical building codes provide little to no information on HVAC design practices; codes such as the UMC and IMC do include much detail on installation requirements, however. Other useful reference materials include items from SMACNA, ACGIH, and technical trade journals.

It seems all the average costs for a complete heating and cooling system replacement I've found on websites are usually at least 1/4 less, mostly half lower, then quotes I've gotten from companies. The worst quote I got was from One Hour Heating & Air Conditioning (the company with the Mike Rowe commercials), for over $15,000! I finally settled on a Carrier dealer, for $10,700 & I'll get $950 of that back in energy co rebates eventually. The company I went with's basic system would have been around $8800 (the only one that sorta matched up with web avg cost). They did all the correct planning as far as I could see, not like One Hour, who just showed me a price guide for the same size units already in place. And they do all the rebate paperwork and submit it to the energy co, One Hour never even mentioned possible rebates! Plus Carrier gets above avg reviews. I would have greatly liked a price under 9 grand, but this company got me 0% APR financing, so at least nothing out of pocket. My advice is stay away from national chains, and shop around with local area companies. Of course, One Hour says local companies will fold before you need warranty service lol. For their cost, there should be a technician living in his work van outside my house hahaha.
I own a small mechanical company. My main work is service and system replacements. I have never been a believer in duct cleaning. The company I worked for before had our duct man come out and do my house. I saw no difference. Preventive maintance is what I recomend. Remove fan and clean, seal fan compartment to prevent dust from being pulled in, filters I install media filters, they are 5″ thick and pleated. I have tested them to make sure static presure was not a issue. Heat exchangers and AC coils need to be cleaned. I will tell you this to do a good cleaning I usually spent 1-2 hrs, When I’m finished I would not have a problem eating my diner on the system. Good filters, clean system and properly tuned up are my recomdation to anyone. I’ve included my email feel free to contact me with any questions. winkcfd@yahoo.com

Had duct cleaners here coupon for 40.00 for complete home I was not here but my husband was. I told my husband that they will prolly ask for more money and I was right. 85 extra to do duct cleaning which I pled because my dryer vent was full of animal hair extensions then for 600 to clean a/c coils I said no. Just do what the coupon said. Do your homework be 100 steps ahead of these con men rember they con people all day long and know the ans to your objections
As a homeowner and an owner of rental property I can tell you that the air ducts sometimes need to be cleaned. If you have had pets or anyone smoking in your home (even a visitor) for any length of time, having the ducts cleaned is really good idea. I had a tenant who did not smoke, but got married to a smoker more than year after moving in. When I realized someone was smoking I had them move out, but the smell was awful. I had the ducts cleaned and sanitized (it was a bit extra). The ducts were shiny like new afterwards. I left the windows open for a few days and we cleaned the place super clean and then replaced the carpets. The duct cleaning was worth every penny because the house looked, smelled, and felt new afterward. I plan to have my own house ducts cleaned again this year as we have two cats. We had them cleaned about 12 years ago and they found building materials in the ducts! If you move into a house that has never had them cleaned, it is good to do it. If you have allergies, clean the ducts to see if it helps. You never know what is in your ducts if you have never had them cleaned.
Replacing a capacitor is easy. Just take a photo of the wires before disconnecting anything (you may need a reference later on). Then discharge the stored energy in the old capacitor (Photo 4). Use needle-nose pliers to pluck one wire at a time from the old capacitor and snap it onto the corresponding tab of the new capacitor. The female crimp connectors should snap tightly onto the capacitor tabs. Wiggle each connector to see if it's tight. If it's not, remove the connector and bend the rounded edges of it so it makes a tighter fit on the tab. When you've swapped all the wires, secure the new capacitor (Photo 5).
Ventilating or ventilation (the V in HVAC) is the process of exchanging or replacing air in any space to provide high indoor air quality which involves temperature control, oxygen replenishment, and removal of moisture, odors, smoke, heat, dust, airborne bacteria, carbon dioxide, and other gases. Ventilation removes unpleasant smells and excessive moisture, introduces outside air, keeps interior building air circulating, and prevents stagnation of the interior air.
I live in Port Orange, FL. I purchased a double wide mobile home and was saddened to learn that the previous owners were HEAVY smokers! They did a good job “hiding” the smoke smell the day we viewed this place. I did not have a home inspection done unfortunately. My question is: can duct cleaning remove the smoke smell from this place. The ceilings have been treated with Kilz and paint. I personally scrubbed down every wall, floor or surface. I also purchased a ODORFREE OZONE machine. It seemed to remove the odor for a short period of time but my friends are again complaining about the “smoke” odor in my home. The Ozone machine was $400 and I’m terribly upset that it didn’t clean the air as was promised.
This is to Blueberry who.wrote.about home rental dust problems on 12/ 06/2016. If you’ve been there 13 years.your landlord has made enough money to have those problems repaired.I would call your city property standards dept. And let them know what.conditions you are having to live.There is no excuse for living in those conditions when most problems like that are easy fixes.Especially if your kids are getting sick. Tell your landlord your.calling City Health Inspector if he doesn’t fix.the problems.
I can't believe the number of people saying a good properly installed central heating system never needs to be cleaned. Maybe they live in hermetically sealed cells? One look into a cold air return and you can see that it definitely needs periodic cleaning. The air in the house "always" has some dust in it and that's where it ends up. We just had ours cleaned and I saw what came out of it, disgusting. But always ask if they use the "air whip" to sweep/beat the inside of the metal duct. If not, don't bother. These folks used a little whip on the end of a pressure hose and swept the entire length of all the ducts. I have lighted bore scope that allowed me to see into the duct after he was done and it was spic and span. But do change your filters often, 2 or 3 times a year.
We bought 2 top of the line Lennox HAC for $29,000 less about $3,500 rebates, thinking they would at least last 10 years. Well, after 6 years, the system leaked. We are paying $1,700 to fix that leak. We thought at least it is still under warranty - yes BUT - the warranty covered $15 & the rest we were up for ,even though they advertise 10 year warranty. We are trying to sell & move out of high cost southern Calif & have looked at 20+ places in Arizona. Most of the houses we looked at were built from 1998 to 2005. We asked if the HAC was original & in most case it was - even though the highs were 115 to 120 & the lows 90F - versus where we live the highs run 85 to 95 & the lows are in the 60s. I asked the repairman WHY ours went out at 6 years. He replied that they just do not build them the same anymore. In Arizona, I did not see any Lennox - mostly Trane or Carrier. We had Fujistu in Australia which were fantastic - nothing went wrong in the 9 years we had them. Also, they had full induction motors not like the energy consuming 2 stage motors in Lennox. Maybe the Japanese built Fujusita still builds quality & the warranty is meaningful?
The most effective way to clean air ducts and ventilation systems is to employ Source Removal methods of cleaning. This requires a contractor to place the system under negative pressure, through the use of a specialized, powerful vacuum. While the vacuum draws air through the system, devices are inserted into the ducts to dislodge any debris that might be stuck to interior surfaces. The debris can then travel down the ducts to the vacuum, which removes it from the system and the home.
BIG THANK YOU for being honest, and advising us that for some reason the fuse/switch was in the reverse position so the AC unit would not properly turn on.   The unit turned back on immediately, and began cooling the house.   And then providing advice that the AC/Heating system needed some TLC, and giving us options to save money by purchasing a maintenance plan that included the filters plus cleaning services since we were already being charged for the service today.
Quality and price should come hand in hand, a too-good-to-be-true price for an efficient air duct cleaning will not give you the quality that you wanted. To make sure you are getting your money’s worth, check reviews of air duct cleaning companies, certifications from industry since this work requires continuous learning due to new techniques and research breakthrough from time to time. Make sure to shop around and get written estimates first.
All modern air conditioning systems, even small window package units, are equipped with internal air filters. These are generally of a lightweight gauze-like material, and must be replaced or washed as conditions warrant. For example, a building in a high dust environment, or a home with furry pets, will need to have the filters changed more often than buildings without these dirt loads. Failure to replace these filters as needed will contribute to a lower heat exchange rate, resulting in wasted energy, shortened equipment life, and higher energy bills; low air flow can result in iced-over evaporator coils, which can completely stop air flow. Additionally, very dirty or plugged filters can cause overheating during a heating cycle, and can result in damage to the system or even fire.
All modern air conditioning systems, even small window package units, are equipped with internal air filters. These are generally of a lightweight gauze-like material, and must be replaced or washed as conditions warrant. For example, a building in a high dust environment, or a home with furry pets, will need to have the filters changed more often than buildings without these dirt loads. Failure to replace these filters as needed will contribute to a lower heat exchange rate, resulting in wasted energy, shortened equipment life, and higher energy bills; low air flow can result in iced-over evaporator coils, which can completely stop air flow. Additionally, very dirty or plugged filters can cause overheating during a heating cycle, and can result in damage to the system or even fire.

Because an air conditioner moves heat between the indoor coil and the outdoor coil, both must be kept clean. This means that, in addition to replacing the air filter at the evaporator coil, it is also necessary to regularly clean the condenser coil. Failure to keep the condenser clean will eventually result in harm to the compressor, because the condenser coil is responsible for discharging both the indoor heat (as picked up by the evaporator) and the heat generated by the electric motor driving the compressor.
I have worked cleaning HVAC in my area for almost 5 years. I always do a thorough inspection and cleaning, providing before and after photos. I have completed some jobs where I felt that it was not entirely necessary, but ultimately what the customer wanted. With that being said, I have endless photos of unspeakable horrors. Hotels are usually nasty, post construction mess is certain, pets and kids create lots off debris, bugs congregate and die, then spiders set up and die, I have even had one supply that was nearly plugged with sand!
CIBSE publishes several guides to HVAC design relevant to the UK market, and also the Republic of Ireland, Australia, New Zealand and Hong Kong. These guides include various recommended design criteria and standards, some of which are cited within the UK building regulations, and therefore form a legislative requirement for major building services works. The main guides are:
Prices for central-air HVAC systems will vary. The national average to hire an HVAC specialist is $2,920-$3,670 but can run as high as $5,000 or even $12,000 depending on the capacity you need and other factors. Installing central air conditioning requires an entire system that works together to draw hot air out of your home. The system includes an outdoor unit, which houses the condenser and compressor, and the evaporator coils. If you don’t have an existing duct system, ductwork will need to be installed, which will affect labor and material costs. Leaking or damaged ducts will also need to be replaced.
Quality and price should come hand in hand, a too-good-to-be-true price for an efficient air duct cleaning will not give you the quality that you wanted. To make sure you are getting your money’s worth, check reviews of air duct cleaning companies, certifications from industry since this work requires continuous learning due to new techniques and research breakthrough from time to time. Make sure to shop around and get written estimates first.
Wiring up the thermostat is usually pretty straightforward if an old one is being replaced. If a thermostat is being put in where one had never been before, that could involve running new wiring. The placement of the thermostat is also important so that its sensors can get an accurate reading of the temperature. A thermostat that is blocked by a bookcase or other large furniture will not get a good reading and will not perform efficiently.
The short answer is yes, duct cleaning, done right by a reputable company will help with the smell. It is likely though the smell is coming from another source, ie the crawl space. It could also be that another rodent is dead in the duct work. A visual inspection would be in order to check for any breach in the duct system. A duct pressure test would be able to tell you how much air is leaking from the system over all. A hole large enough for an animal to enter would loses a great deal of air, over 300 CFM. It would be worth looking into having this test done and it should cost around $200. Cleaning the air handler and evaporator coil will greatly improve the performance of the air conditioner. Dirt and dust on the evaporator acts as insulation and reduces the amount of cooling done be the coil. Any quality duct cleaning should include cleaning the air handler and coil, and the tech should allow you to watch him perform the work as it is done.
Fuses -- Anyone who has worked with electrical systems knows all about fuses and how they fail. They can burn out over time, may just be loose, or can blow out during an electrical storm or due to overload from another failed component. Of course, that's what they're supposed to do; they stop surges from going through and damaging the rest of the system. When a fuse fails, whatever system it was protecting will stop working.

Be careful of dishonest HVAC contractors. There’s no magical formula to see if an HVAC contractor is scamming you, unfortunately, but remember that they typically do this in one of two ways: first, they are charging grossly low prices (far below everyone else), or second, they aren’t including what everyone else is. In the first situation, they will charge you change fees, other hidden fees, or they stole the equipment and are passing themselves off as legitimate contractors (very common in California these days). In the second situation, they are charging you a very fair price, but aren’t including what the other contractors are (i.e. charging $10,500 for the installation which is fair, but not including the ductwork which is a scam unless there is some other, complex stuff going on there).


SEER is useful for comparing one model to another much in the same way that a car's calculate MPG is useful. It's not an accurate prediction of exactly how efficient the system is, but it can tell you which one is more efficient. Also, since SEER is based on a "cooling season", what region you live in will determine how long or short your cooling season is.

We installed a TRANE XL18 HVAC with a TRANE HV80 furnace 16 years ago and it still works great in Tucson, AZ.  We inquired into a replacement for the future since the R-22 refrigerant will be off market at the end of this year.  Our maintenance folks want to sell me a new system anyway (even though the TRANE works great).  We are considering the BOSCH Inverter heat pump as a lower cost option down the road.  Watch out for the tricky salesmen trying to sell beer at champagne prices though. Get estimates on whether you need to replace your current system and how much it could cost.  And if they are factory certified.


The next step was cleaning the cold air returns. He found a good spot to drill an 8” hole for his vacuum hose. The procedure matched the other air ducts except that when he finished at the two cold return registers he drilled several holes in the cold ducts in the basement and blasted air into them. Because of our houses age and the upgraded return system, I noticed that the main sheet metal return duct had no top but was just butted up against the ceiling in the basement. When he blasted air in, dust and crap shot out the edges along the ceiling. Once he finished that he removed the filter and “swept” out anything at the bottom of the return with his hand into the 8” hose.
HRV/ERV Ventilators: These whole-house ventilators exchange air. They are ideal for homes with what is called a “tight envelope,” homes where house wrap has been applied and airgaps in the attic, around windows, doors and outlets have been sealed. Air in these homes becomes stale and polluted, so exchanging the air is important to IAQ. Heat recovery ventilators (HRV) are designed for cold climates. Energy recovery ventilators (ERV) are best for warm climates.  Your cost for an installed HRV or ERV will range from about $2,000 to more than $5,000 based on its capacity and features.

This company deserves more than five stars. They didn't just replace my heater and air conditioner, they built me a new system for my house. Going above and beyond is a understatement. Steve's staff were 2 of the nicest workers I've come across in a long time. Friendly, knowledgeable, and very clean. Truly a top rated company. Thanks Steve.   Great job.
If you are using existing ducting, it will have to be inspected. Proper ducting loses around 2% to 5% of your energy. Old, leaking ducts can lose 50% or more. A contractor will need to have the ducts inspected and replace any parts ahead of time. If you are changing the size of your HVAC system because of significant changes to your home, you might need to replace the ductwork regardless.
Capacitors -- Capacitors help your HVAC motor start from a standstill. Over time they can weaken. As they weaken, they cause the motor to run hotter. This can shorten the life expectancy of your motor. Once a capacitor fails, the whole motor will stop working. You usually won't notice that a capacitor has weakened until your motor stops turning on.
I hope that those customers you have with breathing problems don't follow your advice too closely. You are doing them a disservice. Dirt in your ducts does not always stay there, depending on what the contaminants are. I bet you tell your customers not to worry about mold either- just to kill it with bleach. Educate yourself before opening your mouth- You may kill someone someday with your opinion.
In the middle of summer—even more so in North America—AC repairs are undoubtedly the last thing you want to have to think about. But that won’t keep them from taking place. Fortunately, Service Experts Heating & Air Conditioning is dedicated to completing expert quality AC repair, maintenance and installation throughout the North America area. We certainly don’t want you to be stuck in an uncomfortable home during the hottest days of summer.
Quality and price should come hand in hand, a too-good-to-be-true price for an efficient air duct cleaning will not give you the quality that you wanted. To make sure you are getting your money’s worth, check reviews of air duct cleaning companies, certifications from industry since this work requires continuous learning due to new techniques and research breakthrough from time to time. My mom is located in Arizona and they trust J&M Restoration air duct cleaning company, they have an A+ BBB rating, they used EPA approved sanitizing agents, their technicians are NADCA certified, and the company is certified by the Institute of Inspection, cleaning and Restoration. Make sure to shop around and get written estimates first.
Multiple inventions within this time frame preceded the beginnings of first comfort air conditioning system, which was designed in 1902 by Alfred Wolff (Cooper, 2003) for the New York Stock Exchange, while Willis Carrier equipped the Sacketts-Wilhems Printing Company with the process AC unit the same year. Coyne College was the first school to offer HVAC training in 1899.[12]
Although i love to burn candles, depending on the type your asking for problems big ones! At work one day i had been talking with co workers about these black shadows that were appearing on my ceilings and higher wall areas. They seemed to in the corners and along the stud supports , i could even see what i thought to be where all had been nailed. There would be dark shadows perfectly straight across my ceiling and then real dark circels every few inches within the lines. I thought it was the propane heat but learned quickly that oil heat will do that but not normally propane. A co worker brought me a magazine with a huge article about candles and what actually burns off them when lit, an ashy soot that is attracted to the areas on walls and ceilings that omit the most heat or warmth, of course where the drywall and studs meet and corners of the room. Its been about 8 years since i painted the entire house. I started bending to my love for candles again in the last 3 years, surprise i will be spending part of my summer re painting again!! No more candles ,well maybe at the holidays LOL
I've been in business in Florida for 25 years and purchased a $12,000 duct cleaning system 4 years ago. In the last four years I've cleaned 5 duct systems charging around $400 each. Not a very good return on investment. What I have been doing most the time is I get a call by someone panicked because they called some low priced company to inspect their system and were told they have dangerous black mold. Then they call me to have a look. Most the time they don't have mold, ducts look very clean. However the coils are dirty and the inside of the air handler cabinet needs cleaning. Keep in mind not every system can handle supper high efficiency filters! These filters can block air flow quite a bit right out of the package. Many older systems can't handle pleated filters due to increased static pressure. "Back rooms with low air flow". I have taken many hours of classroom study on indoor air quality. Never got any certification because I don't want to pay another organization dues yearly. I think the problem with duct / system cleaning is most people are suckers for low priced scams that are rip- offs . People call me all the time and ask how much? When I tell them average $400 they hang up. I know I do the job correctly and honestly, and they are going to get racked over the coals by the scam artists by calling $79 whole house duct cleaning guys. People need to check internet, angies list and BBB reviews. But keep in mind even reviews need to be sifted through your rational person filter.
2. If air quality is so important and duct cleaniliness is so uncertain, why not adopt doubling filtering; that is, in addition to the existing main furnace filter, add a filter at each air outlet. I understand replacing so many filters would be a burden, but air outlets can be designed for easy filter replacement. The builders and home design engineers should bear responsibility to provide good and low maintenance homes, rather than prioritizing on fancy or costly featuers for homes.

Furnace cleaners are mostly young men, I know this, I have been one for 15 years or so……so heres the truth, if there are any allergies, children, older people with health issues, we are GOING to make money. do not tell the company you have hired about any health complication. they are salesmen. and they don’t care about you. or your money. make sure they do a good job, then kick them out. you don’t need all the bells and whistles they wanna sell you. any idiot can clean duct work, like I said, I am one of them. I am very good at it, but I don’t have the back bone to sell a widowed old lady a humidifier that she doesn’t need for 500 bucks, overall, if you think you need this service done, which you probably don’t, get it done, do not spend anything over 300$ and do not do it again for at least ten years.


WELL, this summer when I opened them up we had black dust spewing from one of the upstairs vents. It resembled the fuzz that comes off new towels. This prompted us to look into duct cleaning. We heard from someone who had it done several times, said it was worthwhile, and knew of a firm that did a good job. Clean Air America sent a single technician for the appointment and after counting registers and ducts gave me a price of $360.00 which included “sanitizing” the system (a $99 additional fee per can used). The small size of the plenum forced him to connect the 8” round vacuum hose from the truck to the 10” square opening from our humidifier unit. In hindsight, a mistake since it reduced the “negative” pressure in the system.
Despite Bergendahl's experience, Vinick says NADCA's certification standards have improved the situation. "A lot of [service companies] weren't going about it the correct way," he says. “We have an anti-fraud task force, and we’ve gone after some fraudulent duct cleaners with the help of state attorneys general.” He suggests that in addition to NADCA membership, homeowners make sure their cleaners are an established business, have appropriate insurance and are registered to do business in their state and locality.
The Chartered Institution of Building Services Engineers is a body that covers the essential Service (systems architecture) that allow buildings to operate. It includes the electrotechnical, heating, ventilating, air conditioning, refrigeration and plumbing industries. To train as a building services engineer, the academic requirements are GCSEs (A-C) / Standard Grades (1-3) in Maths and Science, which are important in measurements, planning and theory. Employers will often want a degree in a branch of engineering, such as building environment engineering, electrical engineering or mechanical engineering. To become a full member of CIBSE, and so also to be registered by the Engineering Council UK as a chartered engineer, engineers must also attain an Honours Degree and a master's degree in a relevant engineering subject.
In reading through all this about duct cleaning, THE ONE preventative measure people need to realize is that a poorly installed HVAC system that is not sealed and air tight to ensure that ALL indoor air passes through a GOOD air filtration system IS THE best means of ensuring your ducts remain clean. Duct cleaning does not now and will NEVER improve an HVAC systems efficiency. Proper maintenance and installation are the key just as improper installation practices allow for dust infiltration into the duct system. I am a state licensed contractor in Texas, and unless people have their hvac system sealed and/or properly installed, duct cleaning is an absolute waste of money. My duct system is 12 years old as is as clean today as the day I installed the system with ductwork. SO before ANYONE jumps on the bandwagon of duct cleaning, get with your hvac professional FIRST.
Fast forward 1 year and 1 week and the circuit board that HVAC Service had installed has failed again. They came out and said that it failed from water condensation dripping onto it, so we needed to replace it and reroute the pipes to prevent future water damage.  That would cost double what I paid last year.  Why didn't they fix the problem last year at the initial repair instead of putting in a circuit board that was bound to fail again?!? They were strongly recommending that the furnace be completely replace for a huge fee to avoid the same thing happening again.  I paid $59 for them to tell me they didn't fix it right last year. This didn't feel right, so I sought a second opinion.

I am NADCA Certified Air Systems Cleaning Specialist. Over the year I have learned on simple answer to this questions: there air duct cleaners and there are pretenders. There will be no benefit at all if you use on the very cheap pretender because they will not really clean anything. On the other hand if you call a qualified air duct cleaner with a NADCA Certification you will, like 99% of my customers, report improvement with your respiratory problems, you will see less dust and the job will pay for itself with energy savings and repair prevention.

We are a hvac company that provide air duct cleaning service are minimum charge $400 to do a proper air duct cleaning with 2 techs avg 3-6 hours that includes sanitizing. I get phone calls all day about the $99 your not going to get much of a cleaning for that price it for them to get there foot in the door and up sell that the only way for them to stay in business. Just from my 15 years of duct cleaning experience.
All of the products discussed above are registered solely for the purpose of sanitizing the smooth surfaces of unlined (bare) sheet metal ducts. No products are currently registered as biocides for use on fiber glass duct board or fiber glass lined ducts, so it is important to determine if sections of your system contain these materials before permitting the application of any biocide.
×