Just had my air ducts cleaned. They used a high pressure air hose in all the heat ducts and cold air returns. He showed me the stuff that came out, the reason for the duct cleaning was the fact that I had a problem. With rodents. There was quite a few mummified rats and mice, and he said I wouldn’t have to have them done again unless I incur another problem or have renovations done. Cost me 345.00 for a 2 storey large old home. Not a bad price as I had them done when I moved in 28 years ago and it cost me 500.00. Lots of dog hair, toys, balls and assorted goodies came out as well. Took them 2 hours. I did have sanitizer put in the ducts because of the dead rodents.
All these pro duct cleaners answer with "it's common sense, everything operates better when cleaner" etc. But your explanation is correct. Especially so with flex tube ducting where dust gets "stuck" between the lowest valleys (between wire coil supports) where air flow is drastically reduced -- which is more than 50 pct of the entire interior surface area of the flex ducting. That sounds like a bad thing but also has a good effect of trapping dust from escaping.
I believe a $3 [sic] pleated cotton filter is all that is ever needed to keep a system running top notch. A cleaning of the blower squirrel cage and of the evaporator [indoor] coil may be needed one time if fiberglass or no filters have been previously used. The return air grille [or grilles] need vacuumed off occasionally, as they are upstream from the filter. The $3 filter should be changed every 3 months [rule of thumb]....and most of them have a little white square on the cardboard frame to write install date.....and the arrow should point into the duct [if at filter grille]....or towards the furnace [if in ductwork slot]...or towards the blower [if in blower compartment]. My two cents.....
They were quick to come out and diagnose the problem with my furnace, but I thought the estimate of $549 a bit high to replace the circuit board.  So called around and found Leo's Appliance in Concord that sells appliance parts and the circuit board was only $90.49 - that is the retail cost to me, so I imagine the wholesale cost is a lot less.  So BEWARE of this company since they wanted $500!!! to replace the circuit board which is located right in the front of the furnace - extremely easy to access.  I hate it that you cannot trust repair companies.
With today’s consistently rising energy costs, improperly sealed windows, ductwork, and poor insulation can pose serious problems for many home and business owners in Arkansas. Wilson's Heating & Air Conditioning provides complete HVAC system servicing including sales, installation, maintenance and repair, and offers numerous practical solutions that will reduce your energy costs.
I to had an odd layer of white'ish dust building up especially during seasonal periods when the HVAC ran a a lot. I carefully swept up the fine dust into a small pile and had it analyzed. Turns out it was very fine fiberglass powder dust. It turns out it is the insulation form the attic! (My attic has blown in insulation). Turns out if you (I) had small gaps around my HVAC registers in the ceiling whee the airs blows into the room. What occurred in my case was that the exiting air at that seam creates a vacuum effect at the grate vent cover and draws and then blows fine insulation dust from the attic into the house. Removing each register grate and sealing each tin outlet gap with calking between the dry wall ceiling and tin fixed the issue. A couple were so bad with bowed gaps I had to screw down the bowed tin to the attaching stud better. Checking the very same glass top desk that catches and shows any dust accumulation now shows only very small amounts of normal house dust build up over several weeks. A big, big improvement. You might have a look by simply removing a couple vent covers yourself.
Yes everyone should get all their ductwork cleaned, because it does help, incame down with major allergies and had serval operations on my sinues because of this problem of air quality and dust, plus i almost died from one of the operations, i was suffering so much. Yes you can seal your duct system by buyind duct seal t instead of tape to tape all the corners of the vent system, tape wears out and gets brittle, the sealant you can buy at home depot, and you just brush it all over the connections of your ductwork, it comes in a container and it is like a thick paste and dries making a good seal for your ductwork.
NADCA and EPA both have good points. Although, organizations are made to make money. Common sense and looking at NADCA and EPA pre-checklist. If you don't see it in the check list, you don't have to do it! But, if you do, look up Diamond certified co.s and the BBB. Beware of bait and switch scams, $60 vents and the like coupons which claim to help all for the measley sum of $79.00 bucks.
My mom just received service from this company. She paid $609 to have her frion replaced. After two uses the AC stops working. A young rep comes out to the house again and notifies her that her entire AC unit and furnace need to be replace for just shy of ten grand, though when her frion was refilled she was told that her system should last another five years. When they came back to tell her how her entire system needed to be replaced, they were generous enough to offer her a $300 credit on the nearly $10,000 estimate of replacing the entire system that was working fine until they touched it. My best assumption would be that there is a mishap with the system is due to their negligence. Id suggest using another company other than these scam artists.
Some research suggests that cleaning heating and cooling system components (e.g., cooling coils, fans and heat exchangers) may improve the efficiency of your system, resulting in a longer operating life, as well as some energy and maintenance cost savings. However, little evidence exists that cleaning only the ducts will improve the efficiency of the system.
Consider what kind of heating and cooling system you want installed for the square footage of your home. Do you want a full system with a thermostat or a specific machine for the summer like a swamp cooler? Do you need a new furnace just for the winter? For any of these projects, the cost will vary depending on the quality, style and machine size you choose. If you have a tight budget, think of going smaller and upgrading over time. For example, if you can't afford to convert your entire home to solar power, you may want to consider only utilizing it to heat your water. Some other types of heating systems are:
I know it has to have a new concentric venting system installed, I believe it needs new plenums ( mine are rusty but both of these require extra work , so someHVAC persons are saying I do not need either!! RED FLAG THERE. Also, it will need a new drain using PVCP ?? Piping run maybe two, depending on where my evep coil drain is conected (here in TN they use to run them in with the septic lines, now they cannot be run through that way), Lastly I am not where or what these things do beides hold water but I was told It needs a filter rack and new filter base safety pan. THATSSS it that is all I know about this stuff aside from the fact that nothing up there is to code thus far LOL. !!
PickHVAC Tips: Don’t be sold on systems with features you don’t want or need. Called “upselling,” it is rampant in the HVAC industry. Some features are nice – if you want them. If your single-stage furnace was loud and pushed out cold air at the start of the cycle, then a two-stage model will improve those issues. If you didn’t notice them, the upgrade will be a waste of money. That’s just one common example.
Although HVAC is executed in individual buildings or other enclosed spaces (like NORAD's underground headquarters), the equipment involved is in some cases an extension of a larger district heating (DH) or district cooling (DC) network, or a combined DHC network. In such cases, the operating and maintenance aspects are simplified and metering becomes necessary to bill for the energy that is consumed, and in some cases energy that is returned to the larger system. For example, at a given time one building may be utilizing chilled water for air conditioning and the warm water it returns may be used in another building for heating, or for the overall heating-portion of the DHC network (likely with energy added to boost the temperature).[4][5][6]

Because an air conditioner moves heat between the indoor coil and the outdoor coil, both must be kept clean. This means that, in addition to replacing the air filter at the evaporator coil, it is also necessary to regularly clean the condenser coil. Failure to keep the condenser clean will eventually result in harm to the compressor, because the condenser coil is responsible for discharging both the indoor heat (as picked up by the evaporator) and the heat generated by the electric motor driving the compressor.

Ventilation is the process of changing or replacing air in any space to control temperature or remove any combination of moisture, odors, smoke, heat, dust, airborne bacteria, or carbon dioxide, and to replenish oxygen. Ventilation includes both the exchange of air with the outside as well as circulation of air within the building. It is one of the most important factors for maintaining acceptable indoor air quality in buildings. Methods for ventilating a building may be divided into mechanical/forced and natural types.[16]


SEER is useful for comparing one model to another much in the same way that a car's calculate MPG is useful. It's not an accurate prediction of exactly how efficient the system is, but it can tell you which one is more efficient. Also, since SEER is based on a "cooling season", what region you live in will determine how long or short your cooling season is.
I own a small mechanical company. My main work is service and system replacements. I have never been a believer in duct cleaning. The company I worked for before had our duct man come out and do my house. I saw no difference. Preventive maintance is what I recomend. Remove fan and clean, seal fan compartment to prevent dust from being pulled in, filters I install media filters, they are 5″ thick and pleated. I have tested them to make sure static presure was not a issue. Heat exchangers and AC coils need to be cleaned. I will tell you this to do a good cleaning I usually spent 1-2 hrs, When I’m finished I would not have a problem eating my diner on the system. Good filters, clean system and properly tuned up are my recomdation to anyone. I’ve included my email feel free to contact me with any questions. winkcfd@yahoo.com
Clean the condenser fan blades before the start of the cooling season. Brush any dust or debris off gently and then uncover the condenser coils, gently cleaning the dirty side. Then wrap the motor and other electrical components in plastic bags and gently spray from the inside with a hose. Now check the base pan under the unit and clear it out of any debris that has gathered.
HVAC System Quality Installation Contractor Checklist -- This checklist identifies all of the steps the contractor has taken for the Energy Star Certification and identifies what work the contractor has done. If the system is later modified, this checklist can help identify what was done to proper Energy Star specifications and what was added later that may not meet the requirements.

Professional cleaning involves getting the dust and debris outside, so they use outdoor ventilation equipment. It is so important that homeowners make sure the professional contractor is using good equipment then, as they could otherwise spread the spores into the home and further agitate sensitive family members. In the case of mold, a cleaner will only be able to tell you it is there, followed by needing an additional mold professional to come out and test or remove the mold. Air duct cleaning industries do not require state licensing, so make sure to check for a company with references.


With today’s consistently rising energy costs, improperly sealed windows, ductwork, and poor insulation can pose serious problems for many home and business owners in Arkansas. Wilson's Heating & Air Conditioning provides complete HVAC system servicing including sales, installation, maintenance and repair, and offers numerous practical solutions that will reduce your energy costs.
I agree that good filtration and a sealed system will prevent the need for duct cleaning. However, when we do get called it is because the duct work has reached a noticeable state of restriction or dust or the homeowner is hyper-sensitive to these pollutants in their home. Most of the time we find that no filter or a cheap (99 cent) filter is being used or they have serious duct leaks in the system. If you are hiring a cleaner make sure they are using professional cleaning equipment which will consist of a rotating brush system and a vacuum source. Be highly skeptical of the contractor with no branded system or the guy who shows up with just chimney brushes and a shop vac. He will not be able to reach around all the corners or all the runs in your system and he will be taking your money for a superficial cleaning at best. Only trust a company that offers VIDEO inspection and more importantly.... a contractor who repairs, installs and seals ducts if a problem is discovered or heaven forbid, created. Good luck and get your ducts sealed if you do have a leak! It is one of the greatest energy losses to a home other than being poorly insulated.
The University of Virginia - 2005 / The Wharton School of Finance - 2016 / U.S. Naval Aviator 2005-2015. At All Systems Mechanical air conditioning and heating, we believe that the experience our clients have is every bit as important as the products they receive. Simply put, our results speak for themselves, and we'd be happy to help. If you're in the market for a new AC or furnace, make sure that you get a fair price! Try our online calculator; click the tab on the top of this page for more information.

I have been a plumbing/gas/hvac tech for 19 years, before that I installed ductwork in commercial buildings and office towers. As the article states, unless you have undergone some type of extensive reno, or ducts have become contaminated, paying for cleaning is pointless. Its one thing if you have a 30 year old home that has never had a duct cleaning and you can actually see mounds of dust built up , especially in the return side, then go for it. Keep in mind that most duct cleaning companies will only get 80% of the dust , or less at best. Keep in mind that most of the dust in your home is lint from clothes and linens, and skin cells from you and your pets and is constantly being generated. Dust that builds up in ductwork , generally stays in the ductwork. The power of suggestion, scare tactics, up sell!!!

Had duct cleaners here coupon for 40.00 for complete home I was not here but my husband was. I told my husband that they will prolly ask for more money and I was right. 85 extra to do duct cleaning which I pled because my dryer vent was full of animal hair extensions then for 600 to clean a/c coils I said no. Just do what the coupon said. Do your homework be 100 steps ahead of these con men rember they con people all day long and know the ans to your objections

Important Tip: Don’t just pay attention to the high-end of the price range! – which is what I know you are all looking at, but also look at the low range. If a contractor is cheaper than this, ask “why?” Usually it is because they don’t have liability insurance, workman’s compensation insurance, are unlicensed, all of the above, or worst yet, they don’t use HVAC technicians. You are spending a lot of money.  Make sure that they are licensed (In California, check here at CSLB License Checker) and insured.
You might also want to check your home for thermal insulation if you live in extreme heat or freezing temperatures. Insulation keeps the heat and cool air in your home, which can lead to a lower electric bill. If the heated or cool air leaks out, your system turns on more often. There are various types of insulation that you can install in your home and a home energy auditor can point out the best places for it in your house.
Hi John, Thanks for reaching out, we would be happy to help you connect with a pro for your project. You can submit a request to our pros here: www.homeadvisor.com, browse a list of pros that serve your area here: http://www.homeadvisor.com/c.html, or send your info to emailus@homeadvisor.com and a project advisor will reach out to assist you. –HASupport
The key to the continued and efficient operation of your heating and cooling system is periodic maintenance. Cleaning the air duct vent system, and servicing you heating and cooling equipment will keep the system operating at its peak performance. Air ducts are cleaned for two reasons. One: to prevent debris from entering furnace and air conditioning components. Two: to prevent debris from cycling through the home. The air duct cleaning contractor needs to employ cleaning methods which successfully removes debris, and ensures that debris does not enter the occupied space. Most contractors can verify the results of the cleaning through video or pictures.
At the state level the rebates are still substantial. For example, switching to a zoned system can get you a $100 rebate from various A/C companies, and state rebates are also included. In Pennsylvania a high-efficiency air conditioner alone can get you up to $300, and a high-efficiency complete HVAC system can see up to $1000. Maryland's incentives get up to $1,250, with a $100 rebate on a tune up of an existing system.
SEER is useful for comparing one model to another much in the same way that a car's calculate MPG is useful. It's not an accurate prediction of exactly how efficient the system is, but it can tell you which one is more efficient. Also, since SEER is based on a "cooling season", what region you live in will determine how long or short your cooling season is.
DIY: We don’t recommend a DIY approach. Depending on the system, working with gas, electricity and refrigerant create dangers. Beyond that, it is essential that split system components be selected for compatibility. DIY installation of an HVAC system will void the warranty of most brands. The manufacturers won’t stand behind the warranty when anyone other than a certified installer does the work. This is true since improper installation is the main cause of poor system performance and mechanical breakdowns.

If you’re anything like most of our readers, you’ve spent hours online researching HVAC information in preparation for replacing your old heater or air conditioner. I’m the same way; it’s a big investment! You may want to consider saving yourself some time and money by getting an HVAC-Facts Report from this online HVAC installation cost calculator.  Take a look:
Some research suggests that cleaning heating and cooling system components (e.g., cooling coils, fans and heat exchangers) may improve the efficiency of your system, resulting in a longer operating life, as well as some energy and maintenance cost savings. However, little evidence exists that cleaning only the ducts will improve the efficiency of the system.
×