From furnace installation and heating system installation to air conditioning installation and central air installation, Lowe’s has all your HVAC installation needs covered. Lowe’s will coordinate with independent air conditioner installation professionals to make installing central air a breeze. So stop worrying about how to install an air conditioner and contact Lowe’s to help with your air conditioning install.
I agree that good filtration and a sealed system will prevent the need for duct cleaning. However, when we do get called it is because the duct work has reached a noticeable state of restriction or dust or the homeowner is hyper-sensitive to these pollutants in their home. Most of the time we find that no filter or a cheap (99 cent) filter is being used or they have serious duct leaks in the system. If you are hiring a cleaner make sure they are using professional cleaning equipment which will consist of a rotating brush system and a vacuum source. Be highly skeptical of the contractor with no branded system or the guy who shows up with just chimney brushes and a shop vac. He will not be able to reach around all the corners or all the runs in your system and he will be taking your money for a superficial cleaning at best. Only trust a company that offers VIDEO inspection and more importantly.... a contractor who repairs, installs and seals ducts if a problem is discovered or heaven forbid, created. Good luck and get your ducts sealed if you do have a leak! It is one of the greatest energy losses to a home other than being poorly insulated.
It’s 11 years plus in the industry I have only had to sanitize two systems both were slab systems that were in concrete and could be cleaned with a different method than normal duct cleaning. We were able to use water to rinse out the disinfectant. Would you use a chemical on anything else you use to eat or drink with and not rinse it off? The ducts in your home should be thought of as your homes heart and lungs and breathe the same air that you do. And just like us we wouldn’t use bad chemicals in our lungs and heart.

Natural ventilation is the ventilation of a building with outside air without using fans or other mechanical systems. It can be via operable windows, louvers, or trickle vents when spaces are small and the architecture permits. In more complex schemes, warm air is allowed to rise and flow out high building openings to the outside (stack effect), causing cool outside air to be drawn into low building openings. Natural ventilation schemes can use very little energy, but care must be taken to ensure comfort. In warm or humid climates, maintaining thermal comfort solely via natural ventilation might not be possible. Air conditioning systems are used, either as backups or supplements. Air-side economizers also use outside air to condition spaces, but do so using fans, ducts, dampers, and control systems to introduce and distribute cool outdoor air when appropriate.


Fuses -- Anyone who has worked with electrical systems knows all about fuses and how they fail. They can burn out over time, may just be loose, or can blow out during an electrical storm or due to overload from another failed component. Of course, that's what they're supposed to do; they stop surges from going through and damaging the rest of the system. When a fuse fails, whatever system it was protecting will stop working.
One of the best ways to know if your ducts or vents need to be cleaned is to just check them. Your eyes will be able to check for indications of mold, dust or pollen buildup. You might also be able to smell the presence of mold, which would be a clear indicator. Ductwork will have some buildup of dust, since the return registrars pull air back in. However, this doesn't mean your ducts have too much debris, and you can easily clean them with a duster or vacuum.
I originally took off one star because of the SNAFU with getting the part ordered.  When Alberto called me on the phone he admitted the person had "gotten busy with other things" and apologized.  THAT was taking the high road and I was impressed by that.  Sadly, for reasons I won't guess at, Alberto has decided to take the low road in his comments and imply that they got the part as quickly as possible.  Well, we called at 2:30 so did someone spend six and a half hours finding the part??  That seems very doubtful.
AC installation in Fort Smith, AR is vital to comfort, safety, and quality of life. The region is infamous for the unbearable heat that can often become debilitating. This is why investing into an AC to improve the overall lifestyle of your family is well worth the cost. Avoid the constant frustration by seeking the assistance of a professional team.
I forgot about a pot of sweet water I had on the stove to boil. When I finally smelled it the kitchen and dining room I=was smoke filled. I mean thick smoke. I opened doors and windows for a few hours to remove the smoke but the smell is still here and terrible. I had to use the AC and that smell started coming out of the vents. Now what do I do? I have COPD emphysema so I have to be very careful about what I inhale. I already have inhaled too much smoke from all of this which has hurt my lungs even more. I can’t afford for them to get worse over this. How can I get the right person to come out and clean the ducts and furnace or is that the only way to remove that burnt smokey smell. The pot never caught on fire but it sure did produce a lot of smoke. I already have replaced the filter on the furnace. It needed it even though it had just been replaced just last week. I need help or really my lungs need help. Who do I call here in Indpls IN.
Professional cleaning involves getting the dust and debris outside, so they use outdoor ventilation equipment. It is so important that homeowners make sure the professional contractor is using good equipment then, as they could otherwise spread the spores into the home and further agitate sensitive family members. In the case of mold, a cleaner will only be able to tell you it is there, followed by needing an additional mold professional to come out and test or remove the mold. Air duct cleaning industries do not require state licensing, so make sure to check for a company with references.
We installed a TRANE XL18 HVAC with a TRANE HV80 furnace 16 years ago and it still works great in Tucson, AZ.  We inquired into a replacement for the future since the R-22 refrigerant will be off market at the end of this year.  Our maintenance folks want to sell me a new system anyway (even though the TRANE works great).  We are considering the BOSCH Inverter heat pump as a lower cost option down the road.  Watch out for the tricky salesmen trying to sell beer at champagne prices though. Get estimates on whether you need to replace your current system and how much it could cost.  And if they are factory certified.
Reinstall the access panel and disconnect block. Turn on the circuit breaker and furnace switch. Then set the thermostat to a lower temperature and wait for the AC to start (see “Be Patient at Startup,” below). The compressor should run and the condenser fan should spin. If the compressor starts but the fan doesn't, the fan motor is most likely shot. Shut off the power and remove the screws around the condenser cover. Lift the cover and remove the fan blade and motor (Photo 7). Reinstall the blade and secure the cover. Then repower the unit and see if the fan starts. If it doesn't, you've given it your best shot—it's time to call a pro.

We use third party data sources to conduct a criminal search, in the state in which the owner/principal of the company is located, for any relevant criminal activity associated with the owner/principal of the business, within the three years prior to such service professional's application for membership in the HomeAdvisor network. HomeAdvisor's third-party vendor uses a national criminal database ("NCD") to screen our service professionals. The comprehensiveness of the NCD varies by state. Please be aware that the reporting in the NCD is particularly limited in the following states: AL, CO, DE, GA, ID, KS, KY, LA, ME, MA, MI, MS, MT, NE, NV, NH, NM, SD, UT, VA, VT, and WY.
i got angies list deal for 109 air duct clenaing, dryer vent cleaning, and furnace inspection, {healthy duct cleaning} i call the company, they arrive on time. did excellent service what ever i purches i got. they give me furnace inspection and the told me that my furnace is very dirty and they offer me to clean that for 250 extra. i paid and i am very happy from this service. i try before 2 diffrent company that i got deal from them as well the just give me estimate and don’t even do the job. so guys don’t spend time if you need deep cleaning just cal this guy the offer free estimate as well.

fact is most homes have bad filter racks. when you insert the filter it doesn’t seal well to the sides so some of the air and dust bypass it and end up in the supply ductwork and into the house. Most of the dust in the supply ductwork settles down and doesn’t get blown in the house but some of it does when the blower starts up or when you put a new filter. If you have allergies or other health problems put in an electronic air cleaner, get your ducts cleaned and run the fan as much as you can afford. you can also get an ECM motor installed which is going to be worth it if you want to run the fan 24/7. If you have uninsulated metal ducts take down the ones you can and wash them. Then put them back and seal the joints. Cleaning the ductwork also improves airflow which is important to AC and Heat pump systems for efficiency. An electronic air cleaner will also improve airflow and static pressure because they usually have a much larger filter surface area. An electronic air cleaner also keeps the ac coil clean like new which means better efficiency and no cleaning needed. AC furnaces sometimes grow mold around the coil because of the condensation. Electronic air cleaners should be able to filter mold spores but the best remedy is installing a UV light next to the coil which will kill the mold.
What you might not know is that the brand you choose is one of the most important factors in determining a fair HVAC installation cost. So, before delving in-depth, let’s take a quick look at the average prices of a new air conditioner and matching coil by brand…keep in mind, these are the average prices (by brand) that contractors pay for your AC equipment, and it is meant to give you a rough guideline until you are closer to buying:

One of the best ways to know if your ducts or vents need to be cleaned is to just check them. Your eyes will be able to check for indications of mold, dust or pollen buildup. You might also be able to smell the presence of mold, which would be a clear indicator. Ductwork will have some buildup of dust, since the return registrars pull air back in. However, this doesn't mean your ducts have too much debris, and you can easily clean them with a duster or vacuum.


PickHVAC Tips: Oil burns dirty, so it is important to have your plenum and ducts checked to see if they should be cleaned when replacing an oil furnace. If you don’t clean the plenum and ducts when replacing the furnace, the new furnace might not run as efficiently and comfortably as possible due to restricted airflow. This can also reduce the oily smell sometimes associated with oil furnaces.
Preventing against air leakage is great, but the only way to keep dust and debris out of a duct system would be to completely seal off the return-air side of the system, which would render the system useless. Cold-air returns will always pull dust and other particles into the system. A high-MERV rated filter is definitely a good idea, but it does nothing to keep the return side of the system clean. Definitely agree though to use foil tape to seal seams, etc. Duct tape dries out over time and as it does can actually add more particles to the air.
Deciding if central air is worth the cost depends on your needs and local housing market. If you live in a hotter climate, it can definitely be worth the price. Not only can it keep your home at a comfortable temperature, but air conditioning can even save lives during extreme heat waves. But in a milder zone without severe temperatures, window units, fans or the breeze from an open window could be adequate.

A year and a half ago (fall of 2015) we replaced the furnace and air conditioner. From what we could determine this was the third forced air furnace and second air conditioner unit for the house. As part of the installation, we changed out the two 6″ ducts feeding the second floor with 8″ ducts. The idea was to get more cold air to the second floor in the summer. It worked and for the first time the second floor and first floor temperatures were the same when the air conditioner was running. Of course, to make the system work I close down upstairs duct damper doors in the winter and open them up in the summer.

Be careful with HVAC change-outs.  Change-outs are only about 15-20% of the HVAC installation industry. Decrease HVAC installation cost by investing in new ductwork now if needed. Your ducts wear out too, and make sure that your ducts are in fantastic shape if you do this. Many contractors push this because it’s easy and cheap for them, with good pay-off. Do your research and replace them if you need to in order to avoid doing it later, as well as avoid potential health hazards from using old, broken ductwork.


Preventing against air leakage is great, but the only way to keep dust and debris out of a duct system would be to completely seal off the return-air side of the system, which would render the system useless. Cold-air returns will always pull dust and other particles into the system. A high-MERV rated filter is definitely a good idea, but it does nothing to keep the return side of the system clean. Definitely agree though to use foil tape to seal seams, etc. Duct tape dries out over time and as it does can actually add more particles to the air.
If you’re purchasing from a big-box store, you can expect to pay approximately $120-$1,000 for a window unit. Window units are appealing for their quick setup and relatively low cost, but they can use more energy over time than central air and only cool the room in which they’re installed. The price will vary depending on the type of air conditioner you buy and its cooling capacity. Window units, which require minimal installation, are one of the most affordable options on the market. Portable air conditioners don’t have the cooling power of a window unit, but they do have the perk of being transportable from room to room. Expect to pay between $225 and $800 for a portable air conditioner, on average. The cost of an air conditioning system with coils, condenser and line (not including installation or ductwork) can range from approximately $2,000 to $4,000 or more. If you don’t have (and don’t want to put in) ducts, a ductless mini-split air conditioner is a good option, although pricey up front. Pricing can range from $650 to $4,250 per unit on average; you’ll need one unit for each room in which you want temperature control.
While you consider having your air ducts cleaned, it is a good idea to take a look at your dryer vent. If your dryer vent is clogged, you could be losing energy efficiency. Worse yet, you could be increasing the risk of a house fire. Having your dryer vent professionally cared for costs about $130 on average, and could save you a bit of money and a lot of headaches in the future. For more information on the benefits and cost of having your dryer vent cleaned, take a look at our comprehensive cost guide.

Had our ducts cleaned late April, 2016. Sodium Chlorite was sprayed into ducts after cleaning. Ever since, we have been bothered with eye and nasal passage irritation because of a “chemical” and “musty” odor. This odor is present whether or not a/c is on.) We are told the sodium chlorite (“EnviroCon, manufactured by Bio-Cide International) is used in hospital and nursing home settings and is not hazardous to health. The air duct company’s suggestion is that they come out and spray even more sodium chlorite…we absolutely don’t want this done! Have had various other recommendations about what we need to have done to remedy our problem. We will be unable to stay in our home if a resolution cannot be found. We’d be willing to replace the ductwork if necessary. (One professional suggested that the cleaning may have “knocked something loose” inside the ductwork and that is the source of the irritant.) This home was built in 1920…no idea when the present ductwork was installed. Any suggestions would be appreciated.


The performance of vapor compression refrigeration cycles[26] is limited by thermodynamics. These air conditioning and heat pump devices move heat rather than convert it from one form to another, so thermal efficiencies do not appropriately describe the performance of these devices. The Coefficient-of-Performance (COP) measures performance, but this dimensionless measure has not been adopted. Instead, the Energy Efficiency Ratio (EER) has traditionally been used to characterize the performance of many HVAC systems. EER is the Energy Efficiency Ratio based on a 35 °C (95 °F) outdoor temperature. To more accurately describe the performance of air conditioning equipment over a typical cooling season a modified version of the EER, the Seasonal Energy Efficiency Ratio (SEER), or in Europe the ESEER, is used. SEER ratings are based on seasonal temperature averages instead of a constant 35 °C (95 °F) outdoor temperature. The current industry minimum SEER rating is 14 SEER.[27][dead link]

Quality and price should come hand in hand, a too-good-to-be-true price for an efficient air duct cleaning will not give you the quality that you wanted. To make sure you are getting your money’s worth, check reviews of air duct cleaning companies, certifications from industry since this work requires continuous learning due to new techniques and research breakthrough from time to time. My mom is located in Arizona and they trust J&M Restoration air duct cleaning company, they have an A+ BBB rating, they used EPA approved sanitizing agents, their technicians are NADCA certified, and the company is certified by the Institute of Inspection, cleaning and Restoration. Make sure to shop around and get written estimates first.


ISO 16813:2006 is one of the ISO building environment standards.[31] It establishes the general principles of building environment design. It takes into account the need to provide a healthy indoor environment for the occupants as well as the need to protect the environment for future generations and promote collaboration among the various parties involved in building environmental design for sustainability. ISO16813 is applicable to new construction and the retrofit of existing buildings.[32]
A dehumidifier is an air-conditioner-like device that controls the humidity of a room or building. It is often employed in basements which have a higher relative humidity because of their lower temperature (and propensity for damp floors and walls). In food retailing establishments, large open chiller cabinets are highly effective at dehumidifying the internal air. Conversely, a humidifier increases the humidity of a building.
Vinick calls air duct cleaning an essential part of home maintenance, akin to mopping and vacuuming. "It’s like changing the oil in your car,” he says. “If you don’t change the oil, you’re going to have a problem. When your components are loaded up with debris, the system has to work harder. When you remove that debris, you get energy consumption savings.”

My point is that the brand of equipment you choose is going to affect your HVAC installation cost greatly. People often call us for an air conditioning installation job and say, “I would like to install Carrier equipment.” Now, if you are a future client of ours, I’ll have to warn you – I can be a bit of a smart-ass. Why can’t work be fun? Besides…I was in the Navy for 11 years, what do you expect. 

One of the difficulties encountered by many air duct cleaning service companies is that their attention is not really on air duct cleaning. For example, many heating and cooling companies offer duct cleaning as a supplemental service, but of course their primary business is installing and servicing heating and cooling equipment. For these companies, air duct cleaning is not always given the attention it deserves and is often done by less experienced employees whose interest is not in duct cleaning but in repairs and installs. And it is almost always done with inferior air duct cleaning equipment. Still other firms (like carpet cleaners) offer a large variety of services and claim to “do everything.” Because of their lack of focus they may not actually be very good at many, if any, of the services they offer. They cannot simply buy an attachment for their carpet cleaning machine and magically become a great duct cleaner.

I can’t believe I got ripped off by this Air Duct Cleaners. I called them for this $63 coupon per furnace unlimited vents then when they came after he checked it all I hear is I have molds and leak all is worth $499, $799, $899 per furnace but I told him to just clean the duct and patch the single leak per furnace worth $38 each. Still eanding $899 total. All the work he done is in less than an hour he didnt even go to each vent to clean it. All he did is to path the air leak on that entry pipe to the furnace and open the main venting system, vacuum it, and wash the floor of the vent with a solution. Overall time is about 20 mins talking with me discussing all the option which thinking they made me think I don’t really have an option and 40 mins wash and vacuum he took pictures of before and after of only one furnace. He gave me a receipt without the details on what he has done in the house just the name and price. I think we may need a strict law to punish and control all this companies who do this so other company who do good will despise them.


ISO 16813:2006 is one of the ISO building environment standards.[31] It establishes the general principles of building environment design. It takes into account the need to provide a healthy indoor environment for the occupants as well as the need to protect the environment for future generations and promote collaboration among the various parties involved in building environmental design for sustainability. ISO16813 is applicable to new construction and the retrofit of existing buildings.[32]
I had someone out to clean my ducts last weekend. He took a blue bag up in my attic. He came back down in just a few minutes and said I had mold and he even showed me a picture of something saying it was mold but I couldn’t really tell. I refused his service to take care of the mold. He went back up in the attic for a little while and then came down. I never heard any sounds that he was actually up there doing anything. How do I know if he actually cleaned the air ducts?
Air conditioning units are prone to the pitfalls of wear and tear. You can prolong this, however, with proper maintenance procedures. Without regular maintenance even an immaculate AC installation in Fort Smith, Arkansas cannot guarantee performance. Our maintenance service is thorough, leaving no area unattended. If there’s a problem, we’ll catch it early and prevent avoidable breakdowns and costly repairs.

The next step was cleaning the cold air returns. He found a good spot to drill an 8” hole for his vacuum hose. The procedure matched the other air ducts except that when he finished at the two cold return registers he drilled several holes in the cold ducts in the basement and blasted air into them. Because of our houses age and the upgraded return system, I noticed that the main sheet metal return duct had no top but was just butted up against the ceiling in the basement. When he blasted air in, dust and crap shot out the edges along the ceiling. Once he finished that he removed the filter and “swept” out anything at the bottom of the return with his hand into the 8” hose.
The next step was cleaning the cold air returns. He found a good spot to drill an 8” hole for his vacuum hose. The procedure matched the other air ducts except that when he finished at the two cold return registers he drilled several holes in the cold ducts in the basement and blasted air into them. Because of our houses age and the upgraded return system, I noticed that the main sheet metal return duct had no top but was just butted up against the ceiling in the basement. When he blasted air in, dust and crap shot out the edges along the ceiling. Once he finished that he removed the filter and “swept” out anything at the bottom of the return with his hand into the 8” hose.

Central home air conditioner service systems consist of two major components: a condensing unit that sits outside your house, and the evaporator coil (often referred to as an A-coil) that sits in the plenum of your furnace or air handler. The refrigerant in the A-coil picks up the heat from your home and moves it to the outdoor condensing unit. The condensing unit fan blows outside air through the condensing coil to remove the heat. The condensing unit houses the three parts replaceable by a DIYer: the AC contactor, the start/run capacitor(s) and the condenser fan motor. The condensing unit also houses the compressor, but only a pro can replace that. The A-coil has no parts that can be serviced by a DIYer.
×