I am in need of HVAC ADVICE!! I need a new furnace badly, mine is cracked. I have bought both a 95 % AFUE furnace and a 5 Ton evap coil, I figured it should all be replaced at once for both cost and efficency. My question is with all the negaitive things I have heard about companies ripping you off, what type of price should I pay someone for putting in those two items and bringing everything in my attic up to code? I have been quoted $550 - $ 3300. Wide margin here!! Then of course comes the licencing part!! I know in my heart that I should use a licenced contractor but I have had such bad luck and prices from them that honestly one that was licened in Ga. and just not here in TN and is a tech. which charges 1100 - 2200 less sounds good as so long as I pay some type of Profenial HVAC person say $100 to inspect the work after its done and before I pay them.

Having evaporator and condenser coils cleaned could cost between $100 and $400. If your coils can be accessed in-place, you'll be looking at a lower service cost. If your technician needs to remove the them first, the cost should be around $400. Having the evaporator and condenser coils cleaned can have a significant impact on the efficiency of your system. If your coils are excessively dirty, they won't be able to do their job and your system will have to work harder. Keeping up with the hygiene of these components can save you money in both the short and long-term. For example, replacing evaporator coils can cost anywhere from $650 to $1200.


Demonstrate visible evidence of microbial growth in your duct work. Some service providers may attempt to convince you that your air ducts are contaminated by demonstrating that the microorganisms found in your home grow on a settling plate (i.e., petri dish). This is inappropriate. Some microorganisms are always present in the air, and some growth on a settling plate is normal. As noted earlier, only an expert can positively identify a substance as biological growth and lab analysis may be required for final confirmation. Other testing methods are not reliable.
Window air conditioners cost less than central units, averaging $300. These systems generally suffice to keep a room cool on warm spring and summer days. They can bring added comfort for a reasonable price but are less powerful than a central air conditioner. If you have a bigger home with multiple rooms, you will probably need to have a larger system installed. Central air can cool several rooms at once, while window AC units usually only cover one or two rooms at a time.
Our unit is 16 years old and we've had it checked out recently since it seems to be running excessively. Over all the tech says it is putting out well; it's the correct size, we have no shade and we've been having extreme heat with high humidity. The info you provided is very helpful and will help us make an informed decision when the time comes. Thank you so much.
I am NADCA Certified Air Systems Cleaning Specialist. Over the years I have learned on simple answer to this questions: there air duct cleaners and there are pretenders. There will be no benefit at all if you use on the very cheap pretender because they will not really clean anything. On the other hand if you call a qualified air duct cleaner with a NADCA Certification you will, like 99% of my customers, report improvement with your respiratory problems, you will see less dust and the job will pay for itself with energy savings and repair prevention.
I am very interested by your post. We recently had a lead inspection on our property and one thing the lead inspector suggested was to get the air ducts cleaned out. We had our ducts cleaned last year after we under went a large renovation project (since we have a toddler in the house). This year we decided to go for lead compliance and had all our lead removed (we moved out for the work). Recently, my son had a false positive lead test, which prompted us to get a lead dust inspection around the house (including having the vents dust-wiped on the inside). The levels inside the ducts weren't crazy high (but more than would be acceptable for a floor). As it turned out my son's lead levels are very low (but not zero). Is it possible however that lead dust from the inside of a vent can come out? Would this be a scenario where you think air duct cleaning would be beneficial?
I thought the price advertised at 129.95 for duct cleaning was great and called to clean our ducts. When they came in to do the the job I could not be home and my wife dealt with them. My wife ended up paying 954.00. They convinced my wife that there was 1.5 inches of mold built up on the Evaporators and coils. It is not the money, my wife could not go to the basement to witness the mold build up or the coil fouling. We have not cleaned our ducts for at least 10 years. The last price we paid for our duct cleaning was 150.00. My concern is that they told my wife not to turn on the heat for 2 hours due the strong chemicals they used to kill the mold. Are these chemicals approved as safe?
No matter where you bought your air conditioning system, we can repair it. We have years of experience working with all the best central air conditioner brands such as Kenmore, Carrier. Trane, Goodman, and Rheem. As a result, you can rest assured we’re familiar with your air conditioning system and we have the parts you need to complete a successful air conditioner repair.
Free cooling systems can have very high efficiencies, and are sometimes combined with seasonal thermal energy storage so that the cold of winter can be used for summer air conditioning. Common storage mediums are deep aquifers or a natural underground rock mass accessed via a cluster of small-diameter, heat-exchanger-equipped boreholes. Some systems with small storages are hybrids, using free cooling early in the cooling season, and later employing a heat pump to chill the circulation coming from the storage. The heat pump is added-in because the storage acts as a heat sink when the system is in cooling (as opposed to charging) mode, causing the temperature to gradually increase during the cooling season.
PickHVAC Tips: Electricity resistance heat is the most expensive heating type. You don’t want one of these unless you’re heating less than 30 days per year. The upfront cost of an electric furnace is much lower than the cost of a gas furnace. However, operating costs are two to three times higher. If winters are cold where you live, you’ll waste your upfront cost savings in just a few years of high electric bills.
You and your family spend hours sitting on your favorite chairs, couches and sectionals. Over time, dander and body oil become trapped in the upholstery, but with regular cleanings you can keep these delicate fabrics looking, feeling and smelling great. We examine your furniture and select the best process to safely clean and protect any kind of upholstery, including leather. 
Many central air conditioning systems use the furnace blower to distribute cool air through the home. If you do not have a central heating system installed, it is cost-effective to install a heating and air conditioning system at the same time. If you already have central heat, you can use the existing fans and duct system for the central air system.
Equipment used to clean ducts varies widely. The cheaper the equipment used the more you are just wasting money. This is why it's typically not worth doing. In some situations it may be beneficial, but only after determining and investigating the duct system. This should be done by a licensed HVAC contractor and not a duct cleaner that typically do not hold and HVAC license. (Duct cleaners aren't required to be licensed in HVAC in many areas.)

It’s 11 years plus in the industry I have only had to sanitize two systems both were slab systems that were in concrete and could be cleaned with a different method than normal duct cleaning. We were able to use water to rinse out the disinfectant. Would you use a chemical on anything else you use to eat or drink with and not rinse it off? The ducts in your home should be thought of as your homes heart and lungs and breathe the same air that you do. And just like us we wouldn’t use bad chemicals in our lungs and heart.
Stick with a maximum of 16 SEER units in most cases.  Like I said above, contractors push higher SEER units because they make more money, but these units can be expensive at this stage of development, and can drive up your HVAC installation cost.  21 SEER units run about twice the price of a 14 SEER unit, so unless you live in a desert and plan on being there for 30 more years... Likewise, a 16 SEER unit typically costs only about $600-$1,000 more than a 14 SEER, and will usually pay for itself over the lifetime of the unit.
Duct cleaning is a complete scam, I was a “duct cleaning technician” for a whole week before I was fired for not upselling elderly widowed women $2000 extra for “toxic mold remediation” when their ducts were spotless to begin with. The last two days I was employed there I worked as a “helper” alongside a technician thats been with the company 7 years. He scammed every customer on mold and would at times get as much as $2500 extra for treating “toxic mold” in a typical 3 bedroom house in the suburbs. Wait…it gets even better, the “Biocide” the company used was simply a cheap $4.99 per gallon bought at Home Depot air freshener with no anti-microbial properties that was fogged into the HVAC system for 5 minutes, maybe using 1/2 cup of the stuff. In order to provide the customer with evidence of “mold infestation” the technician would be given bogus mold tests that always resulted in “toxic spores present” regardless if you swabbed the actual duct or nothing at all. Not to mention the actual duct cleaning job (typically $400) did basically nothing and the homeowner could’ve done a better job with a shopvac
fact is most homes have bad filter racks. when you insert the filter it doesn’t seal well to the sides so some of the air and dust bypass it and end up in the supply ductwork and into the house. Most of the dust in the supply ductwork settles down and doesn’t get blown in the house but some of it does when the blower starts up or when you put a new filter. If you have allergies or other health problems put in an electronic air cleaner, get your ducts cleaned and run the fan as much as you can afford. you can also get an ECM motor installed which is going to be worth it if you want to run the fan 24/7. If you have uninsulated metal ducts take down the ones you can and wash them. Then put them back and seal the joints. Cleaning the ductwork also improves airflow which is important to AC and Heat pump systems for efficiency. An electronic air cleaner will also improve airflow and static pressure because they usually have a much larger filter surface area. An electronic air cleaner also keeps the ac coil clean like new which means better efficiency and no cleaning needed. AC furnaces sometimes grow mold around the coil because of the condensation. Electronic air cleaners should be able to filter mold spores but the best remedy is installing a UV light next to the coil which will kill the mold.
Just had my air ducts cleaned. They used a high pressure air hose in all the heat ducts and cold air returns. He showed me the stuff that came out, the reason for the duct cleaning was the fact that I had a problem. With rodents. There was quite a few mummified rats and mice, and he said I wouldn’t have to have them done again unless I incur another problem or have renovations done. Cost me 345.00 for a 2 storey large old home. Not a bad price as I had them done when I moved in 28 years ago and it cost me 500.00. Lots of dog hair, toys, balls and assorted goodies came out as well. Took them 2 hours. I did have sanitizer put in the ducts because of the dead rodents.
The bottom line is: no one knows. There are examples of ducts that have become badly contaminated with a variety of materials that may pose risks to your health. The duct system can serve as a means to distribute these contaminants throughout a home. In these cases, duct cleaning may make sense. However, a light amount of household dust in your air ducts is normal. Duct cleaning is not considered to be a necessary part of yearly maintenance of your heating and cooling system, which consists of regular cleaning of drain pans and heating and cooling coils, regular filter changes and yearly inspections of heating equipment. Research continues in an effort to evaluate the potential benefits of air duct cleaning.
Here in Atlanta we get 6 to 10 $49 coupons in the mail weekly…I have always consider them a complete scam….just had my master bathroom& bedroom and guest bath completely remodeled down to the studs…Had my 3 returns nearest the area sealed to prevent sheet rock dust to spread…it worked and I personally cleaned all 7 returns when a 5 HP , new Rigid shop Vac($99 from HD)…took one hour and I found little evidence that “I need my ducts cleaned” Had quotes from $400 to $600…I use the best air filters for my air handler and change it every 2 to 3 months…..any dust is trapped in it and I believe the Air Duct folks are all cons….
Having evaporator and condenser coils cleaned could cost between $100 and $400. If your coils can be accessed in-place, you'll be looking at a lower service cost. If your technician needs to remove the them first, the cost should be around $400. Having the evaporator and condenser coils cleaned can have a significant impact on the efficiency of your system. If your coils are excessively dirty, they won't be able to do their job and your system will have to work harder. Keeping up with the hygiene of these components can save you money in both the short and long-term. For example, replacing evaporator coils can cost anywhere from $650 to $1200.
Appliance Maintenance Book Snow Blower Maintenance Appointment Schedule Appointment for HVAC Maintenance Carpet Cleaning Services Air Duct Cleaning Services Handyman Service Riding Mower Maintenance Sears Warranty and Satisfaction Guarantee Heating and Cooling Home Renovation Tulsa Window Replacement Home Kitchen Design Roof Installation & Replacement Service Home Improvement Cabinet Refacing & Replacement Home Improvement
The three major functions of heating, ventilation, and air conditioning are interrelated, especially with the need to provide thermal comfort and acceptable indoor air quality within reasonable installation, operation, and maintenance costs. HVAC systems can be used in both domestic and commercial environments. HVAC systems can provide ventilation, and maintain pressure relationships between spaces. The means of air delivery and removal from spaces is known as room air distribution.[3]
Here in Atlanta we get 6 to 10 $49 coupons in the mail weekly…I have always consider them a complete scam….just had my master bathroom& bedroom and guest bath completely remodeled down to the studs…Had my 3 returns nearest the area sealed to prevent sheet rock dust to spread…it worked and I personally cleaned all 7 returns when a 5 HP , new Rigid shop Vac($99 from HD)…took one hour and I found little evidence that “I need my ducts cleaned” Had quotes from $400 to $600…I use the best air filters for my air handler and change it every 2 to 3 months…..any dust is trapped in it and I believe the Air Duct folks are all cons….
Fast forward 1 year and 1 week and the circuit board that HVAC Service had installed has failed again. They came out and said that it failed from water condensation dripping onto it, so we needed to replace it and reroute the pipes to prevent future water damage.  That would cost double what I paid last year.  Why didn't they fix the problem last year at the initial repair instead of putting in a circuit board that was bound to fail again?!? They were strongly recommending that the furnace be completely replace for a huge fee to avoid the same thing happening again.  I paid $59 for them to tell me they didn't fix it right last year. This didn't feel right, so I sought a second opinion.
Your contractor will do a load calculation to determine the proper central air conditioning unit for your home. This calculation accounts for the climate, size, shape and orientation of your home, as well as its square footage. A professional will also look at the insulation, windows, walls, floors and other materials that compose your home. He/she will then examine any leaks, seals and existing ducts or vents.

The short answer is yes, duct cleaning, done right by a reputable company will help with the smell. It is likely though the smell is coming from another source, ie the crawl space. It could also be that another rodent is dead in the duct work. A visual inspection would be in order to check for any breach in the duct system. A duct pressure test would be able to tell you how much air is leaking from the system over all. A hole large enough for an animal to enter would loses a great deal of air, over 300 CFM. It would be worth looking into having this test done and it should cost around $200. Cleaning the air handler and evaporator coil will greatly improve the performance of the air conditioner. Dirt and dust on the evaporator acts as insulation and reduces the amount of cooling done be the coil. Any quality duct cleaning should include cleaning the air handler and coil, and the tech should allow you to watch him perform the work as it is done.
Humidifiers/Dehumidifiers: Humidifiers add needed moisture to the air in winter and very dry climates. Dehumidifiers remove dampness any time of the year. Central air conditioners dehumidify too, but in very humid climates, you might want to remove humidity without also cooling the air. You have a good range of options for both of these HVAC accessories. Whole-house humidifiers cost $350 to $800 installed, while dehumidifiers are $1,250 to $2,000 or slightly more.

"Our Pro was the most courteous and informative gentleman that we have had the pleasure to work with, was great. He let us know immediately what the problem was and what the cost to fix it would be. Also, he let us know how to maintain and extend the life of our washer. He was very personable and made us very comfortable with the process. We would have him back in a heartbeat if anything ever goes wrong again. It was the best experience we have ever had with a appliance repair service."

×