The three major functions of heating, ventilation, and air conditioning are interrelated, especially with the need to provide thermal comfort and acceptable indoor air quality within reasonable installation, operation, and maintenance costs. HVAC systems can be used in both domestic and commercial environments. HVAC systems can provide ventilation, and maintain pressure relationships between spaces. The means of air delivery and removal from spaces is known as room air distribution.[3]
Filtration systems -- A second-stage filter is sometimes inserted & used to remove particulates such as pets, smoking or cooking, as well as other odors, gases, and VOCs (volatile organic compounds). A HEPA filter is also available to remove spores, pollens, bacteria and lung-damaging particles. There are also systems that use ultraviolet (UV) light to protect against bacteria and germs.
I guess, I will start with saying that air duct cleaning is almost never needed. It is not a scam, but it is certainly something that uneducated homeowners get suckered into. In regards to air flow, a well balanced HVAC system should be able to deliver more than enough air flow. If you are not getting good air flow, it's because your system may be out of balance. Additionally, regular cleaning/changing of the air filters will solve about 95% of your problem. Though you would be surprised how many people either a. don't have a filter or b. don't know about it and leave it there for 10+years. a washable one should be cleaned every 6 months(spring and fall) and a disposable one should be replaced every 3-4 months.
Wiring up the thermostat is usually pretty straightforward if an old one is being replaced. If a thermostat is being put in where one had never been before, that could involve running new wiring. The placement of the thermostat is also important so that its sensors can get an accurate reading of the temperature. A thermostat that is blocked by a bookcase or other large furniture will not get a good reading and will not perform efficiently.
Mitsubishi Electric is a world leader in air conditioning systems for residential, commercial and industrial use. Challenged to create air conditioning systems that provide exemplary performance in the wide-ranging climatic conditions found throughout Japan, our engineers develop amazingly sophisticated yet durable units and systems capable of constant use under virtually any natural climatic condition on earth.
If not properly installed, maintained and operated, these components may become contaminated with particles of dust, pollen or other debris. If moisture is present, the potential for microbiological growth (e.g., mold) is increased and spores from such growth may be released into the home's living space. Some of these contaminants may cause allergic reactions or other symptoms in people if they are exposed to them. If you decide to have your heating and cooling system cleaned, it is important to make sure the service provider agrees to clean all components of the system and is qualified to do so. Failure to clean a component of a contaminated system can result in re-contamination of the entire system, thus negating any potential benefits. Methods of duct cleaning vary, although standards have been established by industry associations concerned with air duct cleaning. Typically, a service provider will use specialized tools to dislodge dirt and other debris in ducts, then vacuum them out with a high-powered vacuum cleaner.
No one has addressed mfg homes and doesn't seem any of the comments are from people in So CA which of course does make a difference as my dust comes from the outside not from the vents. My windows are open pretty much 365 days a year. Secondly mfg homes don't have basements or attics I keep mine clean with my vacuum as they are only about 2 ft deep. I purchased my home 10 yrs ago and it is a high end home but have never had a problem. I clean my furnace filter about twice a month as I have cats and most everything in there is cat fur. I am not saying they don't ever need to be cleaned but I am questioning mfg homes, I also clean my own filters in my AC unit outside as the HVAC guy told me too he QUATITY they would sell. I use this same company every year now for my tune up and inspection which takes them about 10 minutes. Not a bad return for them and I don't mind the $79 fee. If anyone has more info than this on mfg homes please let me know!

Many central air conditioning systems use the furnace blower to distribute cool air through the home. If you do not have a central heating system installed, it is cost-effective to install a heating and air conditioning system at the same time. If you already have central heat, you can use the existing fans and duct system for the central air system.
If no one in your household suffers from allergies or unexplained symptoms or illnesses and if, after a visual inspection of the inside of the ducts, you see no indication that your air ducts are contaminated with large deposits of dust or mold (no musty odor or visible mold growth), having your air ducts cleaned is probably unnecessary. It is normal for the return registers to get dusty as dust-laden air is pulled through the grate. This does not indicate that your air ducts are contaminated with heavy deposits of dust or debris; the registers can be easily vacuumed or removed and cleaned.
I purchased a Groupon for cleaning of unlimited air ducts and one return vent for $39. I should have checked into their hours first because they only offer services during normal business hours. So, with no evenings or weekends available you have to take time off work. I asked Groupon for a refund when I realized this and they refused because it wasn’t within the three day window. Then they didn’t even show up or call for the appointment. I called them after they were an hour late and they were going to call the local dispatch office and have them call me back within 15 minutes. I did not receive that call. I called again and was told I would get a call back from a manager. That didn’t happen either. So I asked Groupon for a refund again and they gave me Groupon bucks. When the survey came asking if I was satisfied with the Groupon customer service I said no, I want real money. I got my real refund the next day. Seems to me Groupon should stop dealing with these companies.
On the other hand, if family members are experiencing unusual or unexplained symptoms or illnesses that you think might be related to your home environment, you should discuss the situation with your doctor. EPA has published the following publications for guidance on identifying possible indoor air quality problems and ways to prevent or fix them.

As you can see, if we know what the contractor is actually paying for specific equipment, we know what their labor rates are, and we know what they bid the project for, then we can also use some basic algebra (or just let the program do it for us because we’re lazy) to figure out how much of a profit they are making off of us (you) at different bid prices:
Do you live in a historic home and want to tie your new system in to work with existing features? The price will go up to do the job right. All of these things add up to slow down the HVAC company, which takes more time, which costs more money for labor and parts. This is especially true if they are a legitimate company which is licensed, bonded and insured. Simply put, this is the “X-Factor” in your HVAC installation cost. Again, you could get people to do it for cheaper…but you won’t be happy with the results, I promise.
Multiple inventions within this time frame preceded the beginnings of first comfort air conditioning system, which was designed in 1902 by Alfred Wolff (Cooper, 2003) for the New York Stock Exchange, while Willis Carrier equipped the Sacketts-Wilhems Printing Company with the process AC unit the same year. Coyne College was the first school to offer HVAC training in 1899.[12]

I just had my blower module replaced because my AC coil was frozen over. The underside of my coils had a thick mat of dust because I had never had it cleaned. I cleaned it myself by using a soft brush attachement on a shop vac. The inside of the blower appears to have a white/green growth, and I am sure the ductwork of my 30 year old house can’t be in good condition.

Window air conditioners cost less than central units, averaging $300. These systems generally suffice to keep a room cool on warm spring and summer days. They can bring added comfort for a reasonable price but are less powerful than a central air conditioner. If you have a bigger home with multiple rooms, you will probably need to have a larger system installed. Central air can cool several rooms at once, while window AC units usually only cover one or two rooms at a time.
I own a small mechanical company. My main work is service and system replacements. I have never been a believer in duct cleaning. The company I worked for before had our duct man come out and do my house. I saw no difference. Preventive maintance is what I recomend. Remove fan and clean, seal fan compartment to prevent dust from being pulled in, filters I install media filters, they are 5″ thick and pleated. I have tested them to make sure static presure was not a issue. Heat exchangers and AC coils need to be cleaned. I will tell you this to do a good cleaning I usually spent 1-2 hrs, When I’m finished I would not have a problem eating my diner on the system. Good filters, clean system and properly tuned up are my recomdation to anyone. I’ve included my email feel free to contact me with any questions. winkcfd@yahoo.com
Many central air conditioning systems use the furnace blower to distribute cool air through the home. If you do not have a central heating system installed, it is cost-effective to install a heating and air conditioning system at the same time. If you already have central heat, you can use the existing fans and duct system for the central air system.
Hi John, Thanks for reaching out, we would be happy to help you connect with a pro for your project. You can submit a request to our pros here: www.homeadvisor.com, browse a list of pros that serve your area here: http://www.homeadvisor.com/c.html, or send your info to emailus@homeadvisor.com and a project advisor will reach out to assist you. –HASupport
Outdoor Fan Motor -- The outdoor fan, also called the condenser fan, is exposed to external conditions. As such it is most prone to dust and debris and the extreme weather. In desert climates, the outdoor fan motor is subject to heat not only from normal operation but from the outside temperature as well. As it starts to fail, the fan may work fine in the cooler morning hours but stop by afternoon. This can shut down the entire system for hours. When they stop running completely, your air conditioner will no longer work. Running a faulty fan will lead to compressor failure, which is a very costly repair.
If the system is sealed air-tight and a really good filtering system is in place then you should NEVER have to clean your ductwork. Most dust people see in their homes (on beds furniture etc....) is broken down insulation that is being blown into the home from the attic (venturi effect) where the duct bucket (box etc...) is not sealed at the sheetrock ceiling. On the return side, ANY leaks in the ductwork will pull hot attic air and dust into the system, clogging up everything.
We moved to a house built in 1965 from a 1915 house with a dirt basement. Against what I anticipated, the 1965 house was much dustier. It was like felt on top of everything. I cleaned and cleaned and it did become less dusty over time. We then found out a cat lady with over 2 dozen cats lived in the house in the past. We then had to get our furnace replaced and I was able to look down some of the duct work, the dirt and debris was 3-5 inches deep. Additionally, the basement ducts were entirely plugged with debris including dirt, seeds, ants, toys, etc. I had already removed what I could from those. We had our ducts cleaned last year, and the dust in the house is greatly reduced. Also have lost the runny nose I got after moving here. There are duct cleaning con artists out there, but ours did a good job.

Equipment used to clean ducts varies widely. The cheaper the equipment used the more you are just wasting money. This is why it's typically not worth doing. In some situations it may be beneficial, but only after determining and investigating the duct system. This should be done by a licensed HVAC contractor and not a duct cleaner that typically do not hold and HVAC license. (Duct cleaners aren't required to be licensed in HVAC in many areas.)


I agree, if you replace (or wash depending on type) your air filters regularly AND vaccum, then you probably don't need the ducts or air coils cleaned. However, if you purchase a pre-owned home, and the previous owners did not regularly change the air filter or vaccum the home, then duct cleaning is worth the expense especially if you are sensitive to allergens. Especially if the previous owners had pets.
As a person with severe mold allergies, I live in a the South where the climate naturally breeds molds.We noticed a difference when we had our ducts cleaned.The company used a vacumn type system and covered all of our vents with plastic that was held up by the suction. We had no damage, no leaking dust/dirt back into the house and it took several hours. I think if you use a reputable company it makes the world of difference. Now we use better air filters and also have a UV light to prevent mold growth on ours system.We 'd do it again when the time comes. From your car's air filter to your dryer...anything works more efficiently when it is not filthy dirty.That's just common sense.
WELL, this summer when I opened them up we had black dust spewing from one of the upstairs vents. It resembled the fuzz that comes off new towels. This prompted us to look into duct cleaning. We heard from someone who had it done several times, said it was worthwhile, and knew of a firm that did a good job. Clean Air America sent a single technician for the appointment and after counting registers and ducts gave me a price of $360.00 which included “sanitizing” the system (a $99 additional fee per can used). The small size of the plenum forced him to connect the 8” round vacuum hose from the truck to the 10” square opening from our humidifier unit. In hindsight, a mistake since it reduced the “negative” pressure in the system.

Air conditioning and refrigeration are provided through the removal of heat. Heat can be removed through radiation, convection, or conduction. Refrigeration conduction media such as water, air, ice, and chemicals are referred to as refrigerants. A refrigerant is employed either in a heat pump system in which a compressor is used to drive thermodynamic refrigeration cycle, or in a free cooling system which uses pumps to circulate a cool refrigerant (typically water or a glycol mix).
in response to this reply " should your ducts be cleaned", i have to politely correct the person who answered this. you are not using common sense. first, most of the country uses metal duct work, so for you to say what you did, is wrong. second, the duct system in a house is a circulatory system. that means it draws air into the furnace, it gets filtered, and then it is blown out into the house to heat or cool. So, obviously that air is being brought into the house from somewhere right? Yes, its coming from the outside where there are many allergens and dust particles . For you to says that about whether a duct system is sealed or not, makes no difference. The air is coming from somewhere right? It has to originate from somewhere right? Just look on top of your cieling fan. If there is a bunch of dust up there, then there is obviously a bunch in your ducts. And the duct air is being circulated every day, and every hour through your house. Its simple, dust collects everywhere in your house. Imagine if you never dusted your shelves, or tv? There would be a ton of dust after a while. Well, now think about the air in the duct system. Of course theres gonna be a ton of dust in there. For you to say that it is not benififcial to clean the ducts, is plain ignorant. 90% of the air we breathe is in our household. Wouldnt you want that air to be as dust and allergen free? I could go on for hours about the benifits of duct cleaning, but i just wanted to make a quick point that the person whose says it is not benificial to clean them, is not using common sense. Not to mention, giving the people who clean ducts for a living, a bad name. Use your head .

Your cleaning service should involve all aspects of your duct work to maximize energy efficiency and air quality. This includes attending to the heat exchanger, blower, drain pan, plenum and coils as well. In the process, your service provider may find that you're facing larger issues than debris and build-up. The professional may recommend having your furnace repaired if they notice, for example, damage to your heat exchanger or blower motor. Generally, a furnace repair costs between $130 and $500. They may also find that an A/C coil needs to be replaced rather than cleaned and would then recommend A/C repair.
It's always changing: Some newer thermostats take advantage of wireless technology. You can adjust your thermostat remotely so that if you leave and forget to adjust it, or if you are going to be home later than you thought, you can adjust it via your smartphone. Some can even give you reports on how efficient your system is performing based on usage. These are very efficient models, but they are also very expensive with some costing over $250.00.
The Antimicrobials Information Hotline provides answers to questions concerning current antimicrobial issues (disinfectants, fungicides, others) regulated by the pesticide law, rules and regulations. These cover interpretation laws, rules and regulations, and registration and re-registration of antimicrobial chemicals and products. The Hotline also provide information health & safety issues on registered antimicrobial products, product label and the proper and safe use of these antimicrobial products.
Metal is way better than flex duct or ductboard. It gets better airflow, holds up to critters and duct cleaners. I know of no hvac company here that cleans ductwork. (there probably is one somewhere) The mfg's of duct cleaning equipment keep trying to sell us hvac people on their benefits and profit potential but most all hvac people know that unless you have metal ductwork you are NOT doing the customer any favors.
I agree that good filtration and a sealed system will prevent the need for duct cleaning. However, when we do get called it is because the duct work has reached a noticeable state of restriction or dust or the homeowner is hyper-sensitive to these pollutants in their home. Most of the time we find that no filter or a cheap (99 cent) filter is being used or they have serious duct leaks in the system. If you are hiring a cleaner make sure they are using professional cleaning equipment which will consist of a rotating brush system and a vacuum source. Be highly skeptical of the contractor with no branded system or the guy who shows up with just chimney brushes and a shop vac. He will not be able to reach around all the corners or all the runs in your system and he will be taking your money for a superficial cleaning at best. Only trust a company that offers VIDEO inspection and more importantly.... a contractor who repairs, installs and seals ducts if a problem is discovered or heaven forbid, created. Good luck and get your ducts sealed if you do have a leak! It is one of the greatest energy losses to a home other than being poorly insulated.
Since the 1980s, manufacturers of HVAC equipment have been making an effort to make the systems they manufacture more efficient. This was originally driven by rising energy costs, and has more recently been driven by increased awareness of environmental issues. Additionally, improvements to the HVAC system efficiency can also help increase occupant health and productivity.[23] In the US, the EPA has imposed tighter restrictions over the years. There are several methods for making HVAC systems more efficient.
fact is most homes have bad filter racks. when you insert the filter it doesn’t seal well to the sides so some of the air and dust bypass it and end up in the supply ductwork and into the house. Most of the dust in the supply ductwork settles down and doesn’t get blown in the house but some of it does when the blower starts up or when you put a new filter. If you have allergies or other health problems put in an electronic air cleaner, get your ducts cleaned and run the fan as much as you can afford. you can also get an ECM motor installed which is going to be worth it if you want to run the fan 24/7. If you have uninsulated metal ducts take down the ones you can and wash them. Then put them back and seal the joints. Cleaning the ductwork also improves airflow which is important to AC and Heat pump systems for efficiency. An electronic air cleaner will also improve airflow and static pressure because they usually have a much larger filter surface area. An electronic air cleaner also keeps the ac coil clean like new which means better efficiency and no cleaning needed. AC furnaces sometimes grow mold around the coil because of the condensation. Electronic air cleaners should be able to filter mold spores but the best remedy is installing a UV light next to the coil which will kill the mold.

DIY: Most DIY installations go smoothly. The major brands have compatibility checkers to see which of their models will work with the wiring your old thermostat is using. Potential problems involve the need for a C-wire, or common wire, when the existing bundle doesn’t include one. There are solutions discussed in our Thermostat Buying Guide, linked to below.

My best advice has always been that a proper duct cleaning is a valuable investment when moving into a home (new or old), after major renovations and if the ducts have never been cleaned before. It is unlikely that there will be increased air flow, as finding major blockage is unusual, but this will eliminate this as a possible concern if there are air flow concerns. It is also true that the "dust" that is cleared out will most likely never have been distributed through the house unless there has been some work done on the ducts. What is cleared out will be pet hair, toys, clothes, construction material, and biological material (small carcasses and/or feces). Once a proper cleaning is done a follow-up is rarely necessary, but up to the home owners discression.

Hello, I read your comment and I know it was two years ago but I hope you see my message. I am trying to figure out what to do as I was told that there is some cat odor in the finished basement. I think with the air conditioning running that it may carry odor. The litter boxes are always kept clean. I wonder if odor can be trapped in the ducts, if Air Duct Cleaning could help, but it is quite expensive plus I'm concerned that it may not help. Please elaborate as to why you think it doesn't work that well. Do you have any other advise? Did you work in the field of Air Duct Cleaning? Thanks so much!
Quality and price should come hand in hand, a too-good-to-be-true price for an efficient air duct cleaning will not give you the quality that you wanted. To make sure you are getting your money’s worth, check reviews of air duct cleaning companies, certifications from industry since this work requires continuous learning due to new techniques and research breakthrough from time to time. Make sure to shop around and get written estimates first.
I’m really not convinced that duct cleaning is of any value. My roommate wanted the ducts cleaned so he called some company. My scam senses is already tingling. They came in with a big negative pressure fan. Did some blowing and sucking in different vents. Then they tried to upsell a full system cleaning. They wanted to pull the blower and clean the heat transfer box at $700 per heater unit. I have a big house so we have two units. They also tried to sell us some “custom” $250.00 Air Lifetime air filters. At that point I pulled the BS get the hell out bell. After paying $520.00 for just the cleaning, I paid the bill and sent them on their way. I replaced the existing filter with the good old and cheap paper filters at $10.00 each. Duct cleaning… I’m not Impressed.
The EPA is so far behind on useful knowledge because of the lack of funding so don't be mislead. The Hvac old timers were left at the dock so to speak and missed out on the IAQ movement. The ones that are savvy and up to date on the information do Air Duct Cleaning, even tho that will lead to a few less service calls its the right thing to do for their customer. Please take a look into a return duct that has never been cleaned, I dare anyone to say it does not need to be cleaned.
When water damage strikes, you need to act quickly. Time is of the essence. We're available 24/7 to dispatch trained, certified crews, equipment and inspection tools specializing in water damage. With our national footprint and large coverage areas throughout the country we will arrive on site and begin work quickly, minimizing the damage to your home. 
The bottom line is: no one knows. There are examples of ducts that have become badly contaminated with a variety of materials that may pose risks to your health. The duct system can serve as a means to distribute these contaminants throughout a home. In these cases, duct cleaning may make sense. However, a light amount of household dust in your air ducts is normal. Duct cleaning is not considered to be a necessary part of yearly maintenance of your heating and cooling system, which consists of regular cleaning of drain pans and heating and cooling coils, regular filter changes and yearly inspections of heating equipment. Research continues in an effort to evaluate the potential benefits of air duct cleaning.
×