Installing a split system may involve making modifications to the house itself for the necessary lines to be run. The heat exchangers are also more prone to picking up debris and must be cleaned on a regular basis. While they come with protective screens over the fan, care must still be taken to ensure that nothing gets in, especially in a home with children.
In the middle of summer—even more so in North America—AC repairs are undoubtedly the last thing you want to have to think about. But that won’t keep them from taking place. Fortunately, Service Experts Heating & Air Conditioning is dedicated to completing expert quality AC repair, maintenance and installation throughout the North America area. We certainly don’t want you to be stuck in an uncomfortable home during the hottest days of summer.
I own an HVAC company. Dirt in your ducts stays there and hurts no one. It is like dirt on the ground outside. This industry was infiltrated by a bunch of money grubbing low lifes years ago. As a credible company, we do not clean air ducts. Some who were credible probably signed on not knowing what else to do or to try to make a buck another way. These companies, because they also do HVAC work not only rip off private homeowners, they are ripping off legitimate HVAC company's customers and the integrity of what can and should as a rule be a great service industry. Some probably have gotten into this to simply offer what competitors who were ripping off their customers were offering. Anyone cleaning ducts is in my opinion raising a big red flag that they cannot and should not be trusted. Political pressure from NADCA, advertising dollars, manufacturers and marketers of duct cleaning equipment, and intense competition for the customers is the only reason the government and adverstising companies have not run them out of business and that this cancer perpetuates itself.
An air conditioner's compressor contains a refrigerant. As it works, it sends this refrigerant through the system. As warm air blows across the coil that carries this refrigerant, the heat transfers to the refrigerant (cool always absorbs warm). A fan moves the cooled air through the ducting and out of vents that lead into the rooms of your house. The refrigerant returns to the compressor where the absorbed heat is moved outside. The refrigerant is then sent through the coil once again to continue the cycle.
Without proper ventilation, carbon monoxide can be lethal at concentrations of 1000 ppm (0.1%). However, at several hundred ppm, carbon monoxide exposure induces headaches, fatigue, nausea, and vomiting. Carbon monoxide binds with hemoglobin in the blood, forming carboxyhemoglobin, reducing the blood's ability to transport oxygen. The primary health concerns associated with carbon monoxide exposure are its cardiovascular and neurobehavioral effects. Carbon monoxide can cause atherosclerosis (the hardening of arteries) and can also trigger heart attacks. Neurologically, carbon monoxide exposure reduces hand to eye coordination, vigilance, and continuous performance. It can also affect time discrimination.[15]
Air conditioning and refrigeration are provided through the removal of heat. Heat can be removed through radiation, convection, or conduction. Refrigeration conduction media such as water, air, ice, and chemicals are referred to as refrigerants. A refrigerant is employed either in a heat pump system in which a compressor is used to drive thermodynamic refrigeration cycle, or in a free cooling system which uses pumps to circulate a cool refrigerant (typically water or a glycol mix).
I thought the price advertised at 129.95 for duct cleaning was great and called to clean our ducts. When they came in to do the the job I could not be home and my wife dealt with them. My wife ended up paying 954.00. They convinced my wife that there was 1.5 inches of mold built up on the Evaporators and coils. It is not the money, my wife could not go to the basement to witness the mold build up or the coil fouling. We have not cleaned our ducts for at least 10 years. The last price we paid for our duct cleaning was 150.00. My concern is that they told my wife not to turn on the heat for 2 hours due the strong chemicals they used to kill the mold. Are these chemicals approved as safe?
Duct cleaning generally refers to the cleaning of various heating and cooling system components of forced air systems, including the supply and return air ducts and registers, grilles and diffusers, heat exchangers heating and cooling coils, condensate drain pans (drip pans), fan motor and fan housing, and the air handling unit housing (See diagram).
Furnace Circuit Board -- The furnace circuit board controls a variety of functions. It not only handles the regular operation of the furnace, it also monitors the furnace's various safety circuits. Over time, vibrations from the furnace can weaken solder point and cause them to separate. Dirt and debris can cause short-circuits that damage the board. Failure of the circuit board can cause a variety of effects ranging from the fan not turning on to the complete shutdown of the furnace.
I need a complete system replacement , before I was trying to get an evaporator coil replaced , of course the price is between $2200 an $2800 , then get told it probably will over tax my ac unit within months , so now and like everyone else what do you buy 14 ,15 16 17 seer units ,price and how do we know its reasonable  why can't there be '" a estimated price ,in the ball park, a range of prices ,so we can at least go from their .....  Now it's from 7500 to 15000. Frustrating  from the start so everybody good LUCK.   Draw a # from the hat    Unregulated  and who do you BELIEVE, just like on NCIS go with your gut feelin   
Two weeks go by and no phone call from HVAC Service regarding install date, or any update at all.  I call them to check in to see if they have put me on the schedule and when I can expect to have the AC installed.    You can tell by the discussion I had with the lady on the phone that they completely forgot about me and have not scheduled anything.  She says she needs to get in contact with the owner because she has no idea on the availability of the crane.  I was told that she would call me back by the end of the day with an update.  Surprise, surprise, no phone call.  
Asbestos removal tip.  Don’t trust any HVAC installation company that says that they will remove asbestos for you. They will do either one of two things: remove it and do a horrible job because they don’t know how (an illegal act in California, finable by up to $250,000), or they will say they did and never actually do it, which is dangerous to your health. Any HVAC contractor worth their weight will know not to touch it. Call an asbestos abatement company – it should cost around $500-$1,000, and your HVAC installation company will come in right after them and do the installation to decrease cost and inconvenience.

The short answer is yes, duct cleaning, done right by a reputable company will help with the smell. It is likely though the smell is coming from another source, ie the crawl space. It could also be that another rodent is dead in the duct work. A visual inspection would be in order to check for any breach in the duct system. A duct pressure test would be able to tell you how much air is leaking from the system over all. A hole large enough for an animal to enter would loses a great deal of air, over 300 CFM. It would be worth looking into having this test done and it should cost around $200. Cleaning the air handler and evaporator coil will greatly improve the performance of the air conditioner. Dirt and dust on the evaporator acts as insulation and reduces the amount of cooling done be the coil. Any quality duct cleaning should include cleaning the air handler and coil, and the tech should allow you to watch him perform the work as it is done.
EPA does not recommend that air ducts be cleaned except on an as-needed basis because of the continuing uncertainty about the benefits of duct cleaning under most circumstances. EPA does, however, recommend that if you have a fuel burning furnace, stove, or fireplace, they be inspected for proper functioning and serviced before each heating season to protect against carbon monoxide poisoning. Some research also suggests that cleaning dirty cooling coils, fans and heat exchangers can improve the efficiency of heating and cooling systems. However, little evidence exists to indicate that simply cleaning the duct system will increase your system's efficiency.
PickHVAC Tips: Electricity resistance heat is the most expensive heating type. You don’t want one of these unless you’re heating less than 30 days per year. The upfront cost of an electric furnace is much lower than the cost of a gas furnace. However, operating costs are two to three times higher. If winters are cold where you live, you’ll waste your upfront cost savings in just a few years of high electric bills.
Duct cleaning is a band aid, like washing you hands is. Under your description, why wash your hands more than once? If it gets cleaned once, it shouldn't get dirty again. Well that is, unless they touch something dirty. Keeping your hands completely clean is virtually impossible. Same as keeping dust out of your home. You clean your ducts and over a 3-5 year span they get dirty again. Also, duct cleaners are not licensed but should be certified by NADCA(National Air Duct Cleaning Association).
On average, we (Indians in Ontario) receive 3-5 calls per day for duct cleaning services from India. I did get ducts cleaned twice in 25 years. For a newly built house, it should be done as material goes into the ducts. Every year, before turning the heat on, I clean the ducts, using the vacuum pipe or with wet towel. Most of the dust, pet hair, small items get to the ducts from the top floors, not where system is installed. Even in winter months, I open 2-3 windows for air circulation for 15 minutes, specially right after cooking, almost daily. We breath in the same stale air, develop health issues. Also, I have an added air cleaning and fileration system installed. At a low rate, this system constantly cleans the inside air and also that it pulls from the outside. Duct cleaning is a scam, there are other efficient and cost effective methods we can use to purify the inside air.
Some systems include an "economizer mode", which is sometimes called a "free-cooling mode". When economizing, the control system will open (fully or partially) the outside air damper and close (fully or partially) the return air damper. This will cause fresh, outside air to be supplied to the system. When the outside air is cooler than the demanded cool air, this will allow the demand to be met without using the mechanical supply of cooling (typically chilled water or a direct expansion "DX" unit), thus saving energy. The control system can compare the temperature of the outside air vs. return air, or it can compare the enthalpy of the air, as is frequently done in climates where humidity is more of an issue. In both cases, the outside air must be less energetic than the return air for the system to enter the economizer mode.

Concealed behind your walls and mostly ignored, your air ducts serve as vital pathways that deliver warm and cool air throughout your home. While they may be unseen, your air ducts are working whenever you have your air conditioner or furnace running–nearly year round. Attached to your HVAC, air ducts transfer the air from these systems throughout your home. What many homeowners don't realize is that your air ducts, in nearly constant use, continually accumulate dust, grime, debris, pet dander, and allergens throughout the year. A professional air duct cleaning is necessary for better indoor air quality and the health of your family.

Window air conditioners cost less than central units, averaging $300. These systems generally suffice to keep a room cool on warm spring and summer days. They can bring added comfort for a reasonable price but are less powerful than a central air conditioner. If you have a bigger home with multiple rooms, you will probably need to have a larger system installed. Central air can cool several rooms at once, while window AC units usually only cover one or two rooms at a time.


If the one noticeable spot is where the wall [or ceiling or floor] is white.......first.....take a pair of needle nose pliers and bend each louver of the register to a straight outward position [as they all come brand new with a slant to each side]....so the register is shooting all supply air straight outward. If its a round register [in ceiling].....no help there. You also should always burn soy or beeswax candles.
Duct cleaning is a complete scam, I was a “duct cleaning technician” for a whole week before I was fired for not upselling elderly widowed women $2000 extra for “toxic mold remediation” when their ducts were spotless to begin with. The last two days I was employed there I worked as a “helper” alongside a technician thats been with the company 7 years. He scammed every customer on mold and would at times get as much as $2500 extra for treating “toxic mold” in a typical 3 bedroom house in the suburbs. Wait…it gets even better, the “Biocide” the company used was simply a cheap $4.99 per gallon bought at Home Depot air freshener with no anti-microbial properties that was fogged into the HVAC system for 5 minutes, maybe using 1/2 cup of the stuff. In order to provide the customer with evidence of “mold infestation” the technician would be given bogus mold tests that always resulted in “toxic spores present” regardless if you swabbed the actual duct or nothing at all. Not to mention the actual duct cleaning job (typically $400) did basically nothing and the homeowner could’ve done a better job with a shopvac
There is much more to air conditioning than AC installation in Fort Smith, AR then just maintenance and repairs. A variety of other services is required throughout the lifespan of your cooling unit. We are the professional team capable of completing them all. Replacements, troubleshooting, indoor air management, these are all part of our repertoire.
It's always changing: Some newer thermostats take advantage of wireless technology. You can adjust your thermostat remotely so that if you leave and forget to adjust it, or if you are going to be home later than you thought, you can adjust it via your smartphone. Some can even give you reports on how efficient your system is performing based on usage. These are very efficient models, but they are also very expensive with some costing over $250.00.
in response to this reply " should your ducts be cleaned", i have to politely correct the person who answered this. you are not using common sense. first, most of the country uses metal duct work, so for you to say what you did, is wrong. second, the duct system in a house is a circulatory system. that means it draws air into the furnace, it gets filtered, and then it is blown out into the house to heat or cool. So, obviously that air is being brought into the house from somewhere right? Yes, its coming from the outside where there are many allergens and dust particles . For you to says that about whether a duct system is sealed or not, makes no difference. The air is coming from somewhere right? It has to originate from somewhere right? Just look on top of your cieling fan. If there is a bunch of dust up there, then there is obviously a bunch in your ducts. And the duct air is being circulated every day, and every hour through your house. Its simple, dust collects everywhere in your house. Imagine if you never dusted your shelves, or tv? There would be a ton of dust after a while. Well, now think about the air in the duct system. Of course theres gonna be a ton of dust in there. For you to say that it is not benififcial to clean the ducts, is plain ignorant. 90% of the air we breathe is in our household. Wouldnt you want that air to be as dust and allergen free? I could go on for hours about the benifits of duct cleaning, but i just wanted to make a quick point that the person whose says it is not benificial to clean them, is not using common sense. Not to mention, giving the people who clean ducts for a living, a bad name. Use your head .
To qualify for a tax credit from the federal government, you must save the manufacturer's certificate from your system. The IRS won't require the certificate at the time you file your federal tax forms, but they recommend keeping it with your records in case of an audit. It proves that you purchased a qualifying product. The government offers tax credits for:
Preventing against air leakage is great, but the only way to keep dust and debris out of a duct system would be to completely seal off the return-air side of the system, which would render the system useless. Cold-air returns will always pull dust and other particles into the system. A high-MERV rated filter is definitely a good idea, but it does nothing to keep the return side of the system clean. Definitely agree though to use foil tape to seal seams, etc. Duct tape dries out over time and as it does can actually add more particles to the air.
I guess I should present my credentials first, I am a 30 year veteran of the heating and cooling industry. I started at the bottom and have participated in every area of the trade. Installer, service, maint. Ownership, rep, territory manager and so on. A forced air duct system is a large vacume. Like your vacume it has an air intake (return air) and an exhaust (supply registers). A filter just like a vacume (located next to furnace or air handler). Now I want you to visualize something. Put your head inside your vacume cleaner and breath. Get the picture? This is what your duct work looks like. Do you clean your vacume when it’s dirty? If it’s full and the filter is dirty you lose performance and it starts poluting the air you breathe. It’s common sense. I recommend hiring a duct cleaning outfit that you have researched to be honest, background checked, drug tested, insured, and highly recommended by your piers in the area. The service is a necessity, but like everything, it should be done by a qualified company.
After one company just took a cursory glance at our A/C and found nothing wrong, I called HVAC. I called them mostly based on Michael W's post on 8/10/14 where he told us the owner, Alberto, took his feedback and took it SERIOUSLY. That speaks VOLUMES to anyone who has been around long enough to know the characteristics of the serious players are and those who are the wannabes.
If you believe that the AC's not working or you're getting little or no cold air, check these three things first. Make sure all the registers in the house are wide open. Then be sure the furnace filter is clean. Then go outside and clean off the condenser coils (Photo 2). If several registers were closed or the filter was clogged, the reduced airflow could have caused the evaporator coil to ice up and stop cooling your home. If you've changed the filter and opened all the registers and you're still not getting airflow at the registers, deice the A-coil. Move the thermostat mode switch from “Cooling” to “Off” and move the fan switch from “Auto” to “On.” Let the blower run for at least 30 minutes or until there's good airflow at the registers. Then turn the AC back on to test it. If it works for the next 12 hours, you've solved the problem.
×