A do-it-yourself approach will only scratch the surface because it is hard to reach some of the ventilation running underneath the floor or into the wall. Although it may help in clearing some of the dust and debris, you really need a professional to guarantee your system is truly spotless. The proper procedure involves the use of a powerful vacuum system with multi-brush attachments designed to loosen debris and feed into the suction. Particles are then blown outside of the house or passed through a HEPA filter inside.
These factors are included in a "Manual J" calculation. Contractors who make these calculations before recommending a size can take a couple of hours collecting the information and making the calculation. If your contractor doesn't do it, there are services that will do it for around $99. If you're feeling particularly on the ball, there are also free online calculators.
PickHVAC Tips: First, see the PickHVAC tip above about sizing a central air conditioner. It applies to heat pumps just as much. Secondly, Even if the line set for the new heat pump is the correct size, we recommend replacing the set or at least the fittings. Old lines and fittings are a major source of leaks. When refrigerant leaks out, the heat pump efficiency suffers. Eventually, the unit stops providing heating and air conditioning, and it might break down.

Air conditioner size is measured in “tons.” However, the tonnage of an HVAC unit is not actually based on its weight. A “ton” is simply a measure of an air conditioner’s ability to cool your home. One ton is the ability of your air conditioning system to cool 12,000 BTUs (BTU stands for British Thermal Unit) in an hour. Likewise, a “2-ton” central air conditioner is able to cool 24,000 BTUs per hour.
A do-it-yourself approach will only scratch the surface because it is hard to reach some of the ventilation running underneath the floor or into the wall. Although it may help in clearing some of the dust and debris, you really need a professional to guarantee your system is truly spotless. The proper procedure involves the use of a powerful vacuum system with multi-brush attachments designed to loosen debris and feed into the suction. Particles are then blown outside of the house or passed through a HEPA filter inside.
Is duct cleaning worth it? There is not a yes or no answer that suits everyone. On an Air Force base, the system was not air tight and there was leakage around the filters. The system got dirty. A professional company was called out. The Duct was big enough that a technician could go inside the metal duct and clean it. There was a new Air Handler installed and things were sealed up better. in this case it was worth it.
Simply living in your home creates dust and dirt. Have you ever seen dust floating in the air in your home when the sun shines in?  Dust, dirt, pet dander, mold spores, and allergens get pulled into the air handling system in your home. They build up in the ductwork; some of it gets recirculated back into your home, and some of it can be captured by a good quality air filter. Eventually, enough debris builds up to the point where most of it blows back into your home. Your furnace or air conditioner must run longer to cool or heat your home, which costs you more in utility bills. With a service call from Sears Air Duct Cleaning, you can feel comfortable knowing that the accumulation of dust, dirt, dander, mold, and allergens has been cleaned from your HVAC duct system.
You may be familiar with air ducts that are constructed of sheet metal. However, many modern residential air duct systems are constructed of fiber glass duct board or sheet metal ducts that are lined on the inside with fiber glass duct liner. Since the early 1970's, a significant increase in the use of flexible duct, which generally is internally lined with plastic or some other type of material, has occurred.
I was with you until you said avoid steaming cleaning or moisture, there is no way you can remove mold or any other type of biological without moisture. The best way to do this is in fact with a steamer using a commercial disinfectant and a non reactive odor remover so your home smells refreshed and not like a hospital . This is directly contradictory to your article.
I believe a $3 [sic] pleated cotton filter is all that is ever needed to keep a system running top notch. A cleaning of the blower squirrel cage and of the evaporator [indoor] coil may be needed one time if fiberglass or no filters have been previously used. The return air grille [or grilles] need vacuumed off occasionally, as they are upstream from the filter. The $3 filter should be changed every 3 months [rule of thumb]....and most of them have a little white square on the cardboard frame to write install date.....and the arrow should point into the duct [if at filter grille]....or towards the furnace [if in ductwork slot]...or towards the blower [if in blower compartment]. My two cents.....
The cost to replace a central air conditioner is about $5,000. However, this price varies depending on the size of your home and the difficulty of the project. It can cost as much as $12,500 to replace an AC unit. The labor required to remove and dispose of the old system adds to the price. The size of your home, brand of AC unit and ductwork complexity can all raise the cost as well.

The answer to your question is most likely "Yes," but not defiitely. It depends on where the dust is coming from. Now, if your house is more than say, 12 years old then you likely do have leaks in your ducts that can let in insulation particles and dust from your attic. If this is the case then cleaning of the ducts-PROPER CLEANING, which like the article sas doess include EVERYTHING that the conditioned air passes through, such as your indoor evaporator coil and blower housing assembly-is definitely a good first step to getting that dust under control! Of course I highly recommend that you also have your ducts SEALED as well, or else you will have to repeat the cleaning some time down the line. As a 3rd step, consider an electronic air filter. I always thought they were a scam, personally, so I never bothered selling them to my clients. Then one day my manager sent me to install one for a senior couple in a mobile home. The wife had bad allergies, and her eyes were constantly watering and puffy and red. Well, I did a quality check 60 days later and she could not stop praising that air filter! Keep in mind that in a mobile home, duct seals are not as complete as those in other homes due to access issues.


The HVAC installation costs below are based on residential installations only, and are priced for a single unit. Two units should be about twice the price. “Tim, shouldn’t there be a discount?” If people start giving you discounts, they are probably charging you too much to begin with.  That’s our philosophy anyway. Twice the parts and time should be twice the price from a fair contractor. The prices listed include component parts (with warranty), labor, and all materials for a complete HVAC installation.
Some systems include an "economizer mode", which is sometimes called a "free-cooling mode". When economizing, the control system will open (fully or partially) the outside air damper and close (fully or partially) the return air damper. This will cause fresh, outside air to be supplied to the system. When the outside air is cooler than the demanded cool air, this will allow the demand to be met without using the mechanical supply of cooling (typically chilled water or a direct expansion "DX" unit), thus saving energy. The control system can compare the temperature of the outside air vs. return air, or it can compare the enthalpy of the air, as is frequently done in climates where humidity is more of an issue. In both cases, the outside air must be less energetic than the return air for the system to enter the economizer mode.
The cost to replace a central air conditioner is about $5,000. However, this price varies depending on the size of your home and the difficulty of the project. It can cost as much as $12,500 to replace an AC unit. The labor required to remove and dispose of the old system adds to the price. The size of your home, brand of AC unit and ductwork complexity can all raise the cost as well.
If you’re anything like most of our readers, you’ve spent hours online researching HVAC information in preparation for replacing your old heater or air conditioner. I’m the same way; it’s a big investment! You may want to consider saving yourself some time and money by getting an HVAC-Facts Report from this online HVAC installation cost calculator.  Take a look:
If you are using existing ducting, it will have to be inspected. Proper ducting loses around 2% to 5% of your energy. Old, leaking ducts can lose 50% or more. A contractor will need to have the ducts inspected and replace any parts ahead of time. If you are changing the size of your HVAC system because of significant changes to your home, you might need to replace the ductwork regardless.
I guess, I will start with saying that air duct cleaning is almost never needed. It is not a scam, but it is certainly something that uneducated homeowners get suckered into. In regards to air flow, a well balanced HVAC system should be able to deliver more than enough air flow. If you are not getting good air flow, it's because your system may be out of balance. Additionally, regular cleaning/changing of the air filters will solve about 95% of your problem. Though you would be surprised how many people either a. don't have a filter or b. don't know about it and leave it there for 10+years. a washable one should be cleaned every 6 months(spring and fall) and a disposable one should be replaced every 3-4 months.
If your non metal ductwork is that dirty you should just have it replaced AND sealed. Also most duct systems are not very well designed. Look for proper sizing and do not go cheap with one or two intakes (return grills) You need them through-out the house. Here in Austin the duct cleaners are carpet cleaners and chimney swifts. (this is who the duct cleaning equipment mfgs call on when the hvac people do not get on board. They DO clean other types of ductwork and we (the hvac guys) have to fix them. I am not aware of any of these non hvac guys cleaning and servicing the actual equipment. Here in Texas it is against the law for them to do so. Treat the entire house as a system, not just the ductwork and /or hvac equipment. Home performance really does work to increase comfort and air quality while reducing operating costs.
Here in Atlanta we get 6 to 10 $49 coupons in the mail weekly…I have always consider them a complete scam….just had my master bathroom& bedroom and guest bath completely remodeled down to the studs…Had my 3 returns nearest the area sealed to prevent sheet rock dust to spread…it worked and I personally cleaned all 7 returns when a 5 HP , new Rigid shop Vac($99 from HD)…took one hour and I found little evidence that “I need my ducts cleaned” Had quotes from $400 to $600…I use the best air filters for my air handler and change it every 2 to 3 months…..any dust is trapped in it and I believe the Air Duct folks are all cons….
BIG THANK YOU for being honest, and advising us that for some reason the fuse/switch was in the reverse position so the AC unit would not properly turn on.   The unit turned back on immediately, and began cooling the house.   And then providing advice that the AC/Heating system needed some TLC, and giving us options to save money by purchasing a maintenance plan that included the filters plus cleaning services since we were already being charged for the service today.

An alternative to packaged systems is the use of separate indoor and outdoor coils in split systems. Split systems are preferred and widely used worldwide except in North America. In North America, split systems are most often seen in residential applications, but they are gaining popularity in small commercial buildings. The split systems are a great choice for small buildings where ductwork is not feasible or where the space conditioning efficiency is of prime concern [20]. The benefits of ductless air conditioning systems include easy installation, no ductwork, greater zonal control, flexibility of control and quiet operation [21]. In space conditioning, the duct losses can account for 30% of energy consumption [22]. The use of minisplit can result in energy savings in space conditioning as there are no losses associated with ducting.


Monday the following week, no phone calls, or follow up.  I call to get an update and am told that they cannot install my system because they don't have time.  I ask what does that mean, one year? One week? Until the end of summer they say.  What does that mean I ask?  They say at the end of September.  I say thank you for wasting 1 month of my time.


Stick with a maximum of 16 SEER units in most cases.  Like I said above, contractors push higher SEER units because they make more money, but these units can be expensive at this stage of development, and can drive up your HVAC installation cost.  21 SEER units run about twice the price of a 14 SEER unit, so unless you live in a desert and plan on being there for 30 more years... Likewise, a 16 SEER unit typically costs only about $600-$1,000 more than a 14 SEER, and will usually pay for itself over the lifetime of the unit.


It’s 11 years plus in the industry I have only had to sanitize two systems both were slab systems that were in concrete and could be cleaned with a different method than normal duct cleaning. We were able to use water to rinse out the disinfectant. Would you use a chemical on anything else you use to eat or drink with and not rinse it off? The ducts in your home should be thought of as your homes heart and lungs and breathe the same air that you do. And just like us we wouldn’t use bad chemicals in our lungs and heart.


Your contractor will do a load calculation to determine the proper central air conditioning unit for your home. This calculation accounts for the climate, size, shape and orientation of your home, as well as its square footage. A professional will also look at the insulation, windows, walls, floors and other materials that compose your home. He/she will then examine any leaks, seals and existing ducts or vents.
We are a hvac company that provide air duct cleaning service are minimum charge $400 to do a proper air duct cleaning with 2 techs avg 3-6 hours that includes sanitizing. I get phone calls all day about the $99 your not going to get much of a cleaning for that price it for them to get there foot in the door and up sell that the only way for them to stay in business. Just from my 15 years of duct cleaning experience.

This company deserves more than five stars. They didn't just replace my heater and air conditioner, they built me a new system for my house. Going above and beyond is a understatement. Steve's staff were 2 of the nicest workers I've come across in a long time. Friendly, knowledgeable, and very clean. Truly a top rated company. Thanks Steve.   Great job.
Interesting. Giuliano Cuete and Carlo Olcese have the exact same post about pretenders and being NADCA certified, word for word. So how do you become NADCA certified? And does that mean you are not a scam artist or a "blow and do" ripoff? hmmm, interesting. The EPA says that under normal conditions, a properly maintained system should NEVER need it's ducts cleaned.
An air conditioner's compressor contains a refrigerant. As it works, it sends this refrigerant through the system. As warm air blows across the coil that carries this refrigerant, the heat transfers to the refrigerant (cool always absorbs warm). A fan moves the cooled air through the ducting and out of vents that lead into the rooms of your house. The refrigerant returns to the compressor where the absorbed heat is moved outside. The refrigerant is then sent through the coil once again to continue the cycle.
If you are replacing your air conditioning system, make sure that the unit is the proper size for your needs and that all ducts are sealed at the joints. A unit that is too big will cycle on and off frequently, resulting in poor moisture removal, particularly in areas with high humidity. Also make sure that your new system is designed to manage condensation effectively.
An air conditioning system, or a standalone air conditioner, provides cooling and humidity control for all or part of a building. Air conditioned buildings often have sealed windows, because open windows would work against the system intended to maintain constant indoor air conditions. Outside, fresh air is generally drawn into the system by a vent into the indoor heat exchanger section, creating positive air pressure. The percentage of return air made up of fresh air can usually be manipulated by adjusting the opening of this vent. Typical fresh air intake is about 10%.
As a person with severe mold allergies, I live in a the South where the climate naturally breeds molds.We noticed a difference when we had our ducts cleaned.The company used a vacumn type system and covered all of our vents with plastic that was held up by the suction. We had no damage, no leaking dust/dirt back into the house and it took several hours. I think if you use a reputable company it makes the world of difference. Now we use better air filters and also have a UV light to prevent mold growth on ours system.We 'd do it again when the time comes. From your car's air filter to your dryer...anything works more efficiently when it is not filthy dirty.That's just common sense.
My 48 yr old house (mine for the last 4 yrs) has considerable dust in the return plenum (fiber duct). I’m remodeling and recently re-sealed the return plenum AND the site-fabbed transition built when the new unit was installed, 2013. The return was leaky no doubt drawing musty, dusty air from the crawl space due to the Red-Neck fab & seal job! Pitiful craftsmanship! It took me 7 hours to fix the new transition piece. Anyway, the dust in the house is the same “color” as whats in the return duct and I’m getting way too much & too often in the house. I’ve also cleaned my coils, which were not that dirty.
As I type this, I am having my ducts cleaned. About 30 including returns and the furnace. $543.00. I am watching the team do it and can see the clear vacuuming tubing and how dirty it has become. I like the gentleman’s comment on “stick your head in your vacuum and breath”….I get it. The team showed me the machine and it’s filtration system…and they will show me it again after the cleaning. However, like I said before, I am actively seeing the tubing that is clear before they start and how dirty it is once they begin and continue cleaning. Reputable company and not a “fly by night” coupon service. People don’t be so cheap, that is your problem.
A BTU is the amount of energy required to heat or cool one pound of water by one degree Fahrenheit. So a 1-ton air conditioner can cool 12,000 pounds of water by one degree every hour. That’s all it means, so don’t let yourself be lost in jargon! How this affects your HVAC installation cost is that the larger your house is, the more tons will be required to heat and cool it.

Air conditioning units are prone to the pitfalls of wear and tear. You can prolong this, however, with proper maintenance procedures. Without regular maintenance even an immaculate AC installation in Fort Smith, Arkansas cannot guarantee performance. Our maintenance service is thorough, leaving no area unattended. If there’s a problem, we’ll catch it early and prevent avoidable breakdowns and costly repairs.

Do not hire duct cleaners who make sweeping claims about the health benefits of duct cleaning — such claims are unsubstantiated. Do not hire duct cleaners who recommend duct cleaning as a routine part of your heating and cooling system maintenance. You should also be wary of duct cleaners who claim to be certified by EPA. Note: EPA neither establishes duct cleaning standards nor certifies, endorses, or approves duct cleaning companies.
×