You can install the greatest HVAC system ever built, but if your house is not insulated well, it's only going to end up costing you more money. Older homes may have fiberglass insulation that has broken down due to pests, moisture, or improper installation. Spray foam insulation can be damaged by careless repair or modification work or can be improperly installed. If your insulation in compromised, your attempts to save money and be comfortable will be in vain.
I call to follow up at the end of the next day and she said that she has not been able to get in touch with the owner.  By this time, I am starting to get frustrated because I am starting to get the run around.  I question her if I am even on the schedule or if they attempted to schedule a crane.  She says they are extremely busy and that she does not know.  So I say, basically I have waited over 2 weeks and you have not put me on the schedule and I am at the end of the install line.  No answer.  I tell her to talk to her boss and find out what is happening, and I will think about what direction I want to move in at this point.  
My best advice has always been that a proper duct cleaning is a valuable investment when moving into a home (new or old), after major renovations and if the ducts have never been cleaned before. It is unlikely that there will be increased air flow, as finding major blockage is unusual, but this will eliminate this as a possible concern if there are air flow concerns. It is also true that the "dust" that is cleared out will most likely never have been distributed through the house unless there has been some work done on the ducts. What is cleared out will be pet hair, toys, clothes, construction material, and biological material (small carcasses and/or feces). Once a proper cleaning is done a follow-up is rarely necessary, but up to the home owners discression.

I'd have to disagree with all of your statements. Not only are they derived from no experience in the field, you are missing keys facts. Ducts even if air tight will get dirty. If they are not getting dirty, it means they are not working. Your returns side of the duct work is always under negative pressure when the system is operational.Therefore it is always drawing air in. Seeing how dust is made up mostly from dead skin humans shed daily. Around 1.6 Pounds of skin a year per human. Living in your home anything that is air born will be drawn back towards the cold air returns. That is what they are designed for, to draw stale air back to the system to be filtered and sent back through the house.Homes with carpet will actually have cleaner duct work than home with all tile or hardwood. This is because carpets hold onto dust particles and you vacuum them up. Whereas on hardwood or tile, dust can run freely back to the returns. Even if a duct system was sealed 100%, which is next to impossible to achieve 100% would still need to be cleaned. The cleaning may only have to be every 7-10 years for example. Most homes require every 5-7 years. And that's if it was done properly the first time. If you constantly hire people that have no or minimal knowledge of duct cleaning, You home would require cleaning more often. Every 2 years. That's a trade secret, The longer they recommend before the next cleaning, the odds are they did it right. That's not to say there aren't people that lie, because there are. Just have your duct cleaner take pictures before and after cleaning. Not just an outside view. Get in there, picture entire joist liners, Whole main runs and even long round pipes. Also it helps to have a company that guarantees their work. If it's not done right, they will come back and do it until it is. Most companies that do this make sure it is right the first time. Your not getting paid to do the job twice.

Furnace Circuit Board -- The furnace circuit board controls a variety of functions. It not only handles the regular operation of the furnace, it also monitors the furnace's various safety circuits. Over time, vibrations from the furnace can weaken solder point and cause them to separate. Dirt and debris can cause short-circuits that damage the board. Failure of the circuit board can cause a variety of effects ranging from the fan not turning on to the complete shutdown of the furnace.
I even asked if this is something they don't do, as in services on a Saturday night.  I was told by the receptionist that they do and I would just be ok calling another company if they is not  part of their services. They again assured me someone WILL call me in 10 mins.  Well, unless their definition of 10 mins is never, then they got it wrong as I am still waiting to be called 5 days later.
Well, I had the cleaning done. The handler is definitely much quieter. It was explained to me that with the coils clean, the condensation will be able to sweat off instead of sticking to the dust and dirt, therefore the humidity (lots of humidity in florida) will be removed better. I feel as if it was worth it, but, I will definitely change that filter every 3 weeks or so from now on. I don’t want to pay that cost again.
My point is that the brand of equipment you choose is going to affect your HVAC installation cost greatly. People often call us for an air conditioning installation job and say, “I would like to install Carrier equipment.” Now, if you are a future client of ours, I’ll have to warn you – I can be a bit of a smart-ass. Why can’t work be fun? Besides…I was in the Navy for 11 years, what do you expect. 
While a lot of people understand the consequences of AC problems throughout the summer, the summer comes with its own set of unique issues that require a call to the plumber, too. Whether it’s a malfunctioning sprinkler system or a sewer line backup, Service Experts can help. We’ve encountered it all, and you won’t have to worry about any of it with our 24/7/365 Emergency Plumbing Service. When you need a plumber, we are here for you. And, just like all of our other services and products, any plumbing repair or work completed by Service Experts is backed by the same 100% Satisfaction Guarantee*.

Typically speaking, the lower SEER, more basic models are also more reliable.  Reliability is big with us, so we steer clear of features with reliability issues, and it’s as simple as that. When you factor in the price of repairs and the extra expense of the 21-SEER, you may actually lose money! 16 SEER is the sweet-spot, and it is key to reducing your HVAC installation cost.
My 48 yr old house (mine for the last 4 yrs) has considerable dust in the return plenum (fiber duct). I’m remodeling and recently re-sealed the return plenum AND the site-fabbed transition built when the new unit was installed, 2013. The return was leaky no doubt drawing musty, dusty air from the crawl space due to the Red-Neck fab & seal job! Pitiful craftsmanship! It took me 7 hours to fix the new transition piece. Anyway, the dust in the house is the same “color” as whats in the return duct and I’m getting way too much & too often in the house. I’ve also cleaned my coils, which were not that dirty.
Wiring up the thermostat is usually pretty straightforward if an old one is being replaced. If a thermostat is being put in where one had never been before, that could involve running new wiring. The placement of the thermostat is also important so that its sensors can get an accurate reading of the temperature. A thermostat that is blocked by a bookcase or other large furniture will not get a good reading and will not perform efficiently.
To find companies that provide duct cleaning services, check your Yellow Pages under "duct cleaning" or contact the National Air Duct Cleaners Association (NADCA) at the address and phone number in the information section located at the end of this guidance. Do not assume that all duct cleaning service providers are equally knowledgeable and responsible. Talk to at least three different service providers and get written estimates before deciding whether to have your ducts cleaned. When the service providers come to your home, ask them to show you the contamination that would justify having your ducts cleaned.
So, naturally I respond with, “you don’t tell your doctor which medication to prescribe you, do you?” The point is, on the residential level, who you get to install your HVAC unit is far more important than which unit you choose.  Keep your options open and let your HVAC contractor make a few recommendations – that’s why you spent time finding a reputable contractor!
Heaters are appliances whose purpose is to generate heat (i.e. warmth) for the building. This can be done via central heating. Such a system contains a boiler, furnace, or heat pump to heat water, steam, or air in a central location such as a furnace room in a home, or a mechanical room in a large building. The heat can be transferred by convection, conduction, or radiation.

Metal is way better than flex duct or ductboard. It gets better airflow, holds up to critters and duct cleaners. I know of no hvac company here that cleans ductwork. (there probably is one somewhere) The mfg's of duct cleaning equipment keep trying to sell us hvac people on their benefits and profit potential but most all hvac people know that unless you have metal ductwork you are NOT doing the customer any favors.


Internal insulation provides better acoustical (noise) control. Flexible duct is very low cost. These products are engineered specifically for use in ducts or as ducts themselves, and are tested in accordance with standards established by Underwriters Laboratories (UL), the American Society for Testing and Materials (ASTM), and the National Fire Protection Association (NFPA). Many insulated duct systems have operated for years without supporting significant mold growth. Keeping them reasonably clean and dry is generally adequate. However, there is substantial debate about whether porous insulation materials (e.g., fiber glass) are more prone to microbial contamination than bare sheet metal ducts. If enough dirt and moisture are permitted to enter the duct system, there may be no significant difference in the rate or extent of microbial growth in internally lined or bare sheet metal ducts. However, treatment of mold contamination on bare sheet metal is much easier. Cleaning and treatment with an EPA-registered biocide are possible. Once fiberglass duct liner is contaminated with mold, cleaning is not sufficient to prevent re-growth and there are no EPA-registered biocides for the treatment of porous duct materials. EPA, NADCA and NAIMA all recommend the replacement of wet or moldy fiber glass duct material.
You've probably noticed many appliances boasting an Energy Star Certification. What this means is that manufacturer voluntarily built the product to help reduce greenhouse gases and meet non-regulatory guidelines offered by the Environmental Protection Agency. To earn an Energy Star rating, a product or system must be tested by a third party that has been recognized by the EPA for meeting their testing qualifications.
Air duct cleaning service providers may tell you that they need to apply chemical biocide to the inside of your ducts as a means to kill bacteria (germs) and fungi (mold) and prevent future biological growth. They may also propose the application of a "sealant" to prevent dust and dirt particles from being released into the air or to seal air leaks. You should fully understand the pros and cons of permitting application of chemical biocides or sealants. While the targeted use of chemical biocides and sealants may be appropriate under specific circumstances, research has not demonstrated their effectiveness in duct cleaning or their potential adverse health effects. No chemical biocides are currently registered by EPA for use in internally-insulated air duct systems (see Should chemical biocides be applied to the inside of air ducts?).
There are multiple reasons to replace your HVAC system. If you have built additions onto your house, you may find your old system no longer meets the requirements for the new dimensions. Perhaps a new technological breakthrough has provided features that will improve your comfort and air quality. Most often, however, you need to replace your system because it no longer works properly.
In addition, the service provider may propose applying chemical biocides, designed to kill microbiological contaminants, to the inside of the duct work and to other system components. Some service providers may also suggest applying chemical treatments (sealants or other encapsulants) to encapsulate or cover the inside surfaces of the air ducts and equipment housings because they believe it will control mold growth or prevent the release of dirt particles or fibers from ducts. These practices have yet to be fully researched and you should be fully informed before deciding to permit the use of biocides or chemical treatments in your air ducts. They should only be applied, if at all, after the system has been properly cleaned of all visible dust or debris.
The most effective way to clean air ducts and ventilation systems is to employ Source Removal methods of cleaning. This requires a contractor to place the system under negative pressure, through the use of a specialized, powerful vacuum. While the vacuum draws air through the system, devices are inserted into the ducts to dislodge any debris that might be stuck to interior surfaces. The debris can then travel down the ducts to the vacuum, which removes it from the system and the home.
I can’t believe I got ripped off by this Air Duct Cleaners. I called them for this $63 coupon per furnace unlimited vents then when they came after he checked it all I hear is I have molds and leak all is worth $499, $799, $899 per furnace but I told him to just clean the duct and patch the single leak per furnace worth $38 each. Still eanding $899 total. All the work he done is in less than an hour he didnt even go to each vent to clean it. All he did is to path the air leak on that entry pipe to the furnace and open the main venting system, vacuum it, and wash the floor of the vent with a solution. Overall time is about 20 mins talking with me discussing all the option which thinking they made me think I don’t really have an option and 40 mins wash and vacuum he took pictures of before and after of only one furnace. He gave me a receipt without the details on what he has done in the house just the name and price. I think we may need a strict law to punish and control all this companies who do this so other company who do good will despise them.

Demand controlled kitchen ventilation (DCKV) is a building controls approach of controlling the volume of kitchen exhaust and supply air in response to the actual cooking loads in a commercial kitchen. Traditional commercial kitchen ventilation systems operate at 100% fan speed independent of the volume of cooking activity and DCKV technology changes that to provide significant fan energy and conditioned air savings. By deploying smart sensing technology, both the exhaust and supply fans can be controlled to capitalize on the affinity laws for motor energy savings, reduce makeup air heating and cooling energy, increasing safety and reducing ambient kitchen noise levels.[29]


The liquid refrigerant is returned to another heat exchanger where it is allowed to evaporate, hence the heat exchanger is often called an evaporating coil or evaporator. As the liquid refrigerant evaporates it absorbs energy (heat) from the inside air, returns to the compressor, and repeats the cycle. In the process, heat is absorbed from indoors and transferred outdoors, resulting in cooling of the building.
Demand controlled kitchen ventilation (DCKV) is a building controls approach of controlling the volume of kitchen exhaust and supply air in response to the actual cooking loads in a commercial kitchen. Traditional commercial kitchen ventilation systems operate at 100% fan speed independent of the volume of cooking activity and DCKV technology changes that to provide significant fan energy and conditioned air savings. By deploying smart sensing technology, both the exhaust and supply fans can be controlled to capitalize on the affinity laws for motor energy savings, reduce makeup air heating and cooling energy, increasing safety and reducing ambient kitchen noise levels.[29]
I forgot about a pot of sweet water I had on the stove to boil. When I finally smelled it the kitchen and dining room I=was smoke filled. I mean thick smoke. I opened doors and windows for a few hours to remove the smoke but the smell is still here and terrible. I had to use the AC and that smell started coming out of the vents. Now what do I do? I have COPD emphysema so I have to be very careful about what I inhale. I already have inhaled too much smoke from all of this which has hurt my lungs even more. I can’t afford for them to get worse over this. How can I get the right person to come out and clean the ducts and furnace or is that the only way to remove that burnt smokey smell. The pot never caught on fire but it sure did produce a lot of smoke. I already have replaced the filter on the furnace. It needed it even though it had just been replaced just last week. I need help or really my lungs need help. Who do I call here in Indpls IN.
Stick with a maximum of 16 SEER units in most cases.  Like I said above, contractors push higher SEER units because they make more money, but these units can be expensive at this stage of development, and can drive up your HVAC installation cost.  21 SEER units run about twice the price of a 14 SEER unit, so unless you live in a desert and plan on being there for 30 more years... Likewise, a 16 SEER unit typically costs only about $600-$1,000 more than a 14 SEER, and will usually pay for itself over the lifetime of the unit.
As a homeowner and an owner of rental property I can tell you that the air ducts sometimes need to be cleaned. If you have had pets or anyone smoking in your home (even a visitor) for any length of time, having the ducts cleaned is really good idea. I had a tenant who did not smoke, but got married to a smoker more than year after moving in. When I realized someone was smoking I had them move out, but the smell was awful. I had the ducts cleaned and sanitized (it was a bit extra). The ducts were shiny like new afterwards. I left the windows open for a few days and we cleaned the place super clean and then replaced the carpets. The duct cleaning was worth every penny because the house looked, smelled, and felt new afterward. I plan to have my own house ducts cleaned again this year as we have two cats. We had them cleaned about 12 years ago and they found building materials in the ducts! If you move into a house that has never had them cleaned, it is good to do it. If you have allergies, clean the ducts to see if it helps. You never know what is in your ducts if you have never had them cleaned.
You may consider having your air ducts cleaned simply because it seems logical that air ducts will get dirty over time and should be occasionally cleaned. Provided that the cleaning is done properly, no evidence suggests that such cleaning would be detrimental. EPA does not recommend that the air ducts be cleaned routinely, but only as needed. EPA does, however, recommend that if you have a fuel burning furnace, stove or fireplace, they be inspected for proper functioning and serviced before each heating season to protect against carbon monoxide poisoning.
×